Ok you sparkies - can/how this be done?! (for CCTV).
Need 230volt at 10 amps but only draw about .3 of an amp.
About 100 meters from a 230v supply.
Currently 2 unused Cat 5 cables in the duct to where we need this 230v supply.
Can we send low voltage that distance and convert to 230v?!
Thanks from a non sparkie.





Why work on Wednesday and stuff up 2 good long weekends

Create new topic
427 posts

Ultimate Geek
+1 received by user: 80


  Reply # 1563579 1-Jun-2016 11:44
Send private message

Ethernet cable isn't designed for 200+v. Can you use one of the leads as a draw wire to pull through some flex?


1551 posts

Uber Geek
+1 received by user: 311

Lifetime subscriber

  Reply # 1563600 1-Jun-2016 12:23
Send private message

Smallest size cable over that distance will be 10mm2 (buried in duct).

 

that will give you a standard 10A 230V circuit

 

You could put in a permanent connection and a 6 A circuit breaker, that will get you down to a 4mm2 cable


21128 posts

Uber Geek
+1 received by user: 4215

Trusted
Subscriber

  Reply # 1563601 1-Jun-2016 12:28
3 people support this post
Send private message

What CCTV needs 230v? Everything I have seen is all extra low voltage so a simple power over ethernet converter would have dealt with it.

 

70 watts is within the realm of PoE, assuming the 0.3A is actual and not just the rating on a powersupply that is actually going to be much less.





Richard rich.ms

7346 posts

Uber Geek
+1 received by user: 3446

Subscriber

  Reply # 1563610 1-Jun-2016 12:41
Send private message

You might get away with something like this if you go to an intermediate voltage. For example, you could convert down to 24 or 48 volts. This might be doable using existing maritime components. 24 volts is fairly standard, not sure about 48 volts but you could get that with two 24-volt transformers in series. At 24 volts the cables would need to carry roughly 3 amps. I don't know how much loss you would encounter over 100 metres. 

 

 





I reject your reality and substitute my own. - Adam Savage
 


278 posts

Ultimate Geek
+1 received by user: 53

Subscriber

  Reply # 1563612 1-Jun-2016 12:44
Send private message

richms:

 

What CCTV needs 230v? Everything I have seen is all extra low voltage so a simple power over ethernet converter would have dealt with it.

 

70 watts is within the realm of PoE, assuming the 0.3A is actual and not just the rating on a powersupply that is actually going to be much less.

 

 

Exactly what I was thinking!  

 

He did mention 100m though, so pretty much on the limits of an Ethernet run without being repeated, let alone running PoE over it.

 

 


21128 posts

Uber Geek
+1 received by user: 4215

Trusted
Subscriber

  Reply # 1563614 1-Jun-2016 12:58
One person supports this post
Send private message

chimera:

 

Exactly what I was thinking!  

 

He did mention 100m though, so pretty much on the limits of an Ethernet run without being repeated, let alone running PoE over it.

 

 

POE is specced to work out to 100m. 2 runs so worst case put a POE to 12v or whatever the device really takes adapter on both runs and parallel them up.

 

Although in saying that I have only seen 50-60w POE used to power devices with their own internal converters, not seen a seperate standalone 12v output adapter for the higher power POE standards.

 

Since the 802.3at standard only allows you to use 2 pairs, you could always get 4 converters and break the pairs out if it came to it.





Richard rich.ms



237 posts

Master Geek
+1 received by user: 1


  Reply # 1563754 1-Jun-2016 16:23
Send private message

Thanks everyone for your input and will pass it on.
I too was surprised at the 230v requirement but it may be for the connection into the fibre.
Just that we have quite a number of retailers that supply a power source for the CCTV in our small CBD and one has gone sour! It is costing them about $2 per month.




Why work on Wednesday and stuff up 2 good long weekends

21128 posts

Uber Geek
+1 received by user: 4215

Trusted
Subscriber

  Reply # 1563758 1-Jun-2016 16:35
2 people support this post
Send private message

If you can identify the gear on the end then perhaps some other suggestions can be made?





