As in the image, I have a socket with two plugs, a 2400W kettle, if I plug the kettle to one of the two plugs, can I use the other plug as well? Will the socket be overloaded?

Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic
 1 | 2
2123 posts

Uber Geek


  # 1382092 8-Sep-2015 22:10
Send private message

Yes, sockets are 10A each outlet, unlike multiboards that are 10A total because they are plugged in with a 10A plug.




Location: Dunedin

 




3 posts

Wannabe Geek


  # 1382093 8-Sep-2015 22:16
Send private message

Is the 10A for the whole thing(two plugs) or each plug?

 
 
 
 


195 posts

Master Geek

Subscriber

  # 1382098 8-Sep-2015 22:23
Send private message

I AM NOT AN ELECTRICIAN, but:

Assuming that powerpoint was professionally installed and your house wiring is reasonably modern, the powerpoint will be supplied by a circuit rated at 20 amperes.  You can verify this by plugging a small lamp into one of the sockets, turning it on, then turning each circuit breaker on your main switchboard off (and back on again) in turn until you find which one controls that powerpoint.  The rating will be printed on the circuit breaker.  If it's not 20 amperes you've got a problem and should get a sparkie in to look at your wiring.

If you plug a kettle into one of the sockets, you're drawing 2400 W/230 V = 10.4 A, so you're OK to plug another appliance into the second socket as long as it draws less than 9.6 A.  I suspect the 2400 W is a nominal rating based on a 240 V mains supply (as Australia used to have), so the heater offers a resistance of 24 ohms and on a 230 V supply will draw 9.6 A.  Then you're OK even plugging a second heater into the second socket.

At this moment I'm sitting near a 2400 W rated heater on full and a dehumidifier, the two appliances plugged into the same double powerpoint and both running quite happily.

Are you by any chance from Canada or the USA?

606 posts

Ultimate Geek


  # 1382115 8-Sep-2015 23:27
5 people support this post
Send private message

The total loading of the socket outlet fitting can NOT exceed 10 amps.
(Source AS/NZS 3112).

So that PDL 692 double socket can take; 1x10A or 2x5A or 1x6A + 1x4A etc.
It can't take 2x10A as that would give a total loading of 20A.



2123 posts

Uber Geek


  # 1382155 9-Sep-2015 06:35
5 people support this post
Send private message

k1w1k1d:
I don't have that standard, so I cant read it to tell you where/why you are wrong. I suspect this is a case of not reading and/or understanding the document in full.

bijgd:
I am confident it is per socket. So in this case it is you can plug in 2 devices and use 10 amps on each.

Circuit protection also has very little to do with it.


The answer is yes, you can use both outlets however you like.
This thread will be up to three pages of speculation by this afternoon, ignore it.

I am an electrician.




Location: Dunedin

 


2945 posts

Uber Geek

Lifetime subscriber

  # 1382161 9-Sep-2015 07:24
Send private message

andrewNZ: Yes, sockets are 10A each outlet, unlike multiboards that are 10A total because they are plugged in with a 10A plug.


Not quite. Whilst the socket may be 10A per outlet, the wiring behind the socket is almost certainly only 10A. So, almost certainly, the total load on the socket is 10A.

In fact, several sockets will go back to a single fuse, which might be 10A or 15A. So the total load across several sockets will be 10-15A.

Do not be tempted to increase the fuse value... it is there to protect the wiring and prevent fire.

The exception to this is sockets on your stove, which connect back to th stove fuse which has a largwer value.



2123 posts

Uber Geek


  # 1382162 9-Sep-2015 07:27
5 people support this post
Send private message

frankv:
andrewNZ: Yes, sockets are 10A each outlet, unlike multiboards that are 10A total because they are plugged in with a 10A plug.


Not quite. Whilst the socket may be 10A per outlet, the wiring behind the socket is almost certainly only 10A. So, almost certainly, the total load on the socket is 10A.

In fact, several sockets will go back to a single fuse, which might be 10A or 15A. So the total load across several sockets will be 10-15A.

Do not be tempted to increase the fuse value... it is there to protect the wiring and prevent fire.

The exception to this is sockets on your stove, which connect back to th stove fuse which has a largwer value.



no

This geekzone at its worst. Please don't make statements you are not qualified to make.




Location: Dunedin

 


 
 
 
 


2954 posts

Uber Geek


  # 1382166 9-Sep-2015 07:40
Send private message

andrewNZ: This thread will be up to three pages of speculation by this afternoon, ignore it.

I am an electrician.


Try this thread instead http://www.electricalforum.co.nz/index.php?action=more_details&id=1337798708


"There is a difference in the rating - as Pluto says - because each fitting can deliver 10 A total. Meaning a quad gives total 10 A, 2 x doubles = total 20 A, & 4 x singles = 40 A (always provided the cable can deliver that)." AlecK


Amongst the posters pluto (who used to do Telecom power system design) is on the AS/NZS 3000 Wiring Rules committee and AlecK, an inspector both confirm that the fitting is rated for 10A total.

If you want speculation try "Should 16A breakers be used on most 2.5mm circuits if insulation is allowed for?"

Reason for edit Should have used PC

2945 posts

Uber Geek

Lifetime subscriber

  # 1383338 9-Sep-2015 12:11
Send private message

andrewNZ:
frankv:
andrewNZ: Yes, sockets are 10A each outlet, unlike multiboards that are 10A total because they are plugged in with a 10A plug.


Not quite. Whilst the socket may be 10A per outlet, the wiring behind the socket is almost certainly only 10A. So, almost certainly, the total load on the socket is 10A.

In fact, several sockets will go back to a single fuse, which might be 10A or 15A. So the total load across several sockets will be 10-15A.

Do not be tempted to increase the fuse value... it is there to protect the wiring and prevent fire.

