  # 2213744 9-Apr-2019 17:51
Send private message

Paul1977:

 

Well, it turns out this is not wired as expected at all.

 

The fan must be looped directly from the light batten after all, as when I disconnect one of the reds from "1" nothing worked, and when I tried the other both fan and light worked.

 

So I can't do what I want without an electrician, and I am left wondering what the extra wires hooked up to the switch are actually for... which makes me a little nervous as the only thing that happens when I turn on the switch is that the light and fan start - so what are these other wires powering?

 

As it stands I've put it all back how it was before I started looking.

 

 

Seems like I was right on the money with my educated guess that the fan was wired from the existing light rather than from the light switch.

 

 


252 posts

Ultimate Geek


  # 2213798 9-Apr-2019 18:33
Send private message

Paul1977:

Well, it turns out this is not wired as expected at all.


The fan must be looped directly from the light batten after all, as when I disconnect one of the reds from "1" nothing worked, and when I tried the other both fan and light worked.


So I can't do what I want without an electrician, and I am left wondering what the extra wires hooked up to the switch are actually for... which makes me a little nervous as the only thing that happens when I turn on the switch is that the light and fan start - so what are these other wires powering?


As it stands I've put it all back how it was before I started looking.



When the wire was disconnected did you check the lights work in adjacent rooms? Could it be the power loop to the next room?

 
 
 
 




2792 posts

Uber Geek


  # 2213807 9-Apr-2019 18:54
Send private message

Kickinbac: When the wire was disconnected did you check the lights work in adjacent rooms? Could it be the power loop to the next room?

 

I didn't, but I got up in the ceiling and followed the cables. You are correct, it's looped to the laundry and toilet.

 

However the switch appears to be wired backwards with phase going into "1" and the light and loop to other lights coming out of "C". It's meant to be the other way around isn't it?




2792 posts

Uber Geek


  # 2213813 9-Apr-2019 18:57
Send private message

gregmcc:

 

Seems like I was right on the money with my educated guess that the fan was wired from the existing light rather than from the light switch.

 

 

As it turns out, you sure were.


897 posts

Ultimate Geek

Trusted

  # 2213816 9-Apr-2019 19:04
Send private message

Ceiling fed , I believe.

1724 posts

Uber Geek

Trusted
Lifetime subscriber

  # 2213823 9-Apr-2019 19:20
Send private message

Paul1977:

 

Kickinbac: When the wire was disconnected did you check the lights work in adjacent rooms? Could it be the power loop to the next room?

 

I didn't, but I got up in the ceiling and followed the cables. You are correct, it's looped to the laundry and toilet.

 

However the switch appears to be wired backwards with phase going into "1" and the light and loop to other lights coming out of "C". It's meant to be the other way around isn't it?

 

 

 

 

Good practice says power in to "C", lights in "1", from an electrical safety view/operational view it makes no difference.

 

 

 

 


Lock him up!
10790 posts

Uber Geek

Lifetime subscriber

  # 2214351 10-Apr-2019 13:04
Send private message

Paul1977:

 

Well, it turns out this is not wired as expected at all.

 

The fan must be looped directly from the light batten after all, as when I disconnect one of the reds from "1" nothing worked, and when I tried the other both fan and light worked.

 

So I can't do what I want without an electrician, and I am left wondering what the extra wires hooked up to the switch are actually for... which makes me a little nervous as the only thing that happens when I turn on the switch is that the light and fan start - so what are these other wires powering?

 

As it stands I've put it all back how it was before I started looking.

 

 

Interesting. Not what I expected but full points to those who pegged it. Also to you for knowing when to quit. I'm sorry you were not able to do what you wanted, but now you know and I think you went about it in exactly the right way. It always pays to be cautious with something like this. If you want to pursue it, you really will need a proper electrician, and it sounds like it might also involve some building work. It might not be worth it.

 

 

 

 





I don't think there is ever a bad time to talk about how absurd war is, how old men make decisions and young people die. - George Clooney
 


 
 
 
 




2792 posts

Uber Geek


  # 2214358 10-Apr-2019 13:14
Send private message

Rikkitic:

 

Interesting. Not what I expected but full points to those who pegged it. Also to you for knowing when to quit. I'm sorry you were not able to do what you wanted, but now you know and I think you went about it in exactly the right way. It always pays to be cautious with something like this. If you want to pursue it, you really will need a proper electrician, and it sounds like it might also involve some building work. It might not be worth it.

 

 

It could be easily done by a sparky without any building work, but it's not enough of an annoyance to us to pay someone to change it.

 

At least I've learned a few things from the exercise.


4232 posts

Uber Geek


  # 2214359 10-Apr-2019 13:20
Send private message

Paul1977:

 

Rikkitic:

 

Interesting. Not what I expected but full points to those who pegged it. Also to you for knowing when to quit. I'm sorry you were not able to do what you wanted, but now you know and I think you went about it in exactly the right way. It always pays to be cautious with something like this. If you want to pursue it, you really will need a proper electrician, and it sounds like it might also involve some building work. It might not be worth it.

 

 

It could be easily done by a sparky without any building work, but it's not enough of an annoyance to us to pay someone to change it.

 

At least I've learned a few things from the exercise.

 

 

Be quite an easy fix if it's simple enough to just get a piece of cable from the fan to the switch flush box.




