Topic # 222952 5-Sep-2017 12:17
Send private message

Hi,


 


I have an older 60's house which has 1mm wire (black and wire) for the lighting.


I have just put new LED dimmable lights in they have three pin plugs on them.


I have put new sockets into the roof using the 1mm lighting from the switch to the first power point (then new wire after this point), I have then joined the earth off a new circuit about to go in, so the lights can be plugged into the sockets.


I have not connected the earth wire yet as it is going to tee off a new circuit which I need to get the sparky out to connect up.


 


The electronic dimmers have an on / off function plus hold down to dim up  and hold down to dim down.


They have two wires coming out of the dimmer both phase.


 


I have connected the live to one side of the dimmer then the phase wire going to the sockets on the other side.


I have joined the neutrals where the dimmer is with a screw terminal connector.


 


Problems: 


1. When I turn off the light with the electronic dimmer, in the dark you can still see a tiny bit of light coming out of the lights, I have replaced the dimmers and it has the same problem.


2. When something else gets turned on in the house the lights flicker, even if they are turned off.


3. The dimmer does not completely dim up and down only about 20% they are meant to go 95%.


 


I have another circuit which has the earth connected (the lights are plastic and do not have a earth pin on the plug so I don't see how this would matter) to it which is working 100% I cannot understand why this one wont work, 


 


Any suggestions?


 


 


Create new topic
1494 posts

Uber Geek
+1 received by user: 284

Lifetime subscriber

  Reply # 1858880 5-Sep-2017 12:41
Send private message

 

I have just put new LED dimmable lights in they have three pin plugs on them.

 

 

 

I have put new sockets into the roof using the 1mm lighting from the switch to the first power point (then new wire after this point), I have then joined the earth off a new circuit about to go in, so the lights can be plugged into the sockets.

 

 

 

I have not connected the earth wire yet as it is going to tee off a new circuit which I need to get the sparky out to connect up.

 

 

I hope the sparky who is coming out is an inspector, only an inspector can sign off home owner work

 

 

 

 

 

The electronic dimmers have an on / off function plus hold down to dim up  and hold down to dim down.

 

 

 

They have two wires coming out of the dimmer both phase.

 

 

 

 

 

 

 

I have connected the live to one side of the dimmer then the phase wire going to the sockets on the other side.

 

 

 

I have joined the neutrals where the dimmer is with a screw terminal connector.

 

 

 

 

 

 

 

Problems: 

 

 

 

1. When I turn off the light with the electronic dimmer, in the dark you can still see a tiny bit of light coming out of the lights, I have replaced the dimmers and it has the same problem.

 

 

 

have you taken the dimmer out and just used a switch, does this fix the problem, if so then the dimmer is the problem. Not an uncommon one as LED's require so little power a little bit of current leakage through the dimmer will do this.

 

 

2. When something else gets turned on in the house the lights flicker, even if they are turned off.

 

 

 

Another common problem with LED's, the surge of induced voltage from something else turning on will be enough for the LED's to momentary light up.

 

 

3. The dimmer does not completely dim up and down only about 20% they are meant to go 95%.

 

 

 

Sounds like the dimmer isn't correctly matched to the LED's sure it's the recommended dimmer for the LED's?

 

 

 

 

 

I have another circuit which has the earth connected (the lights are plastic and do not have a earth pin on the plug so I don't see how this would matter) to it which is working 100% I cannot understand why this one wont work, 

 

 

 

 

Doesn't matter if the plug has an earth or not, the standards say if the socket has an earth pin, an earth wire must be fitted.

 

 

 

 

 

Any suggestions?

 

 

How about some make models of both the LED lights and the dimmer.

 

 

 

There are fixes for all these problem, but this is way outside the scope of what the average non-electrical person would know, get your spark to sort it out.

 

 

 

 

 

 


2294 posts

Uber Geek
+1 received by user: 813

Subscriber

  Reply # 1859253 5-Sep-2017 21:24
Send private message

Does the dimmer's instructions say that it can be used with LEDs? Some dimmers can only be used with filament lights.

 

It seems like your dimmer control is also an electronic switch. Virtually all electronic switches have an inbuilt snubber circuit, that lets a small amount of power flow through the switch, even when the switch is off. This is why the LEDs keep dimly glowing. Use a mechanical switch with a separate dimmer.

 

Often using a single filament light (a 15W one will do) connected with the LED lights will make the LEDs behave properly. As the dimmer will then see the filament load.

 

Either way, Getting LEDs to work properly is often a kludge. Unless you get LEDs with purpose designed drivers, where the "dimming" commands are sent directly to the drivers. This can usually only be done as part of a proper home automation system. At the very least you need to get the models of dimmers that are recommended by the manufacturer of the LED drivers.

