It depends on the exchange in regards to the power that is being supplied. Larger ones have generators, smaller ones only have battery backup.

 

The generators are tested monthly and from memory have 7-21 days of Diesel to keep them going depending on their business importance and size of the tanks so that's plenty of time before they will need to be refilled.

 

The battery only exchanges I think were good for 4 days. They also can take a generator being cabled in if power is going to be off for any longer so if needs be one will be dropped outside.

 

All DSL cabinets have battery backup to keep them that I think is good for 24-36 hours.

 

All of the above could be completely wrong as I am going from very vague memory on this.

 

The comms I have seen today include: 31 PSTN cabinets and exchanges with mains fail alarms running on backup power with varying capacity.

 

I'm sure the impacts will be minor as this isn't  Spark and/or Chorus's first rodeo and Christchurch Earthquake has proven out the BCP plans.

 

The main impact will be downed overhead cables and how quickly they will be repaired on a per customer / smaller area basis.






2770 posts

Uber Geek
+1 received by user: 448


  Reply # 1931034 5-Jan-2018 20:30
One person supports this post
Send private message

The standby power alternators will basically run indefinitely.  They usually have a main tank outside the building, the contents of which are pumped into a header tank inside. The header tank has a float switch that controls the header tank pump.

 

Going back a few years now. The alternators used to be tested monthly by swtiching off the mains and be run for about an hour. The output would be checked for correct voltage and frequency.

 

The header tank pump auto fill function would also be tested regularly by draining the header tank back into the main tank. There was also an hand pump in case the header pump failed.

 

All in all the system was very robust both in design and in the testing/checking processes. The chances of there ever being an exhange failure due to a power failure at a main exchange was pretty well zero.

 

Even the chance of a smaller battery only exchange failing due to a power supply was virtually nil. If necessary a portable alternator was brought in.

 

All exchange batteries were discharge tested at regular intervals to test their capacity and were replaced when they fell below acceptable limits.

 

It really was a gold plated belts and braces system

 

I don't know what standards apply today but  I never recall any exchange falling due a power outage during my time in the game.





Sony Xperia X running Sailfish
Jolla C
Nokia N1
Dell Inspiron 14z i5


1542 posts

Uber Geek
+1 received by user: 381


  Reply # 1931047 5-Jan-2018 20:54
2 people support this post
Send private message

chevrolux:

 

Yea no idea what the official expected time is. But at Palmy exchange there is an enormous amount of battery power, and then there is also a huge genny. I would of thought it could essentially run on genny power indefinitely provided a supply of fuel was there. Stand to be corrected, but from memory pretty much anywhere there was a NEAX there is a genny (off the top of my head in the Manawatu area anyway). The smaller RLU's (dotted in suburbs and out in rural areas) just have batteries but can all have a genny hooked up to them.

 

I'll never forget that room/floor full of batteries.

 

My response upon first seeing it was; wait, those are not structural I-beams - that's power distribution!


2770 posts

Uber Geek
+1 received by user: 448


  Reply # 1931052 5-Jan-2018 21:16
Send private message

MadEngineer:

 

I'll never forget that room/floor full of batteries.

 

My response upon first seeing it was; wait, those are not structural I-beams - that's power distribution!

 

 

I recall being on a course and visiting the battery room at the Caro Street CAX and  see the boardwalk part way up the sides of the cells so that it was possible to service the batteries. I don't recall the size now but the cells were higher than the average person, hence the need fo the boardwalk. I'm guess each 2.2v cell would have been about 750 mm square or possibly larger.

 

Even much smaller exchange batteries had an awesome capacity to deliver a prodigious amount of current as was demostrated on occasion. I remember new batteries being installed, the electrician slipped with the spanner touching the live side to the frame carrying the cables from the battery room to the switchroom. The frame was earthed. Outside in the power room where I was standiing the nuts on the bolts holding the frame together turned red hot and dropped off onto the floor. These were only 500 A/H batteries.





Sony Xperia X running Sailfish
Jolla C
Nokia N1
Dell Inspiron 14z i5


3474 posts

Uber Geek
+1 received by user: 1249

Subscriber

  Reply # 1931150 6-Jan-2018 09:14
Send private message

MadEngineer:

chevrolux:


Yea no idea what the official expected time is. But at Palmy exchange there is an enormous amount of battery power, and then there is also a huge genny. I would of thought it could essentially run on genny power indefinitely provided a supply of fuel was there. Stand to be corrected, but from memory pretty much anywhere there was a NEAX there is a genny (off the top of my head in the Manawatu area anyway). The smaller RLU's (dotted in suburbs and out in rural areas) just have batteries but can all have a genny hooked up to them.


