Topic # 238210 6-Jul-2018 21:54
Send private message quote this post

Bought a Fujitsu heat pump at NL a month ago and finally got installed today by NL contracted and Fujitsu accredited installer.

 

When I reading the operational manual and opened the intake grille in order to find the wifi password, I found that the installer didn't fit the two included "air cleaning filter"(1 Apple-catechin filter and 1 Ion deodorization filter) onto the normal air filter and took them away. Is this normal and are these filters not needed?

 

Since he only left me 3 piece of paper(1 operation manual, 1 warranty card, 1 electrical safety certificate) and the remote control with holder, I am wondering if there is other accessories that come with the heat pump(indoor + outdoor unit) which is not already installed into the machine and can be taken away? Also, is there any easy way I can check if the installation is good(the heat pump works now but I am not sure if it is working as it suppose to)?

 

Lucky Fujitsu hide the wifi password behind the intake grille otherwise I probably will never find out.


View this topic in a long page with up to 500 replies per page Create new topic
 1 | 2
6682 posts

Uber Geek
+1 received by user: 3437


  Reply # 2050981 7-Jul-2018 10:23
2 people support this post
Send private message quote this post

I doubt those filters do much in reality. They were probably in separate sealed bags in the cartons - they forgot and threw them out with the packaging.  They should find them or get replacements for you - it's not acceptable, they are a standard feature of the unit and should have been fitted.

 

As far as the Wifi password goes, the installers who put in our heat pumps last year had not the foggiest clue on earth as to how to set them up, if I couldn't DIY then there was "a geek guy" in the office who I could contact for help.  

 

They did leave me with a very heavy stack of installation manuals as well as the operation manuals, and a few odd bits and pieces of pipe etc in a bag - but took all the rest of the packaging away.

 

If the heat pump seems to be working as you'd expect, then the rest of the install is probably perfectly fine.

 

 




93 posts

Master Geek
+1 received by user: 10


  Reply # 2051131 7-Jul-2018 15:56
Send private message quote this post

Thank you. I'll call them and ask for the 2 filters on Monday.

 

Another thing I noted today is that they connected the heat pump power directly to a cable from one of the wall socket. I have another 17 years old heat pump in the house which has a dedicated power cable and a dedicated fuse on the switch board. I am wondering if there is any regulations regarding the power source of the heat pump? Cheers




93 posts

Master Geek
+1 received by user: 10


  Reply # 2051641 8-Jul-2018 19:13
Send private message quote this post

Ok, here are some updates:

 

I talked to my neighbor today who is a electrician and he had a brief look at the electrical part of the installation, he say the work has been done is unacceptable, here is what I remembered from what he said:

 

1, there is a square box with on/off switch(sorry, forget what it is called) beside the outside unit, it supposed to be water proof but there is no any seal around the input/output cable hole, which means water and other things can get in.

 

2, the heat pump is labeled "max current 16A", and is wired into a existing wall socket which connected to a ancient ceramic fuse which is labeled 15A. And the fuse is actually used by several wall socket around the living room.

 

3, he said I should receive a COC(sound like this, but can't remember:-( ) but all I got is a Compliance and Electrical Safety Certificate.

 

4, And some other small details that I can't catch clearly...

 

 

 

I paid $1070 for the installation, now feels like being ripped off...

 

 

 

BTW, how can I change the topic subject to "Heat Pump installation"? Since it is not just about "accessary" now...


6682 posts

Uber Geek
+1 received by user: 3437


  Reply # 2052131 9-Jul-2018 17:17
Send private message quote this post

I'd go back to NL first - as the installer was a subcontractor to them, your contract was with NL.  If they don't sort it out ASAP - then go here:

 

https://www.ewrb.govt.nz/about-us/complaints/

 

It sounds dodgy.  The IP rated outdoor isolation switches on heat pumps I had installed last year are sealed, the cables are in conduit running back under the house, the conduit is going in to the bottom of the isolation switches.  I assume that's normal good practice.  It all looks pretty weatherproof to me.

 

They ran separate new cables for each pump back to the switchboard. 

 

 


496 posts

Ultimate Geek
+1 received by user: 101


  Reply # 2052150 9-Jul-2018 17:55
Send private message quote this post

Id complain to NL and say you want another installer to come do the repairs.

 

My understanding is it should have new cable run back to the switchboard with its own breaker? (well mine and others I have seen are)

 

 

 

If you have the installers name / electrical registration number I would be complaining to the EWRB


21234 posts

Uber Geek
+1 received by user: 4271

Trusted
Subscriber

  Reply # 2052151 9-Jul-2018 18:00
Send private message quote this post

My understanding is that as they were extending the circuit from the powerpoint to the aircon it should be on an RCD anyway, so dodgey AF for them to do that.

