SomeoneSomewhere
1882 posts

Uber Geek
+1 received by user: 1086

Lifetime subscriber

  #2513803 28-Jun-2020 08:46
Send private message

Get the electrician to megger the circuit while they are there - this will hopefully pick up any cable faults.




kiwifidget
"Cookie"
3641 posts

Uber Geek
+1 received by user: 1969

Lifetime subscriber

  #2513854 28-Jun-2020 10:55
Send private message

wow, I have this exact problem!

 

House is 12-15y old, the switchboard has RCD thingies in it which often trip, guaranteed when we are away, and takes out the freezer, the garage doors, my pis and a windows server, and the electric gate.

 

We have lost a lot of food this way.

 

Himself is always blaming my pc gear, but maybe its the freezer!

 

So far I mitigate this by using a UPS on the pc gear and get the UPS software to email me when it detects an outage.

 

 





Delete cookies?! Are you insane?!


gregmcc
2173 posts

Uber Geek
+1 received by user: 836

ID Verified
Trusted
Lifetime subscriber

  #2513859 28-Jun-2020 11:10
Send private message

kiwifidget:

 

wow, I have this exact problem!

 

House is 12-15y old, the switchboard has RCD thingies in it which often trip, guaranteed when we are away, and takes out the freezer, the garage doors, my pis and a windows server, and the electric gate.

 

We have lost a lot of food this way.

 

Himself is always blaming my pc gear, but maybe its the freezer!

 

So far I mitigate this by using a UPS on the pc gear and get the UPS software to email me when it detects an outage.

 

 

 

 

 

 

it may not be just 1 thing causing the problem, it's could be several items, it could be a small earth leakage in the defrost element (not enough on it's own) that is enough to trip the RCD.

 

or it could be a faulty RCD, or it could be faulty wiring, with out getting it checked out there is no way to see for sure, don't take for granted that just because someone else has a similar problem that the solution for you will be the same.

 

 




richms
29104 posts

Uber Geek
+1 received by user: 10222

Trusted
Lifetime subscriber

  #2513868 28-Jun-2020 11:52
Send private message

kiwifidget:

 

wow, I have this exact problem!

 

House is 12-15y old, the switchboard has RCD thingies in it which often trip, guaranteed when we are away, and takes out the freezer, the garage doors, my pis and a windows server, and the electric gate.

 

We have lost a lot of food this way.

 

Himself is always blaming my pc gear, but maybe its the freezer!

 

So far I mitigate this by using a UPS on the pc gear and get the UPS software to email me when it detects an outage.

 

 

Do you have any surge protetors downstream of the RCD? That's what has caused a lot of the problems I have had, since they have a MOV to the earth from live and one from neutral, when those conduct on a small transient it can be enough to push the RCD into tripping.

 

 





Richard rich.ms

Daynger
444 posts

Ultimate Geek
+1 received by user: 313


  #2513875 28-Jun-2020 12:31
Send private message

Faults like this can be very hard to find.

 

One in particular I was called to had three previous electricians try to fix to no avail.

 

After about two hours of testing, tracing wires, pulling circuits apart and retesting we found a junction box under the house that had melted and was moist.

 

Being that it was an intermittent fault and it metered out OK half the time and badly the other half it was a right bastard to find.

 

We got it in the end though so customer was happy.

 

 

 

Faulty appliances that involve water are the usual suspects, dishwasher, washing machine, wastemaster and also fridges and freezers.

 

But also ants, rats/mice, leaky homes, old wiring, RCDs downstream of RCDs and even inductance on long cable runs can cause problems. 

 

30mA has decent headroom for inductance, 10mA for schools can be a nightmare.


Fred99
13684 posts

Uber Geek
+1 received by user: 10018


  #2513882 28-Jun-2020 13:03
Send private message

My neighbour had a new circuit board with RCBOs (combined RCD/breakers) - one of which kept tripping.  The RCBO was borked.  My son (sparky) took a quick look before calling the electrician who installed it back.  The RCD function was good / tested fine, but the breaker would consistently trip with a load of ~ 1/2 amp or so. 


 
 
 

Support Geekzone with one-off or recurring donations Donate via PressPatron.

gzt

gzt
18689 posts

Uber Geek
+1 received by user: 7827

Lifetime subscriber

  #2514015 28-Jun-2020 16:21
Send private message

What is left on the problem circuit. If you unplug everything on that circuit does it still trip?

mdav056

616 posts

Ultimate Geek
+1 received by user: 160

Subscriber

  #2514061 28-Jun-2020 16:55
Send private message

gzt: What is left on the problem circuit. If you unplug everything on that circuit does it still trip?

