Hi

 

We are renovating our laundry.

 

I've removed a patch of gib up high so I can install some additional bracing behind the gib to hang my clothes dryer up high in the laundry.

 

I removed the panel and found this mystery wire.

 

It's a bare multistranded twisted core copper wire.  It travels along side a set of 240V cables that supply another part of the house and then it dives down through the wall towards the old laundry sink (1965).

 

I assume it's an earth cable.  Does it attach to the pipes supplying the laundry tub?  I'm moving the laundry tub towards the right hand side, it's not in the way of adding the bracing for the dryer, so I can leave it where it is, but if it is an earth wire for the plumbing does it need to stay in contact with the pipes and also make contact with the new pipes for the new set of taps?

 

 

 





HTPC: Intel i3-2100 / 12GB RAM / AMD HD7750 / 480 GB SSD / 58TB Storage / MediaPortal / MadVR / Win10
AVR: Pioneer Elite SC-LX87 220W 9.2 Ch AVR
Speakers: Wharfedale Jade 7 Fronts / Jade 2c Center / Jade 5 Rears
Subs: iNuke 3000dsp 3000W proamp with 4x 15" JBL Sealed Subs
Display: Samsung 60" UA60H6400 LCD TV
Accessories: Gefen HDMI Detective with splitter


Create new topic
330 posts

Ultimate Geek
+1 received by user: 82


  Reply # 2188419 27-Feb-2019 19:45
Send private message quote this post

How old is the house? It looks like it could be the old main earth or a bonding wire? Is there an earth pin outside the laundry?


3840 posts

Uber Geek
+1 received by user: 1555

Subscriber

  Reply # 2188434 27-Feb-2019 20:21
Send private message quote this post

Yea looks like one of the earth bonds they would tie to the copper water pipe.

I'm sure a plumber would know what to do with it - if anything.

 
 
 
 


76 posts

Master Geek
+1 received by user: 31


  Reply # 2188435 27-Feb-2019 20:22
Send private message quote this post

It's likely that it bonds the sink, not the tap plumbing. If you open the cupboard you can probably find the connection.

 

 

 

Newer rules do not require the sink itself to be bonded, but if you have conductive water piping, especially if it goes all the way into the ground, that should be bonded somewhere.




2759 posts

Uber Geek
+1 received by user: 98


  Reply # 2188467 27-Feb-2019 21:13
Send private message quote this post

the house is 1965.





HTPC: Intel i3-2100 / 12GB RAM / AMD HD7750 / 480 GB SSD / 58TB Storage / MediaPortal / MadVR / Win10
AVR: Pioneer Elite SC-LX87 220W 9.2 Ch AVR
Speakers: Wharfedale Jade 7 Fronts / Jade 2c Center / Jade 5 Rears
Subs: iNuke 3000dsp 3000W proamp with 4x 15" JBL Sealed Subs
Display: Samsung 60" UA60H6400 LCD TV
Accessories: Gefen HDMI Detective with splitter




2759 posts

Uber Geek
+1 received by user: 98


  Reply # 2188468 27-Feb-2019 21:13
Send private message quote this post

What is the difference between bonded and earthed?





HTPC: Intel i3-2100 / 12GB RAM / AMD HD7750 / 480 GB SSD / 58TB Storage / MediaPortal / MadVR / Win10
AVR: Pioneer Elite SC-LX87 220W 9.2 Ch AVR
Speakers: Wharfedale Jade 7 Fronts / Jade 2c Center / Jade 5 Rears
Subs: iNuke 3000dsp 3000W proamp with 4x 15" JBL Sealed Subs
Display: Samsung 60" UA60H6400 LCD TV
Accessories: Gefen HDMI Detective with splitter


76 posts

Master Geek
+1 received by user: 31


  Reply # 2188471 27-Feb-2019 21:18
Send private message quote this post

Earthed is about operating a specific protection device, supplying the circuit associated with it. So the chassis of your washing machine is earthed, so that if a live wire comes loose and hits it, it blows a fuse or MCB. The earth only has to be sized to trip that circuit, not carry any other currents

 

 

 

Bonding is more about ensuring that there can't be a voltage difference between two points, which could be your neighbour having a stuffed earthing system and current going to your place via piping, or current leaking from somewhere else. Because it's not necessarily going to trip any protection and we don't know what circuit is providing the hypothetical current, the conductors have to be somewhat larger just in case.


