Topic # 240080 19-Aug-2018 16:41
Send private message quote this post

Starting to have a 20A circuit breaker on the oven blow quite often..  especially when a George Foreman cooker is also plugged in (to the oven).

 

It's an older style F&P ceramic all-in-one.... can I determine the correct fuse rating ?   What's the opinion about increasing to 25A  (although I don't see

 

any circuit breakers above 20A on line, so maybe 25a fuse wire would do ?)

 

 

 

 


Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic
 1 | 2 | 3
3609 posts

Uber Geek
+1 received by user: 2001

Trusted
Lifetime subscriber

  Reply # 2075858 19-Aug-2018 16:42
Send private message quote this post

Normal oven fuses I thought should be 30 amps

 

John





Ex JohnR VodafoneNZ 17 years 4 days

21389 posts

Uber Geek
+1 received by user: 4336

Trusted
Subscriber

  Reply # 2075860 19-Aug-2018 16:53
Send private message quote this post

Assuming you mean a range and not just an oven then it would usually be a 32A one but don't just swap it. Might have been a gas range initially and someone swapped for electric and didn't bother to upgrade the wiring. Also outlets on a range will take it over 32A if you're using several elements and plugging in something large. Terrible idea to have them and a good thing they did away with them




Richard rich.ms



727 posts

Ultimate Geek
+1 received by user: 31


  Reply # 2075862 19-Aug-2018 16:58
Send private message quote this post

Thanks.. I'll keep looking.


1594 posts

Uber Geek
+1 received by user: 327

Lifetime subscriber

  Reply # 2075864 19-Aug-2018 17:00
Send private message quote this post

ADKM:

 

Starting to have a 20A circuit breaker on the oven blow quite often..  especially when a George Foreman cooker is also plugged in (to the oven).

 

It's an older style F&P ceramic all-in-one.... can I determine the correct fuse rating ?   What's the opinion about increasing to 25A  (although I don't see

 

any circuit breakers above 20A on line, so maybe 25a fuse wire would do ?)

 

 

 

 

 

 

 

 

The fuse rating is there to protect the cable running through your house to the stove, not the stove, I'm assuming you have plug in circuit beakers, replacing it with a bigger circuit breaker could lead to the cable overheating and melting the insulation off and starting a fire.

 

If your current circuit breaker is wired in you are not allowed to change it, the exemption for home owners work specifically says no switchboard work is to be done by home owners.

 

 

 

Your best bet, get an electrician out to check it out

 

 

 

Greg

 

 




727 posts

Ultimate Geek
+1 received by user: 31


  Reply # 2075868 19-Aug-2018 17:19
Send private message quote this post

>The fuse rating is there to protect the cable running through your house to the stove, not the stove, I'm assuming you have plug in circuit beakers, replacing it with a bigger circuit breaker could lead to the cable >overheating and melting the insulation off and starting a fire.

 

I'm mindful of that, but if 30A is the norm it would explain why the 20A keep blowing. Presumably the wiring is up to spec. Late 1970s vintage house.

 

 

 

If your current circuit breaker is wired in you are not allowed to change it, the exemption for home owners work specifically says no switchboard work is to be done by home owners.

 

They are plug in. I do see (now) 32Amp ones but 25 may be worth trying first.

 

 

 

 


1594 posts

Uber Geek
+1 received by user: 327

Lifetime subscriber

  Reply # 2075873 19-Aug-2018 17:27
Send private message quote this post

I would be pretty sure that because there is a 20A circuit breaker plugged in, the wiring is only 2.5mm2, if you put a 32A circuit breaker, you will for sure cook your wiring.


21389 posts

Uber Geek
+1 received by user: 4336

Trusted
Subscriber

  Reply # 2075880 19-Aug-2018 18:13
One person supports this post
Send private message quote this post

ADKM:

 

I'm mindful of that, but if 30A is the norm it would explain why the 20A keep blowing. Presumably the wiring is up to spec. Late 1970s vintage house.

 

 

Probably because the range has been swapped over at some stage as part of a renovation, and the electrics are the one place that people always cheap out on with kitchens since a fancy tap looks so much more impressive than wiring that noone ever sees when browsing houses for sale.

 

Chances are that when the place was coming up for sale people commented on it having "old fuses" so they just went and got plug in breakers for everything to make it look better than it was, and there is also a good chance that they have been swapped around if they are not tied into the bases since people will swap them to avoid tripping a power circuit that they are trying to run 3 heaters on etc.

