  Reply # 2213323 9-Apr-2019 07:12
Send private message quote this post

The fact that you have 3 red wires and only 2 black wires is an indication that something slightly different is happening. Where is the missing neutral conductor connected?

Glurp
9725 posts

Uber Geek
+1 received by user: 4644

Subscriber

  Reply # 2213338 9-Apr-2019 08:31
Send private message quote this post

Until a simple test is performed, it's all conjecture.

 

 





I reject your reality and substitute my own. - Adam Savage
 


 
 
 
 


2744 posts

Uber Geek
+1 received by user: 455


  Reply # 2213364 9-Apr-2019 09:23
Send private message quote this post

The ability to test is something a lot of people ignore. The code of practice requires you to have a multimeter available.

If it's an installation old enough to have conduit wiring I wouldn't assume that the wires were necessarily phase and neutral. Lighting circuits were commonly wired with power at the light fitting and only the phase sent down for switching. That should have been with red wires or wires sleeved red but who knows what happens on a friday?

Glurp
9725 posts

Uber Geek
+1 received by user: 4644

Subscriber

  Reply # 2213374 9-Apr-2019 09:40
Send private message quote this post

I couldn't live without a multimeter but in this situation, all that is needed is to establish if each red wire controls each device. It is a very simple test to disconnect them one at a time (after cutting the power, of course) and seeing what happens. If, as expected, they control the devices separately, then the switch can be installed and there is no need to worry about what the black wires or anything else does. Electrically, nothing gets changed except the red wires are switched individually instead of together. Of course, the fan and light could always be 120 volt US imports connected in series, but that isn't very likely.

 

 

 

 





I reject your reality and substitute my own. - Adam Savage
 


1704 posts

Uber Geek
+1 received by user: 410


  Reply # 2213411 9-Apr-2019 10:26
Send private message quote this post

If you have to ask advice here , you really ARNT competent.

 

If you have to ask advice here , you shouldnt be doing to job.

 

 

 




2611 posts

Uber Geek
+1 received by user: 756


  Reply # 2213431 9-Apr-2019 11:23
One person supports this post
Send private message quote this post

1101: If you have to ask advice here , you really ARNT competent. If you have to ask advice here , you shouldnt be doing to job.

 

I disagree that asking for advice automatically disqualifies you as being able to do a job. By that logic nobody would be able to anything.




2611 posts

Uber Geek
+1 received by user: 756


  Reply # 2213433 9-Apr-2019 11:27
Send private message quote this post

larknz: The fact that you have 3 red wires and only 2 black wires is an indication that something slightly different is happening. Where is the missing neutral conductor connected?

 

I agree, which is why I haven't just gone ahead and done it already because it isn't quite what I would have expected.




2611 posts

Uber Geek
+1 received by user: 756


  Reply # 2213435 9-Apr-2019 11:32
Send private message quote this post

Bung: If it's an installation old enough to have conduit wiring I wouldn't assume that the wires were necessarily phase and neutral. Lighting circuits were commonly wired with power at the light fitting and only the phase sent down for switching. That should have been with red wires or wires sleeved red but who knows what happens on a friday?

 

What you've described is how all the other switches in the house that I have previously changed have been wired, with only phase going to the switch.

 

As @Rikkitic pointed out, this is easy for me to test - I just didn't get a chance to do this last night.


265 posts

Ultimate Geek
+1 received by user: 4


  Reply # 2213492 9-Apr-2019 12:16
2 people support this post
Send private message quote this post

Aside from the electrical wiring issue, which I would recommend engaging an electrician, there is the reason it was wired like this in the first place which I would assume would be to meet ventilation requirements for the bathroom.  If you split these then don't engage the fan when needed you would get moisture build up and in turn mould.  Whilst having the light and fan connected may be annoying for when you just want the light on to grab a toothbrush, you will be thankful there is a failsafe there in case you forget to turn the fan on when it is needed, as it sounds like you are unlikely to run the shower with the light off if you need it on to find a toothbrush.


821 posts

Ultimate Geek
+1 received by user: 102

Trusted

  Reply # 2213573 9-Apr-2019 13:04
Send private message quote this post

1101: If you have to ask advice here , you really ARNT competent.
If you have to ask advice here , you shouldnt be doing to job.



Whilst I somewhat agree with your comments ( although you aren’t a competent speller ;-)) ) ,
this site is full of people asking for advice.
There’s hardly a week goes by without someone asking how to wire their house for a network, and from the questions asked it’s obvious they have absolutely no technical knowledge in that area.

265 posts

Ultimate Geek
+1 received by user: 4


  Reply # 2213592 9-Apr-2019 13:26
Send private message quote this post

Brunzy:
1101: If you have to ask advice here , you really ARNT competent.
If you have to ask advice here , you shouldnt be doing to job.



