Topic # 230296 17-Feb-2018 08:55
Send private message

My landlord has removed a previous shower that was put in before they purchased the property. 

 

When the contractors began doing the work for the new shower they discovered the previous work appears to have been done by a non-professional without a permit.  In opening up the wall cavity it was discovered that the shower outlet is directly above a standard power point located on the other face of the wall and without any separation between the two.  I am concerned that this is not safe and if the shower outlet leaks, water will cascade down onto the power box and cause a short circuit or fire.

 

My understanding (and logic suggests) that this is not to code and that the power point would need to be moved to a location further along the wall away from the shower fittings.  If that is the case I assume that until work is done to remedy this situations their insurance will be void.

 

I want to approach the owners and rental agency to advise them of this but want to be reasonably sure that I am correct and not barking up the wrong tree.  The landlords are really nice people and I am sensitive to the fact that this has cost them much more than they expected already, so I am looking for any alternative to make the arrangement safe and to code for everyone's protection.

 

Any information and regulations I can refer to regarding this would be helpful.


Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic
 1 | 2
Mad Scientist
18701 posts

Uber Geek
+1 received by user: 2381

Trusted
Lifetime subscriber

  Reply # 1959471 17-Feb-2018 09:05
2 people support this post
Send private message

Oh dear that's a tough one. I presume this is Auckland? The land of cowboys doing illegal building works using fake materials?

 

This sounds really dangerous.

 

I think you should bring it up to the landlord and at the very least request an electrician to inspect. At the very least he can disconnect the socket and stop it from electrocuting your family.


1582 posts

Uber Geek
+1 received by user: 317

Lifetime subscriber

  Reply # 1959482 17-Feb-2018 09:37
One person supports this post
Send private message

How about a photo as it's not really clear about the relationship between the location of the shower outlet and the electrical outlet, or even a hand drawn sketch

 

 

 

Some measurements between the 2 would be good just to confirm if ok or not

 

 




9 posts

Wannabe Geek
+1 received by user: 2


  Reply # 1959499 17-Feb-2018 10:20
Send private message

I've been working on that! :-)

 

 

 

Here is a drawing of the original layout:

 

Click to see full size

 

This is what the layout looked like when the landlords bought the place:  The pipes that previously ran up the wall (now removed) were redirected to the shared wall to the room behind.  To hide the plumbing a tile box similar to ones for putting your shampoo etc. was put in.  The pipes were directed as you see them in the third photo.  What you cannot see is that the two pipes to to a mixer (between them) and a pipe then runs horizontally to the outlet to the shower hose pretty well directly above the PP.

 

Click to see full size

 

This is a photo of the new shower base.  You can see in the top of picture the power outlet in the next room.

 

The two pipes directed up the wall go to the mixer, which then sends a pipe to the outlet to the shower hose, lying directly above the PP.

 

Click to see full size

 

 

 

 


Mad Scientist
18701 posts

Uber Geek
+1 received by user: 2381

Trusted
Lifetime subscriber

  Reply # 1959509 17-Feb-2018 10:48
Send private message

Or if they refuse propose a deal where if electrician finds nothing wrong you pay.



9 posts

Wannabe Geek
+1 received by user: 2


  Reply # 1959514 17-Feb-2018 10:55
Send private message

Hi Batman:

 

I am concerned that the owners have no idea this is an issue.  The property manager obviously believed that the outlet above the PP was no longer used, yet in the end that is what has happened.  I don't want anyone to be at risk about this, so if, having established (via this community) that my concerns are valid, I plan to write to the PM to get them to follow up.  Right now I just need to know if this IS a breach of the wiring regs - that confirms if their insurance is void.  If not then the option to investigate further is theirs.


