  Reply # 1813100 5-Jul-2017 10:31
Send private message

Axeman480:

 

These guys here made up our last wetback for our old fire .  http://www.superiorheating.co.nz/wetbacks.php    

 

 

 

 

That's who I bought wetbacks off when i lived in Blenheim.  Good guys.  Helped me figure out how to get two wetbacks on one fire.





Mike



16 posts

Geek


  Reply # 1813104 5-Jul-2017 10:38
Send private message

Thank you so much for all your replies. Firstly I can't see where the wetback booster is installed. Looks like it is in the back of the woodburner. BUT the weirdest thing has happened. I lit the fire last night with mains water off. Once it got hot the pipes made massive noises and the copper pipe that takes the hot water to the ? became so hot I was scared of a house fire, so ended up turning the mains water back on to be safe. Opened the woodburner door this  morning expecting the burner to be full of water - it was dry!!! No leak over night so I am now more clueless as to what has happened. I haven't cancelled the plumber as I really need his advice as to what to do? Try and remove the booster, leave it alone till it leaks again, or plug it anyway? 

 

I have been through all the paper work here and have not kept the details of the burner other than the receipt so have no clue what it looks like.


 
 
 
 


Try Wrike: fast, easy, and efficient project collaboration software


16 posts

Geek


  Reply # 1813107 5-Jul-2017 10:40
Send private message

Thanks for that link Axeman480, I will email them and see if they can help.


630 posts

Ultimate Geek
+1 received by user: 250

Subscriber

  Reply # 1813132 5-Jul-2017 11:32
Send private message

Didn't keep any pics of those repairs, but here are a couple pics that might help. These are the mid 80's to early 90's type (similar to the extant rural woodfire) 
Later models are listed here: http://www.kent.co.nz/technical

 

The 1st is one of ours installed (& burning) today. The 90° brass fittings are screwed onto the wetback threaded ends that extend out the back of the fire.
You can't see the attachment flanges as they are under the rear sheetmetal.

 

The 2nd shows the neighbour's Kent fire (I'm rewelding his firebox) with the cover and wetback removed - you can see where it mounts.

 

 




16 posts

Geek


  Reply # 1813142 5-Jul-2017 11:55
Send private message

 

This shows mine, sorry can't get any clearer than this. The closest pip is the cold in, the other is the hot out.


2930 posts

Uber Geek
+1 received by user: 676


  Reply # 1813145 5-Jul-2017 11:59
Send private message

jancor:

 

Thank you so much for all your replies. Firstly I can't see where the wetback booster is installed. Looks like it is in the back of the woodburner. BUT the weirdest thing has happened. I lit the fire last night with mains water off. Once it got hot the pipes made massive noises and the copper pipe that takes the hot water to the ? became so hot I was scared of a house fire, so ended up turning the mains water back on to be safe. Opened the woodburner door this  morning expecting the burner to be full of water - it was dry!!! No leak over night so I am now more clueless as to what has happened. I haven't cancelled the plumber as I really need his advice as to what to do? Try and remove the booster, leave it alone till it leaks again, or plug it anyway? 

 

 

It is likely that by removing the water flow, you have allowed the wet back to get hot enough to reflow some of the welds/solder joints that may have been the source of the leak,

 

However there is no guarantee that next time you stoke up a fire that the newly sealed leaks will not open up again

 

They might stay sealed for sometime or they might not, or new holes might continue to develop.

 

For a long term fix you will have to replace the wetback unit,




16 posts

Geek


  Reply # 1813150 5-Jul-2017 12:20
Send private message

wellygary:

 

jancor:

 

Thank you so much for all your replies. Firstly I can't see where the wetback booster is installed. Looks like it is in the back of the woodburner. BUT the weirdest thing has happened. I lit the fire last night with mains water off. Once it got hot the pipes made massive noises and the copper pipe that takes the hot water to the ? became so hot I was scared of a house fire, so ended up turning the mains water back on to be safe. Opened the woodburner door this  morning expecting the burner to be full of water - it was dry!!! No leak over night so I am now more clueless as to what has happened. I haven't cancelled the plumber as I really need his advice as to what to do? Try and remove the booster, leave it alone till it leaks again, or plug it anyway? 

 

 

It is likely that by removing the water flow, you have allowed the wet back to get hot enough to reflow some of the welds/solder joints that may have been the source of the leak,

 

However there is no guarantee that next time you stoke up a fire that the newly sealed leaks will not open up again

 

They might stay sealed for sometime or they might not, or new holes might continue to develop.

 

For a long term fix you will have to replace the wetback unit,

 

Yes I agree that it a guess how long it will last. I think I will see what the plumber suggests, but personally I think I will get it plugged as soon as it leaks again, then save up for a replacement. That link (above) have replied and can supply a new one. I just have to send them mine so they can match it. Sounds like a great job for the Summer. 


2352 posts

Uber Geek
+1 received by user: 255


  Reply # 1813195 5-Jul-2017 13:45
Send private message

If the fire needs replacing and you are in an Urban/clean air zone there are limits on which fires can still have wetbacks.

