Lizard1977

2045 posts

Uber Geek

ID Verified

#142533 16-Mar-2014 10:03
Send private message

We are moving things around our house, and that means bringing my large desktop PC and my wife's similarly oversized PC into the same room.  We've got a long desk where both PCs will reside side by side.  The problem is that the room has very few power sockets on the wall.  On the wall we have the PCs against, there is only a single wall socket.  On the opposite wall there is a double socket and two single sockets.  However, the desk won't work on that wall, and the other two walls of the room are already occupied.

I'm wondering whether the power draw on a single wall socket will be too much.  Is there a way to work out the power draw/capacity of the socket?  The equipment that we will be using on that socket includes 1xPC (650W PSU), 1xPC (760W PSU), 2 x LED monitors, 1 x powered speakers (25W RMS), 1 x stereo (70W+70W RMS), and one inkjet printer.

If the single socket can't handle the power draw, then we have the short term option of running an extension cord from the opposite wall around the room but that's not ideal.  It would be better to have an electrician replace the single socket with a double socket.  How expensive would that likely be?

Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic
 1 | 2 | 3
gregmcc
2136 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #1006588 16-Mar-2014 10:12
Send private message

The standard NZ domestic power outlet is 10A, although you also need to check to see what size fuse/circuit breaker is supplying this.

Saying this, 2 computers and their assocated accessories should run just fine off 1 outlet

sbiddle
30853 posts

Uber Geek

Retired Mod
Trusted
Biddle Corp
Lifetime subscriber

  #1006594 16-Mar-2014 10:25
Send private message

A standard power socket is rated at 10A and the fuse or circuit breaker will typically be 10A, but could be 15A. Basic ohms law will let you work out the load.

Your PC's won't use anywhere near the PSU rating unless they're under full load which is highly unlikely. Unless you have the PC's fully kitted out with HDD's and high end video cards and actual draw is probably around 1/4 of this tops.


Bung
6361 posts

Uber Geek

Subscriber

  #1006613 16-Mar-2014 10:58
Send private message

The only thing typically 10A is the cheap breaker built into plug strips. The fuse or breaker rating is determined by the .cable and its surroundings. Short term current higher than nominal probably wouldn't trip either. In an office if you ever manage to trip the breaker it's surprising sometimes how many other computers are affected.



Lizard1977

2045 posts

Uber Geek

ID Verified

  #1006617 16-Mar-2014 11:05
Send private message

Thanks. I figured the socket would be 10A, but I wasn't sure whether that 10A would be shared across all the sockets in the room. Our fuse board is on the old-ish side (that's a whole other story) and it looks like the fuse/circuit breaker is either 16A or 6A (i'm guessing the former).

The PCs wouldn't be at full load all the time, but I figured the PSU wattage would indicate maximum usage. I reckon the total maximum wattage would be no higher than 1700W, which at 240V gives about 7A and 34ohms. So I think the single socket approach should be fine...

Sideface
9236 posts

Uber Geek

Trusted
DR
Lifetime subscriber

  #1006641 16-Mar-2014 11:46
Send private message

The item that draws the most power is the printer - although inkjets don't draw as much as laser printers.




Sideface


gregmcc
2136 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #1006648 16-Mar-2014 11:55
Send private message

Bung: The only thing typically 10A is the cheap breaker built into plug strips. The fuse or breaker rating is determined by the .cable and its surroundings. Short term current higher than nominal probably wouldn't trip either. In an office if you ever manage to trip the breaker it's surprising sometimes how many other computers are affected.



I think you need to re-read what you said here, the fuse or breaker rating IS NOT determined by the cable and it's surrroundings, you need to go and take a look at a circuit breaker and read the number on it, a 10A circuit breaker has a rating of 10 amps.

If everything is done right then the  size and length of cable that the circuit breaker suppplies will be able to handle the rated maximum capacity of the fuse or circuit breaker, been a power circuit at least the rating of the outlet, in this case 10A

ArcticSilver
729 posts

Ultimate Geek


  #1006650 16-Mar-2014 11:57
Send private message

Lizard1977: Thanks. I figured the socket would be 10A, but I wasn't sure whether that 10A would be shared across all the sockets in the room. Our fuse board is on the old-ish side (that's a whole other story) and it looks like the fuse/circuit breaker is either 16A or 6A (i'm guessing the former).

