Geekzone: technology news, blogs, forums
Guest
Welcome Guest.
You haven't logged in yet. If you don't have an account you can register now.


PSLog

291 posts

Ultimate Geek


#304656 24-May-2023 16:30
Send private message quote this post

I'm planning to use a Shelly PM1 Plus (wifi relay) to control the on/off times of my water heater to take advantage of off-peak electricity tarifs.
I would like to have the ability to force the heater to be ON (over-riding the relay) in case I have wifi issues.

If I wire the Shelly device in, direct from the switchboard supply, it seems that I can use the existing switch (in a socket made up of a switch/cable out configuration) to provide this over-ride switch.

However, someone has told me that is illegal because the hot water cylinder must have a local isolating switch - and not rely on a switchboard circuit-breaker for this function.

Comments?

As an alternative (to installing a second isolating switch) does the Shelly PM1 - Plus's bluetooth function allow the relay to be forced ON?

I know the work needs to be done by a registered sparky - I'm just scoping the details of the job. It may be that, as yet, not too many sparkies are that familiar with these devised yet.

Thanks in advance

View this topic in a long page with up to 500 replies per page Create new topic
 1 | 2 | 3 | 4 | 5 | 6
cruxis
472 posts

Ultimate Geek


  #3079448 24-May-2023 18:03
Send private message quote this post

I stuck one on mine, I was also told not to touch the switchboard end. So I chucked it inside a isolating switch outside the house. But my 3KW hot water box/cylinder is outside the house easy access. It has been working fine for over a year. Works with home assistant perfectly too.

 


 
 
 
 

Shop now on Samsung phones, tablets, TVs and more (affiliate link).
lloydw
21 posts

Geek


#3079454 24-May-2023 18:57
Send private message quote this post

I looked at doing something similar last year, but then read some stories online about them getting really hot when under load for extended periods of time. It’s ideal to have it outdoors like yours, but I was concerned about putting mine inside my already warm hot water closet 😀

PSLog

291 posts

Ultimate Geek


  #3079460 24-May-2023 19:34
Send private message quote this post

cruxis:

I stuck one on mine, I was also told not to touch the switchboard end. So I chucked it inside a isolating switch outside the house. But my 3KW hot water box/cylinder is outside the house easy access/p>



So, is that switch an ON override or an OFF override.

An OFF override is no problem legally - whereas an ON override MAY be a problem.


Re-overheating, the PM1 Plus has thermal overload protection. This is different from the one pictured, which it (I think) the PM1.



MadEngineer
4223 posts

Uber Geek

Trusted

  #3079468 24-May-2023 20:17
Send private message quote this post

Well you’re going to be wiring it in series with the existing switch and not removing it so you will still have the ability to control it.




You're not on Atlantis anymore, Duncan Idaho.

hairy1
3330 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #3079469 24-May-2023 20:18
Send private message quote this post

I had a sparky wire one into the circuit prior to the switch next the water cylinder. It was acting as an OFF over-ride and all protections are still in place.

 

I don't like having the PM in the wall and am shortly replacing it with a PM2 Pro in the switchboard after the circuit breaker. This will also act as an OFF over-ride so I will be able to control when the heater is able to heat. I am not removing any switches.





My views (except when I am looking out their windows) are not those of my employer.


mattenz
190 posts

Master Geek


  #3080472 28-May-2023 20:04
Send private message quote this post

I have that setup. It works well, to me it's sufficient override for it to default on after getting power, which can be interrupted either by the isolator or circuit board.

Nate001
630 posts

Ultimate Geek


  #3080477 28-May-2023 20:20
Send private message quote this post

I tried this a while ago but strongly advise against it.

Long story short, the device cannot handle a standard hot water heater and I lost confidence regarding its safety in my house so removed it.

I logged the device temperature and it shot over 100c when under a 3kW load after 30minutes of constant load. Looking on the Shelly facebook page many people had similar issues and concerns.

Either use the Shelly to control a contactor, or don’t use it all.



PSLog

291 posts

Ultimate Geek


#3080544 29-May-2023 07:57
Send private message quote this post

Really?
Any comments on this?

Nate001
630 posts

Ultimate Geek


  #3082553 30-May-2023 20:09
Send private message quote this post

PSLog: Really?
Any comments on this?

 

Here are two of many threads on the facebook support page with someone running a hot water cylinder using a shelly. 