1582 posts

Uber Geek
+1 received by user: 317

Lifetime subscriber

  Reply # 1959516 17-Feb-2018 10:58
Send private message

Tronhar:

 

I've been working on that! :-)

 

 

 

Here is a drawing of the original layout:

 

Click to see full size

 

This is what the layout looked like when the landlords bought the place:  The pipes that previously ran up the wall (now removed) were redirected to the shared wall to the room behind.  To hide the plumbing a tile box similar to ones for putting your shampoo etc. was put in.  The pipes were directed as you see them in the third photo.  What you cannot see is that the two pipes to to a mixer (between them) and a pipe then runs horizontally to the outlet to the shower hose pretty well directly above the PP.

 

Click to see full size

 

This is a photo of the new shower base.  You can see in the top of picture the power outlet in the next room.

 

The two pipes directed up the wall go to the mixer, which then sends a pipe to the outlet to the shower hose, lying directly above the PP.

 

Click to see full size

 

 

 

 

 

 

 

 

Looking at the pictures the power point is actually on the wall of another room that backs on to the shower wall, in this case there is no problem as the key is "safe under normal conditions"

 

This power point under normal conditions would not be in a damp area (such as a bathroom), a leaking pipe or fitting dripping down the inside of the wall and getting the wiring and the back of the power point wet would not be normal conditions.

 

The proposed new layout looks good to me as the defined damp areas AS/NZS3000 (electrical wiring standard) do not extend through the surface of the wall to a power point on the other side of the same wall

 

 




9 posts

Wannabe Geek
+1 received by user: 2


  Reply # 1959524 17-Feb-2018 11:09
Send private message

Ironically, the reason the whole thing has just been rebuilt is because there was a major leak that originated in the pipes to the mixer, resulting in flooding to the bedroom behind and the hallway to that room - located on the left wall of the shower in the photo.  That was a MAJOR leak under pressure.  So there is history here.


gzt

10035 posts

Uber Geek
+1 received by user: 1516


  Reply # 1959525 17-Feb-2018 11:11
Send private message

Did the area around the point get wet in that deluge?



9 posts

Wannabe Geek
+1 received by user: 2


  Reply # 1959548 17-Feb-2018 11:49
Send private message

Hi GZT:

 

As I tried to explain the area that flooded on that occasion was on the right of the stud, so it was separated from the PP.  To the best of my knowledge no work was done on the pipe from the mixer to the outlet for the hose, which IS above the PP.


201 posts

Master Geek
+1 received by user: 46


  Reply # 1959593 17-Feb-2018 13:26
Send private message

gregmcc:

 

Tronhar:

 

I've been working on that! :-)

 

 

 

Here is a drawing of the original layout:

 

Click to see full size

 

This is what the layout looked like when the landlords bought the place:  The pipes that previously ran up the wall (now removed) were redirected to the shared wall to the room behind.  To hide the plumbing a tile box similar to ones for putting your shampoo etc. was put in.  The pipes were directed as you see them in the third photo.  What you cannot see is that the two pipes to to a mixer (between them) and a pipe then runs horizontally to the outlet to the shower hose pretty well directly above the PP.

 

Click to see full size

 

This is a photo of the new shower base.  You can see in the top of picture the power outlet in the next room.

 

The two pipes directed up the wall go to the mixer, which then sends a pipe to the outlet to the shower hose, lying directly above the PP.

 

Click to see full size

 

 

 

 

 

 

 

 

Looking at the pictures the power point is actually on the wall of another room that backs on to the shower wall, in this case there is no problem as the key is "safe under normal conditions"

 

This power point under normal conditions would not be in a damp area (such as a bathroom), a leaking pipe or fitting dripping down the inside of the wall and getting the wiring and the back of the power point wet would not be normal conditions.

 

The proposed new layout looks good to me as the defined damp areas AS/NZS3000 (electrical wiring standard) do not extend through the surface of the wall to a power point on the other side of the same wall

 

 

 

 

 

 

all of this reply is correct, if the gpo is installed in the shower then that is in Zone 0 which is then illegal, as the powerpoint is on the wall backing on to the shower then that is ok as per  the regs 


gzt

10035 posts

Uber Geek
+1 received by user: 1516


  Reply # 1959597 17-Feb-2018 13:37
Send private message

The pdf regs appear to back that up:

https://www.google.co.nz/search?q=nz+electrical+code+of+practice+homeowner

The zone diagrams do not go inside the wall. Plumbing is not mentioned unless it is metal plumbing. That's the way it looks to me.

