  # 1385112 10-Sep-2015 17:26
Send private message

bijgd: If overloaded, will any of my appliances or sockets be burned or damaged?


Without good knowledge of what appliances you have and how you are using them, there is no way to be 100% sure.

With a bit of common sense and following manufactures instructions there should not be any problems

Hmm, what to write...
1046 posts

Uber Geek

Trusted
Subscriber

  # 1385120 10-Sep-2015 17:49
Send private message

gregmcc:
bijgd: If overloaded, will any of my appliances or sockets be burned or damaged?


Without good knowledge of what appliances you have and how you are using them, there is no way to be 100% sure.

With a bit of common sense and following manufactures instructions there should not be any problems


I believe the sockets are tested by the manufacturer to 45 Amps, so don't stress




Matthew


 
 
 
 


8894 posts

Uber Geek


  # 1385125 10-Sep-2015 18:17
Send private message

mdooher:
gregmcc:
bijgd: If overloaded, will any of my appliances or sockets be burned or damaged?


Without good knowledge of what appliances you have and how you are using them, there is no way to be 100% sure.

With a bit of common sense and following manufactures instructions there should not be any problems


I believe the sockets are tested by the manufacturer to 45 Amps, so don't stress


Old ones with damaged/weak contacts have been known to spit sparks and smoke - especially when connected to high load appliances.
If the plugs aren't fitting snug and/or there's any sight/sound/smell of something not right, get the socket replaced.

Some appliances might not like it if the breaker trips. I guess my printer wouldn't be too happy if power was cut when the heads were exposed - they'd dry out quite quickly.  It wouldn't be too good to go away for a week and find that the circuit your fridge/freezer was on had had tripped. Some electronic gizmos might not like intermittent supply from dodgy switches/plugs.

If a breaker keeps tripping, then check total loads on that circuit.  If there's not enough total to trip the breaker, then one of the appliances may be faulty - and potentially dangerous.

gzt

10978 posts

Uber Geek


  # 1385284 10-Sep-2015 22:22
Send private message

mdooher:
gregmcc:
bijgd: If overloaded, will any of my appliances or sockets be burned or damaged?


Without good knowledge of what appliances you have and how you are using them, there is no way to be 100% sure.

With a bit of common sense and following manufactures instructions there should not be any problems


I believe the sockets are tested by the manufacturer to 45 Amps, so don't stress

I am unsure if you have knowledge of a particular manufacturer or if you are referring to the test standard and test specification. I looked at as/nz 3122 2000 and the minimum test specification to meet the standard appeared to be far lower than what you suggest there.

Hmm, what to write...
1046 posts

Uber Geek

Trusted
Subscriber

  # 1385382 11-Sep-2015 08:50
Send private message

gzt:
mdooher:
gregmcc:
bijgd: If overloaded, will any of my appliances or sockets be burned or damaged?


Without good knowledge of what appliances you have and how you are using them, there is no way to be 100% sure.

With a bit of common sense and following manufactures instructions there should not be any problems


I believe the sockets are tested by the manufacturer to 45 Amps, so don't stress

I am unsure if you have knowledge of a particular manufacturer or if you are referring to the test standard and test specification. I looked at as/nz 3122 2000 and the minimum test specification to meet the standard appeared to be far lower than what you suggest there.

Clipsal do, So I assume Schneider do as well...as for HPM, who cares it's junk surprised




Matthew


1140 posts

Uber Geek


  # 1385394 11-Sep-2015 09:09
Send private message

Surprised nobody has asked, How old is the house? Whilst there's alot of talk about the socket and it's rating it doesn't matter for jack if someone's just replaced old sockets with new ones ontop of old wiring or stupid wiring, If some idiots run 1.5mm TPS then thats only rated for 16a IIRC, You need 2.5mm for 20a.

The best bet is to get a Sparky out to pop the socket off and check the wire if there is any doubt. Clearly if the house if 2 years old with a COF for the electrical then dont worry - you should be ok but if in doubt have someone inspect




Most problems are the result of previous solutions...

All comment's I make are my own personal opinion and do not in any way, shape or form reflect the views of current or former employers unless specifically stated 

430 posts

Ultimate Geek

Subscriber

  # 1385692 11-Sep-2015 14:08
Send private message

Just catching up on this discussion:

10A socket outlets in NZ are designed to NZS 3112.  The thermal test (overload) requires them to be tested at 11A.  For twin or multi-outlets the test is through ONE socket only, with the others under no load.  So a 4-way 10A socket outlet is tested at 11A, not 44A. However the heating in a socket outlet usually occurs at the contact points on the pins where the maximum current is 10A.

The switches on socket outlets come under NZS 3113.  A switch controlling one socket has to be thermally tested at 10A.  It also has to be tested for motor starting duty at 40A, but that test is for a brief turn-on of 2 seconds every minute, which is not an overload test.  If the switch serves more than one socket (which I have never seen) it has to be rated and tested at the combined rated load of the sockets (or of the protective device if there is one, as in a power strip).

Manufacturers may test at higher currents than these, but who knows.

Of course there's always an upstream breaker or fuse protecting the circuit wiring.  My guess is that the common conductors and wiring terminations within most multiple socket outlets would be capable of handling the full rated current of the circuit protection without too much problem, but they don't have to do that.





McLean


 
 
 
 


1530 posts

Uber Geek


  # 1385903 11-Sep-2015 20:03
Send private message

In the real world you can run a lot more than 10A through a socket. Currently in the tropics in the Pacific, 230v supply, NZ/aus socket with 4.4kw rated instant shower heater plugged in. The landlord supplied 1.5mm extension cord used to get soft insulation by the end of the shower, so I judiciously upgraded to a 2.5mm flex I made up. Ideally would be 4mm cable but you gotta roll with the punches when you are in the wild sometimes. The house wiring will be 2.5mm anyway. It is just noticeably warm to touch at the end of a 10/15 min shower now.

I am not an electrician

1 | 2 
Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic



Twitter and LinkedIn »



Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

Samsung Galaxy Fold now available in New Zealand
Posted 6-Dec-2019 00:01


NZ company oDocs awarded US$ 100,000 Dubai World Expo grant
Posted 5-Dec-2019 16:00


New Zealand Rugby Selects AWS-Powered Analytics for Deeper Game Insights
Posted 5-Dec-2019 11:33


IMAGR and Farro bring checkout-less supermarket shopping to New Zealand
Posted 5-Dec-2019 09:07


Wellington Airport becomes first 5G connected airport in the country
Posted 3-Dec-2019 08:42


MetService secures Al Jazeera as a new weather client
Posted 28-Nov-2019 09:40


NZ a top 10 connected nation with stage one of ultra-fast broadband roll-out completed
Posted 24-Nov-2019 14:15


Microsoft Translator understands te reo Māori
Posted 22-Nov-2019 08:46


Chorus to launch Hyperfibre service
Posted 18-Nov-2019 15:00


Microsoft launches first Experience Center worldwide for Asia Pacific in Singapore
Posted 13-Nov-2019 13:08


Disney+ comes to LG Smart TVs
Posted 13-Nov-2019 12:55


Spark launches new wireless broadband "Unplan Metro"
Posted 11-Nov-2019 08:19


Malwarebytes overhauls flagship product with new UI, faster engine and lighter footprint
Posted 6-Nov-2019 11:48


CarbonClick launches into Digital Marketplaces
Posted 6-Nov-2019 11:42


Kordia offers Microsoft Azure Peering Service
Posted 6-Nov-2019 11:41



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.


Support Geekzone »

Our community of supporters help make Geekzone possible. Click the button below to join them.

Support Geezone on PressPatron



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.