The PCs wouldn't be at full load all the time, but I figured the PSU wattage would indicate maximum usage. I reckon the total maximum wattage would be no higher than 1700W, which at 240V gives about 7A and 34ohms. So I think the single socket approach should be fine...


You'll be fine, easily!

You wont reach your power supply's maximum. No need to worry there, I would expect around 350watts per PC under load.

I run a computer LAN (www.got-lan.co.nz) and do the power for it. I load 6 computers onto 1 10a circuit. 2 is a very light load.

The monitors, speakers, stereo and inkjet will most likely not equate to a 3rd PC worth of power. I would estimate with everything going, on full load you'd be lucky to use 5amps (or 1150 watts out of 2300).



Lizard1977

2045 posts

Uber Geek

ID Verified

  #1006654 16-Mar-2014 12:01
Send private message

Thanks everyone, puts my mind at ease. I think we might invest in a decent multiboard to handle 7 plugs, to try and keep things nice and tidy...

Sideface
9236 posts

Uber Geek

Trusted
DR
Lifetime subscriber

  #1006673 16-Mar-2014 12:29
Send private message

IF you know how to do simple mains wiring, consider replacing your single socket with a 4-way power point (cost about $25)



I have 4 of these in my PC room - one on each wall.




Sideface


sir1963
3221 posts

Uber Geek

Subscriber

  #1006682 16-Mar-2014 12:48
Send private message

Lizard1977: We are moving things around our house, and that means bringing my large desktop PC and my wife's similarly oversized PC into the same room.  We've got a long desk where both PCs will reside side by side.  The problem is that the room has very few power sockets on the wall.  On the wall we have the PCs against, there is only a single wall socket.  On the opposite wall there is a double socket and two single sockets.  However, the desk won't work on that wall, and the other two walls of the room are already occupied.

I'm wondering whether the power draw on a single wall socket will be too much.  Is there a way to work out the power draw/capacity of the socket?  The equipment that we will be using on that socket includes 1xPC (650W PSU), 1xPC (760W PSU), 2 x LED monitors, 1 x powered speakers (25W RMS), 1 x stereo (70W+70W RMS), and one inkjet printer.

If the single socket can't handle the power draw, then we have the short term option of running an extension cord from the opposite wall around the room but that's not ideal.  It would be better to have an electrician replace the single socket with a double socket.  How expensive would that likely be?


Ok lets add up the power draw.
PC 650 W (this is a maximum, normal use will be lower)
PC 760 W (this is a maximum, normal use will be lower)
2 LED monitors , lets say 50w each = 100w
Speakers  25W
Stereo 140w (Maximum, normal would probably be 20w)
Printer allow 100W (will be less )

So total maximum = 1775w maximum (= 7.7A @ 230v)

A Standard power outlet is 10A, with a nominal voltage of 230V that gives a maximum wattage 2300W
so you are well within this limit.

HOWEVER, here is where you may have problems.
In most situations multiple power outlets are wired in series, typically on a 15A-15A circuit breaker depending on wire size (1.5mm/2.5mm), so for that circuit you can draw about 3500W to 4600W. SO... depending on what else is running on the same circuit you can still have problems.
For example if you were to run a 2300 fan heater in another room on a circuit with a 15A breaker you would end up close 18A, this will eventually cause the breaker to trip (probably after a few hours, I won't go into close/course protection).

You commonly see this in kitchens where people run multiple high wattage appliances like a frypan and kettle at the same time.

Lizard1977

2045 posts

Uber Geek

ID Verified

  #1006686 16-Mar-2014 12:52
Send private message

Thanks for that breakdown Sir1963. I guess that "series" issue is what I was thinking of when I wondered about the total draw of the entire room. Worth keeping in mind, but in practice the sockets on the other walls won't be used. There isn't any other tech in the room, so it should be okay.

Lizard1977

2045 posts

Uber Geek

ID Verified

  #1006689 16-Mar-2014 12:53
Send private message

Nice idea Sideface but I wouldn't trust my wiring skills that far. One day we will get the whole house re-wired, and when that day comes we'll definitely be improving the number and accessibility of power sockets, not to mention wiring for data as well.

