samgdan:

 

SO In summary:

 

 

 

the current way that it is connected works but it is NOT  RCD protected.

The below is the correct way to have the powerpoint RCD protected.

 

Can someone confirm if that is correct?

 

 

 

 

 

 

 

This appears to be the correct wiring, but without a clear photo of the markings on the plastic I can't be 100% sure.

 

 

 

BUT

 

 

 

There was a time when the out terminals were wired as the power in that this caused damage to the electronics for the RCD. Regardless of what has happened to cause the incorrect wiring this RCD show now be checked by an electrician for correct wiring and be checked for correct function (using a RCD tester) to ensure that the RCD fault detection is still working.

 

 

 

The rules say simply pressing the test button and it tripping is all that is required which may be fine for a newly installed unit, but for your safety get it tested fully tested or replaced.

 

 

 

Test results should be :- Trip value should be between 15mA to 30mA above or below is a fail

 

Trip time 300mS or less

 

 

 

 




samgdan

160 posts

Master Geek


  #2524518 17-Jul-2020 08:54
Send private message

Thanks everyone for the help. As i have another bathroom with a pdl rcd i will be arranging today and electrician to have a look.
Its a small job so i might have to wait a couple of days for someone to be available. 😊

samgdan

160 posts

Master Geek


  #2524977 17-Jul-2020 20:34
Send private message

Update:

surprisingly the electrician came late this afternoon and corrected the connection as suggested by you guys.

Also he suggested to connect the heater towel rail to the N out and AP out, in that way the heater towel will be protected as well by the RCD.

As i wasn't sure about that i just said to leave things as they are.

Question:
Is the electrician suggestion good?



Froglotion
208 posts

Master Geek


  #2525004 17-Jul-2020 21:55
Send private message

Why would you not want the towel rail protected?


Bung
6484 posts

Uber Geek

Subscriber

  #2525024 17-Jul-2020 22:49
Send private message

Did the electrician check the wiring of the RCD in your other bathroom?

gregmcc
2147 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #2525039 18-Jul-2020 05:21
Send private message

samgdan: Update:

surprisingly the electrician came late this afternoon and corrected the connection as suggested by you guys.

Also he suggested to connect the heater towel rail to the N out and AP out, in that way the heater towel will be protected as well by the RCD.

As i wasn't sure about that i just said to leave things as they are.

Question:
Is the electrician suggestion good?

 

 

 

Depending on the location of the towel rail it may be required, there are specific zones in a bathroom that required RCD protection and the towel rail may be in that zone. even if it's not it would still be a good idea to have it on the RCD provided it wasn't too expensive.

 

 

 

Did the Electrician check the trip time and trip value of the RCD with his RCD tester?

 

 

 

 


samgdan

160 posts

Master Geek


  #2525335 18-Jul-2020 21:28
Send private message

Froglotion:

 

Why would you not want the towel rail protected?

 

 

the access to the cable for the heater towel rail is not the best, the electrician was out of the attic already when he suggested that, so he offered to come back next week (he came late and I did not wanted him to finish super late)


samgdan

160 posts

Master Geek


  #2525336 18-Jul-2020 21:29
Send private message

Bung: Did the electrician check the wiring of the RCD in your other bathroom?

 

 

 

Yes he did, no issue there he said it was well connected.


samgdan

160 posts

Master Geek


  #2525337 18-Jul-2020 21:38
Send private message

gregmcc:

 

samgdan: Update:

surprisingly the electrician came late this afternoon and corrected the connection as suggested by you guys.

Also he suggested to connect the heater towel rail to the N out and AP out, in that way the heater towel will be protected as well by the RCD.

As i wasn't sure about that i just said to leave things as they are.

Question:
Is the electrician suggestion good?

 

 

 

Depending on the location of the towel rail it may be required, there are specific zones in a bathroom that required RCD protection and the towel rail may be in that zone. even if it's not it would still be a good idea to have it on the RCD provided it wasn't too expensive.

 

 

 

Did the Electrician check the trip time and trip value of the RCD with his RCD tester?

 

 

 

 

 

 

 

 

I dont know much the "zones" for electrical plugs in the bathroom but i think it should need to be protected as it is not far from the bath tube. I think i will ask to connect the heater towel rail to the RCD.

 

Regarding the "trip time and trip value" I did not ask for that, I will next time he comes around.

 

 

 

so just to double check, for the heater towel rail to be RCD protected should be connected as below.

 

Is that right?

 

 

 

 

 


Bung
6484 posts

Uber Geek

Subscriber

  #2525357 18-Jul-2020 22:53
Send private message

Your sparky will know.

Do you know that until these shots of the rear view of a PDL rcd on Geekzone turned up on google I couldn't find anything showing the terminations other than the PDL instruction sheet drawings.

1 | 2 
View this topic in a long page with up to 500 replies per page Create new topic





News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.