The exception to this is sockets on your stove, which connect back to th stove fuse which has a largwer value.



no

This geekzone at its worst. Please don't make statements you are not qualified to make.


This is geekzone at its worst. Please don't make statements that you don't back up. Please do explain where I've gone wrong.


2123 posts

Uber Geek


  # 1383560 9-Sep-2015 18:00
Send private message

Alright then.
I'll be making some assumptions based on the photo. It it highly likely that this house is quite new based on the type and state of the wall, skirting, fittings and curtain.

frankv: Not quite. Whilst the socket may be 10A per outlet, the wiring behind the socket is almost certainly only 10A.

The wiring behind this socket outlet will be 2.5mm² (or perhaps bigger if it's a large house). Good for a lot more than 10 amps.

frankv: So, almost certainly, the total load on the socket is 10A.

In fact, several sockets will go back to a single fuse, which might be 10A or 15A. So the total load across several sockets will be 10-15A.

The circuit breaker will be 25A (it could be 20A but that's unlikely). There is zero chance it is 10A.

frankv: Do not be tempted to increase the fuse value... it is there to protect the wiring and prevent fire.

Congrats, you got one right... Except that it is almost certain that in this case circuit breakers are installed not fuses, therefore not replaceable.

frankv:

The exception to this is sockets on your stove, which connect back to th stove fuse which has a largwer value.

This is totally irrelevant.





Location: Dunedin

 


1715 posts

Uber Geek

Trusted
Lifetime subscriber

  # 1383562 9-Sep-2015 18:03
One person supports this post
Send private message

andrewNZ: k1w1k1d:
I don't have that standard, so I cant read it to tell you where/why you are wrong. I suspect this is a case of not reading and/or understanding the document in full.

bijgd:
I am confident it is per socket. So in this case it is you can plug in 2 devices and use 10 amps on each.

Circuit protection also has very little to do with it.


The answer is yes, you can use both outlets however you like.
This thread will be up to three pages of speculation by this afternoon, ignore it.

I am an electrician.



it doesn't matter if it's a single socket, double socket or quad socket, it's classed as 1 outlet for the purpose of the regs

I am an Electrician


1715 posts

Uber Geek

Trusted
Lifetime subscriber

  # 1383566 9-Sep-2015 18:22
Send private message

look at it like this, the circuit breaker is time/current based, if it's a 10a circuit breaker it won't trip instantly when the current rises slightly above 10a, running your kettle and another appliance for a few minutes together will not result in the breaker tripping, there are tables provided by circuit breaker manufactures that show loading vs. time characteristic of each size of their circuit breakers.

Off the top of my head (don't take this as a fact, but just from my memory), a 10A circuit breaker (with a standard C curve trip) will pass 15amps for 4 hours before tripping, the higher the current, the shorter the trip time, remember that there is also a cool down time once tripped, resetting right away will not result in another 4 hours of use as the bi-metal strip will have to cool down to ambient to get the 4 hours out of it again.

Remember the circuit breaker is sized to protect the cable, not the outlet or the appliance plugged in.

The standard power circuit should be a 20A circuit breaker, this will give you up to 17m of distance, a typical length for a power circuit in a house.


Yes, I am an Electrician

8816 posts

Uber Geek

Lifetime subscriber

  # 1384580 9-Sep-2015 19:30
Send private message

im pretty sure 2.5mm2 cable is rated for 16A when its surrounded by insulation. and that multiple sockets are generally connected to one circuit breaker/fuse.

the wall socket is generally the weakest link in the chain

1715 posts

Uber Geek

Trusted
Lifetime subscriber

  # 1384596 9-Sep-2015 19:44
Send private message

Jase2985: im pretty sure 2.5mm2 cable is rated for 16A when its surrounded by insulation. and that multiple sockets are generally connected to one circuit breaker/fuse.

the wall socket is generally the weakest link in the chain



Depends on the distance, 20A, up to 16 meters surrounded by thermal insulation




3 posts

Wannabe Geek


  # 1384960 10-Sep-2015 13:11
Send private message

If overloaded, will any of my appliances or sockets be burned or damaged?

 1 | 2
Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic



Twitter and LinkedIn »



Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

Facebook Portal to land in New Zealand
Posted 19-Sep-2019 18:35


Amazon Studios announces New Zealand as location for its upcoming series based on The Lord of the Rings
Posted 18-Sep-2019 17:24


The Warehouse chooses Elasticsearch service
Posted 18-Sep-2019 13:55


Voyager upgrades core network to 100Gbit
Posted 18-Sep-2019 13:52


Streaming service Acorn TV launches in New Zealand with selection with British shows
Posted 18-Sep-2019 08:55


Bitcoin.com announces partnership with smartphone manufacturer HTC
Posted 16-Sep-2019 21:30


Finalists Announced for Microsoft NZ Partner Awards
Posted 16-Sep-2019 19:37


OPPO Showcases New CameraX Capabilities at Google Developer Days China 2019
Posted 15-Sep-2019 12:42


New Zealand PC Market returns to growth
Posted 15-Sep-2019 12:24


Home sensor charity director speaks about the preventable death which drives her to push for healthy homes
Posted 11-Sep-2019 08:46


Te ao Maori Minecraft world set to inspire Kiwi students
Posted 11-Sep-2019 08:43


Research reveals The Power of Games in New Zealand
Posted 11-Sep-2019 08:40


Ring Door View Cam now available in New Zealand
Posted 11-Sep-2019 08:38


Vodafone NZ to create X Squad
Posted 10-Sep-2019 10:25


Huawei nova 5T to be available 20th September
Posted 5-Sep-2019 11:55



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.


Support Geekzone »

Our community of supporters help make Geekzone possible. Click the button below to join them.

Support Geezone on PressPatron



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.