 

Sparky in to assess it all is the best course of action, and if they are still the original 70's breakers with the little red button then they are well past needing to be replaced.





Richard rich.ms

5043 posts

Uber Geek
+1 received by user: 1618


  Reply # 2075883 19-Aug-2018 18:36
One person supports this post
Send private message quote this post

ADKM:

 

They are plug in. I do see (now) 32Amp ones but 25 may be worth trying first.

 

 

I know it's bad to use all caps, but DO NOT DO THIS.

 

As already stated, the fuse or breaker's job is to protect the cable from overload. Do not assume that the cable is rated higher. This is the sort of thing that starts fires and kills people.


1996 posts

Uber Geek
+1 received by user: 331

Trusted

  Reply # 2075886 19-Aug-2018 18:48
One person supports this post
Send private message quote this post

gregmcc:

I would be pretty sure that because there is a 20A circuit breaker plugged in, the wiring is only 2.5mm2, if you put a 32A circuit breaker, you will for sure cook your wiring.


I'm normally in the "go forth and diy" camp on these electrical threads, however I completely agree here. I'm not a sparky, though, so my opinion should be taken with a grain of salt.

There's probably a 90% chance that someone has just mixed up the breakers as richms says, but that leaves a 10% chance of the cable to your most power hungry appliance being overloaded without useful circuit protection, which is electrical fire territory. You need a sparky to assess the cable and figure out which case it is

3609 posts

Uber Geek
+1 received by user: 2001

Trusted
Lifetime subscriber

  Reply # 2075889 19-Aug-2018 19:08
Send private message quote this post

Oven cable should then be isolated and mega ohm test done and resistance

John




Ex JohnR VodafoneNZ 17 years 4 days



727 posts

Ultimate Geek
+1 received by user: 31


  Reply # 2075901 19-Aug-2018 20:05
Send private message quote this post

Thanks for the replies. I'll get the wiring looked at to make sure a higher rated fuse is safe.

 

Rich you are right, they've been changed/swapped as some stage. About half of them are the older type with fuse wire and the others are the 'red button' variety.

 

I wondered if the 20A one might have replaced a bigger one at some stage...hence asking about the usual rating  I can't see the wiring of course, but from the wall to

 

the oven that's much gruntier than a standard 3 pin wall sockets. Not sure what 2.5mm2 is.

 

Can these things, as they age, trip at a lower current?  Maybe another 20 amp one might solve the problem.


1594 posts

Uber Geek
+1 received by user: 327

Lifetime subscriber

  Reply # 2075904 19-Aug-2018 20:15
Send private message quote this post

ADKM:

 

Thanks for the replies. I'll get the wiring looked at to make sure a higher rated fuse is safe.

 

Rich you are right, they've been changed/swapped as some stage. About half of them are the older type with fuse wire and the others are the 'red button' variety.

 

I wondered if the 20A one might have replaced a bigger one at some stage...hence asking about the usual rating  I can't see the wiring of course, but from the wall to

 

the oven that's much gruntier than a standard 3 pin wall sockets. Not sure what 2.5mm2 is.

 

Can these things, as they age, trip at a lower current?  Maybe another 20 amp one might solve the problem.

 

 

 

 

The red button ones are well known for becoming tired and nuisance tripping, or tripping and not been able to reset.

 

You won't be able to buy an exact replacement as they havn't been made for 20+ years, but there are other brand plug in replacements available.

 

 

 

 




727 posts

Ultimate Geek
+1 received by user: 31


  Reply # 2075906 19-Aug-2018 20:26
One person supports this post
Send private message quote this post

Thanks Greg, I see them around and will try a new 20A one first.  I'm sure that'll be ok with everyone.


1601 posts

Uber Geek
+1 received by user: 408


  Reply # 2075949 19-Aug-2018 22:03
Send private message quote this post

Was there a gas oven previously installed? Is there an isolation switch above or near your oven?




727 posts

Ultimate Geek
+1 received by user: 31


  Reply # 2076044 20-Aug-2018 10:23
Send private message quote this post

MadEngineer:

 

Was there a gas oven previously installed? Is there an isolation switch above or near your oven?

 

 

 

 

I'm pretty sure the oven is original and yes, there is a isolation switch above in (in the wall).

 

And we have no gas supply here.


 1 | 2 | 3
Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic

Twitter »

Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.