Whilst I somewhat agree with your comments ( although you aren’t a competent speller ;-)) ) ,
this site is full of people asking for advice.
There’s hardly a week goes by without someone asking how to wire their house for a network, and from the questions asked it’s obvious they have absolutely no technical knowledge in that area.

 

[EDIT: I see now whose spelling you were referring to]

 

I agree... why must so many DIY in areas they are not competent, skilled or qualified in... but feel they can once they bounce ideas around in a forum...

 

There a re qualified licensed people out there for a reason, it is not just for your safety now but for the safety of the next owner of the house.  Not to mention the non-electrical implications.

 

 

 

 


neb

883 posts

Ultimate Geek
+1 received by user: 193

Lifetime subscriber

  Reply # 2213600 9-Apr-2019 13:30
Send private message quote this post

Rikkitic:

If the red wires are disconnected one at a time as suggested above, it will become clear if either device is looped off the other. If it behaves as expected, the switch can be changed without problem.

 

 

This assumes however that the house is wired as expected, and wires are colour-coded as expected, e.g. no active/neutral reversed. I've been in several houses, all dating back about 30-40 years, that have over time accreted a complete mishmash of wiring with things patched in by previous owners wherever they was a conduit, who-knows-what sort of connections (not helped by the change in colour codes during that period), etc. This place has the heat pump connected into the circuit for the fridge, wires draped at random across the attic like cobwebs, switches with no obvious function in the walls and four wires leading to them including odd colours like grey and white, and who-knows what else.

378 posts

Ultimate Geek
+1 received by user: 85

Subscriber

  Reply # 2213731 9-Apr-2019 16:42
Send private message quote this post

gregmcc: BTW quite big difference between an electrician and an electrical engineer, "Electrical Engineers create designs that electricians have to fix to make work as intended"

 

Maybe tongue in cheek I realise, but methinks you are not an electrical engineer.





McLean


1649 posts

Uber Geek
+1 received by user: 369

Lifetime subscriber

  Reply # 2213740 9-Apr-2019 17:25
Send private message quote this post

mclean:

 

gregmcc: BTW quite big difference between an electrician and an electrical engineer, "Electrical Engineers create designs that electricians have to fix to make work as intended"

 

Maybe tongue in cheek I realise, but methinks you are not an electrical engineer.

 

 

 

 

no, not an electrical engineer, but way better an Electrical Inspector! ;)

 

 




2611 posts

Uber Geek
+1 received by user: 756


  Reply # 2213743 9-Apr-2019 17:43
Send private message quote this post

Well, it turns out this is not wired as expected at all.

 

The fan must be looped directly from the light batten after all, as when I disconnect one of the reds from "1" nothing worked, and when I tried the other both fan and light worked.

 

So I can't do what I want without an electrician, and I am left wondering what the extra wires hooked up to the switch are actually for... which makes me a little nervous as the only thing that happens when I turn on the switch is that the light and fan start - so what are these other wires powering?

 

As it stands I've put it all back how it was before I started looking.


1 | 2 | 3 | 4 | 5
View this topic in a long page with up to 500 replies per page Create new topic



Twitter »

Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

Orcon announces new always-on internet service for Small Business
Posted 18-Apr-2019 10:19


Spark Sport prices for Rugby World Cup 2019 announced
Posted 16-Apr-2019 07:58


2degrees launches new unlimited mobile plan
Posted 15-Apr-2019 09:35


Redgate brings together major industry speakers for SQL in the City Summits
Posted 13-Apr-2019 12:35


Exported honey authenticated on Blockchain
Posted 10-Apr-2019 21:19


HPE and Nutanix partner to deliver hybrid cloud as a service
Posted 10-Apr-2019 21:12


Southern Cross and ASN sign contract for Southern Cross NEXT
Posted 10-Apr-2019 21:09


Data security top New Zealand consumer priority when choosing a bank
Posted 10-Apr-2019 21:07


Samsung announces first 8K screens to hit New Zealand
Posted 10-Apr-2019 21:03


New cyber-protection and insurance product for businesses launched in APAC
Posted 10-Apr-2019 20:59


Kiwis ensure streaming is never interrupted by opting for uncapped broadband plans
Posted 7-Apr-2019 09:05


DHL Express introduces new MyDHL+ online portal to make shipping easier
Posted 7-Apr-2019 08:51


RackWare hybrid cloud platform removes barriers to enterprise cloud adoption
Posted 7-Apr-2019 08:50


Top partner named at MYOB High Achievers Awards
Posted 7-Apr-2019 08:48


Great ideas start in Gisborne with hackathon event back for another round
Posted 7-Apr-2019 08:42



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.


Support Geekzone »

Our community of supporters help make Geekzone possible. Click the button below to join them.

Support Geezone on PressPatron



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.