2792 posts

Uber Geek


  # 2214364 10-Apr-2019 13:29
Send private message

chevrolux:

 

Paul1977:

 

Rikkitic:

 

Interesting. Not what I expected but full points to those who pegged it. Also to you for knowing when to quit. I'm sorry you were not able to do what you wanted, but now you know and I think you went about it in exactly the right way. It always pays to be cautious with something like this. If you want to pursue it, you really will need a proper electrician, and it sounds like it might also involve some building work. It might not be worth it.

 

 

It could be easily done by a sparky without any building work, but it's not enough of an annoyance to us to pay someone to change it.

 

At least I've learned a few things from the exercise.

 

 

Be quite an easy fix if it's simple enough to just get a piece of cable from the fan to the switch flush box.

 

 

Getting cable to it would be easy as there's a straight drop down the wall. But I'm fuzzy on the rules about home owners running new cable, so will probably just flag it.


3019 posts

Uber Geek


  # 2214369 10-Apr-2019 13:51
Send private message

New cable would be an alteration that needs inspection before livening. On a risk basis it seems borderline as you can relocate fittings as long as the original cable is TPS.

1724 posts

Uber Geek

Trusted
Lifetime subscriber

  # 2214547 10-Apr-2019 18:01
Send private message

Paul1977:

 

chevrolux:

 

Paul1977:

 

Rikkitic:

 

Interesting. Not what I expected but full points to those who pegged it. Also to you for knowing when to quit. I'm sorry you were not able to do what you wanted, but now you know and I think you went about it in exactly the right way. It always pays to be cautious with something like this. If you want to pursue it, you really will need a proper electrician, and it sounds like it might also involve some building work. It might not be worth it.

 

 

It could be easily done by a sparky without any building work, but it's not enough of an annoyance to us to pay someone to change it.

 

At least I've learned a few things from the exercise.

 

 

Be quite an easy fix if it's simple enough to just get a piece of cable from the fan to the switch flush box.

 

 

Getting cable to it would be easy as there's a straight drop down the wall. But I'm fuzzy on the rules about home owners running new cable, so will probably just flag it.

 

 

There are a number of factors, is the current hole that the cables go down big enough?

 

If not is there enough ceiling space for drill and extension bits to drill a new hole down.

 

As currently there is no earth (or sign of it at the switch) a new earth will have to be run back to the fuse board

 

 

 

So it's not really straight forward......

 

 


Lock him up!
10790 posts

Uber Geek

Lifetime subscriber

  # 2214553 10-Apr-2019 18:22
Send private message

Surely the electrician who installed the fan would have earthed it?

 

 





I don't think there is ever a bad time to talk about how absurd war is, how old men make decisions and young people die. - George Clooney
 


1724 posts

Uber Geek

Trusted
Lifetime subscriber

  # 2214554 10-Apr-2019 18:26
2 people support this post
Send private message

Rikkitic:

 

Surely the electrician who installed the fan would have earthed it?

 

 

 

 

 

 

You would think, but common practice to not connect an earth to ceiling extract fans as usually they don't require one, if the original circuit didn't have an earth wire


neb

1233 posts

Uber Geek

Trusted
Lifetime subscriber

  # 2215204 11-Apr-2019 18:43
One person supports this post
Send private message

chevrolux:

Be quite an easy fix if it's simple enough to just get a piece of cable from the fan to the switch flush box.

 

 

Unfortunately I think that's how 95% of all dodgy wiring ends up being done:

 

 

Be quite an easy fix if it's simple enough to just get a piece of cable from $source to $dest

 

 

Not saying the OP will put in dodgy wiring, but a general observation on the recipe used for dodgy wiring. With an optional side order of "we can take a tap from $this_wire_here" or "we can reuse $random_colour_wire we have lying around".

1 | 2 | 3 | 4 | 5
View this topic in a long page with up to 500 replies per page Create new topic



Twitter and LinkedIn »



Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

Microsoft launches first Experience Center worldwide for Asia Pacific in Singapore
Posted 13-Nov-2019 13:08


Disney+ comes to LG Smart TVs
Posted 13-Nov-2019 12:55


Spark launches new wireless broadband "Unplan Metro"
Posted 11-Nov-2019 08:19


Malwarebytes overhauls flagship product with new UI, faster engine and lighter footprint
Posted 6-Nov-2019 11:48


CarbonClick launches into Digital Marketplaces
Posted 6-Nov-2019 11:42


Kordia offers Microsoft Azure Peering Service
Posted 6-Nov-2019 11:41


Spark 5G live on Auckland Harbour for Emirates Team New Zealand
Posted 4-Nov-2019 17:30


BNZ and Vodafone partner to boost NZ Tech for SME
Posted 31-Oct-2019 17:14


Nokia 7.2 available in New Zealand
Posted 31-Oct-2019 16:24


2talk launches Microsoft Teams Direct Routing product
Posted 29-Oct-2019 10:35


New Breast Cancer Foundation app puts power in Kiwi women's hands
Posted 25-Oct-2019 16:13


OPPO Reno2 Series lands, alongside hybrid noise-cancelling Wireless Headphones
Posted 24-Oct-2019 15:32


Waikato Data Scientists awarded $13 million from the Government
Posted 24-Oct-2019 15:27


D-Link launches Wave 2 Unified Access Points
Posted 24-Oct-2019 15:07


LG Electronics begins distributing the G8X THINQ
Posted 24-Oct-2019 10:58



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.


Support Geekzone »

Our community of supporters help make Geekzone possible. Click the button below to join them.

Support Geezone on PressPatron



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.