  # 2262211 21-Jun-2019 21:12
One person supports this post
Send private message quote this post

Hmm make sure the RCB is rated to carry that sort of load too.




               The Biggest and the Best.

2119 posts

Uber Geek
+1 received by user: 1200


  # 2262264 22-Jun-2019 00:06
3 people support this post
Send private message quote this post

Daisy chaining is never great, maybe this board instead.
You're not coming close to max load. I'd be genuinely surprised if you draw more than 1000w (4ish amps).

I'd expect your PC's to draw maybe 250-300W fully loaded probably only 100-150w most of the time.
Lamps are stuff all, and could be totally insignificant if you put LED lamps in them.
Monitors are probably going to draw less than the desk lamps
Printer is part time load and is insignificant.

I'd recommend against changing the sockets yourself. Despite how easy it seams, old houses can have some nasty traps, including wiring that falls apart when disturbed.





Location: Dunedin

 


 
 
 
 




5 posts

Wannabe Geek
+1 received by user: 3


  # 2262300 22-Jun-2019 09:00
Send private message quote this post

sen8or: Standard 10 amp socket should be good for around 4kw of power drain before tripping the circuit breaker / fuse (I think its 4.4 but could be mistaken). If old style house (with ceramic fuses and fuse wire), double check what gauge the fuse wire is, should be 10 or 16 amp, if a MCB, check rating, again likely to be 10 or 16 Even with commercial / office installations, the run multiple circuits off the one MCB (i.e. a wall of sockets is only likely to feed back to a handful of breakers) as PCs and other normal office equipment doesn't draw much load

 

 

 

Nice one - I appreciate the advice and thanks for taking the time to reply. 




5 posts

Wannabe Geek
+1 received by user: 3


  # 2262301 22-Jun-2019 09:01
Send private message quote this post

andrewNZ: Daisy chaining is never great, maybe this board instead.
You're not coming close to max load. I'd be genuinely surprised if you draw more than 1000w (4ish amps).

I'd expect your PC's to draw maybe 250-300W fully loaded probably only 100-150w most of the time.
Lamps are stuff all, and could be totally insignificant if you put LED lamps in them.
Monitors are probably going to draw less than the desk lamps
Printer is part time load and is insignificant.

I'd recommend against changing the sockets yourself. Despite how easy it seams, old houses can have some nasty traps, including wiring that falls apart when disturbed.

 

Nice one - I appreciate the advice and thanks for taking the time to reply and yep I think I will use LED in the lamps and thanks too for the suggestion of the board. 


3368 posts

Uber Geek
+1 received by user: 1116

Trusted
Lifetime subscriber

  # 2262336 22-Jun-2019 10:30
Send private message quote this post

@RolemasterGM - being in a similar boat to you in terms of an old house and limited AC outlets, I've got a couple of power boards around the place too but not daisy chained as, fortunately, I don't need to. When purchasing I was wary of cheap stuff so went for this more expensive one (not hyper expensive) for my entertainment unit which had the benefit of adding a couple of USB sockets. I got the 6 socket version for my network.


5477 posts

Uber Geek
+1 received by user: 1914


  # 2262345 22-Jun-2019 10:31
4 people support this post
Send private message quote this post

RolemasterGM:

 

sen8or: Standard 10 amp socket should be good for around 4kw of power drain before tripping the circuit breaker / fuse (I think its 4.4 but could be mistaken). If old style house (with ceramic fuses and fuse wire), double check what gauge the fuse wire is, should be 10 or 16 amp, if a MCB, check rating, again likely to be 10 or 16 Even with commercial / office installations, the run multiple circuits off the one MCB (i.e. a wall of sockets is only likely to feed back to a handful of breakers) as PCs and other normal office equipment doesn't draw much load

 

 

 

Nice one - I appreciate the advice and thanks for taking the time to reply. 

 

 

This post had been set as the answer to this thread. Apologies in advance for all caps but IF YOU DRAW 4kW FROM A STANDARD 10 AMP OUTLET YOU WILL ALMOST CERTAINLY START A FIRE. THIS IS VERY DANGEROUS. DO NOT DO IT.


579 posts

Ultimate Geek
+1 received by user: 197


  # 2262353 22-Jun-2019 10:50
Send private message quote this post

4KW is about 17A, which is way over the 10A rating of most wall sockets!

 

As RunningMan advised DO NOT DO THIS!


 
 
 
 


2858 posts

Uber Geek
+1 received by user: 496


  # 2262410 22-Jun-2019 11:22
Send private message quote this post

RunningMan:

RolemasterGM:


sen8or: Standard 10 amp socket should be good for around 4kw of power drain before tripping the circuit breaker / fuse (I think its 4.4 but could be mistaken). If old style house (with ceramic fuses and fuse wire), double check what gauge the fuse wire is, should be 10 or 16 amp, if a MCB, check rating, again likely to be 10 or 16 Even with commercial / office installations, the run multiple circuits off the one MCB (i.e. a wall of sockets is only likely to feed back to a handful of breakers) as PCs and other normal office equipment doesn't draw much load


 


Nice one - I appreciate the advice and thanks for taking the time to reply. 



