  #732682 14-Dec-2012 17:42
Send private message

Evilg:
nickb800: I eased up the screws holding the socket in question and shone a torch in there - yup only two wires connected to the socket, both black, and no sign of a third (earth) wire in the wall cavity (no flush box, was just screwed into wood panelling). Definitely getting the sparky around now, im starting to wonder if they even used mains cabling for that outlet or if it was just low voltage figure-8 cable!


Sounds like fun... electricians of previous decades are notorious for the number 8 fencing wire and "she'll be right" attitude.... you would not believe the things I have seen!

Good job checking it out, and yes, a good electrician is certainly needed at this point.


I think you mean people who think they can do electrical work, but are not electricians, see lots of results of home owners who give it a go and screw it up badly!


 
 
 
 

Send money globally for less with Wise - one free transfer up to NZ$900 (affiliate link).
gregmcc
2145 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #732683 14-Dec-2012 17:45
Send private message

Bung:
Evilg:
Sounds like fun... electricians of previous decades are notorious for the number 8 fencing wire and "she'll be right" attitude.... you would not believe the things I have seen!



I don't think a real electrician would use 2 core for a power point. I do wonder though why so many light fittings were installed without an earth. It may have been legal at the time but how much would the saving in wire cost have been?


no so much the time or cost, but in the 60's and 70's there wasn't any call for an earth as most of the light fittings were bakerlite or wood. Not many  light fittings or that era had any kind of external metal work, so no earth required

nickb800

2715 posts

Uber Geek

Trusted

  #732684 14-Dec-2012 17:47
Send private message

gregmcc:
nickb800:
richms: If it is showing nothing on L-N and connected 2 pin devices are working in the outlet, the tester is is defiantly wrong.


I'm wondering if the indicators on the front are indicating something different to what we would intuitively think from their description, because based on L-E being lit and L-N not being lit, you would think that means that the socket would not function, however on the diagramatic description on the back it says that that combination means earth not connected.

For correct wiring, it says that we should expect L-E and L-N lit, but not N-L, and this is exactly what happens on 95% of the outlets in the house, leading me to suspect that the tester is correct


Um... L-N is the same as N-L



And yet there are separate indicators for each (and the diagrams on the device suggesting that a correctly wired plug will have L-N but not N-L lit), hence my suggestion that they are indicating something different to what we would intuitively think



gregmcc
2145 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #732690 14-Dec-2012 18:09
Send private message

nickb800:
gregmcc:
nickb800:
richms: If it is showing nothing on L-N and connected 2 pin devices are working in the outlet, the tester is is defiantly wrong.


I'm wondering if the indicators on the front are indicating something different to what we would intuitively think from their description, because based on L-E being lit and L-N not being lit, you would think that means that the socket would not function, however on the diagramatic description on the back it says that that combination means earth not connected.

For correct wiring, it says that we should expect L-E and L-N lit, but not N-L, and this is exactly what happens on 95% of the outlets in the house, leading me to suspect that the tester is correct


Um... L-N is the same as N-L



And yet there are separate indicators for each (and the diagrams on the device suggesting that a correctly wired plug will have L-N but not N-L lit), hence my suggestion that they are indicating something different to what we would intuitively think



This again reaffirms what I say way back in this thread about a dodgy tester, seems to me that N-L should infact be labeled N-E, this been the case then this tester is non-compliant and should not be used.

Can you take a photo of the offending tester and post it here

kiwirock
685 posts

Ultimate Geek


  #732715 14-Dec-2012 18:51
Send private message

Yeah it'd be interesting to see a pic of it. Does sound dodgy, that's if the "-" between the letters doesn't mean minus or takeaway because of some poorly thought out explanation of what it means to someone who reads English.

If L-E was actually live minus E (and actually L+N) then it'd be correct on both the good and bad socket. If N-L was neutral minus live (and therefore actually L+E) it would be correct to be out on the one with missing earth. But that's a long shot that the true meaning is lost in translation of the instructions from what - Chinese manufactured and understood operation to English of what "-" means?


kiwirock
685 posts

Ultimate Geek


  #732716 14-Dec-2012 18:55
Send private message

And if N-L meant neutral minus live (meaning N+E) then that would be correct if it was out. But again, only in some really mistranslated or explained labeling would that remotely explain anything.

Bung
6395 posts

Uber Geek

Subscriber

  #732734 14-Dec-2012 19:33
Send private message

One pair of LEDs indicate presence of L-N,and L-E connections and the other LED shows L N reversal. The recall of a similar model was because the front labelling confused the issue and the L-N L-E and N-L labels were removed. Presumably the instructions give the correct diagnosis based on the lit and unlit LEDs.



nickb800

2715 posts

Uber Geek

Trusted

  #732892 15-Dec-2012 13:00
Send private message

Bung: One pair of LEDs indicate presence of L-N,and L-E connections and the other LED shows L N reversal. The recall of a similar model was because the front labelling confused the issue and the L-N L-E and N-L labels were removed. Presumably the instructions give the correct diagnosis based on the lit and unlit LEDs.


Ah you've figured it out.

My model is the same as the recalled one here, albeit hamer branded, http://www.jaycar.com.au/news.asp?ID=1281, and re-reading the email from Hamer, they consider that it is fine for professionals, just confusing for consumers, hence Jaycar recalling it (from the consumer market where they operate) and Hamer continuing it (for the professional market in which they operate). 

But at the end of the day, the patterns of the neon indicators are correct when considered with the diagrams on the back, and the pattern with the first neon lit and the rest unlit still indicates earth not connected, and this corroborates with what I saw behind the socket.

