  Reply # 746614 18-Jan-2013 05:19 Send private message

Bung:
gregmcc: If the boot is in place then it meets the segeration requirments


Not as far as Telecom was concerned or the Telecommunications Carriers' Forum Code of Practice

"35.3.  Under NO circumstances shall Low Voltage (LV e.g., 230 V) sockets, switches or
modules be mounted on the same faceplate as TNV or ELV components (voltage
levels at which telecommunications and data services operate). The joint
Australia/New Zealand Wiring Rules (AS/NZS 3000) require that all faceplates
comply with AS/NZS 3112, clause 3.2 of which prohibits mixing of these voltage
levels on the same faceplate.  "


This is a code of practice issued by a private company, there is no legal requirnment for it to be followed, what matters are the electrical regulations and the AS/NZS 3000, BTW AS/NZS 3112 only says that a facplate that has a socket shall not incorprate an ELV outlet such as telecoms. but it would make a plate that has a light switch ok to have it with

1454 posts

Uber Geek
+1 received by user: 81


  Reply # 746627 18-Jan-2013 07:24

AS/NZS 3000 Amd 1 refers to the earlier Telecom version of the TCF Code. I'd expect that to change to the TCF code eventually.

"3.9.8.4   Proximity to non-electrical services

(c)  Telecommunication services   Requirements for the separation of
telecommunications cables from low voltage and high voltage systems
are provided—
(i) for Australia, in AS/ACIF S009  Installation requirements for
customer cabling (Wiring Rules); and
(ii) for New Zealand, in PTC 103 and PTC 106. "

PTC 106

"5.1.3 Connection of 230 V and ELV/TNV on same TO faceplate
(1)   Under NO circumstances shall Low Voltage (LV e.g., 230 V) sockets,
switches or modules be mounted on the same faceplate as TNV or ELV
components (voltage levels at which telecommunications and data services
operate).
 
The joint Australia/New Zealand Wiring Rules (AS/NZS 3000) require that all faceplates
comply with AS/NZS 3112, clause 3.2 of which prohibits mixing of these voltage levels on the
same faceplate. "


I don't have 3112 to check whether Clause 3.2 refers to all faceplates or just to socket outlets as you say.

Apart from safety issues if the faceplate has LV services on it only Registered persons (or the home owner if he lives in the house) can legally remove it. That would stop nearly all Telco staff.

5971 posts

Uber Geek
+1 received by user: 109

Trusted
Subscriber

  Reply # 746628 18-Jan-2013 07:31 Send private message

Yep, PTC106 are referenced in AS/NZ3000-2007, this does (and I have had that clarified by the appropriate oracle) that this makes the refernced section of PTC106 law!.

Cyril

5971 posts

Uber Geek
+1 received by user: 109

Trusted
Subscriber

  Reply # 746629 18-Jan-2013 07:41 Send private message

antoniosk:
cyril7: Hi, AS/NZ3000-2007 was issued in .....................2007, but the separation requirement has been there from way before that, we are talking 15yrs or more.

I work in an industry where we are managing data and electrical installers who flaunt this law daily, and the ELWB (electrical wiring board) are now taking note and persecuting these electricians who are placing the public safety at risk.

Cyril


Persecuting? Crikey, that's one way of getting people to follow the rules, rather than simple one off fines!


The EWRB used to have public floggings each month, these were held on the last page of Electron, these seem to now stay behind locked doors since Electron has taken a PDF only life.

Cyril

4788 posts

Uber Geek
+1 received by user: 126

Trusted

  Reply # 746641 18-Jan-2013 08:28 One person supports this post Send private message

timbosan:
I generally remove a square or rectangle around the nogs, and again near studs (for face plates) then simply patch it up, fill the gaps, and repaint.


In a rush, I've seen this done with a chainsaw.  Just notch the dwang, forming a small slot by running down with the tip of the chainsaw blade, sit the coax into this and repatch with filler.  Rough, yep.

865 posts

Ultimate Geek
+1 received by user: 73

Subscriber

  Reply # 747061 18-Jan-2013 18:22 Send private message

cyril7: Yep, PTC106 are referenced in AS/NZ3000-2007, this does (and I have had that clarified by the appropriate oracle) that this makes the refernced section of PTC106 law!.

Cyril


Sorry the standards are not law, the regulations are law, the standards are the reccomended way to comply with the law.

3.9.9.2 basially says cables of different voltage levels must either both be double insulated, or insulated for the highest voltage present or by segeration

typically cat5 coax are not rated for 230v/400v, but the use of a segeration boot at the face plate does provide the insulation rating required, speration is required where the cables leave the enclosure.

quoting the PTC is a waste of time as it is only a recommedation and only applys  to POTS, not to ethernet/tv aerials/any other extra low voltage circuit.



5971 posts

Uber Geek
+1 received by user: 109

Trusted
Subscriber

  Reply # 747107 18-Jan-2013 20:15 Send private message

Ummm sorry but the regulations now make AS/NZ3000 now law, this has been for some time, essentially the legislated regulation has extended to the standard, well as I was last advised by the oracles.

