  # 2319404 17-Sep-2019 19:53
One person supports this post
Send private message quote this post

sparkz25:

 

mattwnz:

 

This is what it looks like now to correct it. Guessing the big box was needed so it matched the screw holes of the old switch.

 

 

 

 

 

Yeah Nah, I wouldn't take that either, still in zone 0 and it doesn't look like there is a gland in the bottom.

 

The simplest solution would have been to mount the powerpoint on a post outside of the tank.

 

I would at a guess say the plug has been chopped off and joined in that box now.

 

 

 

 

 

 

For this junction box to be in Zone 0 it must be IPX7, a close up of the sticker that shows the rating or make and model would be good so this can be checked, a photo that shows how the cable goes in to the box would be good as well, bet it's just a standard cable gland which will not be IPX7

 

Judging by what's there it would seem to be a rushed "Fix".

 

The solution is to mount a junction box on a post outside the container, bringing the cable thru a hole in the side.

 

 

 

 




15230 posts

Uber Geek


  # 2319455 17-Sep-2019 20:15
Send private message quote this post

Thanks. I can see from the photo that has TK written on the side and googling it, it looks like it is one of these, which says it is IP 66 https://www.vynco.co.nz/products/enclosures/spelsberg-tk-series-ps 

 

So is that box no good. Should they replace it with an IP67 one at the very least?


 
 
 
 


1725 posts

Uber Geek

Trusted
Lifetime subscriber

  # 2319539 18-Sep-2019 04:35
Send private message quote this post

mattwnz:

 

Thanks. I can see from the photo that has TK written on the side and googling it, it looks like it is one of these, which says it is IP 66 https://www.vynco.co.nz/products/enclosures/spelsberg-tk-series-ps 

 

So is that box no good. Should they replace it with an IP67 one at the very least?

 

 

 

 

Correct, so it looks like another poor quality repair, did they issue an ESC/CoC for the repairs? If you like I'll copy PM you the relevant section of AS/NZS3000 so you have something to quote them


799 posts

Ultimate Geek


  # 2319557 18-Sep-2019 06:59
Send private message quote this post

The whole interconnection stuff should be completely outside of the inner zone. The problem arises when the pump doesn't keep the water at low level for any reason, hence the junction box will get submersed.





- ISP1: T-OneBox FTTH modem, 1/.5G, full DS, VLAN7, VoIP + ipTV streaming flat

 

- ISP2: 4G/LTE USB modem + TL-MR3020, 100/40M data plan (wireless fallback)

 

- NET: ZBOX nano router, 2 C2960X-48TS-L, 2 GWN7630, GWN7610, EL1600usb

 

- SVR: E3C236 32G/20TB, 2 H2 16G/500GB, HC2 4TB, 2 C2 1TB | 2 HC2 14/1TB

 

- IoT+3D: LoRaWAN, 5G, CCU3 (openHAB/MQTT), 2 Ender-3, UM2E+, UM3, CNC

 

- USR: NUC8i7HVK, EliteBook 840, Aspire E5, N2, Galaxy Tab, mobiles, 2 4K TVs

 

- ipPBX: GRP2613, GO-Box 100, SPA112 (Fax and W-48, a 1948 Siemens phone)


4244 posts

Uber Geek


  # 2319562 18-Sep-2019 07:13
2 people support this post
Send private message quote this post

Wow... I'm the first person to play a bit fast and loose with electrical stuff. But sticking a hot point in a water tank?!?!? What kind if Sparky does this.....

I wouldn't want them back, and as gregmcc says, and would report immediately to the respective authorities.

600 posts

Ultimate Geek


  # 2319592 18-Sep-2019 09:09
Send private message quote this post

What does it look like if you remove the cover?


515 posts

Ultimate Geek


  # 2319653 18-Sep-2019 10:53
Send private message quote this post

3rd times a charm, they'll need to come back and remedy that properly....


 
 
 
 


8916 posts

Uber Geek

Lifetime subscriber

  # 2319747 18-Sep-2019 13:06
One person supports this post
Send private message quote this post

given your other issues i wouldnt be using them for anything else and reporting them.




15230 posts

Uber Geek


  # 2319909 18-Sep-2019 17:15
Send private message quote this post

gregmcc:

 

mattwnz:

 

Thanks. I can see from the photo that has TK written on the side and googling it, it looks like it is one of these, which says it is IP 66 https://www.vynco.co.nz/products/enclosures/spelsberg-tk-series-ps 

 

So is that box no good. Should they replace it with an IP67 one at the very least?