I'll never forget that room/floor full of batteries.


My response upon first seeing it was; wait, those are not structural I-beams - that's power distribution!



I would love to see what happens if say a screw driver was dropped between some live plates. Would be such a site!

3709 posts

Uber Geek
+1 received by user: 781


  Reply # 1931176 6-Jan-2018 11:31
3 people support this post
Send private message

Or a sight, too.

2806 posts

Uber Geek
+1 received by user: 1058

Subscriber

  Reply # 1931179 6-Jan-2018 11:38
Send private message

chevrolux:I would love to see what happens if say a screw driver was dropped between some live plates. Would be such a site!


That would be both fun and scary to see. As arc welders typically only output around 50V no load, and often a lot less under load. As they are basically just a large constant current power supply.

I'm just picturing the amount of short circuit current available at 48V, and the damage that that much current could do. Presumably the bus bars have been designed with enough separation, so that If a short occurs. The gap will be too large for an arc to be sustained after the thing that caused the short has melted away or exploded.





2770 posts

Uber Geek
+1 received by user: 448


  Reply # 1931214 6-Jan-2018 12:22
Send private message

chevrolux:
MadEngineer:

 

chevrolux:

 

 

 

Yea no idea what the official expected time is. But at Palmy exchange there is an enormous amount of battery power, and then there is also a huge genny. I would of thought it could essentially run on genny power indefinitely provided a supply of fuel was there. Stand to be corrected, but from memory pretty much anywhere there was a NEAX there is a genny (off the top of my head in the Manawatu area anyway). The smaller RLU's (dotted in suburbs and out in rural areas) just have batteries but can all have a genny hooked up to them.

 

 

 

I'll never forget that room/floor full of batteries.

 

 

 

My response upon first seeing it was; wait, those are not structural I-beams - that's power distribution!

 



I would love to see what happens if say a screw driver was dropped between some live plates. Would be such a site!

 

Are you talking about the plates in the battery cell? As you possibly know many exchanges batteries used to be open top cells with the plates and electrolyte open the the atmosphere. There were glass plates arranged to cover most of the exposed area, but the cells were still open. When a boost charge was being applied there was a lot more hydrogen gas released from the cells, the glass plates would help contain the splashes from the bubbles of hydrogen, and also help stop debris from dropping into the cell.

 

We used to read the S.G.s by placing a hydrometer float into the electrolyte. There was alway a smell of hydrogen gas when you went into the battery room particularly during a booster charge. Hence the sign on the door "NO NAKED FLAMES".

 

So in reply to your statement about the effects of dropping screw driver it would depend.

 

If it were between to adjacent plates possibly not much would happen. As the potential difference between two adjacent plates is quite small. Over time the plates shed bits from their surface and this stuff drops to the bottom. Gradually it builds up till it bridges the gap between the plates. This is what causes most batteries to gradually fail. You don't see anything spectacular.

 

It it were across several plates then there may be a bit more to see, perhaps some red hot metal and an increased hydrogen output. It there was a spark and the corrrect concentrations of hydrogen were present then I wouldn't want to be anywhere close by. I seem to remember several years ago an AVO meter being placed on a cell with spectaular results when the metal name/information/plate on the base of the meter made contact with the plate connectors.





Sony Xperia X running Sailfish
Jolla C
Nokia N1
Dell Inspiron 14z i5


2770 posts

Uber Geek
+1 received by user: 448


  Reply # 1931218 6-Jan-2018 12:44
One person supports this post
Send private message

Aredwood:
chevrolux:I would love to see what happens if say a screw driver was dropped between some live plates. Would be such a site!


That would be both fun and scary to see. As arc welders typically only output around 50V no load, and often a lot less under load. As they are basically just a large constant current power supply.

I'm just picturing the amount of short circuit current available at 48V, and the damage that that much current could do. Presumably the bus bars have been designed with enough separation, so that If a short occurs. The gap will be too large for an arc to be sustained after the thing that caused the short has melted away or exploded.

 

The arc distance for a 50 volt supply is pretty small. The bus bar gaps were way way more than that. If there was ever a short, generally the material causing the short would turn red hot and melt breaking the short circuit. There wasn't a great amount of sparking going on.

 

Wearing metal band wrist watches was not a smart idea while doing any work around bus bars.