 

Yes, with nothing at all on this RCD-controlled circuit.  However, some stuff on another different RCD-controlled set of outlets that comes off the same contact breaker (only discovered this today when I went ant/animal hunting behind the outlets).  No livestock, all connections tight.





gml


mdav056

616 posts

Ultimate Geek
+1 received by user: 160

Subscriber

  #2514063 28-Jun-2020 16:57
Send private message

richms:

 

kiwifidget:

 

wow, I have this exact problem!

 

House is 12-15y old, the switchboard has RCD thingies in it which often trip, guaranteed when we are away, and takes out the freezer, the garage doors, my pis and a windows server, and the electric gate.

 

We have lost a lot of food this way.

 

Himself is always blaming my pc gear, but maybe its the freezer!

 

So far I mitigate this by using a UPS on the pc gear and get the UPS software to email me when it detects an outage.

 

 

Do you have any surge protetors downstream of the RCD? That's what has caused a lot of the problems I have had, since they have a MOV to the earth from live and one from neutral, when those conduct on a small transient it can be enough to push the RCD into tripping.

 

 

 

 

No surge protectors, nothing at all





gml


mdav056

616 posts

Ultimate Geek
+1 received by user: 160

Subscriber

  #2516815 3-Jul-2020 15:34
Send private message

I have now traced out the whole circuit that I'm having problems with:

 

 

RCD B is the one I am having trouble with, which used to run just the fridge.  Now it is running off RCD A perfectly.  However, Outlet A went to a distribution box (Kambrook, says 86 on it, and that just might be the year I bought it).  I removed this outlet box, and lo! RCD (not now connected to anything) has not popped off for the last 3 days.

 

Could a problem with this outlet box lead to an RCD popping on a later part of the circuit?  I presume so, and this is what appears to be happening.

 

If so, the whole circuit is rather a botch-up, isn't it?





gml


mdav056

616 posts

Ultimate Geek
+1 received by user: 160

Subscriber

  #2516817 3-Jul-2020 15:35
Send private message

I meant, I removed the distribution box.





gml


 
 
 
 

Shop now for Lego sets and other gifts (affiliate link).
SomeoneSomewhere
1882 posts

Uber Geek
+1 received by user: 1086

Lifetime subscriber

  #2516885 3-Jul-2020 16:37
Send private message

In theory that shouldn't happen, but it's not exactly unheard of.


gregmcc
2173 posts

Uber Geek
+1 received by user: 836

ID Verified
Trusted
Lifetime subscriber

  #2516896 3-Jul-2020 16:59
Send private message

mdav056:

 

I have now traced out the whole circuit that I'm having problems with:

 

 

RCD B is the one I am having trouble with, which used to run just the fridge.  Now it is running off RCD A perfectly.  However, Outlet A went to a distribution box (Kambrook, says 86 on it, and that just might be the year I bought it).  I removed this outlet box, and lo! RCD (not now connected to anything) has not popped off for the last 3 days.

 

Could a problem with this outlet box lead to an RCD popping on a later part of the circuit?  I presume so, and this is what appears to be happening.

 

If so, the whole circuit is rather a botch-up, isn't it?

 

 

 

 

Does this kambrook  "box" have built in surge protection? if so then it is a very likely offender

 

 


mdav056

616 posts

Ultimate Geek
+1 received by user: 160

Subscriber

  #2516982 3-Jul-2020 19:24
Send private message

gregmcc:

 

mdav056:

 

I have now traced out the whole circuit that I'm having problems with:

 

 

RCD B is the one I am having trouble with, which used to run just the fridge.  Now it is running off RCD A perfectly.  However, Outlet A went to a distribution box (Kambrook, says 86 on it, and that just might be the year I bought it).  I removed this outlet box, and lo! RCD (not now connected to anything) has not popped off for the last 3 days.

 

Could a problem with this outlet box lead to an RCD popping on a later part of the circuit?  I presume so, and this is what appears to be happening.

 

If so, the whole circuit is rather a botch-up, isn't it?

 

 

 

 

Does this kambrook  "box" have built in surge protection? if so then it is a very likely offender

 

 

No, it doesn't.





gml