 

 

 

 

Correct, so it looks like another poor quality repair, did they issue an ESC/CoC for the repairs? If you like I'll copy PM you the relevant section of AS/NZS3000 so you have something to quote them

 

 

 

 

Thanks, I have access to a copy of the previous edition which has that clause in it. The tank installw as part of the overall electrical work on the building, which I understand they have provided a CoC for the entire house build. I don't think there was any additional paperwork for the repair job yesterday as far as I know, unless he gave that to the builder who contracted him for the job.

 

I have pasted the images of the IP ratings of the box and the cable entry into the box which is inside the tank, and the box is IP66, not IP67. We have now  been told the pump circuit is on an RCD, although we don't know which circuit or RCD it is on, as the circuit isn't identified on the switch or in the meterboard. They  also said that the wires were connected within the outside round conduit box as shown below, which is a Marley product, which is directly behind the box on the inside of the tank, and is close to ground level.  Marley has said this  box  is rated at IP 53. Although it can be IP66   if the lid of the conduit box is cement fixed to the body of the fitting, where gluing obviously wouldn't be a good idea should the  pump needs replacing and needs rewiring in again.  I would have thought it would be better for the connection to be inside the box in the tank, if a proper IP67 box is used, than outside the tank in this type of box, certainly in the case of nuisance tripping of the RCD. I think we will need to get another electrician in to look at it this and see what they say. There is also an overlow on the tank into a soakpit, so water should never get this high in the manhole part of the tank.

 

 

 

 

 

 

 

 

 

 


1725 posts

Uber Geek

Trusted
Lifetime subscriber

  # 2319925 18-Sep-2019 17:25
Send private message quote this post

The box does not comply, regardless of if the connections are in this box or in the conduit box on the outside.

 

 

 

The cable gland may or may not comply, depends on the brand, Elmark brand ones do they are IP68, can't tell from the picture what brand it is.

 

Easiest way to see if it's on a RCD is to turn off all the RCD's and see if it still runs when you operate the float switch.

 

I would be surprised if it is on a RCD!

 

 




15230 posts

Uber Geek


  # 2319929 18-Sep-2019 17:28
Send private message quote this post

Thanks, I will try that to test if it is on an RCD.




15230 posts

Uber Geek


  # 2319973 18-Sep-2019 19:23
Send private message quote this post

After testing all the RCD etc, I discovered that the pump doesn't appear to be working at all, as the plumber had the value set so all the taps were running off the mains supply. Switching the valve  over to the tank pump, it is not working with all RCDs and other circuit breakers on. So will have to go back to the electrician anyway to check there is power to it.  


1 | 2 
Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic



Twitter and LinkedIn »



Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

Chorus to launch Hyperfibre service
Posted 18-Nov-2019 15:00


Microsoft launches first Experience Center worldwide for Asia Pacific in Singapore
Posted 13-Nov-2019 13:08


Disney+ comes to LG Smart TVs
Posted 13-Nov-2019 12:55


Spark launches new wireless broadband "Unplan Metro"
Posted 11-Nov-2019 08:19


Malwarebytes overhauls flagship product with new UI, faster engine and lighter footprint
Posted 6-Nov-2019 11:48


CarbonClick launches into Digital Marketplaces
Posted 6-Nov-2019 11:42


Kordia offers Microsoft Azure Peering Service
Posted 6-Nov-2019 11:41


Spark 5G live on Auckland Harbour for Emirates Team New Zealand
Posted 4-Nov-2019 17:30


BNZ and Vodafone partner to boost NZ Tech for SME
Posted 31-Oct-2019 17:14


Nokia 7.2 available in New Zealand
Posted 31-Oct-2019 16:24


2talk launches Microsoft Teams Direct Routing product
Posted 29-Oct-2019 10:35


New Breast Cancer Foundation app puts power in Kiwi women's hands
Posted 25-Oct-2019 16:13


OPPO Reno2 Series lands, alongside hybrid noise-cancelling Wireless Headphones
Posted 24-Oct-2019 15:32


Waikato Data Scientists awarded $13 million from the Government
Posted 24-Oct-2019 15:27


D-Link launches Wave 2 Unified Access Points
Posted 24-Oct-2019 15:07



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.


Support Geekzone »

Our community of supporters help make Geekzone possible. Click the button below to join them.

Support Geezone on PressPatron



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.