Kia ora, we're being asked by Vector whether we want single or three phase power for our new build. As I understand it, there's no longer any significant advantage with 3-phase for solar PV (a some-day project), but there is for car fast charging e.g. a 22kw charger. At the moment both our cars are internal combustion, but it seems inevitable that we'll go electric with at least one of them eventually. I'm putting cabling inthe garage wall for that eventuality. But from what I'm reading, putting a 22kw charger in a garage is not worthwhile, and hence I think there's no longer any reason to go for 3-phase?


Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic
 1 | 2
RunningMan
8912 posts

Uber Geek


  #2756530 7-Aug-2021 14:37
Send private message

If there isn't a significant cost difference, then go 3 phase. Much easier to do it now than later. There's only a handful of current EVs that will take 22kW AC (Renault Zoe is the most obvious, and given it cannot DC charge, then AC is important), however plenty that will do 11kW (16 amp 3 phase). If you're potentially looking at charging 2 EVs, then the extra capacity may be important, be it being able to charge 2 simultaneously, or just 1 rapidly.




lyndondrake

236 posts

Master Geek

ID Verified

  #2756532 7-Aug-2021 14:39
Send private message

It's a pretty big cost difference, estimated to be $7-10k difference. But I hadn't realised that even the 11kw chargers needed 3 phase. (& Yes I imagine we'll have 2 cars charging eventually)


MrAmerica
128 posts

Master Geek
Inactive user


  #2756534 7-Aug-2021 14:46
Send private message

I put 3 phase in mine but I have a large shed/man cave/ workshop with a couple things that run on 3 phase. I ran it to the house as well just in case we went EV (which we are about to do for one car) There is a chart in this link for Tesla that shows range per hour vs power https://www.tesla.com/en_NZ/support/home-charging-installation/faq

If I sign up to one of the free hour per day power companies on 3 phase I can throw 75kms range into the car per hour at 16A per phase. On single its just 50k range per hour at 32A.




sparkz25
750 posts

Ultimate Geek
Inactive user


  #2756554 7-Aug-2021 16:29
Send private message

If you are rural definitely go 3 phase, if you're in town and have the option, I would also go 3 phase.

 

If you don't want to do it now at least run the cable for the main incomer so that you can change over at a later date!

 

The cable is cheap now and it will be much easier to install it now than later on having to dig up the driveway and concrete and pay someone to run it all again, may as well do it first time and then have the option for it in the future.

 

Edit: How Much cable are we talking? as in the distance from the pole/pillar to the meter box?


RunningMan
8912 posts

Uber Geek


  #2756580 7-Aug-2021 18:23
Send private message

lyndondrake:[snip] But I hadn't realised that even the 11kw chargers needed 3 phase. (& Yes I imagine we'll have 2 cars charging eventually)

 

 

Excuse the rounding errors, but as a guide:

 

8 amp single phase = 1.9 kW

 

16 amp single phase = 3.6 kW

 

32 amp single phase = 7.2 kW

 

16 amp three phase = 11 kW

 

32 amp three phase = 22 kW

 

There's nothing common that goes above 32 amp per phase so if you want more than 7 kW you need three phase supply and a vehicle with onboard three phase charger.


lyndondrake

236 posts

Master Geek

ID Verified

  #2756589 7-Aug-2021 19:27
Send private message

It's about 30m so it's not insignificant, but it's a helpful suggestion to run the cable now and maybe only liven one up for now?


sparkz25
750 posts

Ultimate Geek
Inactive user


  #2756595 7-Aug-2021 19:48
Send private message

lyndondrake:

 

It's about 30m so it's not insignificant, but it's a helpful suggestion to run the cable now and maybe only liven one up for now?

 

 

 

 

At that distance, I would definitely allow for it now, and you can just liven up one phase, for now, that shouldn't be a problem at all.

 

 


 
 
 
 

Shop now for Lenovo laptops and other devices (affiliate link).
Scott3
3946 posts

Uber Geek

Lifetime subscriber

  #2756635 7-Aug-2021 23:58
Send private message

For benefit of people who stumble across this this via searches:

 

My understanding is that the Auckland lines company vectors "standard" residential connections are:

 

  • 60A single phase (Approx 14kW)
  • 60A three phase (Approx 41kW)

I understand that the vector charge the same monthly connection fees for the above two connection's. This is not the case in all area, some lines companies charge substantially more monthly fees for a three phase connection, something to check out if you are deciding between the two.