212 posts

Master Geek
+1 received by user: 56

Lifetime subscriber

  Reply # 2188480 27-Feb-2019 21:43
One person supports this post
Send private message quote this post

A house that age probably has galv steel or copper water pipes. The wire is probably a bond between the main switchboard and the pipework. Just be careful if you plan to disconnect it. There a small chance, especially if there is a fault with the main, that there will be a voltage difference between the wire snd the pipework. People have been killed doing this, although it is pretty rare.
Get someone who knows what they are doing if you need to disconnect it.

330 posts

Ultimate Geek
+1 received by user: 82


  Reply # 2188483 27-Feb-2019 21:51
One person supports this post
Send private message quote this post

larknz: A house that age probably has galv steel or copper water pipes. The wire is probably a bond between the main switchboard and the pipework. Just be careful if you plan to disconnect it. There a small chance, especially if there is a fault with the main, that there will be a voltage difference between the wire snd the pipework. People have been killed doing this, although it is pretty rare.
Get someone who knows what they are doing if you need to disconnect it.

 

 

 

 

 

DO NOT DISCONNECT IT!!!!!

 

get a sparky to check it first as it could be the main earth for the house.

 

Back in the day if its was a galv pipe coming in to the property it would sometimes be used as the main earth instead of dropping a pin, so when the galv pipe finally gave out the property had no earth because the plumbers/council had replaced the galv pipe with pvc.

 

 


212 posts

Master Geek
+1 received by user: 56

Lifetime subscriber

  Reply # 2188484 27-Feb-2019 21:57
Send private message quote this post

sparkz25:

larknz: A house that age probably has galv steel or copper water pipes. The wire is probably a bond between the main switchboard and the pipework. Just be careful if you plan to disconnect it. There a small chance, especially if there is a fault with the main, that there will be a voltage difference between the wire snd the pipework. People have been killed doing this, although it is pretty rare.
Get someone who knows what they are doing if you need to disconnect it.


 


 


DO NOT DISCONNECT IT!!!!!


get a sparky to check it first as it could be the main earth for the house.


Back in the day if its was a galv pipe coming in to the property it would sometimes be used as the main earth instead of dropping a pin, so when the galv pipe finally gave out the property had no earth because the plumbers/council had replaced the galv pipe with pvc.


 



That is what I was implying when I said get someone who knows what they are doing. Maybe I should have been a bit more explicit, although I did mention that death was possible.



2759 posts

Uber Geek
+1 received by user: 98


  Reply # 2188488 27-Feb-2019 22:04
Send private message quote this post

I don't need to disconnect it. I think I'll just leave it be.





HTPC: Intel i3-2100 / 12GB RAM / AMD HD7750 / 480 GB SSD / 58TB Storage / MediaPortal / MadVR / Win10
AVR: Pioneer Elite SC-LX87 220W 9.2 Ch AVR
Speakers: Wharfedale Jade 7 Fronts / Jade 2c Center / Jade 5 Rears
Subs: iNuke 3000dsp 3000W proamp with 4x 15" JBL Sealed Subs
Display: Samsung 60" UA60H6400 LCD TV
Accessories: Gefen HDMI Detective with splitter


Create new topic


Donate via Givealittle


Twitter »

Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

Amazon introduces new Kindle with adjustable front light
Posted 21-Mar-2019 20:14


A call from the companies providing internet access for the great majority of New Zealanders, to the companies with the greatest influence over social media content
Posted 19-Mar-2019 15:21


Two e-scooter companies selected for Wellington trial
Posted 15-Mar-2019 17:33


GeForce GTX 1660 available now
Posted 15-Mar-2019 08:47


Artificial Intelligence to double the rate of innovation in New Zealand by 2021
Posted 13-Mar-2019 14:47


LG demonstrates smart home concepts at LG InnoFest
Posted 13-Mar-2019 14:45


New Zealanders buying more expensive smartphones
Posted 11-Mar-2019 09:52


2degrees Offers Amazon Prime Video to Broadband Customers
Posted 8-Mar-2019 14:10


D-Link ANZ launches D-Fend AC2600 Wi-Fi Router Protected by McAfee
Posted 7-Mar-2019 11:09


Slingshot commissions celebrities to design new modems
Posted 5-Mar-2019 08:58


Symantec Annual Threat Report reveals more ambitious, destructive and stealthy attacks
Posted 28-Feb-2019 10:14


FUJIFILM launches high performing X-T30
Posted 28-Feb-2019 09:40


Netflix is killing content piracy says research
Posted 28-Feb-2019 09:33


Trend Micro finds shifting threats require kiwis to rethink security priorities
Posted 28-Feb-2019 09:27


Mainfreight uses Spark IoT Asset Tracking service
Posted 28-Feb-2019 09:25



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.


Support Geekzone »

Our community of supporters help make Geekzone possible. Click the button below to join them.

Support Geezone on PressPatron



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.