Topic # 230250 14-Feb-2018 18:59
Send private message

I've spent the last 5 days living with and searching for a buzzing noise in my house. Every 7-15 minutes it would vibrate loudly for 4 seconds, with the time getting shorter each buzz.

 

Tonight we turned the power off and discovered its coming from the condensation pump in the ceiling, for our on wall heat pump. 

 

 

 

Can anyone tell me how these work? We had the heat pumps disconnected and reconnected at the end of last year for some drainage work. We have only used them once since then on air conditioning mode. 

 

The heat pumps are turned off now until we can get someone to look at the pump. 

 

 

 

 


Create new topic
21286 posts

Uber Geek
+1 received by user: 4290

Trusted
Subscriber

  Reply # 1958257 14-Feb-2018 19:01
Send private message

Well the ones at work do that to pump the condensation out. Is it actually pumping out ok?





Richard rich.ms



245 posts

Master Geek
+1 received by user: 18


  Reply # 1958262 14-Feb-2018 19:11
Send private message

Is it a normal noise? 

 

We have only used the air conditioning once (about 2 weeks ago) in the 5 years we have had it, have never heard the pump noise at all. 

 

I would have thought any condensation would be gone by now


21286 posts

Uber Geek
+1 received by user: 4290

Trusted
Subscriber

  Reply # 1958265 14-Feb-2018 19:13
Send private message

condensation is a non stop thing when cooling, the pipe from my bedroom one is about 3-4 seconds per drip even when its been on for a month. The work ones that drain into a sink are about a cupfull every hour in this humidity.





Richard rich.ms

4960 posts

Uber Geek
+1 received by user: 1573


  Reply # 1958269 14-Feb-2018 19:15
Send private message

When in cooling mode, condensation forms on the inside unit - depending on the installation, sometimes it can drain away by gravity, sometimes it requires a pump. It's perfectly normal for the pump to run for a few seconds periodically to clear the built up condensation.

 

It shouldn't be unduly noisy though.


4960 posts

Uber Geek
+1 received by user: 1573


  Reply # 1958272 14-Feb-2018 19:17
Send private message

esawers:

 

I would have thought any condensation would be gone by now

 

 

What do you mean gone by now? If the unit is running in cooling mode, it will be generating condensation almost continuously. The higher the humidity, the more it will generate.




245 posts

Master Geek
+1 received by user: 18


  Reply # 1958273 14-Feb-2018 19:17
Send private message

Should it still be running every 15 minutes when the heat pump has been off for 2 weeks? 

 

Edit: Should have said, we only used it once overnight, 2 weeks ago. I have now powered them off on the outside switch to stop the pump noise. 


4960 posts

Uber Geek
+1 received by user: 1573


  Reply # 1958274 14-Feb-2018 19:20
Send private message

esawers:

 

Should it still be running every 15 minutes when the heat pump has been off for 2 weeks? 

 

 

 

 

Yes. Possibly more often.

 

It's not running because it was switched off, it's running because it's switched on.


21286 posts

Uber Geek
+1 received by user: 4290

Trusted
Subscriber

  Reply # 1958276 14-Feb-2018 19:21
One person supports this post
Send private message

If the pumps not in properly, it might be pumping up into a pipe, and then it draining back down into it slowly till it gets high enough to trigger it again. Quite unusual to have pumps on home ones tho since the cheap back to back install most people go for will usually let it just go out the wall and down with the exposed piping to ground level.





Richard rich.ms

4960 posts

Uber Geek
+1 received by user: 1573


  Reply # 1958283 14-Feb-2018 19:28
Send private message

esawers:

 

Edit: Should have said, we only used it once overnight, 2 weeks ago. I have now powered them off on the outside switch to stop the pump noise. 

 

 

That's kind of like disconnecting the battery in your car because every time you drive it, you hear the engine running!

 

It's supposed to pump. It will always do it on cooling mode, and it will do it more as the humidity rises, or you turn the interior temp down. As @richms says, the only ones that won't do it are when you can get a gravity drain where it doesn't need to push uphill for any section of the pipework - a simple back to back home installation is often like this.




245 posts

Master Geek
+1 received by user: 18


  Reply # 1958287 14-Feb-2018 19:36
Send private message

I'm thinking the pump hasn't been connected properly when they reinstalled it. 

 

I understand it would pump the condensation away when its in cooling mode, and possibly for a day or two after? 

 

But not when they have been turned off for 2 weeks... ?

 

The house is vibrating every 7 minutes 24 hours a day


2895 posts

Uber Geek
+1 received by user: 1096

Subscriber

  Reply # 1958372 15-Feb-2018 00:54
2 people support this post
Send private message

richms:

If the pumps not in properly, it might be pumping up into a pipe, and then it draining back down into it slowly till it gets high enough to trigger it again. Quite unusual to have pumps on home ones tho since the cheap back to back install most people go for will usually let it just go out the wall and down with the exposed piping to ground level.




This will be the problem. Failed check valve in the pump. Water in the outlet pipe leaks back into the pump reservoir until the water level switch gets triggered. Pump runs to drain reservoir, water leaks back and the cycle repeats.





4960 posts

Uber Geek
+1 received by user: 1573


  Reply # 1958643 15-Feb-2018 15:27
Send private message

esawers:

 

I understand it would pump the condensation away when its in cooling mode, and possibly for a day or two after? 

 

But not when they have been turned off for 2 weeks... ?

 

 

Ahh, sorry, I didn't realise it was doing it with the unit switched off! It could certainly run for may 30 mins, but not more than that. Def a fault.


Create new topic

Twitter »

Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

The Warehouse leaps into the AI future with Google
Posted 15-Aug-2018 17:56


Targus set sights on enterprise and consumer growth in New Zealand
Posted 13-Aug-2018 13:47


Huawei to distribute nova 3i in New Zealand
Posted 9-Aug-2018 16:23


Home robot Vector to be available in New Zealand stores
Posted 9-Aug-2018 14:47


Panasonic announces new 2018 OLED TV line up
Posted 7-Aug-2018 16:38


Kordia completes first live 4K TV broadcast
Posted 1-Aug-2018 13:00


Schools get safer and smarter internet with Managed Network Upgrade
Posted 30-Jul-2018 20:01


DNC wants a safer .nz in the coming year
Posted 26-Jul-2018 16:08


Auldhouse becomes an AWS Authorised Training Delivery Partner in New Zealand
Posted 26-Jul-2018 15:55


Rakuten Kobo launches Kobo Clara HD entry level reader
Posted 26-Jul-2018 15:44


Kiwi team reaches semi-finals at the Microsoft Imagine Cup
Posted 26-Jul-2018 15:38


KidsCan App to Help Kiwi Children in Need
Posted 26-Jul-2018 15:32


FUJIFILM announces new high-performance lenses
Posted 24-Jul-2018 14:57


New FUJIFILM XF10 introduces square mode for Instagram sharing
Posted 24-Jul-2018 14:44


OPPO brings advanced technology to the smartphone market with new device
Posted 24-Jul-2018 09:20



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.