Forgot to mention ... if the manual says2.4kw and it had cop 3 doesn't it make it 7kw eq of a heat pump



Batman

Mad Scientist
30014 posts

Uber Geek
+1 received by user: 6217

Trusted
Lifetime subscriber

  #887817 1-Sep-2013 16:08
Send private message

Let me rephrase ... if a 6kw hhet pump fujirsu nocria has cop 4.44 what would the outdoor unit max out? I will try to find out

Handle9
11925 posts

Uber Geek
+1 received by user: 9675

Trusted
Lifetime subscriber

  #887824 1-Sep-2013 16:24
Send private message

joker97: Let me rephrase ... if a 6kw hhet pump fujirsu nocria has cop 4.44 what would the outdoor unit max out? I will try to find out


The units are rated for heating or cooling not electrical power. You divide by the COP to get power consumption.

Your example means 6kW of heating consumes 6kW ÷ 4.44 = 1.35kW power consumption.

This COP does not take into account the power used by the electrical defrost element on the outdoor unit.