 

I understand that other area regions / lines company areas other residential connections are sometimes offered, for example:

 

  • 100A single phase (Approx 23kW)
  • 60A two phase (Approx 28kW) - I have a family members semi rural house with this setup.

 

 

For OP, the key decision points are:

Do/might you need to run any "Three phase" equipment? If so get three phase. 

 

In short, three phase induction motors are better than single phase ones, so most stationary industrial machines run three phase motors. Many welders use two of three phases to get the 400v phase to phase voltage. If you ever plan to have a workshop with stuff like bigger lathes, mills, compressor, welder etc, then three phase power would be super handy. Means you can pick up cheap ex-industrial / ex-commercial gear cheap too.

 

Some bigger (really big) heat pump's are three phase only (as an example Mitsubishi electrics 22.4kW and 25kW heating PEA series dusted heat pumps are three phase only). Same deal for bigger (25kW+) swimming pool heat pumps.

 

Some stuff is three phase, simply because of the amount of power it draws, and is a basic resistance load that could be run off single phase of one had enough capacity. Common examples would be Clay Kiln's, Sauna's etc.

 

Is 60A single phase (approx 14kW) going to be enough?

 

Comes down to how big / power hungry the house is. A big factor to this is if your house is going to be all electric, or use other fuels like gas. And generally how much power hungry stuff you have (spa pool, swimming pool, water pump)

 

Note that it is the pole fuse that will blow if this is exceeded (for many minutes if only just), which means no power for a couple of hours and paying for the lines company to come out and replace it. If you want you can have a main breaker installed in your property (instead of the typical main switch) which should protect the pole fuse, but with the advantage of being self re-settable. Electrician will need to do a calculation based on a bunch of stuff and may require you to go three phase, or have a main breaker added.

 

My house is a 60A single phase. As an example of load that would take to exceed that (all at the same time):

 

  • Hot water 16A
  • Oven 16A
  • Lounge heat pump flat out 8A
  • Tumble dryer 8A
  • Induction cooktop (32A @50%): 16A.

That's me past my 60A limit if I did all that stuff at once. Could also use:

 

  • 8A of lighting
  • 2x 8A fan heaters
  • 8A of misc plug in load (TV's, computers, Electronic's, chargers, rice cooker etc.)
  • 8A EV charger
  • 8A hair dryer

 

 

I consider my setup (all electric fairly small 3 bedroom +study house) to be about on the limits of a 60A supply, but have never blown a pole fuse. But if OP is going to have stuff like dual ovens in their kitchen (A steam oven and a normal oven looks like a sweet setup), 90cm induction cooktop (43A feed needed), spa pool, swimming pool or similar, three phase would be a good call.

 

 

 

Other things to consider;

 

Solar (/battery): In short, with current tech, single phase solar solutions are a little cheaper than thee phase solutions. Three phase battery solutions are harder to come by.

 

One big issue with three phase solar setups is phase balance. As an example if one had a solar setup that with current lighting conditions was generating 3.6kW, and was set up with either a thee phase inverter (or matching numbers of micro inverters on each phase), it would be making 1.2kW on each phase. Lets say everything in the house was off, except for a 3.6kW hot water cylinder connected to a single phase. Phases will be as follow's:

 

     

  1. 1.2 solar - 3.6kW load = 2.4kW Import
  2. 1.2kW Export
  3. 1.2kW Export

 

The issue with the above, is that power companies pay around 6c/kWh for exports, but charge 18 - 30 c/kWh for imports, and it is calculated per phase. So the above situation would result in a charge from the power company. If it was a single phase setup, net demand is zero, no import or export, so no charge from the power company...

 

 

 

Next issue is that many current battery products (such as tesla power wall), are single phase only. No three phase option (other than having three of them, one on each phase, great but $$$). The two phase family members house I mentioned above recently had a solar + battery setup installed. Installers recommended that the phase loading be changed from a fairly even spread, to everything (solar, battery & all load) to being on one phase. Means they could use single phase solar gear (no such thing as two phase inverters, so would have needed two separate single phase ones), they don't waste any generation to exports, that could potentially self consume, and the Battery back's up everything (5kW max draw).

