#250858 28-May-2019 15:50
Send private message

I have just connected a brand new Powercom Macan MRT 1000VA/1000W On Line UPS but when I turn it on (hold the on/off switch for 3 seconds) the RCD on the main switchboard trips after only 1 second.

 

Do I have to wait for the battery to fully charge or something?





Rob

Create new topic

dan

dan
1134 posts

Uber Geek

Lifetime subscriber

  #2247226 28-May-2019 15:52
Send private message

its probably faulty - it should not be tripping your RCD  (assuming your RCD has no issue)




robfish

683 posts

Ultimate Geek

Lifetime subscriber

  #2247259 28-May-2019 16:55
Send private message

No this is the only thing which trips the RCD. If I put it on another circuit it trips that RCD too.
Supplier is happy to replace it or refund me the money (which is the option SWMBO prefers)




Rob

Zeon
3916 posts

Uber Geek

Trusted

  #2247270 28-May-2019 17:22
Send private message

An RCD trips if the return path is through the earth - and presuming the housing of the UPS is earthed, could it be some loose cable inside? Probably best to get the supplier to review.





Speedtest 2019-10-14




richms
28175 posts

Uber Geek

Trusted
Lifetime subscriber

  #2247327 28-May-2019 18:58
Send private message

Have you tried another mains cable into the input of the UPS?





Richard rich.ms

robfish

683 posts

Ultimate Geek

Lifetime subscriber

  #2247345 28-May-2019 19:40
Send private message

Yes I am an electrician by trade. I am convinced that the UPS is faulty.




Rob

sparkz25
750 posts

Ultimate Geek
Inactive user


  #2247390 28-May-2019 22:20
Send private message

robfish: Yes I am an electrician by trade. I am convinced that the UPS is faulty.

 

The only thing that I can think of is there is a short between neutral and earth some where in the unit or enough leakage to trip.

 

If its new i would take it back and get a new one.


Aredwood
3885 posts

Uber Geek


  #2247409 28-May-2019 22:40

Is the UPS output fully isolated from the incoming mains? (equivalent to an isolating transformer?) Or does it actually contain an MEN link on it's output terminals? As some appliances dont work properly if the neutral is not linked to the earth. (mostly gas appliances that use electronic flame sensing).

A local MEN link would be needed to cover the scenario where the input power cable gets unplugged. As the switchboard MEN link wont be available to the UPS anymore.





 
 
 
 

Shop now on Samsung phones, tablets, TVs and more (affiliate link).
robfish

683 posts

Ultimate Geek

Lifetime subscriber

  #2247432 29-May-2019 06:19
Send private message

Aredwood:As the switchboard MEN link wont be available to the UPS anymore.

You may be onto something here (with regard to an earthed neutral).

If, on the load side of an RCD, the neutral becomes earthed, it will trip.
Maybe this UPS is not designed to work with an RCD




Rob

Fred99
13684 posts

Uber Geek


  #2247433 29-May-2019 06:34
Send private message

Stumbled on this from Schneider - UPS causing RCD to trip seems to be a common enough problem for them to offer an faq (word doc)

 

This document examines one of the most common site issues with UPS systems, which is the tripping of the earth leakage protection, Residual Current Device (RCD) also known as an Earth Leakage Circuit Breaker (ELCB).

 

 


sparkz25
750 posts

Ultimate Geek
Inactive user


  #2247437 29-May-2019 06:37
Send private message

Fred99:

 

Stumbled on this from Schneider - UPS causing RCD to trip seems to be a common enough problem for them to offer an faq (word doc)

 

 

 

 

That link does not work


Fred99
13684 posts

Uber Geek


  #2247438 29-May-2019 06:40
Send private message

sparkz25:

 

That link does not work

 

 

Link fixed.


cyril7
9058 posts

Uber Geek

ID Verified
Trusted
Subscriber

  #2247441 29-May-2019 06:47
Send private message

Hi, all switch mode supplies (including the one in the UPS) have filter capacitors from both P and N to E, there may also be MOV's, if those two caps have slightly different impedance at 50Hz, then you will have a differential current and trip the RCD. It might seem like a lot of variance in impedance is required, but infact it is not and the issue is common. Typically the variation is only enough to trip a 10mA RCD, but its not uncommon for this difference to be enough to trip a 30mA one. I might suggest you look at providing a seperate circuit for your UPS that does not go via an RCD. This is quite common practice for many products, especially those with motors (Fridge/heat pumps) that will often trip RCDs due to either start current leakage or in many modern inverter models the switch mode supply filter cap leakage as mentioned.

 

Cyril


robfish

683 posts

Ultimate Geek

Lifetime subscriber

  #2247447 29-May-2019 07:02
Send private message

Thanks Cyril (and others).
I now have to think about the way forward.
I might even try a cheaper UPS for just my ONT, Edgerouter, switch and PoE switch (cameras and APs)




Rob

Create new topic





News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.