Cyril

865 posts

Ultimate Geek
+1 received by user: 73

Subscriber

  Reply # 747124 18-Jan-2013 20:31 Send private message

cyril7: Ummm sorry but the regulations now make AS/NZ3000 now law, this has been for some time, essentially the legislated regulation has extended to the standard, well as I was last advised by the oracles.

Cyril


As a person who is involved in the industry and have repeatly have been told every 2 years, "The regulations are the law, the standards are the advised method to obtain compliance"

Standards are an approved method.

Saying that....prove me wrong....quote the relevent legislation that says that the standards are the law

246 posts

Master Geek
+1 received by user: 20

Trusted

  Reply # 747134 18-Jan-2013 21:02 Send private message

cyril7: Ummm sorry but the regulations now make AS/NZ3000 now law, this has been for some time, essentially the legislated regulation has extended to the standard, well as I was last advised by the oracles.

Cyril

Specifically, NZ Electrical Safety Regulations 2010, Section 5, regulation 57.

Edit: Hit the enter button too early....




Michael Skyrme - Instrumentation & Controls

865 posts

Ultimate Geek
+1 received by user: 73

Subscriber

  Reply # 747152 18-Jan-2013 21:32 Send private message

MikeSkyrme:
cyril7: Ummm sorry but the regulations now make AS/NZ3000 now law, this has been for some time, essentially the legislated regulation has extended to the standard, well as I was last advised by the oracles.

Cyril

Specifically, NZ Electrical Safety Regulations 2010, Section 5, regulation 57.

Edit: Hit the enter button too early....


Part 5
Safety of installations
57 Low voltage and extra-low voltage installations to comply
with AS/NZS 3000
(1) Every installation that operates at low voltage or extra-low
voltage must comply with either Part 1 or Part 2 of AS/NZS
3000.
(2) A person who installs any part of a low voltage installation
must—
(a) before starting the installation, hold a declaration of
conformity that complies with regulation 58 for that part
of the installation; and
(b) ensure that the installation complies with the relevant
Part of AS/NZS 3000 identified in the declaration of
conformity; and
(c) in the case of an installation designed under Part 1 of
AS/NZS 3000, ensure that the installation is installed in
accordance with the design identified in the declaration
of conformity.
(3) The installer must retain a copy of the declaration of conformity
for an installation for at least 3 years, and make a copy of
it available to the Secretary on request.
(4) A person who installs a low voltage installation commits a
grade A offence if he or she fails to comply with subclause
(2) or (3).
Compare: SR 1997/60 r 69A



Basically here is an approved method (AS/NZS3000), it still does not make the standard law, and reading the regulation it deals more with DOC's than anything else.



2893 posts

Uber Geek
+1 received by user: 33

Trusted

  Reply # 747257 19-Jan-2013 09:11 Send private message

3000:2007 is superseded (I'm told by an electrician), there is a newer version which must be referenced but many electricians still reference 2007. I've got 3000:2007 at work but not the new one (we do not do electrical installations, just for information).

Must comply with either part 1 or part 2? In 3000:2007 part 1 is definitions and part 2 is all the installation practice clauses. So if the install complies with part 1 (definitions) it is fine?

Clause 7.5.4:
Exception: SELV and PELV circuit conductors installed in accordance with
Clause 3.9.8.3 may be contained within the same wiring system as low
voltage circuits.

Clause 3.9.8.2:
Cables of low voltage circuits and cables of extra-low voltage circuits may
be enclosed in the same wiring system only where one of the following
arrangements is employed:
(a) The low voltage cables shall be of a type providing the equivalent of
double insulation.
(b) All cables or each conductor of a multi-core cable shall be insulated
for the highest voltage present.
(c) The low voltage cables shall be installed in a separate compartment of
a common cable trunking system having fixed and continuous barriers
between compartments.

Network and phone cables comply with clause 3.9.8.2 b), but the ends which are stripped do not so it needs a separate face plate. Also, if the owner replace e.g. a phone face plate and there is mains on it he might bring the wires too close together. Different face plates mean segregation of the wire ends, or it does when flush boxes are used, our electrician used mounting brackets.




You can never have enough Volvos!


865 posts

Ultimate Geek
+1 received by user: 73

Subscriber

  Reply # 747265 19-Jan-2013 09:47 Send private message

Niel: 3000:2007 is superseded (I'm told by an electrician), there is a newer version which must be referenced but many electricians still reference 2007. I've got 3000:2007 at work but not the new one (we do not do electrical installations, just for information).

Must comply with either part 1 or part 2? In 3000:2007 part 1 is definitions and part 2 is all the installation practice clauses. So if the install complies with part 1 (definitions) it is fine?

Clause 7.5.4:
Exception: SELV and PELV circuit conductors installed in accordance with
Clause 3.9.8.3 may be contained within the same wiring system as low
voltage circuits.