 

Possibly pushing it, having that house all on one 60A phase (drinking water pump, electric fence machine, pool with 2x pumps, 2x bigish heatpumps, 32A EV charger etc), but they have the hot water & pool on timers so they run in the middle of the day when there is solar output, they avoid charging the EV while cooking dinner, and they have the 5kW of output from the battery to chip in unless it has gone flat. No issues so far.

 

Hopefully in the next decade or so there will be a polyphase battery solution, that can produce unbalanced output to match phase loading, and can move power between phases to avoid the simultaneous export & import situation. That said, a lot of north america is single phase, and a lot Europe has "Net metering" so phase balance doesn't matter, so the market for the product may be kinda small.

 

 

 

EV's

 

First thing, is that people who don't have EV's often overestimate their need for charging speed at home. As long as an overnight charge adds enough range to cover the next day's needs, you are golden. And note it is very rare to start from zero %.

 

A 8h overnight charge from a wall outlet (at 8A) adds about 100km of range. A 8h overnight charge from a 32A wall-box ads about 350km range.

 

Also note that for very rare use case situation's can be covered by spending 30mins at a fast charger if you have one nearby.

 

Surprising numbers of EV owners make do with the the slow 8A cord as their main charging method.

 

Times it is nice to have fairly faster charging ability at home:

 

  • Ability to top off quickly during the day. - Say you do 80km commuting / running errands in the morning, come home to pack bags / have lunch for say 2.5 hours in the middle of the day before heading out of town. 7.4kW charging would have replaced that 80km in that time, but charging from a wall outlet would have only replaced about 20km.
  • If you have a longer commute, and faster charging is either needed to cover that, or for that to fit in your power companies off peak window.
  • You do back to back long trips, and want the ability to be fully charged when you wake up.
  • You have a EV with a massive battery pack, i.e. Rivian R1T with 180kWh pack. charging that at 7kW is going to take 25 hours, faster charging would be nice...

 

 

I would recommend that any EV owner with a 40kWh battery or bigger have a wall charger installed. Kinda nice to be able to fully recharge overnight and top off fairly quickly, and the $2k cost of the setup pales in comparison to the cost of the car.

 

Most better EV's at the moment support charging close to maxing out a 32A single phase connection (cira 7.4kW). A decent number also support 3x16A charging (11kW). Ability to charge at 22kW (3x32A) is rare - pritty much just the zoe at the moment.

 

In terms of wall boxes, 3 phase ones generally cost only slightly more, Generally they all support 32A, but have jumpers inside to slow them down if your wiring can't handle that.

 

For dwellings that are close to maxing out their capacity, EV wall-boxes are available that do the following:

 

  • Share a set amount of power (say 32A) around multiple EV's dynamically (say 50:50 at the start, then 100:0 once one finishes)
  • Measure your house's total (single phase) draw, and slow down the EV charging if required to avoid overload. For example:

https://oemaudio.co.nz/electric-vehicle-charging-products/eo-mini-pro-2-wall-charger-white-active-load-management-package

 

 

 

But to answer the headline question, if it is a bigger house, and charging two EV's at once, three phase would definitely be nice to have.


Batman
Mad Scientist
29724 posts

Uber Geek

Trusted
Lifetime subscriber

  #2756641 8-Aug-2021 07:18
Send private message

if a house is $ 1 million dollars, what is another 10k?


lyndondrake

236 posts

Master Geek

ID Verified

  #2756645 8-Aug-2021 08:18
Send private message

Scott3:

 

For benefit of people who stumble across this this via searches: …

 

But to answer the headline question, if it is a bigger house, and charging two EV's at once, three phase would definitely be nice to have.

 

 

This is awesome - just the kind of detail I needed. The only difference is that Vector are offering us 32A, 60A, or 100A fuses, as well as the 1- or 3-phase choice (& we're in Auckland).

 

Batman:

 

 

if a house is $ 1 million dollars, what is another 10k?

 

 

I still have to find the cash, but yes I agree more or less. It's one of those things which can't be deferred until later in any sensible way and which future-proofs the house in significant and helpful ways.

 


  #2756647 8-Aug-2021 08:54
Send private message

I don't think there's likely to be a serious need for >7kW charging of a single EV - that allows for a full battery charge overnight for almost any car on the market, and needing to do two days in a row at full range is going to be unusual, especially on those vehicles with a very large battery. I would expect single-phase chargers to be *much* cheaper than three phase given the RCDs, cable etc. required.