 

If you have something they dont want to work on like an old fuse panel they cant drill etc they should just not start the job. Bit hard if the fridgies have done their part before the electrical guy said that it shouldnt be done, but thats the risk they take with installing things blind like so many aircon installers will do.





Richard rich.ms

1572 posts

Uber Geek
+1 received by user: 311

Lifetime subscriber

  Reply # 2052153 9-Jul-2018 18:18
Send private message quote this post

skewt:

 

Id complain to NL and say you want another installer to come do the repairs.

 

My understanding is it should have new cable run back to the switchboard with its own breaker? (well mine and others I have seen are)

 

 

 

If you have the installers name / electrical registration number I would be complaining to the EWRB

 

 

 

 

their is no actual requirement to run a cable back to the switchboard if the circuit you are tapping in to is suitably rated and you won't cause other problems doing so.

 

 


1572 posts

Uber Geek
+1 received by user: 311

Lifetime subscriber

  Reply # 2052154 9-Jul-2018 18:26
Send private message quote this post

richms:

 

My understanding is that as they were extending the circuit from the powerpoint to the aircon it should be on an RCD anyway, so dodgey AF for them to do that.

 

If you have something they dont want to work on like an old fuse panel they cant drill etc they should just not start the job. Bit hard if the fridgies have done their part before the electrical guy said that it shouldnt be done, but thats the risk they take with installing things blind like so many aircon installers will do.

 

 

 

 

No requirement for heat pumps to be on an RCD, if a power point was there instead of a heat pump then a RCD would be required.

 

 

 

The OP has been asking questions relating to the electrical side of things over on another forum and got some pointers on what to look for, mostly it compliant (not fully), but a pretty poor installation overall.

 

 

 

 

 

 


1550 posts

Uber Geek
+1 received by user: 157

Subscriber

  Reply # 2052191 9-Jul-2018 19:24
One person supports this post
Send private message quote this post

begs the question, how can the installer be Fujitsu Accredited?

 

If thats the standard of accreditation then the Fujitsu marketing campaign isnt true. 

 

Suggest you let them know your troubles. 




93 posts

Master Geek
+1 received by user: 10


  Reply # 2052252 9-Jul-2018 20:36
Send private message quote this post

Here are some updates:

 

I went to their office this morning told the receptionist that I am worrying about the safety of the installation, but the receptionist told me the heat pump is meant to be installed onto the wall socket and is perfectly safe. She also said she will let the installer know my concerns and will call me back when the installer is free. No call till now. Also both the receptionist and the installer don't know anything about the 2 missing filters.

 

I have a computer, 2 monitors, 2 sets of speakers plus several USB devices, and a vacuum machine(weekend only) on the same fuse(15A). The heat pump is rated 9A 2120W with max current 16A. I don't think there are much left for my existing equipment after the heat pump.

 

Like gregmcc said, I asked the same question on a electrical forum and got replies from several electricians. The result is installing a heat pump by wiring into an existing wall socket is perfectly legal, and it is not necessary install a dedicated circuit/fuse/breaker, but the installer has to check if it will overload the existing circuit. So it is a legal installation, but poorly done. Also the outside isolator has to be sealed, the installer can't get away with this part.

 

I've also talked to all my neighbors all of their heat pump installation is done on a dedicated circuit to the switchboard with a new circuit breaker, the only difference is none of them is using Fujitsu(so not Fujitsu accredited installers).

 

I wish I have asked someone I know or installer recommended by my neighbor to do the job, but the damn Fujitsu heat pumps has to be installed by their accredited installer in order to receive the 6 years warranty.

 

I'll see if they will call me back tomorrow.


13974 posts

Uber Geek
+1 received by user: 2488

Trusted
Subscriber

  Reply # 2052441 10-Jul-2018 09:40
Send private message quote this post

I have two heat pumps, both on dedicated circuits. I'd talk to NL and have this redone, otherwise I'd try to escalate to whoever registers electricians or such.





AWS Certified Solution Architect Professional, Sysop Administrator Associate, and Developer Associate
TOGAF certified enterprise architect
Professional photographer


1201 posts

Uber Geek
+1 received by user: 472


  Reply # 2052450 10-Jul-2018 09:50
Send private message quote this post

Hibino:

 

Another thing I noted today is that they connected the heat pump power directly to a cable from one of the wall socket. I have another 17 years old heat pump in the house which has a dedicated power cable and a dedicated fuse on the switch board. I am wondering if there is any regulations regarding the power source of the heat pump? Cheers

 

 

Its should be easy to find out if there is a wiring error. If the heatpump is rated more than 2300 Watts, 2.3KW, then its not suitable to be installed on a 10 Amp wall socket. 3450 Watts on a 15 Amp wall Socket

 

As a test. You could switch the heat pump on, set it to max power. Then plug a power hungry device (ie a 2300 Watt heater), into the same plug socket. If it trips, you are overloading the wall socket, and that should not happen.

