Topic # 191992 23-Feb-2016 12:59
Send private message

Hi there, looking to put an induction cooktop in, it is 30A 7.2KW. How much would i be looking for to redo the fuse etc?
The cable that is currently attached is the white TPS with markings of 600/1000v, it's pretty thick. Will this wire need replacing as well as the circuit breaker or just the CB?
I've heard people saying that you can just connect it to a 20A and ensure you don't use all elements at full power, doesn't sound right but understand it. Would like to do it the right way though.

Filter this topic showing only the reply marked as answer Create new topic
4314 posts

Uber Geek
+1 received by user: 2312

Trusted

  Reply # 1497811 23-Feb-2016 13:07
3 people support this post
Send private message

A qualified sparky is your best bet.




566 posts

Ultimate Geek
+1 received by user: 82

Trusted

  Reply # 1497813 23-Feb-2016 13:08
Send private message

DarthKermit:

A qualified sparky is your best bet.



I know there are a couple on here which will give me an idea before wasting a sparky's time with questions over the phone or coming to the house etc.

270 posts

Ultimate Geek
+1 received by user: 37

Trusted

  Reply # 1497835 23-Feb-2016 13:53
Send private message

Yes, unless you can verify the cable size and that this corresponds to being suitable for the 32A MCB (a 6mm2 is normally sufficient, but length of cable run also needs to be factored in to the calculation), you may need to replace both the cable and MCB.

 

As this involves permanent wiring, and wiring inside the distribution board, you will need a sparky to carry out the work.





Michael Skyrme - Instrumentation & Controls

Glurp
7595 posts

Uber Geek
+1 received by user: 3549

Subscriber

  Reply # 1497838 23-Feb-2016 13:57
Send private message

I'm sure this is terribly wrong for all kinds of reasons, but you could just connect two 20-amp circuits in parallel. Or not?

 

 

 

Mod (N8) edit: DO NOT TRY THE ABOVE.

 

 





I reject your reality and substitute my own. - Adam Savage
 


1572 posts

Uber Geek
+1 received by user: 311

Lifetime subscriber

  Reply # 1497852 23-Feb-2016 14:12
6 people support this post
Send private message

Rikkitic:

 

I'm sure this is terribly wrong for all kinds of reasons, but you could just connect two 20-amp circuits in parallel. Or not?

 

 

 

 

 

 

**DANGER*          *DO NOT TRY THE ABOVE ADVICE**

 

 

 

2 x 20A circuits run in parallel does not equal 40A, it's way more and will lead to all kinds of other problems.

 

 

 

Get suitable advice from an electrician, cable size, cable length, loading and maximum demand all have a bearing on what can and can't be done, none of which can be figured out without a site visit.

 

 




566 posts

Ultimate Geek
+1 received by user: 82

Trusted

  Reply # 1497863 23-Feb-2016 14:34
Send private message

gregmcc:

Rikkitic:


I'm sure this is terribly wrong for all kinds of reasons, but you could just connect two 20-amp circuits in parallel. Or not?


 



 


**DANGER*          *DO NOT TRY THE ABOVE ADVICE**


 


2 x 20A circuits run in parallel does not equal 40A, it's way more and will lead to all kinds of other problems.


 


Get suitable advice from an electrician, cable size, cable length, loading and maximum demand all have a bearing on what can and can't be done, none of which can be figured out without a site visit.


 



Cheers for that, will give someone a ring. Will i be charged for them to come out and do a quote on what has to be done?

7678 posts

Uber Geek
+1 received by user: 2527

Subscriber

  Reply # 1497865 23-Feb-2016 14:38
Send private message

depends on the company, some will some wont, ask on the phone its free :)


404 posts

Ultimate Geek
+1 received by user: 119


  Reply # 1497873 23-Feb-2016 14:46
4 people support this post
Send private message

Rikkitic:

 

I'm sure this is terribly wrong for all kinds of reasons, but you could just connect two 20-amp circuits in parallel. Or not?

 

 

 

 

 

 

Sweet Baby Jeebus, this one needs to be removed from the thread before someone takes it on board....

 

Depending on the age of your house, you may need the wiring replaced if its under the required diameter for your house. As others have said above.

 

Its a safety thing ensuring you don't die or burn your house down, get it done right first time

 

 




566 posts

Ultimate Geek
+1 received by user: 82

Trusted

  Reply # 1497921 23-Feb-2016 16:00
Send private message

I reckon its about 10 meters at the most to the board. house built in 2003.

Here are some pics

Click to see full size

Click to see full size


7678 posts

Uber Geek
+1 received by user: 2527

Subscriber

  Reply # 1497928 23-Feb-2016 16:16
4 people support this post
Send private message

get an electrician


1572 posts

Uber Geek
+1 received by user: 311

Lifetime subscriber

  Reply # 1497964 23-Feb-2016 17:05
Send private message

Fabian: I reckon its about 10 meters at the most to the board. house built in 2003.

Here are some pics

Click to see full size

Click to see full size

 

 

 

the other side of the cable has the size and type rating on it. Hard to tell from that picture the size, but get an electrician

 

 


168 posts

Master Geek
+1 received by user: 24


  Reply # 1497965 23-Feb-2016 17:06
Send private message

Gencalc tells me that a 4mm2 TPS is good for 30A over 10 metres so you may be okay with the wiring you have as most stoves run in at least 4mm2 cable.

 

But you must get an electrician to check the wiring, circuit breaker and to connect it. You don't want to burn you house down!


214 posts

Master Geek
+1 received by user: 9


  Reply # 1505275 2-Mar-2016 23:08
Send private message

You can connect the cooktop to the wall providing you know how to. But you cannot replace a MCB on the panel , that is the law. So no matter what you need a sparky. 


Filter this topic showing only the reply marked as answer Create new topic

Twitter »

Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

Hawaiki Transpacific cable ready-for-service
Posted 20-Jul-2018 11:29


Microsoft Dynamics 365 Business Central launches
Posted 10-Jul-2018 10:40


Spark completes first milestone in voice platform upgrade
Posted 10-Jul-2018 09:36


Microsoft ices heated developers
Posted 6-Jul-2018 20:16


PB Technologies charged for its extended warranties and warned for bait advertising
Posted 3-Jul-2018 15:45


Almost 20,000 people claim credits from Spark
Posted 29-Jun-2018 10:40


Cove sells NZ's first insurance policy via chatbot
Posted 25-Jun-2018 10:04


N4L helping TAKA Trust bridge the digital divide for Lower Hutt students
Posted 18-Jun-2018 13:08


Winners Announced for 2018 CIO Awards
Posted 18-Jun-2018 13:03


Logitech Rally sets new standard for USB-connected video conference cameras
Posted 18-Jun-2018 09:27


Russell Stanners steps down as Vodafone NZ CEO
Posted 12-Jun-2018 09:13


Intergen recognised as 2018 Microsoft Country Partner of the Year for New Zealand
Posted 12-Jun-2018 08:00


Finalists Announced For Microsoft NZ Partner Awards
Posted 6-Jun-2018 15:12


Vocus Group and Vodafone announce joint venture to accelerate fibre innovation
Posted 5-Jun-2018 10:52


Kogan.com to launch Kogan Mobile in New Zealand
Posted 4-Jun-2018 14:34



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.