 

 

 

But the higher capacity is going to be useful when considering a charger or two, large heat pump, electric stove/oven etc.

 

 

 

It also gives you the option to consider continuous-flow electric hot water.


lyndondrake

236 posts

Master Geek

ID Verified

  #2756648 8-Aug-2021 09:27
Send private message

SomeoneSomewhere:

 

But the higher capacity is going to be useful when considering a charger or two, large heat pump, electric stove/oven etc.

 

It also gives you the option to consider continuous-flow electric hot water.

 

 

I hadn't thought about continuous-flow hot water. That is a very interesting thought. Saves all that space used for a hot water tank.

 

And yes, it's not so much for one charger, but the long-term thought about an eventual progression in battery capacity (= higher charging demand), and multiple vehicles. Admittedly all of that is mitigated by the option for solar PV and battery storage but unless fully off-grid then the inbound grid power is still vital.


afe66
3181 posts

Uber Geek

Lifetime subscriber

  #2756652 8-Aug-2021 10:29
Send private message

I'd go three phase for a new build because of cost of retrofitting but then I'm also interested in workshop equipment that runs on three phase. Ie lathe drills etc.

Whether you really need it for charging car us interesting question unless you have huge commute its not vital.

Almost everyone can probably charge with single phase overnight.

My 24kw uk nisan leaf can draw 32A and I installed a dedicated 32A as cost over 16A was minimal, but 3 years after install I haven't found need to modify the main board for 32A. But I only do 200 km per week.


Most if new cars commng out in Europe can do at least 7kw (32a)

But if you gave two cars each wanting to draw 32A single phase that's quite a draw.

Ps might have three cars in future if teenagers start driving evs


zenourn
271 posts

Ultimate Geek

Trusted
DR

  #2756654 8-Aug-2021 10:48
Send private message

I'd recommend 3-phase. We have it and have two EVs and even though neither supports 3-phase charging and only charge at modest rates it is great being able to split load over the phases.

 

We sometimes use over 100 A (have power monitoring system, see major contributors below) which would be pushing it for a single phase connection.

 

7.2 kW (32A) EV1
3.6 kW (16A) EV2
3.6 kW (16A) Hot water
4 kW (18A) Heat pumps
3.3 kW (15A) Oven
1 kW (5A) Base load


neb

neb
11294 posts

Uber Geek

Trusted
Lifetime subscriber

  #2756786 8-Aug-2021 15:08
Send private message

sparkz25:

If you don't want to do it now at least run the cable for the main incomer so that you can change over at a later date!

 

 

That's not just for EVs, it's also if you have a basement or similar that someone might in the future decide to use as a workshop, having it already wired for 3-phase will be a selling point at that time.

 1 | 2
Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic





News and reviews »

Logitech G522 Gaming Headset Review
Posted 18-Jun-2025 17:00


Māori Artists Launch Design Collection with Cricut ahead of Matariki Day
Posted 15-Jun-2025 11:19


LG Launches Upgraded webOS Hub With Advanced AI
Posted 15-Jun-2025 11:13


One NZ Satellite IoT goes live for customers
Posted 15-Jun-2025 11:10


Bolt Launches in New Zealand
Posted 11-Jun-2025 00:00


Suunto Run Review
Posted 10-Jun-2025 10:44


Freeview Satellite TV Brings HD Viewing to More New Zealanders
Posted 5-Jun-2025 11:50


HP OmniBook Ultra Flip 14-inch Review
Posted 3-Jun-2025 14:40


Flip Phones Are Back as HMD Reimagines an Iconic Style
Posted 30-May-2025 17:06


Hundreds of School Students Receive Laptops Through Spark Partnership With Quadrent's Green Lease
Posted 30-May-2025 16:57


AI Report Reveals Trust Is Key to Unlocking Its Potential in Aotearoa
Posted 30-May-2025 16:55


Galaxy Tab S10 FE Series Brings Intelligent Experiences to the Forefront with Premium, Versatile Design
Posted 30-May-2025 16:14


New OPPO Watch X2 Launches in New Zealand
Posted 29-May-2025 16:08


Synology Premiers a New Lineup of Advanced Data Management Solutions
Posted 29-May-2025 16:04


Dyson Launches Its Slimmest Vaccum Cleaner PencilVac
Posted 29-May-2025 15:50









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.