I have just connected a brand new Powercom Macan MRT 1000VA/1000W On Line UPS but when I turn it on (hold the on/off switch for 3 seconds) the RCD on the main switchboard trips after only 1 second.

 

Do I have to wait for the battery to fully charge or something?





Rob

Create new topic

dan

1154 posts

Uber Geek

Lifetime subscriber

  #2247226 28-May-2019 15:52
Send private message

its probably faulty - it should not be tripping your RCD  (assuming your RCD has no issue)




610 posts

Ultimate Geek

Lifetime subscriber

  #2247259 28-May-2019 16:55
Send private message

No this is the only thing which trips the RCD. If I put it on another circuit it trips that RCD too.
Supplier is happy to replace it or refund me the money (which is the option SWMBO prefers)




Rob

 
 
 
 


3525 posts

Uber Geek

Trusted

  #2247270 28-May-2019 17:22
Send private message

An RCD trips if the return path is through the earth - and presuming the housing of the UPS is earthed, could it be some loose cable inside? Probably best to get the supplier to review.





Speedtest 2019-10-14


22990 posts

Uber Geek

Trusted
Subscriber

  #2247327 28-May-2019 18:58
Send private message

Have you tried another mains cable into the input of the UPS?





Richard rich.ms



610 posts

Ultimate Geek

Lifetime subscriber

  #2247345 28-May-2019 19:40
Send private message

Yes I am an electrician by trade. I am convinced that the UPS is faulty.




Rob

509 posts

Ultimate Geek


  #2247390 28-May-2019 22:20
Send private message

robfish: Yes I am an electrician by trade. I am convinced that the UPS is faulty.

 

The only thing that I can think of is there is a short between neutral and earth some where in the unit or enough leakage to trip.

 

If its new i would take it back and get a new one.


3885 posts

Uber Geek

Subscriber

  #2247409 28-May-2019 22:40

Is the UPS output fully isolated from the incoming mains? (equivalent to an isolating transformer?) Or does it actually contain an MEN link on it's output terminals? As some appliances dont work properly if the neutral is not linked to the earth. (mostly gas appliances that use electronic flame sensing).

A local MEN link would be needed to cover the scenario where the input power cable gets unplugged. As the switchboard MEN link wont be available to the UPS anymore.





 
 
 
 




610 posts

Ultimate Geek

Lifetime subscriber

  #2247432 29-May-2019 06:19
Send private message

Aredwood:As the switchboard MEN link wont be available to the UPS anymore.

You may be onto something here (with regard to an earthed neutral).

If, on the load side of an RCD, the neutral becomes earthed, it will trip.
Maybe this UPS is not designed to work with an RCD




Rob

9226 posts

Uber Geek


  #2247433 29-May-2019 06:34
Send private message

Stumbled on this from Schneider - UPS causing RCD to trip seems to be a common enough problem for them to offer an faq (word doc)

 

This document examines one of the most common site issues with UPS systems, which is the tripping of the earth leakage protection, Residual Current Device (RCD) also known as an Earth Leakage Circuit Breaker (ELCB).

 

 


509 posts

Ultimate Geek


  #2247437 29-May-2019 06:37
Send private message

Fred99:

 

Stumbled on this from Schneider - UPS causing RCD to trip seems to be a common enough problem for them to offer an faq (word doc)

 

 

 

 

That link does not work


9226 posts

Uber Geek


  #2247438 29-May-2019 06:40
Send private message

sparkz25:

 

That link does not work

 

 

Link fixed.


7257 posts

Uber Geek

Trusted
Subscriber

  #2247441 29-May-2019 06:47
Send private message

Hi, all switch mode supplies (including the one in the UPS) have filter capacitors from both P and N to E, there may also be MOV's, if those two caps have slightly different impedance at 50Hz, then you will have a differential current and trip the RCD. It might seem like a lot of variance in impedance is required, but infact it is not and the issue is common. Typically the variation is only enough to trip a 10mA RCD, but its not uncommon for this difference to be enough to trip a 30mA one. I might suggest you look at providing a seperate circuit for your UPS that does not go via an RCD. This is quite common practice for many products, especially those with motors (Fridge/heat pumps) that will often trip RCDs due to either start current leakage or in many modern inverter models the switch mode supply filter cap leakage as mentioned.

 

Cyril




610 posts

Ultimate Geek

Lifetime subscriber

  #2247447 29-May-2019 07:02
Send private message

Thanks Cyril (and others).
I now have to think about the way forward.
I might even try a cheaper UPS for just my ONT, Edgerouter, switch and PoE switch (cameras and APs)




Rob

Create new topic



Twitter and LinkedIn »



Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

Withings launches three new devices to help monitor heart health from home
Posted 13-Feb-2020 20:05


Auckland start-up Yourcar matches new car buyers with dealerships
Posted 13-Feb-2020 18:05


School gardens go high tech to teach kids the importance of technology
Posted 13-Feb-2020 11:10


Malwarebytes finds Mac threats outpace Windows for the first time
Posted 13-Feb-2020 08:01


Amazon launches Echo Show 8 in Australia and New Zealand
Posted 8-Feb-2020 20:36


Vodafone New Zealand starts two year partnership with LetsPlay.Live
Posted 28-Jan-2020 11:24


Ring launches indoor-only security camera
Posted 23-Jan-2020 17:26


New report findings will help schools implement the digital technologies curriculum content
Posted 23-Jan-2020 17:25


N4L to upgrade & support wireless internet inside schools
Posted 23-Jan-2020 17:22


Netflix releases 21 Studio Ghibli works
Posted 22-Jan-2020 11:42


Vodafone integrates eSIM into device and wearable roadmap
Posted 17-Jan-2020 09:45


Do you need this camera app? Group investigates privacy implications
Posted 16-Jan-2020 03:30


JBL launches headphones range designed for gaming
Posted 13-Jan-2020 09:59


Withings introduces ScanWatch wearable combining ECG and sleep apnea detection
Posted 9-Jan-2020 18:34


NZ Police releases public app
Posted 8-Jan-2020 11:43



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.


Support Geekzone »

Our community of supporters help make Geekzone possible. Click the button below to join them.

Support Geezone on PressPatron



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.