timmmay:The zoned ones with automatic adjustments would seem to be more adaptable and probably need less design.

 



 

Yeah, nah.

 

In a high volume, low pressure system like ducted aircon, a change in flow rate in any duct will affect the flow rate in all the others. Unless the system is correctly designed it will produce surging and hunting between zones. Even in an un-zoned system opening or closing a door will affect the flow rate to other rooms.

 

While ours is un-zoned, I looked at the calculations the engineer did before our install. It involved loads and flow rates for each room and the ducting was sized accordingly. The downside of the way it is installed is that to effectively zone now will require individual room control rather than just the bedroom end of the house from the living end.





“We’ve arranged a society based on science and technology, in which nobody understands anything about science technology. Carl Sagan 1996


Affiliate link
 
 
 

Affiliate link: Norton Secure VPN helps secure private information using bank-grade encryption when using public Wi-Fi on your PC, Mac, or mobile device.
  #2777182 13-Sep-2021 07:38
Send private message

We installed six high wall heat pump units (four bedrooms, media & family rooms) in our previous home and controlled each room separately. The advantage being ultimate room control and the disadvantage being that each room would take forever to warm up. We then settled on leaving the family room unit on all the time so that warmth would spread around the house.

 

For our current house we installed a ducted system with six zones. No more ice-cold rooms and the whole house is warm. We also installation of a heat exchange system from Cleanaire to add fresh clean air into the ducts, this reduces the overall co2 levels and we wake up refreshed. A final advantage being we don't need to adjust the settings regardless of what the weather we're having. As the cost of running the two systems would be similar, we're happier with our ducted solution. 


timmmay
18587 posts

Uber Geek

Trusted
Subscriber

  #2777191 13-Sep-2021 08:20
Send private message

Dingbatt:

 

Yeah, nah.

 

In a high volume, low pressure system like ducted aircon, a change in flow rate in any duct will affect the flow rate in all the others. Unless the system is correctly designed it will produce surging and hunting between zones. Even in an un-zoned system opening or closing a door will affect the flow rate to other rooms.

 

While ours is un-zoned, I looked at the calculations the engineer did before our install. It involved loads and flow rates for each room and the ducting was sized accordingly. The downside of the way it is installed is that to effectively zone now will require individual room control rather than just the bedroom end of the house from the living end.

 

 

I don't fully understand. Our unit has electric dampers in the ceiling space opening and closing depending on the temperature in each room. Each room has a grill for return air, though it works fine if doors are open or closed. I'm not really sure what you mean by surging or hunting. The only problem we really have is the spill zone overheating sometimes, which I explained above.

 

Pretty sure no calculations were done at all for our system and it's worked well so far. Two large ducts come off the ceiling unit, splitting into smaller ducts for each room. The large lounge has two diffusers, all other rooms have one.




timmmay
18587 posts

Uber Geek

Trusted
Subscriber

  #2777276 13-Sep-2021 11:47
Send private message

Also, upgrade to the thicker R1.0 insulation. I did some estimates based on my limited knowledge, from memory it cut heat loss in our case down from about 30% to about 15%, ie about 1.2kw less lost in the ceiling cavity.


1 | 2 
View this topic in a long page with up to 500 replies per page Create new topic





News and reviews »

Belkin Screenforce Tempered Glass Screen Protector and Bumper - Apple Watch
Posted 15-Aug-2022 17:20


Samsung Introducing Galaxy Z Flip4 and Galaxy Z Fold4
Posted 11-Aug-2022 01:00


Samsung Unveils Health Innovations with Galaxy Watch5 and Galaxy Watch5 Pro
Posted 11-Aug-2022 01:00


Google Bringing First Cloud Region to Aotearoa New Zealand
Posted 10-Aug-2022 08:51


ANZ To Move to FIS Modern Banking Platform
Posted 10-Aug-2022 08:28


GoPro Hero10 Black Review
Posted 8-Aug-2022 17:41


Amazon to Acquire iRobot
Posted 6-Aug-2022 11:41


Samsung x LIFE Picture Collection Brings Iconic Moments in History to The Frame
Posted 4-Aug-2022 17:04


Norton Consumer Cyber Safety Pulse Report: Phishing for New Bait on Social Media
Posted 4-Aug-2022 16:50


Microsoft Announces New Solutions for Threat Intelligence and Attack Surface Management
Posted 3-Aug-2022 21:54


Seagate Addresses Hyperscale Workloads with Enterprise-Class Nytro SSDs
Posted 3-Aug-2022 21:50


Visa Launching Eco-friendly Payment Solutions in New Zealand
Posted 3-Aug-2022 21:48


NCR Delivers Services to Run Bank of New Zealand ATM Network
Posted 30-Jul-2022 11:06


New HP Portfolio Supports New Era of Hybrid Work
Posted 28-Jul-2022 17:14


Harman Kardon Launches Citation MultiBeam 1100 Soundbar
Posted 28-Jul-2022 17:10









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.