 

https://www.facebook.com/groups/ShellyIoTCommunitySupport/permalink/5020988484667142/ 

 

https://www.facebook.com/groups/ShellyIoTCommunitySupport/permalink/5677050682394249/

 

 


eonsim
387 posts

Ultimate Geek

Trusted

  #3082565 30-May-2023 20:30
Send private message quote this post

@PSLog For high loads you should ideally be using a Shelly EM or 3EM, you use the CT-clamp for power monitoring (and can use the extra one or two clamps to monitor other key circuits, or whole house load) and you get a suitable contractor installed on the hotwater cylinder circuit and linked to the EM/3EM. The EM then controls the contractor to turn on or off the hotwater cylinder, with out putting any load on the Shelly, much safer and no chance of the shelly melting or shutting down due to over heating with a high load, as all the load is going through the contractor which is designed to handle it.


PSLog

291 posts

Ultimate Geek


  #3082570 30-May-2023 20:39
Send private message quote this post

Thanks for the replies.
My element is 2kW, giving only an 8.33 amp load.
That is very close to half the rated load for the Shelly.
I'm going to try it, but stick a temperature sensor to the device and monitor it for the first week or so

hairy1
3330 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #3082575 30-May-2023 21:01
Send private message quote this post

The device is New Zealand AS certified for 16 Amps so there shouldn't be an issue with ruining a 3kW heater.





My views (except when I am looking out their windows) are not those of my employer.


Nate001
630 posts

Ultimate Geek


  #3082577 30-May-2023 21:04
Send private message quote this post

2kW is a lot more manageable. Truth is you don't need a EM device for a fixed size load, you could control it with a standard shelly and simply multiple by the on time for energy usage. This would eliminate the resistive load shunt which generates extra heat.


Klathman
300 posts

Ultimate Geek


  #3082648 31-May-2023 09:24
Send private message quote this post

We have a Shelley 1PM on the spa pool and haven't received any over-temperature warning.

 

It's a 15amp circuit, and we're regularly hitting 2.7-2.9KW while it's heating.

 

The plug is outside which I guess will help cool it down over the winter though.


Ge0rge
2023 posts

Uber Geek

Trusted
Lifetime subscriber

  #3082685 31-May-2023 11:03
Send private message quote this post

One thing I note with these devices is that the maximum conductor cross-sectional area is limited to between 0.5 to 1.5 mm² (from here).

 

NZECP 51:2001 states that for storage water heaters up to 3kW, 1.5mm² stranded conductors are the minimum. For storage water heaters between 3kW and 6kW, 2.5mm² is the minimum wire size.

 

I would argue that, based solely on the above, that a Shelly 1/1PM device should not be used for any load above 3kW, unless it is controlling a contactor.

 

 

 

 

 

 

 

 


 1 | 2 | 3 | 4 | 5 | 6
View this topic in a long page with up to 500 replies per page Create new topic





News and reviews »

Logitech Introduces New G522 Gaming Headset
Posted 21-May-2025 19:01


LG Announces New Ultragear OLED Range for 2025
Posted 20-May-2025 16:35


Sandisk Raises the Bar With WD_BLACK SN8100 NVME SSD
Posted 20-May-2025 16:29


Sony Introduces the Next Evolution of Noise Cancelling with the WH-1000XM6
Posted 20-May-2025 16:22


Samsung Revelas Its 2025 Line-up of Home Appliances and AV Solutions
Posted 20-May-2025 16:11


Hisense NZ Unveils Local 2025 ULED Range
Posted 20-May-2025 16:00


Synology Launches BeeStation Plus
Posted 20-May-2025 15:55


New Suunto Run Available in Australia and New Zealand
Posted 13-May-2025 21:00


Cricut Maker 4 Review
Posted 12-May-2025 15:18


Dynabook Launches Ultra-Light Portégé Z40L-N Copilot+PC with Self-Replaceable Battery
Posted 8-May-2025 14:08


Shopify Sidekick Gets a Major Reasoning Upgrade, Plus Free Image Generation
Posted 8-May-2025 14:03


Microsoft Introduces New Surface Copilot+ PCs
Posted 8-May-2025 13:56


D-Link A/NZ launches DWR-933M 4G+ LTE Cat6 Wi-Fi 6 Mobile Hotspot
Posted 8-May-2025 13:49


Synology Expands DiskStation Lineup with DS1825+ and DS1525+
Posted 8-May-2025 13:44


JBL Releases Next Generation Flip 7 and Charge 6
Posted 8-May-2025 13:41









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.







GoodSync is the easiest file sync and backup for Windows and Mac