Geekzone: technology news, blogs, forums
Guest
Welcome Guest.
You haven't logged in yet. If you don't have an account you can register now.




543 posts

Ultimate Geek

Subscriber

# 109442 19-Sep-2012 21:41
Send private message

Hi guys

I hope someone can help me with this one. As i have tried to look and have had nothing but conflicting ideas on the issue.

I am trying to drive an engine underwater. I have measured it to run at 8A@12V.

Now here is where the confusion is. Wire and connectors are rated at Voltages and amps. So if i have a connector that says it is rated for 300V@8A. Some sites say I have an exact limit on the part of 8A where as some say I have a limit of 2400W so at 12V I should be able to run 200A.

So which one is correct?

I think it should be in Watts. But i am in no way a qualified and up till now I have only been working at low voltage and low amps.




Geoff E

Create new topic
3267 posts

Uber Geek

Trusted

  # 688499 19-Sep-2012 23:26
Send private message

The voltage rating is the breakdown voltage of the wire. If you are to leave the cable in water then it might absorb moisture which will eventually corrode the wire (but will be a long time).

The current rating is irrespective of voltage or cable length. It is the maximum current that will give a known temperature rise under normal ambient conditions for the purpose the cable was designed for (e.g. outdoors rated cable will handle more heat). When you work at extreme temperature then you de-rate the cable accordingly.

There is a 3rd spec which is not a limitation on the cable but a limitation on your application. Wire has a finite resistance which causes a voltage drop so the longer the cable the more the voltage drop. In house wiring the test is to draw maximum current at the furthest socket and measure the voltage drop (between no load and maximum load) which should be less than I think it is 20V (or something like that). If the drop is greater then you need to increase the wire size, if the drop is less then you could have saved money by using thinner cable. But primarily this test checks for poor connections which will heat up and could start a fire, not checking your wire size.

For your application if you get a cable which has a datasheet it will state the resistance per km of cable so you can work out the resistance for your length x2 (because current flows down one wire and returns up the other). Then resistance times current gives you the theoretical voltage drop due to the cable length. I would try to keep it below 5%, or not more than 10% of the applied voltage. Remember 10% voltage drop is 20% power drop.

You might be able to increase the voltage you apply to the cable to compensate for the voltage drop, but remember the voltage drop depends on the load which will not be constant. The ultimate is a cable with a pair of sense wires back to the power supply so it changes the power supply output voltage to always get e.g. 12V at the other end of the cable irrespective of the load.

For short cables of only a few meters this is all academic and just use whatever 8A rated wire you can find. It is in water anyway so will be cooled down much better than if it was in air.

(I assume you measured 8A under load and in the target application, not free running.)




You can never have enough Volvos!


22894 posts

Uber Geek

Trusted
Subscriber

  # 688666 20-Sep-2012 11:03
Send private message

If anything the current will go down with voltage as voltage drop becomes more critical.

That is why 1mm cable is fine for 10A on mains stuff, but would be well undersized in car use etc.




Richard rich.ms

 
 
 
 


gzt

11026 posts

Uber Geek


  # 689809 22-Sep-2012 10:38
Send private message

geocom: Now here is where the confusion is. Wire and connectors are rated at Voltages and amps. So if i have a connector that says it is rated for 300V@8A. Some sites say I have an exact limit on the part of 8A where as some say I have a limit of 2400W so at 12V I should be able to run 200A. So which one is correct?


The relationship above is exactly backwards. Simple example -

10 volts at 10 watts = 1 amp
100 volts at 10 watts = 0.1 amp (100ma)

Taking this a bit further - a connector capable of reliably handing 200A at 12V is huge. Like the lugs on your starter motor or car battery earth.


3267 posts

Uber Geek

Trusted

  # 689924 22-Sep-2012 16:47
Send private message

Connector (and switch) ratings are done different from wire, because they need to handle a make/break surge (or spec'ed as not capable of). Here you also need to consider AC vs. DC, it uses different plating to handle the make/break current. Specs are also derated with increased ambient temperature. You need to stick within the specifications or else it will not last.

Wire is just wire. The current will cause a temperature rise in the wire. On double the length wire you get double the temperature rise, but spread over double the cable length so the temperature rise at any one point is still the same. But the issue is with length causing a voltage drop so your motor will not get the full voltage. Double the cable length and you get double the voltage loss which translates to 4 times the power loss. The higher the voltage the lower the effective percentage power loss (which is why power lines are run at higher voltage). Suppose you get 5V loss on 240V, it is only 2%. But 5V loss on 10V is 50%. It all depends on your application, there is not exact current rating for cable size.




You can never have enough Volvos!




543 posts

Ultimate Geek

Subscriber

  # 689937 22-Sep-2012 17:16
Send private message

gzt:
geocom: Now here is where the confusion is. Wire and connectors are rated at Voltages and amps. So if i have a connector that says it is rated for 300V@8A. Some sites say I have an exact limit on the part of 8A where as some say I have a limit of 2400W so at 12V I should be able to run 200A. So which one is correct?


The relationship above is exactly backwards. Simple example - 

10 volts at 10 watts = 1 amp
100 volts at 10 watts = 0.1 amp (100ma)

Taking this a bit further - a connector capable of reliably handing 200A at 12V is huge. Like the lugs on your starter motor or car battery earth.



I dont see how its backwards.

