EgorNZ:
HarmLessSolutions:
In our case the inverter came 'preloaded' with a relatively unforgiving grid voltage acceptance. Following inverter shut downs our installer widened those parameters to +/-5% which solved the problem, until Powerco installed new infrastructure in our area which has increased the voltage again.
I suggest you ask your installer to check that your settings are as wide as they can be under current regulations (i.e. +/-5%) and bear in mind that the upcoming changes to AS/NZS 4777.1:2024 which I'm advised will allow setting to be +/-10% are likely to arrive in NZ early next year.
Interesting, thanks!
Does your Fronius throw errors about the grid voltage? I was just looking at the docs and saw there are codes for this. But the only errors my system produces are about grid frequency.
As I mentioned above our 8.2 Primo regularly shows "Notice: State 567" in a dark band on the bottom of its display. I've even watched the display over time during what should have been maximum generation conditions and the output hovers around 7.5kW but when it rises to 7.9+kW the error displays and the output reverts back to ~7.5kW again. This was while we had the Evnex drawing >7kW so this wasn't an export limiting measure on the inverter's part, other than as a result of grid over voltage.
Also the above behaviour occurs too briefly for it to register in the logging of its data.