Richard rich.ms

2709 posts

Uber Geek
+1 received by user: 1006

Subscriber

  Reply # 1563908 1-Jun-2016 22:58
Send private message

Since you said that the 2 cat5 cables are unused, this makes it easy. Just strip back both cables. Twist all of the conductors in each cable together. So you would then be using each cat5 as if it was only a single strand cable. Assuming each strand is 26AWG, you will have just over 1mm2 in total cable size. If you then run 48VDC over it, 1.5A will then give you 70W. And you will have about 5.5V of volt drop. I haven't allowed for possible temp rise of the cable increasing the volt drop though.

 

 

 

Also the definition of "extra low voltage" is less than 120V ripple free DC. Or 50V AC. Of course it doesn't say if that is in reference to ground, or max line to line voltage. So you might be able to connect one of the conductors to +120VDC. And the other to -120VDC. So you will have a total of 240VDC at the far end. And if you have switchmode stepdown adaptors at the far end, that can handle anything between 100-240VAC. Virtually all of them simple rectify the mains to DC anyway. Before stepping it down. So you would be able to wire the +-120VDC into the existing power supplies. Main difficulty would be finding an off the shelf power supply that outputs +-120VDC.

 

 

 

But the easiest way is to simply to offer to pay that retailer $3 per month for the power used. Im guessing that you are a landlord or working on behalf of the landlord. So you / they would be able to account for that $3/month at the next rent review.

 

Any idea if that retailer tries to bill their ISP for the power used by the default supplied modem/router? Or bill their cellphone network for the power used to charge their cellphone? Chorus has a term in their standard UFB contract that they are not responsible for paying for the power used by their fibre ONT. Kind of scary that they had to include that clause.






632 posts

Ultimate Geek
+1 received by user: 174


  Reply # 1563917 1-Jun-2016 23:39
Send private message

Any idea if that retailer tries to bill their ISP for the power used by the default supplied modem/router? Or bill their cellphone network for the power used to charge their cellphone? Chorus has a term in their standard UFB contract that they are not responsible for paying for the power used by their fibre ONT. Kind of scary that they had to include that clause.

 

That's because the ONT is actually part of the Chorus Network, not the customer's.




237 posts

Master Geek
+1 received by user: 1


  Reply # 1564131 2-Jun-2016 11:49
Send private message

Will toss these ideas to the contractor.
Appreciate the detail you have given.
Thanks




Why work on Wednesday and stuff up 2 good long weekends

Create new topic

Twitter »

Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

N4L helping TAKA Trust bridge the digital divide for Lower Hutt students
Posted 18-Jun-2018 13:08


Winners Announced for 2018 CIO Awards
Posted 18-Jun-2018 13:03


Logitech Rally sets new standard for USB-connected video conference cameras
Posted 18-Jun-2018 09:27


Russell Stanners steps down as Vodafone NZ CEO
Posted 12-Jun-2018 09:13


Intergen recognised as 2018 Microsoft Country Partner of the Year for New Zealand
Posted 12-Jun-2018 08:00


Finalists Announced For Microsoft NZ Partner Awards
Posted 6-Jun-2018 15:12


Vocus Group and Vodafone announce joint venture to accelerate fibre innovation
Posted 5-Jun-2018 10:52


Kogan.com to launch Kogan Mobile in New Zealand
Posted 4-Jun-2018 14:34


Enable doubles fibre broadband speeds for its most popular wholesale service in Christchurch
Posted 2-Jun-2018 20:07


All or Nothing: New Zealand All Blacks arrives on Amazon Prime Video
Posted 2-Jun-2018 16:21


Innovation Grant, High Tech Awards and new USA office for Kiwi tech company SwipedOn
Posted 1-Jun-2018 20:54


Commerce Commission warns Apple for misleading consumers about their rights
Posted 30-May-2018 13:15


IBM leads Call for Code to use cloud, data, AI, blockchain for natural disaster relief
Posted 25-May-2018 14:12


New FUJIFILM X-T100 aims to do better job than smartphones
Posted 24-May-2018 20:17


Stuff takes 100% ownership of Stuff Fibre
Posted 24-May-2018 19:41



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.