Looking for some help with the following problem: I'm trying to control 26 water valve stations with a newly purchased Hunter Irrigation Controller. It is replacing an old controller. The old controller was energizing 26 valves with 24vdc .24 amp solenoids at 26 different times,1 at a time. The new controller will do the same except its output is 24vac. I would like to keep the 24vdc solenoids and build circuit boards to convert 24vac to 24vdc. I know if I make a simple bridge rectifier(NTE166) it will work "if" I keep the - leads separate from each solenoid. I really don't want to do that. The problem I am having is if I use - as a common for the other solenoids I will get 12vdc on the the non-energized solenoids(energizing them) when I only programmed 1 to turn on. I believe I am getting AC ripple. I read you can control this ripple by inserting a capacitor and a resistor in the circuit(see schematic). I don't know what rating cap and resistor to use. Any help would be appreciated.    

 


Create new topic

k14

580 posts

Ultimate Geek
+1 received by user: 75


  Reply # 1621292 2-Sep-2016 11:09
2 people support this post
Send private message

Why don't you just buy 24AC solenoids? They are the standard irrigation solenoids, might cost you a bit up front but is by far the simplest way to go about things. Look on ebay if you wan to save some $$, irrigation equipment is very expensive over here.


5069 posts

Uber Geek
+1 received by user: 2062


  Reply # 1621315 2-Sep-2016 11:38
Send private message

Think─źng out loud here but what if you use a diode on the negative lead for each solenoid?  This will force unidirectional current flow.





Mike

239 posts

Master Geek
+1 received by user: 25


  Reply # 1621639 2-Sep-2016 20:38
Send private message

Don't make it difficult.
You can get power supplies for roughly $100nz, 50~240vac input 24dc out, quite often the ins and outs are selectable. Google for local supply of a unit.

Why didn't you get a controller that matched your solenoids?




Masterpiece Calibration Ltd, isf certified

 

www.mastercal.co.nz

 

 

"I'm not a robot!"

539 posts

Ultimate Geek
+1 received by user: 125

Subscriber

  Reply # 1621866 3-Sep-2016 11:38
Send private message

Masterpiece: Don't make it difficult.
You can get power supplies for roughly $100nz, 50~240vac input 24dc out, quite often the ins and outs are selectable. Google for local supply of a unit.

Why didn't you get a controller that matched your solenoids?

 

 

 

+1, I would try connecting a 24VDC power supply to your controller as it will be stepped down and rectified anyway power the controller's IC and 24VDC should be passed through to the solenoids.

 

If you really want to rectify the AC input yourself you need to connect the AC outputs of your power supply to the AC inputs of the rectifier, and the DC outputs of the rectifier to the AC inputs of the controller.

 

Image result for bridge rectifier

 

If you find other solenoids a powering when they're not meant to be you have probably mistakenly connected your solenoid common to your AC neutral insted of your rectified DC negative.

 

If you find DC is not being passed through the controller due to an internal isolation transformer your only option is to use a rectifier for each solenoid. Or as @MikeAqua alluded to you could try simply adding a diode to the controller-side of the solenoid's common and seeing how they will work on a half-wave.

 

 


1772 posts

Uber Geek
+1 received by user: 620

Trusted
Subscriber

  Reply # 1621870 3-Sep-2016 11:50
Send private message

I'd run the 24VAC into interposing relays with a 24VDC power supply for the contact side. Simple and cheap to do. 

 


You won't get a nice DC signal from a bridge rectifier.


3098 posts

Uber Geek
+1 received by user: 1198

Subscriber

  Reply # 1622743 4-Sep-2016 21:29
Send private message

k14:

 

Why don't you just buy 24AC solenoids? They are the standard irrigation solenoids, might cost you a bit up front but is by far the simplest way to go about things. Look on ebay if you wan to save some $$, irrigation equipment is very expensive over here.

 

 

 

 

Fully agree. Also AC is better because if moisture gets through the insulation of your solenoid wiring. With DC you will get electrolytic corrosion, While with AC you don't tend to get it.

 

Also have you tried AC onto your existing solenoids to see if they will still work?

 

I have an old Toro DDC 8 irrigation controller. Which runs on and outputs 24VAC. I opened it up to see how it switches it's outputs. It uses 1A TRIACs. So my controller probably won't like having rectifier circuits connected to it's outputs. And it definitely won't work if I connect DC to it's power input terminals.

 

 






Create new topic

Twitter »

Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.