  Reply # 2076393 20-Aug-2018 18:15
Send private message quote this post

But the whole point was to stop it tripping out, which it shouldn't do.

Well if you "do the maths" as I suggested earlier you will see that it shoud trip.




Rob



727 posts

Ultimate Geek
+1 received by user: 31


  Reply # 2076400 20-Aug-2018 18:26
Send private message quote this post

But Rob, we don't *want* it to trip.  By shouldn't I meant it should be setup so it doesn't happen.

 

Isn't household oven wiring normally 30 amps for the 1970s?  If it's proved we have the right gauge /size to handle 30 amps I could try a 25A fuse. Incidentally it wasn't being run with everything on Full. Hot plates were on simmer and the main oven about 200 degrees.


21534 posts

Uber Geek
+1 received by user: 4387

Trusted
Subscriber

  Reply # 2076404 20-Aug-2018 18:31
Send private message quote this post

Uprating a breaker which is only suspected of being swapped out for a lower rating one is just asking for trouble.

 

This is as logical as those people that go jamming random metal things into fuses because they keep blowing.





Richard rich.ms



727 posts

Ultimate Geek
+1 received by user: 31


  Reply # 2076408 20-Aug-2018 18:39
Send private message quote this post

Not quite Rich, talking about going from  20A circuit breaker to 20A fuse wire to start with.  Mainly to see if it makes any difference, proving the CB is tripping incorrectly.


3169 posts

Uber Geek
+1 received by user: 1221

Subscriber

  Reply # 2076512 20-Aug-2018 21:06
Send private message quote this post

ADKM:

> Can't you just plug the GF grill into a different power point?


Could do, with an extension cord.  But the whole point was to stop it tripping out, which it shouldn't do. (It isn't 2 phase nor is that wired in here.)


Someone said to ring F&P so I did. The girl there wasn't very convincing and said the current rating was 52A.    I don't think that helps.


If I can get a holder, I'll try some 20A fuse wire and see what happens.  That saves $30 or so on a circuit breaker that may be no different to what's here now.


 



Don't use 20A fuse wire. As most fuses are only regarded as coarse protection. While most circuit breakers are regarded as close protection. The difference being the ratio between rated current, and the current at which the fuse will blow / breaker trips in a given time.

For example, a cable that can be safely protected by a 20A breaker. Would likely only be safe with a 15A fuse.

A 20A wire fuse would probably take a good hour to blow at 40A.

Please, please, Just get an electrician in to check and advise you on the correct rating for the circuit.

The electrical codes have lots of different sections that have to all be consulted to work out the correct current rating for a fuse or breaker on a given cable. This can't be calculated without a sparky visiting your house to check your installation.

Note also that there is no actual requirement to run a 32A circuit to a stove. So 20A could easily be the correct current rating for your circuit.





474 posts

Ultimate Geek
+1 received by user: 77

Subscriber

  Reply # 2076535 20-Aug-2018 22:38
Send private message quote this post

Hot plates were on simmer and the main oven about 200 degrees.

"Simmerstats" and thermostats do not limit the current they just switch it on and off.
Trust me, it is entirely understandable that a range and a George Forman Grill will trip a 20A breaker. Yes a fuse will take longer to blow but it will also heat up and tend to overheat the assembly, introducing another fire risk.
That cable looks at least 4mm (probably even 7/.036) which can legally and safely be protected by a 32A breaker and probably solving your problem.




Rob

231 posts

Master Geek
+1 received by user: 53


  Reply # 2076584 21-Aug-2018 06:40
One person supports this post
Send private message quote this post

what circuit breaker are you using???? the plug in type push button re settable? if so bin it as that will be your problem!!!! those things have a tendency to fail and be a pain like that, whats the distance form the switch board? that picture of the cable looks to be a 4mm or a 6mm and will be fin on a 25A mcb.

 

and you shouldnt be using fuse wire what soever now days as the fusing factor is far to high, a HRC fuse would be better than fuse wire.


1639 posts

Uber Geek
+1 received by user: 419


  Reply # 2078058 23-Aug-2018 16:11
Send private message quote this post

Yeah it does look like 4mm/6mm but some weird chinese rubbish due to the larger than usual earth.  Typically that size cable has a 2.5mm earth.

 

 

 

Do you leave those fuse holders emtpy?   It's a good way to kill someone.  Albeit painfully.


1604 posts

Uber Geek
+1 received by user: 333

Lifetime subscriber

  Reply # 2078074 23-Aug-2018 17:34
Send private message quote this post

MadEngineer:

 

Yeah it does look like 4mm/6mm but some weird chinese rubbish due to the larger than usual earth.  Typically that size cable has a 2.5mm earth.

 

 

 

 

 

 

It's just older cable, it was the 90's sometime that 6mm2 cables were allowed the smaller earths


1 | 2 | 3 
Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic

Twitter »

Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.