#171263 11-Apr-2015 12:55
Send private message



non dimmable driver for a led downlight

driver has no ground connector, and ground not shown in diagram. the driver case is fully isolated.

where should the ground wire in the cable go? put in a connector like this and leave it out? thanks.

http://www.bunnings.co.nz/deta-screw-connectors-40a-8pk-_p00310429

p.s. a spiky is coming..

p.s. all light fittings on separate circuit from power. other fittings who had ground connectors which doesn't really do/connect anything, just a place holder in the connector block.

Create new topic
5085 posts

Uber Geek

Trusted

  #1281061 11-Apr-2015 12:57
Send private message

As it says in that picture "driver must be installed by a qualified electrician". Get him to sort that detail out, that's his job.




Whatifthespacekeyhadneverbeeninvented?




394 posts

Ultimate Geek


  #1281145 11-Apr-2015 16:18
One person supports this post
Send private message

"a spiky is coming" but I won't be home to ask questions.

a bit of know how wouldn't hurt? I understand double insulated and non grounded appliances don't need ground wire connected, but do wonder the proper way to handle said ground wire - which doesn't seem to be connecting to anything from a like-for-like light fitting I replaced.

I guess Darwin frowns upon RCD quite often.

 
 
 
 


5085 posts

Uber Geek

Trusted

  #1281159 11-Apr-2015 16:59
Send private message

What is a spiky?




Whatifthespacekeyhadneverbeeninvented?




394 posts

Ultimate Geek


  #1281160 11-Apr-2015 17:08
Send private message

sparky my bad... no wonder he hasn't come yet.

20 posts

Geek


  #1281162 11-Apr-2015 17:22
Send private message

DarthKermit: What is a spiky?


That would be a punk sparky wearing a "god save the queen" shirt and with a safety pin through their nose.

1540 posts

Uber Geek


  #1281204 11-Apr-2015 19:38
Send private message

hangon: "a spiky is coming"
I guess Darwin frowns upon RCD quite often.


Incidentally a RCD doesn't need earth to operate. But that is outside the scope of this discussion.

3267 posts

Uber Geek

Trusted

  #1281209 11-Apr-2015 19:58
Send private message

If the driver has a double insulated symbol (a square within a square) then it is (supposedly) certified as being insulated sufficiently and an earth connection would have no effect as you can't get a leakage path from mains via the low voltage output to earth.

Typically if a fitting has a metal housing and has mains in it, then the metal needs to be earth.  Modern LED fittings with an external driver, even if the fitting is metal, would not need an earth wire if the driver is double insulated.  Older wiring rules however allowed metal light fittings to be wired without an earth wire (or at least that is how it was in our original-condition 1960's house).

I am not an electrician, but I am an electronic engineer who designs products according to standards so can comment from a product design point of view.




You can never have enough Volvos!


 
 
 
 


23003 posts

Uber Geek

Trusted
Subscriber

  #1281240 11-Apr-2015 21:40
Send private message

When mine were done by a sparky, the TPS jacket was stripped back some way, the earths were bent back 180 degrees and twisted , the live and neutrals went into the transformer, and the clamp just clamped on the live and neutrals, there was tape applied around both white TPS jackets and covering the twisting of the earths. No terminal was put on the earths.

I thought the exposed central conductors and twisted earths were a bit crap (I would use other words here but have been told off in the past on another forum) but apparently its the best they can do because the standards don't mandate things have large enough terminal blocks or a clamping arrangement that is good enough to clamp the sheath of 2 pieces of 1.5mm 2C+E cable, letalone the 3 that some lights had.




Richard rich.ms

1647 posts

Uber Geek

Lifetime subscriber

  #1281254 11-Apr-2015 21:58
Send private message

StGabriel:

That would be a punk sparky wearing a "god save the queen" shirt and with a safety pin through their nose.