Sony Xperia X running Sailfish
Jolla C
Nokia N1
Dell Inspiron 14z i5


452 posts

Ultimate Geek
+1 received by user: 138


  Reply # 1931231 6-Jan-2018 13:15

That's the reason I never wear any jewellery at work. I have seen the scars from an expanding watch scrap across a car battery. Not pretty, and bloody painful.


122 posts

Master Geek
+1 received by user: 32


  Reply # 1931316 6-Jan-2018 14:52
Send private message

Looking through the UFB documentation https://www.crowninfrastructure.govt.nz/wp-content/uploads/2011/12/Network-Infrastructure-Project-Agreement-NIPA-26-January-2017-redacte....pdf (PDF page 115) it specifies 8 hours back up power supply is required as a minimum and if a generator is not on site, then there needs to be a facility to plug one in.

2360 posts

Uber Geek
+1 received by user: 782

Trusted
Lifetime subscriber

  Reply # 1931435 6-Jan-2018 19:26
One person supports this post
Send private message

chevrolux: I would love to see what happens if say a screw driver was dropped between some live plates. Would be such a site - sight !

 

I've seen photos, when I am back at work I will see if I can dig any out to share.

 

Many of the bus bars are rated up to 3000+ AMPs at 48V DC, they get pretty warm when under full load. So whenever screwdrivers / spanners have been dropped across the positive and negative terminals it tends to leave a dent in the bus bar and the tool completely disintegrates. It's covered in the Chorus Protecting The Network (PTN) videos that everyone needs to take annually if you are going to go onsite into a Chorus / Spark exchange. A quick google will find the first video.






1430 posts

Uber Geek
+1 received by user: 150


  Reply # 1931551 7-Jan-2018 07:07
Send private message

richms:

 

Starscream122:

 

show us a pic of a passive splitter in a street?

 

 

They are in the pits that you see them working on occasionally, not much to see there, when I snooped over the sholder of a guy working it just looked like coils of the thin fiber that they were joining onto the ones going to houses.

 

 

I'm on Auckland's North Shore and several times I've seen open Chorus pits that have what looks like a stack of white dinner plates extending out of the pit. I assumed that the fibre cables were somehow connected to whatever this stack thing is. Is that a passive splitter?


7674 posts

Uber Geek
+1 received by user: 2527

Subscriber

  Reply # 1931554 7-Jan-2018 07:32
Send private message

https://www.pcworld.co.nz/article/481730/pictures_ufb_-_chorus_fibre_home_installation_part_2_/

 

this might be one in a cabinet

 

i imagine they are much the same in the pits


6193 posts

Uber Geek
+1 received by user: 251

Trusted
Subscriber

  Reply # 1931555 7-Jan-2018 07:32
Send private message

Hi, "white dinner plates", this sounds more like a splicing cassette, ie where the splice joints are housed, but the splitter can be attached to that assembly depending on exact setup.

 

Cyril


1 | 2 | 3
View this topic in a long page with up to 500 replies per page Create new topic

Twitter »

Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

Microsoft Dynamics 365 Business Central launches
Posted 10-Jul-2018 10:40


Spark completes first milestone in voice platform upgrade
Posted 10-Jul-2018 09:36


Microsoft ices heated developers
Posted 6-Jul-2018 20:16


PB Technologies charged for its extended warranties and warned for bait advertising
Posted 3-Jul-2018 15:45


Almost 20,000 people claim credits from Spark
Posted 29-Jun-2018 10:40


Cove sells NZ's first insurance policy via chatbot
Posted 25-Jun-2018 10:04


N4L helping TAKA Trust bridge the digital divide for Lower Hutt students
Posted 18-Jun-2018 13:08


Winners Announced for 2018 CIO Awards
Posted 18-Jun-2018 13:03


Logitech Rally sets new standard for USB-connected video conference cameras
Posted 18-Jun-2018 09:27


Russell Stanners steps down as Vodafone NZ CEO
Posted 12-Jun-2018 09:13


Intergen recognised as 2018 Microsoft Country Partner of the Year for New Zealand
Posted 12-Jun-2018 08:00


Finalists Announced For Microsoft NZ Partner Awards
Posted 6-Jun-2018 15:12


Vocus Group and Vodafone announce joint venture to accelerate fibre innovation
Posted 5-Jun-2018 10:52


Kogan.com to launch Kogan Mobile in New Zealand
Posted 4-Jun-2018 14:34


Enable doubles fibre broadband speeds for its most popular wholesale service in Christchurch
Posted 2-Jun-2018 20:07



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.