Before putting too much money into a wetback that might last longer than your fire you should check that you'll get some use out of it. Maybe look at approved wetback fires for your area.



16 posts

Geek


  Reply # 1813210 5-Jul-2017 13:54
Send private message

Thanks, it isn't a problem where I live. I have decided to just plug up the pipes and think about long term decision in the Summer. Will miss the constant hot water but this is the best solution for now.


2510 posts

Uber Geek
+1 received by user: 903

Subscriber

  Reply # 1813496 5-Jul-2017 23:39
Send private message

jancor:

 

Thank you so much for all your replies. Firstly I can't see where the wetback booster is installed. Looks like it is in the back of the woodburner. BUT the weirdest thing has happened. I lit the fire last night with mains water off. Once it got hot the pipes made massive noises and the copper pipe that takes the hot water to the ? became so hot I was scared of a house fire, so ended up turning the mains water back on to be safe. Opened the woodburner door this  morning expecting the burner to be full of water - it was dry!!! No leak over night so I am now more clueless as to what has happened. I haven't cancelled the plumber as I really need his advice as to what to do? Try and remove the booster, leave it alone till it leaks again, or plug it anyway? 

 

I have been through all the paper work here and have not kept the details of the burner other than the receipt so have no clue what it looks like.

 

 

Those massive noises would have been steam bubbles forming and collapsing again. Are you sure that your cylinder didn't drain out somewhere while the water was turned off? How much water went through the water meter when you turned the water back on? I take it that your wetback is a normal direct circulating low pressure hot water type? Or do you have mains pressure hot water?






6 posts

Wannabe Geek
+1 received by user: 1


  Reply # 1813522 6-Jul-2017 06:27
Send private message

This is interesting, I always thought thermosyphon couldn't run downhill but looking at the wetback pipes I am obviously wrong. Is it just the cold that run down and up again?

630 posts

Ultimate Geek
+1 received by user: 250

Subscriber

  Reply # 1813529 6-Jul-2017 07:15
Send private message

MrAmerica: This is interesting, I always thought thermosyphon couldn't run downhill but looking at the wetback pipes I am obviously wrong. Is it just the cold that run down and up again?

 

The cold feed comes up the lower pipe from the floor, goes into one side of the heat exchanger.
Heated water comes out the other side, rises up the other pipe.

 

I tested with a flowmeter and was surprised how well it works.




16 posts

Geek


  Reply # 1813586 6-Jul-2017 09:56
Send private message

No,the cylinder didn't drain. The cylinder is the original cylinder 1988, so not a new fancy one. Second night of a fire last night without a leak!! 


16507 posts

Uber Geek
+1 received by user: 4608

Trusted
Lifetime subscriber

  Reply # 1813599 6-Jul-2017 10:02
One person supports this post
Send private message

Your story worries me, I half expected to see a story about a house burning down in the news today. I really think you need to get someone reputable and knowledgeable in and follow their advice. Pretty sure my insurance says stuff like "if repairs and maintenance are required, and aren't carried out in a timely fashion, by suitably qualified people, and your house burns to the ground, we won't pay out". 

 

 

 

I am not saying the advice here you have been given isn't correct, but these are people who have not seen your particular problem in person, and have no stake in your house not burning to the ground. 1 Small omitted detail could be disastrous.

 

 




16 posts

Geek


  Reply # 1813604 6-Jul-2017 10:15
Send private message

Plumber is here now to rectify the problem. No worries of the house burning down as I turned the water back  on. It's an old set up and very basic. I appreciate all the replies here, they helped very much.


1 | 2 
Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic



Twitter »

Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

Amazon launches the International Shopping Experience in the Amazon Shopping App
Posted 19-Apr-2018 08:38


Spark New Zealand and TVNZ to bring coverage of Rugby World Cup 2019
Posted 16-Apr-2018 06:55


How Google can seize Microsoft Office crown
Posted 14-Apr-2018 11:08


How back office transformation drives IRD efficiency
Posted 12-Apr-2018 21:15


iPod laws in a smartphone world: will we ever get copyright right?
Posted 12-Apr-2018 21:13


Lightbox service using big data and analytics to learn more about customers
Posted 9-Apr-2018 12:11


111 mobile caller location extended to iOS
Posted 6-Apr-2018 13:50


Huawei announces the HUAWEI P20 series
Posted 29-Mar-2018 11:41


Symantec Internet Security Threat Report shows increased endpoint technology risks
Posted 26-Mar-2018 18:29


Spark switches on long-range IoT network across New Zealand
Posted 26-Mar-2018 18:22


Stuff Pix enters streaming video market
Posted 21-Mar-2018 09:18


Windows no longer Microsoft’s main focus
Posted 13-Mar-2018 07:47


Why phone makers are obsessed with cameras
Posted 11-Mar-2018 12:25


New Zealand Adopts International Open Data Charter
Posted 3-Mar-2018 12:48