Having said that, if it was me I would feel exactly the same way and probably pay to have it removed. Could be the landlord will feel the same way and be happy to pay for it.

1976 posts

Uber Geek
+1 received by user: 325

Trusted

  Reply # 1959598 17-Feb-2018 13:39
Send private message

So we've established that it's not against code.

 

Let's think about what would happen if there was a leak (i.e. not normal conditions).

 

a) you get a series of drips down the wall, some hit the socket and drop out the face of the socket. Provided there is no continuous flow of water, then the water won't be 'live'

 

b) the wall cavity fills up with water and there is a continuous flow of water out of the of the socket. This conducts both sides of the circuit, creating a short, and tripping the circuit breaker, eliminating hazard. 

 

 

 

Basically, I'm pretty sure you'll be fine. But if you find the breaker tripping in a year's time, then you know what's going on


gzt

10035 posts

Uber Geek
+1 received by user: 1516


  Reply # 1959600 17-Feb-2018 13:43
Send private message

^post assumes you have RCD circuit breakers and not some ancient fusebox.

2902 posts

Uber Geek
+1 received by user: 1096

Subscriber

  Reply # 1959610 17-Feb-2018 14:12
One person supports this post
Send private message

Are they building a platform for the shower to sit on? Looks like the whole job is getting done on the cheap, if they are not willing to cut the slab a little more. To move the water pipes and waste. So the shower tray can sit directly on the concrete.







9 posts

Wannabe Geek
+1 received by user: 2


  Reply # 1959664 17-Feb-2018 18:33
Send private message

To answer the recent questions:

 

Yep it is an ancient board with fuses and not circuit breakers

 

Yep they have raised the shower up to clear the pipes, however that said the pipes were MUCH higher, perhaps 200mm above the previous tile level, so maybe 250mm above the concrete.  To get the connections down to where they were they tried capping the pipes just above GL, this failed and flooded the apartment, so they had to jack-hammer down to get to where the photo was taken.  Now the shower is complete I have no expectation that the shower itself will be revisited..


 1 | 2
Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic

Twitter »

Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

Intel introduces new NUC kits and NUC mini PCs
Posted 16-Aug-2018 11:03


The Warehouse leaps into the AI future with Google
Posted 15-Aug-2018 17:56


Targus set sights on enterprise and consumer growth in New Zealand
Posted 13-Aug-2018 13:47


Huawei to distribute nova 3i in New Zealand
Posted 9-Aug-2018 16:23


Home robot Vector to be available in New Zealand stores
Posted 9-Aug-2018 14:47


Panasonic announces new 2018 OLED TV line up
Posted 7-Aug-2018 16:38


Kordia completes first live 4K TV broadcast
Posted 1-Aug-2018 13:00


Schools get safer and smarter internet with Managed Network Upgrade
Posted 30-Jul-2018 20:01


DNC wants a safer .nz in the coming year
Posted 26-Jul-2018 16:08


Auldhouse becomes an AWS Authorised Training Delivery Partner in New Zealand
Posted 26-Jul-2018 15:55


Rakuten Kobo launches Kobo Clara HD entry level reader
Posted 26-Jul-2018 15:44


Kiwi team reaches semi-finals at the Microsoft Imagine Cup
Posted 26-Jul-2018 15:38


KidsCan App to Help Kiwi Children in Need
Posted 26-Jul-2018 15:32


FUJIFILM announces new high-performance lenses
Posted 24-Jul-2018 14:57


New FUJIFILM XF10 introduces square mode for Instagram sharing
Posted 24-Jul-2018 14:44



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.