  Reply # 1396545 29-Sep-2015 12:21
Send private message

re. HWC - no, my understanding is typically those air-to-water heat pumps are not designed to run very hot - mine only heats up the water to about 35 degrees. This isn't enough to heat the HWC without a big heat exchanger. Although I have heard of systems that advertise this feature - just not convinced how effective it would be. Added to that, I installed solar evacuated tubes which handle my HWC, along with nighly electric boosting when required. 

re. Garage - no pipes run to the garage, but I ensure I insulated between the garage slab and the house (attached garage) to try and stop heat seepage.



96 posts

Master Geek
+1 received by user: 3


  Reply # 1396582 29-Sep-2015 13:19
Send private message

Happy to answer any questions, I installed my underfloor system myself and just got a plummer to hook up the heat pump. 


My old man's a plumber so I was wondering if I this was an option. Do you know what this roughly worked out cost wise? Most quotes I've had to get it installed are around 25K.

 
 
 
 


1477 posts

Uber Geek
+1 received by user: 154

Subscriber

  Reply # 1396586 29-Sep-2015 13:24
Send private message

I got a decent NZ-made heat pump from Hot Water Heat Pumps which cost $7-8K (in 2011), then the pipes and manifold were pretty cheap - I think a couple of hundred $ per 100m length of pipe (one length per zone). The manifold was under a grand - I would go for quality tho - I went cheap and spend my life worrying I am going to wake up with an inch of water inside!

From memory my entire system cost about 12K all up - not including my time to run the pipes pre-pour.

3725 posts

Uber Geek
+1 received by user: 203

Trusted

  Reply # 1396595 29-Sep-2015 13:33
Send private message

I have had 2 quotes come back to me recently for UFH. One from Leap and other from John Guest. It's a 450 square meter double storey house. Leap is $30,500 and John Guest is $24,000 for both floors. I am still going through the fine details of both but JG looks good considering it's sold overseas as well. Price is for a Bosch 18kW gas boiler unit though as heat source. Heat Pump + small buffer tank is extra $5k + GST




Do whatever you want to do man.

  

1477 posts

Uber Geek
+1 received by user: 154

Subscriber

  Reply # 1396601 29-Sep-2015 13:39
Send private message

FYI - this is the heatpump I have (http://www.waterheating.co.nz/Products/Residential/Underfloor+Heating/7GUb9-1/). It is 9kW and has an onboard circulating pump and buffer tank which means you just hook the flow/return pipes to your underfloor manifold and turn it on. My house is 260sqm, two story (including a 48sqm garage which I don't heat). The ground floor foot print is about 150sqm (excl. garage) and this 9kW unit works great - remembering I only run it from 9pm till 7am. In the middle of winter it runs full time during that period, but for example at the moment it turns on at 9pm and usually flicks off again about 2-3am.

2721 posts

Uber Geek
+1 received by user: 967


  Reply # 1396602 29-Sep-2015 13:39
Send private message

Have you considered a ground to water heat pump? 

Efficient and the capital outlay maybe justified by the longer heating season in Dunedin.




Mike

1477 posts

Uber Geek
+1 received by user: 154

Subscriber

  Reply # 1396606 29-Sep-2015 13:41
Send private message

Yep - geothermal is ideal if you have the capital up front, and the land area to install it. Wish I could have done this, looked at it seriously but it was prohibitively expensive and I just didn't have the room on my site.

3725 posts

Uber Geek
+1 received by user: 203

Trusted

  Reply # 1396607 29-Sep-2015 13:41
Send private message

SumnerBoy: FYI - this is the heatpump I have (http://www.waterheating.co.nz/Products/Residential/Underfloor+Heating/7GUb9-1/). It is 9kW and has an onboard circulating pump and buffer tank which means you just hook the flow/return pipes to your underfloor manifold and turn it on. My house is 260sqm, two story (including a 48sqm garage which I don't heat). The ground floor foot print is about 150sqm (excl. garage) and this 9kW unit works great - remembering I only run it from 9pm till 7am. In the middle of winter it runs full time during that period, but for example at the moment it turns on at 9pm and usually flicks off again about 2-3am.


Do you have UFH on the first floor of your house? If so, does it works well and if not, does first floor still stays warm from rising heat from ground floor?




Do whatever you want to do man.

  

1477 posts

Uber Geek
+1 received by user: 154

Subscriber

  Reply # 1396612 29-Sep-2015 13:46
Send private message

No UFH on the first floor. We only have two bedrooms up there and they typically sit at a couple of degrees below the ground floor. So between 18-20 degrees. Again, insulation is the biggest factor, if you can trap as much of that warm air inside it should retain the heat pretty well. If I had a living area upstairs I might have needed some secondary heating tho. But in the 4 yrs we have been living here there has never been a heater plugged in upstairs.



96 posts

Master Geek
+1 received by user: 3


  Reply # 1396614 29-Sep-2015 13:53
Send private message

MikeAqua: Have you considered a ground to water heat pump? 

Efficient and the capital outlay maybe justified by the longer heating season in Dunedin.


I'd love to go geothermal but we don't have the land area on site



96 posts

Master Geek
+1 received by user: 3


  Reply # 1396617 29-Sep-2015 14:01
Send private message

SumnerBoy: FYI - this is the heatpump I have (http://www.waterheating.co.nz/Products/Residential/Underfloor+Heating/7GUb9-1/). It is 9kW and has an onboard circulating pump and buffer tank which means you just hook the flow/return pipes to your underfloor manifold and turn it on. My house is 260sqm, two story (including a 48sqm garage which I don't heat). The ground floor foot print is about 150sqm (excl. garage) and this 9kW unit works great - remembering I only run it from 9pm till 7am. In the middle of winter it runs full time during that period, but for example at the moment it turns on at 9pm and usually flicks off again about 2-3am.