You mean a Chorus installer wink




Ding Ding Ding Ding Ding : Ice cream man , Ice cream man


3136 posts

Uber Geek


  #1281318 12-Apr-2015 09:22
Send private message

richms: When mine were done by a sparky, the TPS jacket was stripped back some way, the earths were bent back 180 degrees and twisted , the live and neutrals went into the transformer, and the clamp just clamped on the live and neutrals, there was tape applied around both white TPS jackets and covering the twisting of the earths. No terminal was put on the earths.

I thought the exposed central conductors and twisted earths were a bit crap (I would use other words here but have been told off in the past on another forum) but apparently its the best they can do because the standards don't mandate things have large enough terminal blocks or a clamping arrangement that is good enough to clamp the sheath of 2 pieces of 1.5mm 2C+E cable, letalone the 3 that some lights had.


Maybe the choice of transformer means that additional junction boxes are needed to comply. The Standard does require that the earth appears at each lighting point in case it is required by a change in fitting. This means that leaving earths unterminated at intermediate points doesn't comply.

3235 posts

Uber Geek

Subscriber

  #1281350 12-Apr-2015 10:32
Send private message

We've had two different registered sparkys do different led fittings in our place and neither of them attached the earth to the drivers. Even though the drivers we have do have an earth connector on them.

BDFL - Memuneh
65619 posts

Uber Geek

Administrator
Trusted
Geekzone
Lifetime subscriber



394 posts

Ultimate Geek


  #1281760 13-Apr-2015 08:56
Send private message

 
Maybe the choice of transformer means that additional junction boxes are needed to comply. The Standard does require that the earth appears at each lighting point in case it is required by a change in fitting. This means that leaving earths unterminated at intermediate points doesn't comply.


My case was about a single switch controlling a single light fitting. My understanding is that for multiple fittings the ground connection needs to be available at each point in case a replacement needs to be earthed.

Thanks, particularly richms and CYaBro for sharing your experiences. I called upon a new sparky I'd be interested in seeing how he handles details like this (and whether he'd go the extra mile get the insulation snug and fit now that is an IC rated, and get the driver above insulation). I've seen the tape before, not convinced but wasn't really bothered.



394 posts

Ultimate Geek


  #1282373 13-Apr-2015 17:51
Send private message

Thanks StGabriel for the link on page 22
If no earth terminal on light fitting, place earth wire in a floating insulated connector behind fitting. 

more reading under section 5, and general electrical safety tips around home in appendix b.

sparky says either tape or connector would be fine...

Create new topic



Twitter and LinkedIn »



Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

Withings launches three new devices to help monitor heart health from home
Posted 13-Feb-2020 20:05


Auckland start-up Yourcar matches new car buyers with dealerships
Posted 13-Feb-2020 18:05


School gardens go high tech to teach kids the importance of technology
Posted 13-Feb-2020 11:10


Malwarebytes finds Mac threats outpace Windows for the first time
Posted 13-Feb-2020 08:01


Amazon launches Echo Show 8 in Australia and New Zealand
Posted 8-Feb-2020 20:36


Vodafone New Zealand starts two year partnership with LetsPlay.Live
Posted 28-Jan-2020 11:24


Ring launches indoor-only security camera
Posted 23-Jan-2020 17:26


New report findings will help schools implement the digital technologies curriculum content
Posted 23-Jan-2020 17:25


N4L to upgrade & support wireless internet inside schools
Posted 23-Jan-2020 17:22


Netflix releases 21 Studio Ghibli works
Posted 22-Jan-2020 11:42


Vodafone integrates eSIM into device and wearable roadmap
Posted 17-Jan-2020 09:45


Do you need this camera app? Group investigates privacy implications
Posted 16-Jan-2020 03:30


JBL launches headphones range designed for gaming
Posted 13-Jan-2020 09:59


Withings introduces ScanWatch wearable combining ECG and sleep apnea detection
Posted 9-Jan-2020 18:34


NZ Police releases public app
Posted 8-Jan-2020 11:43



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.


Support Geekzone »

Our community of supporters help make Geekzone possible. Click the button below to join them.

Support Geezone on PressPatron



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.