Bung
6361 posts

Uber Geek

Subscriber

  #1006702 16-Mar-2014 13:40
Send private message

gregmcc:
Bung: The only thing typically 10A is the cheap breaker built into plug strips. The fuse or breaker rating is determined by the .cable and its surroundings. Short term current higher than nominal probably wouldn't trip either. In an office if you ever manage to trip the breaker it's surprising sometimes how many other computers are affected.



I think you need to re-read what you said here, the fuse or breaker rating IS NOT determined by the cable and it's surrroundings, you need to go and take a look at a circuit breaker and read the number on it, a 10A circuit breaker has a rating of 10 amps.


Step back a bit. How does the rating of the protection get chosen? Do you see 1 socket and put in a 10 amp breaker or do you look at the appropriate breaker for the size of cable and how surrounded in insulation it will be?

]

gzt

gzt
16921 posts

Uber Geek

Lifetime subscriber

  #1006732 16-Mar-2014 14:59
Send private message

Is there a way to work out the power draw/capacity of the socket?  The equipment that we will be using on that socket includes 1xPC (650W PSU), 1xPC (760W PSU), 2 x LED monitors, 1 x powered speakers (25W RMS), 1 x stereo (70W+70W RMS)

Rule of thumb maximum allowed power draw for one socket at wall outlet is 2400W. (10A@240V)

But, if you are getting within shouting distance of 2400W for long periods of time or unattended you do not want to be using a multiplug type thing (due to increased fire risk).

sbiddle: Your PC's won't use anywhere near the PSU rating unless they're under full load which is highly unlikely.

Agree. If peace of mind is required you can get a rough indication of total loading using $25 power meter and some typical activities running on the machines.

Lizard1977: It would be better to have an electrician replace the single socket with a double socket. How expensive would that likely be?

My guess is $70-$140 to get the upgrade depending on area etc.




Signature goes here.


sir1963
3221 posts

Uber Geek

Subscriber

  #1006738 16-Mar-2014 15:16
Send private message

Lizard1977: Thanks for that breakdown Sir1963. I guess that "series" issue is what I was thinking of when I wondered about the total draw of the entire room. Worth keeping in mind, but in practice the sockets on the other walls won't be used. There isn't any other tech in the room, so it should be okay.


The power outlets in the room may well be on the same breaker as the power outlets in another room.

It is not uncommon with breakers for 4-6 sockets to be on the same breaker.

 1 | 2 | 3
Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic





News and reviews »

Logitech Introduces New G522 Gaming Headset
Posted 21-May-2025 19:01


LG Announces New Ultragear OLED Range for 2025
Posted 20-May-2025 16:35


Sandisk Raises the Bar With WD_BLACK SN8100 NVME SSD
Posted 20-May-2025 16:29


Sony Introduces the Next Evolution of Noise Cancelling with the WH-1000XM6
Posted 20-May-2025 16:22


Samsung Reveals Its 2025 Line-up of Home Appliances and AV Solutions
Posted 20-May-2025 16:11


Hisense NZ Unveils Local 2025 ULED Range
Posted 20-May-2025 16:00


Synology Launches BeeStation Plus
Posted 20-May-2025 15:55


New Suunto Run Available in Australia and New Zealand
Posted 13-May-2025 21:00


Cricut Maker 4 Review
Posted 12-May-2025 15:18


Dynabook Launches Ultra-Light Portégé Z40L-N Copilot+PC with Self-Replaceable Battery
Posted 8-May-2025 14:08


Shopify Sidekick Gets a Major Reasoning Upgrade, Plus Free Image Generation
Posted 8-May-2025 14:03


Microsoft Introduces New Surface Copilot+ PCs
Posted 8-May-2025 13:56


D-Link A/NZ launches DWR-933M 4G+ LTE Cat6 Wi-Fi 6 Mobile Hotspot
Posted 8-May-2025 13:49


Synology Expands DiskStation Lineup with DS1825+ and DS1525+
Posted 8-May-2025 13:44


JBL Releases Next Generation Flip 7 and Charge 6
Posted 8-May-2025 13:41









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.







Backblaze unlimited backup