Bung:gregmcc: If the boot is in place then it meets the segeration requirments
Not as far as Telecom was concerned or the Telecommunications Carriers' Forum Code of Practice
"35.3. Under NO circumstances shall Low Voltage (LV e.g., 230 V) sockets, switches or
modules be mounted on the same faceplate as TNV or ELV components (voltage
levels at which telecommunications and data services operate). The joint
Australia/New Zealand Wiring Rules (AS/NZS 3000) require that all faceplates
comply with AS/NZS 3112, clause 3.2 of which prohibits mixing of these voltage
levels on the same faceplate. "
This is a code of practice issued by a private company, there is no legal requirnment for it to be followed, what matters are the electrical regulations and the AS/NZS 3000, BTW AS/NZS 3112 only says that a facplate that has a socket shall not incorprate an ELV outlet such as telecoms. but it would make a plate that has a light switch ok to have it with