Cool, thanks that's really good to know. We're looking at heating ~170sqm, I might give those guys a call

fwiw here's the layout - 

917 posts

Ultimate Geek
+1 received by user: 38


  Reply # 1396852 29-Sep-2015 21:07
Send private message

The New Zealand building code has weak insulation and window performance requirements so a standard build can be costly to centrally heat. A build in the same climate overseas may have over double the insulation.

 

 

The concrete slab should have a thermal break and perimeter insulation along the edge. 80% of concrete heat loss is from the edge.

 


 

Windows and doors should be thermally broken if they're aluminium. The standard R2.2 and R3.2 insulation in the walls and ceiling is too low but it's normal for over 50% of heat loss in a new house to be through the windows because of poor quality products an excessive glass area.

 

 

Many people have had problems with ducted heat pumps because they are difficult to install and as so few are installed in New Zealand the installers may not know what they're doing.

 

 

Many underfloor hydronic systems in New Zealand have been installed directly into the concrete slab so the slab itself must be heated. There are systems where you can have the pipes installed over the slab inside a plastic interlayer that goes over the concrete and under the floor. As that isn't directly heating the concrete it may be more responsive. Central heating can be set up to have different parts of the house as separate zones.

 

 

 

The Hot Water Heat Pumps company does a range that can supply hot water for both central heating and general usage. The Daikin Altherma can be set up to provide the house's hot water and summer cooling too. The Altherma is probably more efficient but it should have a higher price tag.

 

 

Dunedin doesn't have very cold temperatures but they won't work as efficiently at 0 degrees as at 7.

 

 

Hydronic heat pumps can be set up to work with radiator central heating too if you don't want underfloor heating. Underfloor provides the most even heating as heat rises.

 

 

Ground source heat pumps are more suitable in places with geothermally warmed earth or large seasonal differences. As the underground temperature stays stable across the year it allows a heat pump to work well when the air is too cold for air source heat pumps to work efficiently. They may make sense in places like parts of Central Otago and Rotorua but I doubt the economics add up for them in any coastal area.

 

 


1625 posts

Uber Geek
+1 received by user: 493

Subscriber

  Reply # 1398356 2-Oct-2015 00:32
Send private message

According to the tech specs page on the Altherma site it has a 3kW electric bosser element fitted. Also it doesn't quote what water temps have been used when calculating the COP. As all you need to do when testing is to leave a hot tap running full bore so that the unit can't build up any temp in it's cylinder. This means that the incoming water temp to the condenser/heat exchanger is only around 15deg So good COP is easy. Now try feeding in 50deg water and have the altherma heat to 55deg Very much doubt it will still get it's claimed COP. (this situation will happen whenever the cylinder just needs "topping up"). And since the max temp it can produce is 55. (which it says on the specs page) The electric element will be needed to get to 60deg for legionella control.

So I doubt that a hot water heatpump used to supply domestic hot water would work well enough where you are. Especially as you can just get a big electric cylinder and heat it using night rate power. Any efficiency savings will be lost from having to pay daytime power rates to run a domestic hot water heatpump during the day. As lower temps at night mean lower efficiency.

A hot water heatpump for just underfloor should be fine though. But still check those lines company policies.







96 posts

Master Geek
+1 received by user: 3


  Reply # 1398391 2-Oct-2015 01:34
Send private message

Also the quotes I've had so far put the hot water heating option at around $4.5K including the cylinder. I'm thinking I'll just go gas powered water, instant on demand hot water.

1477 posts

Uber Geek
+1 received by user: 154

Subscriber

  Reply # 1398447 2-Oct-2015 08:38
Send private message

Interesting point about running the underfloor heat pump during the day/night and how it would affect COP. My theory has always been to run it only from 9pm - 7am, and thus take advantage of the cheap night rates (almost 1/3 of day rates). My assumption is that that is a far better return than the improvement in COP by running it during the day. Depending on where you are of course, but in ChCh we probably only have a month of so of regular below-zero nights, so generally speaking the unit is hopefully not having to work in freezing conditions too often.

This is all un-quantified however!

1 | 2 
View this topic in a long page with up to 500 replies per page Create new topic



Twitter »

Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

Nothing nebulous about Microsoft’s cloud-transition
Posted 21-Jul-2017 15:34


We’re spending more on tech, but not as much as Australians
Posted 21-Jul-2017 11:43


Endace announces EndaceFabric for network-wide packet recording
Posted 20-Jul-2017 20:49


Acorn 6: MacOS image editing for the rest of us
Posted 20-Jul-2017 17:04


HTC faces backlash over keyboard pop-up ads
Posted 19-Jul-2017 15:53


BNZ adds Visa credit cards to Android Pay wallet
Posted 18-Jul-2017 19:44


Still living in a Notification hell – Om Malik
Posted 18-Jul-2017 13:00


Duet Display uses iPad to extend Mac, PC
Posted 18-Jul-2017 10:58


PC sales could be worse
Posted 17-Jul-2017 07:34


Crypto-currencies, tulips, market bubbles
Posted 17-Jul-2017 06:38


NZ Tech Podcast: Big batteries, solar cars, cold war, IoT
Posted 16-Jul-2017 16:53


Vodafone Australia mulls Wisp alliance, NZ implications
Posted 13-Jul-2017 16:49


Rural health professionals see fibre pay-off
Posted 13-Jul-2017 11:52


Vodafone announces expansion of $5 Daily Roaming
Posted 13-Jul-2017 10:20


Intel unveils powerful Intel Xeon Scalable processors
Posted 12-Jul-2017 20:41



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.