The connector is rated for 300V@8A therefore Watts is Voltage*Amps so 300*8=2400W. If you want to work out the Amp at 12V you take 2400W/12=200A.

Anyway to be safe i am going to up the connector to a 16A connector better to go over than be right on the mark. The cable in this case is able to run at 16A anyway far higher than i will be using and the cable will be shorter than 1/2 a meter.




Geoff E

gzt

11026 posts

Uber Geek


  # 689959 22-Sep-2012 18:17
Send private message

geocom: I dont see how its backwards. The connector is rated for 300V@8A therefore Watts is Voltage*Amps so 300*8=2400W. If you want to work out the Amp at 12V you take 2400W/12=200A.

Watts is a measure of the power output of the system - the measure of actual work performed in the real world.

If you are getting 2400 watts of output at 300 volts you will see 8 amps flowing in that circuit.

If you are getting 2400 watts of output at 12 volts then you will see 200 amps flowing in that circuit.

The less voltage you are using, the more current (amps) you need to get the same power output.

For cable size the flow of amps in the system is the important part. More amps flowing > bigger cables required.

Does that make things a bit clearer?

3267 posts

Uber Geek

Trusted

  # 690036 22-Sep-2012 22:29
Send private message

geocom: The connector is rated for 300V@8A therefore Watts is Voltage*Amps so 300*8=2400W. If you want to work out the Amp at 12V you take 2400W/12=200A.

No, it does not work that way for contact rating.  Typically the DC current rating is also lower than the AC current rating, because the changing of polarity in AC helps with self cleaning and reduces the instantaneous power dissipated in the contact when it makes/breaks (or something like that, too late at night to think).  You need to refer to the relay/switch datasheet to get the correct rating for the application.




You can never have enough Volvos!


 
 
 
 




543 posts

Ultimate Geek

Subscriber

  # 690043 22-Sep-2012 22:40
Send private message

Niel:
geocom: The connector is rated for 300V@8A therefore Watts is Voltage*Amps so 300*8=2400W. If you want to work out the Amp at 12V you take 2400W/12=200A.

No, it does not work that way for contact rating.  Typically the DC current rating is also lower than the AC current rating, because the changing of polarity in AC helps with self cleaning and reduces the instantaneous power dissipated in the contact when it makes/breaks (or something like that, too late at night to think).  You need to refer to the relay/switch datasheet to get the correct rating for the application.


Yep fully understand that i though that gzt was saying that my understanding of Wattage was backwards.




Geoff E

gzt

11026 posts

Uber Geek


  # 690096 23-Sep-2012 10:13
Send private message

geocom: The connector is rated for 300V@8A therefore Watts is Voltage*Amps so 300*8=2400W. If you want to work out the Amp at 12V you take 2400W/12=200A.

geocom: Yep fully understand that i though that gzt was saying that my understanding of Wattage was backwards.

It is. You are taking the amperage rating of a connector at a particular voltage - and then converting that to watts and saying the same connector will handle that number of watts at any voltage/current you want to name.

I don't want to be a bad guy but you made a serious mistake there - and if you do not understand it there will be smoke and fire.



543 posts

Ultimate Geek

Subscriber

  # 690338 23-Sep-2012 22:52
Send private message

It's not backwards. Converting the max to wattage is just wrong.

In this case i had conflicting reports from different sites. Neither site I had used in the past. So i had no real ability to tell which one i should believe. Both made sense but conflicted on the main point. After all there are many items that are rated in Watts such as resistors.

So i had some real doubts. Knowing the risks of if the wires get hot enough the plastic will melt which will cause a spark if the 2 wires meet. I decided to ask on a place i trust. At least I now know with 100% certainty which one is correct.




Geoff E

Create new topic



Twitter and LinkedIn »



Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

Netflix releases 21 Studio Ghibli works
Posted 22-Jan-2020 11:42


Vodafone integrates eSIM into device and wearable roadmap
Posted 17-Jan-2020 09:45


Do you need this camera app? Group investigates privacy implications
Posted 16-Jan-2020 03:30


JBL launches headphones range designed for gaming
Posted 13-Jan-2020 09:59


Withings introduces ScanWatch wearable combining ECG and sleep apnea detection
Posted 9-Jan-2020 18:34


NZ Police releases public app
Posted 8-Jan-2020 11:43


Suunto 7 combine sports and smart features on new smartwatch generation
Posted 7-Jan-2020 16:06


Intel brings innovation with technology spanning the cloud, network, edge and PC
Posted 7-Jan-2020 15:54


AMD announces high performance desktop and ultrathin laptop processors
Posted 7-Jan-2020 15:42


AMD unveils four new desktop and mobile GPUs including AMD Radeon RX 5600
Posted 7-Jan-2020 15:32


Consolidation in video streaming market with Spark selling Lightbox to Sky
Posted 19-Dec-2019 09:09


Intel introduces cryogenic control chip to enable quantum computers
Posted 10-Dec-2019 21:32


Vodafone 5G service live in four cities
Posted 10-Dec-2019 08:30


Samsung Galaxy Fold now available in New Zealand
Posted 6-Dec-2019 00:01


NZ company oDocs awarded US$ 100,000 Dubai World Expo grant
Posted 5-Dec-2019 16:00



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.


Support Geekzone »

Our community of supporters help make Geekzone possible. Click the button below to join them.

Support Geezone on PressPatron



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.