sparkz25:

 

mattwnz:

 

This is what it looks like now to correct it. Guessing the big box was needed so it matched the screw holes of the old switch.

 

 

 

 

 

Yeah Nah, I wouldn't take that either, still in zone 0 and it doesn't look like there is a gland in the bottom.

 

The simplest solution would have been to mount the powerpoint on a post outside of the tank.

 

I would at a guess say the plug has been chopped off and joined in that box now.

 

 

 

 

 

 

For this junction box to be in Zone 0 it must be IPX7, a close up of the sticker that shows the rating or make and model would be good so this can be checked, a photo that shows how the cable goes in to the box would be good as well, bet it's just a standard cable gland which will not be IPX7

 

Judging by what's there it would seem to be a rushed "Fix".

 

The solution is to mount a junction box on a post outside the container, bringing the cable thru a hole in the side.

 

 

 

 




mattwnz

20141 posts

Uber Geek


  #2319455 17-Sep-2019 20:15
Send private message

Thanks. I can see from the photo that has TK written on the side and googling it, it looks like it is one of these, which says it is IP 66 https://www.vynco.co.nz/products/enclosures/spelsberg-tk-series-ps 

 

So is that box no good. Should they replace it with an IP67 one at the very least?


gregmcc
2147 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #2319539 18-Sep-2019 04:35
Send private message

mattwnz:

 

Thanks. I can see from the photo that has TK written on the side and googling it, it looks like it is one of these, which says it is IP 66 https://www.vynco.co.nz/products/enclosures/spelsberg-tk-series-ps 

 

So is that box no good. Should they replace it with an IP67 one at the very least?

 

 

 

 

Correct, so it looks like another poor quality repair, did they issue an ESC/CoC for the repairs? If you like I'll copy PM you the relevant section of AS/NZS3000 so you have something to quote them




Tinkerisk
4224 posts

Uber Geek


  #2319557 18-Sep-2019 06:59
Send private message

The whole interconnection stuff should be completely outside of the inner zone. The problem arises when the pump doesn't keep the water at low level for any reason, hence the junction box will get submersed.





- NET: FTTH, OPNsense, 10G backbone, GWN APs, ipPBX
- SRV: 12 RU HA server cluster, 0.1 PB storage on premise
- IoT:   thread, zigbee, tasmota, BidCoS, LoRa, WX suite, IR
- 3D:    two 3D printers, 3D scanner, CNC router, laser cutter


chevrolux
4962 posts

Uber Geek
Inactive user


  #2319562 18-Sep-2019 07:13
Send private message

Wow... I'm the first person to play a bit fast and loose with electrical stuff. But sticking a hot point in a water tank?!?!? What kind if Sparky does this.....

I wouldn't want them back, and as gregmcc says, and would report immediately to the respective authorities.

skewt
750 posts

Ultimate Geek


  #2319592 18-Sep-2019 09:09
Send private message

What does it look like if you remove the cover?


hsvhel
1237 posts

Uber Geek

ID Verified

  #2319653 18-Sep-2019 10:53
Send private message

3rd times a charm, they'll need to come back and remedy that properly....





Referral Link Quic

 

Free Setup use R502152EQH6OK on check out

 

 


 
 
 

Cloud spending continues to surge globally, but most organisations haven’t made the changes necessary to maximise the value and cost-efficiency benefits of their cloud investments. Download the whitepaper From Overspend to Advantage now.
  #2319747 18-Sep-2019 13:06
Send private message

given your other issues i wouldnt be using them for anything else and reporting them.


mattwnz

20141 posts

Uber Geek


  #2319909 18-Sep-2019 17:15
Send private message

gregmcc:

 

mattwnz:

 

Thanks. I can see from the photo that has TK written on the side and googling it, it looks like it is one of these, which says it is IP 66 https://www.vynco.co.nz/products/enclosures/spelsberg-tk-series-ps 

 

So is that box no good. Should they replace it with an IP67 one at the very least?

 

 

 

 

Correct, so it looks like another poor quality repair, did they issue an ESC/CoC for the repairs? If you like I'll copy PM you the relevant section of AS/NZS3000 so you have something to quote them

 

 

 

 

Thanks, I have access to a copy of the previous edition which has that clause in it. The tank installw as part of the overall electrical work on the building, which I understand they have provided a CoC for the entire house build. I don't think there was any additional paperwork for the repair job yesterday as far as I know, unless he gave that to the builder who contracted him for the job.

 

I have pasted the images of the IP ratings of the box and the cable entry into the box which is inside the tank, and the box is IP66, not IP67. We have now  been told the pump circuit is on an RCD, although we don't know which circuit or RCD it is on, as the circuit isn't identified on the switch or in the meterboard. They  also said that the wires were connected within the outside round conduit box as shown below, which is a Marley product, which is directly behind the box on the inside of the tank, and is close to ground level.  Marley has said this  box  is rated at IP 53. Although it can be IP66   if the lid of the conduit box is cement fixed to the body of the fitting, where gluing obviously wouldn't be a good idea should the  pump needs replacing and needs rewiring in again.  I would have thought it would be better for the connection to be inside the box in the tank, if a proper IP67 box is used, than outside the tank in this type of box, certainly in the case of nuisance tripping of the RCD. I think we will need to get another electrician in to look at it this and see what they say. There is also an overlow on the tank into a soakpit, so water should never get this high in the manhole part of the tank.

 

 

 

 

 

 

 

 

 

 


gregmcc
2147 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #2319925 18-Sep-2019 17:25
Send private message

The box does not comply, regardless of if the connections are in this box or in the conduit box on the outside.

 

 

 

The cable gland may or may not comply, depends on the brand, Elmark brand ones do they are IP68, can't tell from the picture what brand it is.

 

Easiest way to see if it's on a RCD is to turn off all the RCD's and see if it still runs when you operate the float switch.

 

I would be surprised if it is on a RCD!

 

 


mattwnz

20141 posts

Uber Geek


  #2319929 18-Sep-2019 17:28
Send private message

Thanks, I will try that to test if it is on an RCD.


mattwnz

20141 posts

Uber Geek


  #2319973 18-Sep-2019 19:23
Send private message

After testing all the RCD etc, I discovered that the pump doesn't appear to be working at all, as the plumber had the value set so all the taps were running off the mains supply. Switching the valve  over to the tank pump, it is not working with all RCDs and other circuit breakers on. So will have to go back to the electrician anyway to check there is power to it.  


1 | 2 
Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic





News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.