Also re: the sleepout wiring, the sleepout is a classic skyline/versatile/similar style single garage, and would be less than 20 years old, so sounds like it would definately be classed under more recent electrical regs. Having said that, it is fed from a 15A old style circuit breaker, which sounds appropriate for 1.5mm^2 TPS? Although the 'master' fuse on the subboard is 20A ceramic fuse.

Either way, the wiring is a dogs breakfast, and a sparky has been arranged, I'm sure it'll help his family for Christmas

gregmcc
2145 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #732898 15-Dec-2012 13:21
Send private message

nickb800:
Bung: One pair of LEDs indicate presence of L-N,and L-E connections and the other LED shows L N reversal. The recall of a similar model was because the front labelling confused the issue and the L-N L-E and N-L labels were removed. Presumably the instructions give the correct diagnosis based on the lit and unlit LEDs.


Ah you've figured it out.

My model is the same as the recalled one here, albeit hamer branded, http://www.jaycar.com.au/news.asp?ID=1281, and re-reading the email from Hamer, they consider that it is fine for professionals, just confusing for consumers, hence Jaycar recalling it (from the consumer market where they operate) and Hamer continuing it (for the professional market in which they operate). 

But at the end of the day, the patterns of the neon indicators are correct when considered with the diagrams on the back, and the pattern with the first neon lit and the rest unlit still indicates earth not connected, and this corroborates with what I saw behind the socket.

Also re: the sleepout wiring, the sleepout is a classic skyline/versatile/similar style single garage, and would be less than 20 years old, so sounds like it would definately be classed under more recent electrical regs. Having said that, it is fed from a 15A old style circuit breaker, which sounds appropriate for 1.5mm^2 TPS? Although the 'master' fuse on the subboard is 20A ceramic fuse.

Either way, the wiring is a dogs breakfast, and a sparky has been arranged, I'm sure it'll help his family for Christmas


Good move ;)

Ropenuts
133 posts

Master Geek


  #732899 15-Dec-2012 13:34
Send private message

Kitchen Creators needs someone to shift some kitchens around....

nickb800

2715 posts

Uber Geek

Trusted

  #732920 15-Dec-2012 14:59
Send private message

Ropenuts: Kitchen Creators needs someone to shift some kitchens around....

Haha I can't get away from it, even on geekzone! Down here for xmas this year unfortunately, otherwise could do with the $$

Ropenuts
133 posts

Master Geek


  #732932 15-Dec-2012 16:00
Send private message

Hahaha all good man. Knew it was you!

nickb800

2715 posts

Uber Geek

Trusted

  #736276 22-Dec-2012 11:29
Send private message

Got the sparky around earlier in the week, fixed the outlet. Looks like the previous owner had moved the wall out a bit, and moved the outlet in the process, and didnt extend the ground. All it took was ~100mm or earth cable!

Sparky thought the subboard in the sleepout was supplied fine, but since all the fuses were fed by wires through the front of the board rather than from behind (meaning that live but insulated cables were exposed) he was going to suggest to the landlord that the board be replaced.

kiwirock
685 posts

Ultimate Geek


  #736307 22-Dec-2012 13:10
Send private message

nickb800: Got the sparky around earlier in the week, fixed the outlet. Looks like the previous owner had moved the wall out a bit, and moved the outlet in the process, and didnt extend the ground. All it took was ~100mm or earth cable!

Sparky thought the subboard in the sleepout was supplied fine, but since all the fuses were fed by wires through the front of the board rather than from behind (meaning that live but insulated cables were exposed) he was going to suggest to the landlord that the board be replaced.


Can't say I've come across the new DIN rail system in any places I've rented yet. Always had the old ceramic fuses on hard board. Something nostalgic about them.



kiwirock
685 posts

Ultimate Geek


  #736308 22-Dec-2012 13:11
Send private message

I take it the inside board has been upgraded? Or has an RCD in front of everything?

1 | 2 | 3 | 4
View this topic in a long page with up to 500 replies per page Create new topic





News and reviews »

Māori Artists Launch Design Collection with Cricut ahead of Matariki Day
Posted 15-Jun-2025 11:19


LG Launches Upgraded webOS Hub With Advanced AI
Posted 15-Jun-2025 11:13


One NZ Satellite IoT goes live for customers
Posted 15-Jun-2025 11:10


Bolt Launches in New Zealand
Posted 11-Jun-2025 00:00


Suunto Run Review
Posted 10-Jun-2025 10:44


Freeview Satellite TV Brings HD Viewing to More New Zealanders
Posted 5-Jun-2025 11:50


HP OmniBook Ultra Flip 14-inch Review
Posted 3-Jun-2025 14:40


Flip Phones Are Back as HMD Reimagines an Iconic Style
Posted 30-May-2025 17:06


Hundreds of School Students Receive Laptops Through Spark Partnership With Quadrent's Green Lease
Posted 30-May-2025 16:57


AI Report Reveals Trust Is Key to Unlocking Its Potential in Aotearoa
Posted 30-May-2025 16:55


Galaxy Tab S10 FE Series Brings Intelligent Experiences to the Forefront with Premium, Versatile Design
Posted 30-May-2025 16:14


New OPPO Watch X2 Launches in New Zealand
Posted 29-May-2025 16:08


Synology Premiers a New Lineup of Advanced Data Management Solutions
Posted 29-May-2025 16:04


Dyson Launches Its Slimmest Vaccum Cleaner PencilVac
Posted 29-May-2025 15:50


OPPO Reno13 Pro 5G Review 
Posted 29-May-2025 15:33









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.







Backblaze unlimited backup