This post had been set as the answer to this thread. Apologies in advance for all caps but IF YOU DRAW 4kW FROM A STANDARD 10 AMP OUTLET YOU WILL ALMOST CERTAINLY START A FIRE. THIS IS VERY DANGEROUS. DO NOT DO IT.



If this is going to trigger the end of the world can you explain why a 15 Amp socket only differs in the size of the earth/ground pin?
The current carrying pins are the same as the 10 Amp socket.

Edit: the Electrical Safety Regs prohibit putting a 10 Amp plug on anything drawing more than 10 Amps.

22260 posts

Uber Geek
+1 received by user: 4784

Trusted
Subscriber

  # 2262412 22-Jun-2019 11:30
4 people support this post
Send private message quote this post

Bung:

 

If this is going to trigger the end of the world can you explain why a 15 Amp socket only differs in the size of the earth/ground pin?
The current carrying pins are the same as the 10 Amp socket.

 

Because the area of the pin is plenty, but they needed a key to stop the high draw things going into sockets that were not built to have enough contact area, and to stop people using 1mm extension cords with those loads.

 

A quality socket will take a considerable overload with no problems when it is in good condition. Unfortunately houses do not have electrical WOFs like portable buildings to make sure that things are still ok, and the dire state of many rentals electrics is something that IMO should have been tackled rather than the BS insulation topups that the govt has made people do.

 

Plenty of 70s houses out there with origional PDL sockets with the little flappy switch that barely connects and opened out metal that just touches the pins enough when its held at the right angle. Still earlier houses with the TRS cable in place, rewirable fuses and one socket per room if you're lucky. Overload one of those and watch it burn.

 

Overload a new 600 series socket with a 20 amp welder with the plug changed and the plug will barely get warm. While its new.





Richard rich.ms

755 posts

Ultimate Geek
+1 received by user: 144


  # 2262502 22-Jun-2019 14:59
Send private message quote this post

Brunzy: I wouldn’t worry too much, as regardless of what you add, when it gets too much it will trip the breaker/blow the fuse .

 

Er...no. That's how fires start. Overloading.

 

 

 

It isn't too much, but if you plugged in say a heater, vacuum cleaner or freezer or such, then it could be. And it doesn'r always trip.

 

 


neb

1048 posts

Uber Geek
+1 received by user: 233

Lifetime subscriber

  # 2263875 25-Jun-2019 11:18
Send private message quote this post

Aredwood: Could also be the load side of 2 different MCBs linked together. Meaning that you wont be able to trace which MCB feeds that socket, solely by turning off the MCBs 1 at a time.

It might also be fed from the hot water cylinder circuit, or an old nightstore heater circuit. Especially if those loads are supplied by a separate meter that is billed at a cheaper rate.

 

 

Ah, the dual-MCB thing is a distinct possibility, thanks! I can turn off groups of them via the RCDs that control a block of three or four MCBs, which will be quicker than toggling each MCB separately. The hot water is on a separate circuit, will see if turning that off de-powers the mystery socket.

1 | 2 | 3 
Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic



Twitter and LinkedIn »



Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

Dunedin selects Telensa to deliver smart street lighting for 15,000 LEDs
Posted 18-Jul-2019 10:21


Sprint announces a connected wallet card with built-in IoT support
Posted 18-Jul-2019 08:36


Educational tool developed at Otago makes international launch
Posted 17-Jul-2019 21:57


Symantec introduces cloud access security solution
Posted 17-Jul-2019 21:48


New Zealand government unveils new digital service to make business easier
Posted 16-Jul-2019 17:35


Scientists unveil image of quantum entanglement
Posted 13-Jul-2019 06:00


Hackers to be challenged at University of Waikato
Posted 12-Jul-2019 21:34


OPPO Reno Z now available in New Zealand
Posted 12-Jul-2019 21:28


Sony introduces WF-1000XM3 wireless headphones with noise cancellation
Posted 8-Jul-2019 16:56


Xero announces new smarter tools, push into the North American market
Posted 19-Jun-2019 17:20


New report by Unisys shows New Zealanders want action by social platform companies and police to monitor social media sites
Posted 19-Jun-2019 17:09


ASB adds Google Pay option to contactless payments
Posted 19-Jun-2019 17:05


New Zealand PC Market declines on the back of high channel inventory, IDC reports
Posted 18-Jun-2019 17:35


Air New Zealand uses drones to inspect aircraft
Posted 17-Jun-2019 15:39


TCL Electronics launches its first-ever 8K TV
Posted 17-Jun-2019 15:18



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.


Support Geekzone »

Our community of supporters help make Geekzone possible. Click the button below to join them.

Support Geezone on PressPatron



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.