Clause 3.9.8.2:
Cables of low voltage circuits and cables of extra-low voltage circuits may
be enclosed in the same wiring system only where one of the following
arrangements is employed:
(a) The low voltage cables shall be of a type providing the equivalent of
double insulation.
(b) All cables or each conductor of a multi-core cable shall be insulated
for the highest voltage present.
(c) The low voltage cables shall be installed in a separate compartment of
a common cable trunking system having fixed and continuous barriers
between compartments.

Network and phone cables comply with clause 3.9.8.2 b), but the ends which are stripped do not so it needs a separate face plate. Also, if the owner replace e.g. a phone face plate and there is mains on it he might bring the wires too close together. Different face plates mean segregation of the wire ends, or it does when flush boxes are used, our electrician used mounting brackets.


the insulation of phone or data cables are not rated for 230v so they don't comply with part B
I'm picking you are looking at the 300V rating on the cable, this is a fire rating not a voltage rating

2893 posts

Uber Geek
+1 received by user: 33

Trusted

  Reply # 747330 19-Jan-2013 12:30 Send private message

No, I did not look at the cable actually. How about a) then, equivalent of double insulation i.e. 2 layers?

It is not hard to find 1500V dielectric, 300V rated network cable. For example http://www.pacificcable.com/Cat_6_Tutorial.htm
The rated voltage is continuous. The dielectric rating is safety in brief overvoltage due to surges, lightning, etc. The company I work at makes electric fence energizers which output 10,000V but still needs a dielectric withstand voltage test primary to secondary.

Another one:
http://www.drakauk.com/products/special_cables/special9.php
1000V dielectric

Given that Cat6 has an extra shield and plastic layer and jacket thicker than the internal wires insulation, I do not see issue.

You also get specialist cables like a so called pink cable rated over 3000V dielectric withstand.




You can never have enough Volvos!


865 posts

Ultimate Geek
+1 received by user: 73

Subscriber

  Reply # 747334 19-Jan-2013 12:40 Send private message

Niel: No, I did not look at the cable actually. How about a) then, equivalent of double insulation i.e. 2 layers?

It is not hard to find 1500V dielectric, 300V rated network cable. For example http://www.pacificcable.com/Cat_6_Tutorial.htm
The rated voltage is continuous. The dielectric rating is safety in brief overvoltage due to surges, lightning, etc. The company I work at makes electric fence energizers which output 10,000V but still needs a dielectric withstand voltage test primary to secondary.

Another one:
http://www.drakauk.com/products/special_cables/special9.php
1000V dielectric

Given that Cat6 has an extra shield and plastic layer and jacket thicker than the internal wires insulation, I do not see issue.

You also get specialist cables like a so called pink cable rated over 3000V dielectric withstand.


The shield in cat6 is effectly a current carry conductor so that rules out the double insulation, and i've yet to see a cat5/6 cable that is stamped with the markings that it meets the standard for LV installation

5971 posts

Uber Geek
+1 received by user: 109

Trusted
Subscriber

  Reply # 747337 19-Jan-2013 12:43 Send private message

Hi Greg, I will concede that yes the standard does not appear to have its status elevated to be a true extension of the regulation and thus law, but the regulations have been changed (as of 2010) to pretty much make adherence to the standard as if it were law, the following link pretty much explains the status.

http://www.standards.co.nz/touchstone/Issue+11/Electrical/Standards+and+electrical+installation+and+equipment+new+regulations+due+in+early+2010.htm

Regardless, failure to adhere to separation requirements in the standard and referenced comments of PTC106 (ie LV and ELV on a single faceplate) will bring action from the wiring board as failures to adhere to legal regulations via the standard.

And to the poster that said that AS/NZ3000-2007 is out of date, this is incorrect, there are several ammendments, but its still the current standard.

Cheers
Cyril

1 | 2 | 3 | 4 | 5
Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic




Twitter »
Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





Trending now »

Hot discussions in our forums right now:

How stable are snap IP addresses?
Created by Physn, last reply by timmmay on 23-Oct-2014 10:38 (19 replies)
Pages... 2


Spark Socialiser
Created by freitasm, last reply by freitasm on 22-Oct-2014 18:39 (34 replies)
Pages... 2 3


$39 iPhone plan goneburger
Created by MadEngineer, last reply by Demeter on 23-Oct-2014 16:09 (16 replies)
Pages... 2


American legal jurisdiction in New Zealand
Created by ajobbins, last reply by gzt on 21-Oct-2014 14:58 (30 replies)
Pages... 2


iPad Air 2 and iPad Mini 3. Gonna get one?
Created by Dingbatt, last reply by Geektastic on 23-Oct-2014 15:13 (98 replies)
Pages... 5 6 7


Snap have failed our company!
Created by dafman, last reply by NonprayingMantis on 23-Oct-2014 11:56 (36 replies)
Pages... 2 3


Theif taunts 12 year old via stolen laptop
Created by macuser, last reply by charsleysa on 22-Oct-2014 23:49 (12 replies)

22nd Only: PB Tech BROTHER HL1110 Mono laser Printer $15 shipped(after $30 cashback)
Created by loceff13, last reply by loceff13 on 23-Oct-2014 08:55 (23 replies)
Pages... 2



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.

Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.