 

 


1944 posts

Uber Geek
+1 received by user: 303

Trusted

  Reply # 2052500 10-Jul-2018 10:43
Send private message quote this post

Wiggum:

 

Hibino:

 

Another thing I noted today is that they connected the heat pump power directly to a cable from one of the wall socket. I have another 17 years old heat pump in the house which has a dedicated power cable and a dedicated fuse on the switch board. I am wondering if there is any regulations regarding the power source of the heat pump? Cheers

 

 

Its should be easy to find out if there is a wiring error. If the heatpump is rated more than 2300 Watts, 2.3KW, then its not suitable to be installed on a 10 Amp wall socket. 3450 Watts on a 15 Amp wall Socket

 

As a test. You could switch the heat pump on, set it to max power. Then plug a power hungry device (ie a 2300 Watt heater), into the same plug socket. If it trips, you are overloading the wall socket, and that should not happen.

 

 

 

 

As above from Greg, there's no requirement in regulation for the heat pump to have a dedicated circuit. Could possibly be argued best practice, but you certainly can't demand it as of right, especially with a fixed price install. 

 

There's also no requirement that the circuit support the max demand of it's sockets and the heat pump together. Every house will have several double outlets on a 16A fuse/MCB and there's no chance of supplying every outlet at full capacity simultaneously. A heater and heat pump tripping the fuse isn't evidence to call the installer back on. The fuse is protecting from overload, so no safety issue. There's more of a grey area argument if you can't use the heatpump and a few appliances at the same time, especially if those appliances were plugged in when the installer visited - TV etc as the OP said. The installer could reasonably argue that you wouldn't need to use a plug in heater at full boar at the same time as the heat pump at full boar. 


2811 posts

Uber Geek
+1 received by user: 1060

Subscriber

  Reply # 2052522 10-Jul-2018 11:33
Send private message quote this post

timmmay:

I have two heat pumps, both on dedicated circuits. I'd talk to NL and have this redone, otherwise I'd try to escalate to whoever registers electricians or such.



What is the running current of your heatpumps? You might simply have larger models. Meaning that the running current could put the circuit right at its limit. Or maybe your existing circuits can't be extended while still complying with the voltage drop rules. Meaning putting the heatpump on a dedicated circuit would probably be cheaper than replacing the cable in that circuit with a larger size.






13974 posts

Uber Geek
+1 received by user: 2488

Trusted
Subscriber

  Reply # 2052600 10-Jul-2018 12:57
Send private message quote this post

Aredwood:
timmmay:

 

I have two heat pumps, both on dedicated circuits. I'd talk to NL and have this redone, otherwise I'd try to escalate to whoever registers electricians or such.

 



What is the running current of your heatpumps? You might simply have larger models. Meaning that the running current could put the circuit right at its limit. Or maybe your existing circuits can't be extended while still complying with the voltage drop rules. Meaning putting the heatpump on a dedicated circuit would probably be cheaper than replacing the cable in that circuit with a larger size.

 

Not sure about current, but they're 7.5kw heating 8.5kw cooling, which is larger than average. That's probably pushing a bit under 10A.





AWS Certified Solution Architect Professional, Sysop Administrator Associate, and Developer Associate
TOGAF certified enterprise architect
Professional photographer


 1 | 2
View this topic in a long page with up to 500 replies per page Create new topic

Twitter »

Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

Microsoft Dynamics 365 Business Central launches
Posted 10-Jul-2018 10:40


Spark completes first milestone in voice platform upgrade
Posted 10-Jul-2018 09:36


Microsoft ices heated developers
Posted 6-Jul-2018 20:16


PB Technologies charged for its extended warranties and warned for bait advertising
Posted 3-Jul-2018 15:45


Almost 20,000 people claim credits from Spark
Posted 29-Jun-2018 10:40


Cove sells NZ's first insurance policy via chatbot
Posted 25-Jun-2018 10:04


N4L helping TAKA Trust bridge the digital divide for Lower Hutt students
Posted 18-Jun-2018 13:08


Winners Announced for 2018 CIO Awards
Posted 18-Jun-2018 13:03


Logitech Rally sets new standard for USB-connected video conference cameras
Posted 18-Jun-2018 09:27


Russell Stanners steps down as Vodafone NZ CEO
Posted 12-Jun-2018 09:13


Intergen recognised as 2018 Microsoft Country Partner of the Year for New Zealand
Posted 12-Jun-2018 08:00


Finalists Announced For Microsoft NZ Partner Awards
Posted 6-Jun-2018 15:12


Vocus Group and Vodafone announce joint venture to accelerate fibre innovation
Posted 5-Jun-2018 10:52


Kogan.com to launch Kogan Mobile in New Zealand
Posted 4-Jun-2018 14:34


Enable doubles fibre broadband speeds for its most popular wholesale service in Christchurch
Posted 2-Jun-2018 20:07



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.