#136513 29-Nov-2013 18:36
Send private message

I would like to decommission our F&P Paprika free standing oven.
It is on a dedicated 230volt 30amp circuit with a fixed connection (as wired to the standard in 1969/70).

Once the Oven is removed, can the circuit support 1x 15amp socket & 4x 10amp sockets (with an estimated 6kw in use at peak times)?

This is for two different/separate induction plates, a small toaster oven, a dish washer & a spare hot point for other kitchen use.

I can provide model/power consumption spec's if required.

Thanks in Advance!

Create new topic
DarthKermit
5346 posts

Uber Geek

Trusted

  #943078 29-Nov-2013 18:43
Send private message

I'm not a sparky, but I think you'd need to have a sub main with circuit breakers rated appropiately for the outlets you mentioned.

This could cost more than just running lighter guage cables from your fuseboard to your kitchen.




Whatifthespacekeyhadneverbeeninvented?




andrewNZ
2487 posts

Uber Geek
Inactive user


  #943115 29-Nov-2013 19:37
Send private message

Short answer is maybe.

I'd suggest getting someone to look. It's not as simple as banging on some fittings, there is probably a lot more work in it than you think. you're more than likely going to need work done in the switchboard to bring the new stuff up to the required standard.

You may be holding a can of worms...

gregmcc
2147 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #943139 29-Nov-2013 20:23
Send private message

What kind of wiring is there in the house? White plastic TPS or black rubber TRS, if it's white TPS then that shouldn't be a problem as long as you change the size of the fuse at the fuse board end.

Now this is where the fun begins, now that you are changing from a 30amp outlet to a mixture of 10Amp and 15amp outlets you must install a suitiable RCD protection, this means fitting an RCD circuit breaker at your fuse board, now been a fuse board from the 70's your now going to be stuck with upgrading the entire fuse board to a modern distrubition board as modern RCD's will not fit on an old fuse board, and depending on the state of the wiring you may need to get a good portion of the house re-wired.

Basically you are about to open a very large can of worms here, best thing you can do it put the can down and walk away.



richms
28172 posts

Uber Geek

Trusted
Lifetime subscriber

  #943149 29-Nov-2013 20:51
Send private message

do it with a subboard that you put the breakers in. There are horrid surface din breaker enclosures that some sparkys will put onto an old phenolic or whatever the later stuff is fuse board, but chances are there is not enough space on it and it will just end up a mess. I have seen 2 houses which have had the old cooktop replaced with a small breaker panel and a few sockets when a gas cooktop was put in its place.

There is all sorts of things they have to do with earth loop impedance on things to make sure it is compliant as well. Poor sparkys having to have all that compliance to deal with. I am glad I have a good sparky as a relative to deal with all that carry on ;)

Im not sure what the maximum that you can have a circuit with power points on it protected at. I seem to recall 25 or 27A from a previous discussion.




Richard rich.ms

Porboynz
110 posts

Master Geek


  #944358 2-Dec-2013 20:30
Send private message

iROK: I would like to decommission our F&P Paprika free standing oven.
It is on a dedicated 230volt 30amp circuit with a fixed connection (as wired to the standard in 1969/70).

Once the Oven is removed, can the circuit support 1x 15amp socket & 4x 10amp sockets (with an estimated 6kw in use at peak times)?

This is for two different/separate induction plates, a small toaster oven, a dish washer & a spare hot point for other kitchen use.

I can provide model/power consumption spec's if required.

Thanks in Advance!


Well you can go from a larger gauge wire to a lighter gauge TPE wire OK, but not the other way around.  Therefore the initial 30 amp wiring run probably can be reused (5mm?)  The main issue as mentioned is that the proposed power outlets will not be protected by an RCD as oven feeder circuits usually bypass RCD's on fuse boards (assuming they are fitted).  The fuse rating will also be incorrect for a HP circuit.  I think if you need to ask the question it really does mean you really should get an electrician involved, but its always good to know what you are up for, right?  Good luck.

iROK

26 posts

Geek


  #944400 2-Dec-2013 21:36
Send private message

Some interesting replies, thank your for your feedback.
OK, so electricity 101; 230V X 30A = 6.9kW of max power can be consumed on this circuit before overloading & 'blowing' a fuse (wire).
Is that a correct statement?

I know the 30A fuse & holder will need to be fully upgraded to the RCD type as the old fitting is too big, and that's OK.

What I want to know; can the EXISTING 30A rated wire (of whatever gauge they used for this type of over range circuit in 1970) be kept in place?
Why does new wiring have to be installed?

AND if it does, can I have the fittings I desire be installed (1x 15A, 3-4x 10A)

YES I will be getting a SPARKY in, just getting one at a time I can be there too...



andrewNZ
2487 posts

Uber Geek
Inactive user


  #944410 2-Dec-2013 21:48
Send private message

Whether or not the cable can be reused depends on several things including what it is and what shape its in.

Ultimately, it will probably be replaced and you'll likely end up with 2 circuits.

 
 
 

Trade NZ and US shares and funds with Sharesies (affiliate link).
cyril7
9058 posts

Uber Geek

ID Verified
Trusted
Subscriber

  #944419 2-Dec-2013 22:15
Send private message

I know the 30A fuse & holder will need to be fully upgraded to the RCD type as the old fitting is too big, and that's OK.


You are confusing MCB and RCD, these are not exactly the same thing, by messing with the switchboard you expose yourself to some serious upgrades to meet standard.

Aside of that the existing cable assuming it was a 4 or 6mm TPS can be retained with a 20A MCB plus any RCD protection and a set of 10A sockets on it, why the 15A though.

Cyril

richms
28172 posts

Uber Geek

Trusted
Lifetime subscriber

  #944440 2-Dec-2013 23:16
Send private message

15A for a decent coffee maker, a deep fryer or an arc welder ;)




Richard rich.ms

webwat
2036 posts

Uber Geek

Trusted

  #955805 21-Dec-2013 13:40
Send private message

richms: 15A for a decent coffee maker, a deep fryer or an arc welder ;)

Mite need a big aircon on the kitchen bench, or a 3kVA UPS to run the sandwich maker.




Time to find a new industry!


iROK

26 posts

Geek


  #955877 21-Dec-2013 15:30
Send private message

Nahh, just it's just a 2.8kw Induction Hob.

Am waiting for the E.Inspector to sign off on the proposed change(s), which might not happen till next year now.
Apparently Gas BBQ's need inspecting too :-P

I'll have to post a photo when done.


iROK

26 posts

Geek


  #990178 19-Feb-2014 09:53
Send private message

The BILL finally came in last week... $530 with certification.
Traditional Stove gone & Dishwasher in it's place, 2x Induction units on top & a SMART Oven above. 
Photo below





Create new topic





News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.