samgdan:
SO In summary:
the current way that it is connected works but it is NOT RCD protected.
The below is the correct way to have the powerpoint RCD protected.
Can someone confirm if that is correct?
This appears to be the correct wiring, but without a clear photo of the markings on the plastic I can't be 100% sure.
BUT
There was a time when the out terminals were wired as the power in that this caused damage to the electronics for the RCD. Regardless of what has happened to cause the incorrect wiring this RCD show now be checked by an electrician for correct wiring and be checked for correct function (using a RCD tester) to ensure that the RCD fault detection is still working.
The rules say simply pressing the test button and it tripping is all that is required which may be fine for a newly installed unit, but for your safety get it tested fully tested or replaced.
Test results should be :- Trip value should be between 15mA to 30mA above or below is a fail
Trip time 300mS or less