 

Have a read of http://sound.whsites.net/lamps/dimmers+leds.html And you will see why dimmers and LEDs always cause problems.

 

And agree that you need to get a sparkie in to sort out your issues. And are you in New Zealand or the USA? As in your first sentence, if you were meaning to say "black and white wire" As USA uses black and white for their wiring colours, instead of red and black in NZ.






 
 
 
 


5394 posts

Uber Geek
+1 received by user: 2597


  Reply # 1859269 5-Sep-2017 21:43
Send private message

I'm confused as to why the OP would be wanting to wire an LED "lamp" with a 3 pin plug, but instead of "hard wired" into an existing lighting circuit, by putting 3 pin power outlets into the ceiling so they can plug in.  WTF?

 

As far as getting a sparky to sort the issue, there's not enough good information provided to even start asking the right question(s) over the phone. 

 

I wouldn't count on a sparky being able to give an answer based on info provided.  Even if the basics can be sorted as to what the concept is, I wouldn't count on the average sparky being able to sort possible compatibility issues between the probably unknown LED lamps and dimmers if they don't know what they're dealing with. They'd make it safe, but making it work as hoped might be a long shot.

 

 

 

 


1494 posts

Uber Geek
+1 received by user: 284

Lifetime subscriber

  Reply # 1859329 6-Sep-2017 05:29
Send private message

Fred99:

 

I'm confused as to why the OP would be wanting to wire an LED "lamp" with a 3 pin plug, but instead of "hard wired" into an existing lighting circuit, by putting 3 pin power outlets into the ceiling so they can plug in.  WTF?

 

 

 

 

typically LED down lights are supplied with a 3 pin plug on them

 

 

 

 

As far as getting a sparky to sort the issue, there's not enough good information provided to even start asking the right question(s) over the phone. 

 

I wouldn't count on a sparky being able to give an answer based on info provided.  Even if the basics can be sorted as to what the concept is, I wouldn't count on the average sparky being able to sort possible compatibility issues between the probably unknown LED lamps and dimmers if they don't know what they're dealing with. They'd make it safe, but making it work as hoped might be a long shot.

 

 

 

 

 

 

These are all typical LED problems, most domestic sparkies should be able to figure out the solution to all these problems without too much bother


2299 posts

Uber Geek
+1 received by user: 237


  Reply # 1859495 6-Sep-2017 10:10
Send private message

Sturz:

 

I have just put new LED dimmable lights in they have three pin plugs on them.

 

I have put new sockets into the roof using the 1mm lighting from the switch to the first power point (then new wire after this point), I have then joined the earth off a new circuit about to go in, so the lights can be plugged into the sockets.

 

I have not connected the earth wire yet as it is going to tee off a new circuit which I need to get the sparky out to connect up.

 

 

I know that you can't just tee an earth off an existing circuit it has to come from the switchboard and connecting sockets to a 1mm circuit could be another problem area. Take Greg's advice and get your electrician involved.




2 posts

Wannabe Geek


  Reply # 1859497 6-Sep-2017 10:11
Send private message

gregmcc:

 

Fred99:

 

I'm confused as to why the OP would be wanting to wire an LED "lamp" with a 3 pin plug, but instead of "hard wired" into an existing lighting circuit, by putting 3 pin power outlets into the ceiling so they can plug in.  WTF?

 

 

 

 

 

 

 

 

 

That's what they came with. (2 pin p and n) 

 

 

 

And sorry its red and black wire.

 

 

 

 

 

Bung:

 

Sturz:

 

I have just put new LED dimmable lights in they have three pin plugs on them.

 

I have put new sockets into the roof using the 1mm lighting from the switch to the first power point (then new wire after this point), I have then joined the earth off a new circuit about to go in, so the lights can be plugged into the sockets.

 

I have not connected the earth wire yet as it is going to tee off a new circuit which I need to get the sparky out to connect up.

 

 

I know that you can't just tee an earth off an existing circuit it has to come from the switchboard and connecting sockets to a 1mm circuit could be another problem area. Take Greg's advice and get your electrician involved.

 

 

 

 

Why not? I have a new circuit going in,  I am going to get the sparky to put an RCBO in, it is running 1.5mm cable back to the board, then I have just connected the earth wire from that circuit to my other light circuit. As long as all the earths are connected I don't see the issue?  its an old circuit board there is no RCD's.

 

 

 

 


2299 posts

Uber Geek
+1 received by user: 237


  Reply # 1859540 6-Sep-2017 11:06
Send private message

Presumably because your 2nd circuit could be removed without somebody knowing that it was supplying an earth to another circuit.


1494 posts

Uber Geek
+1 received by user: 284

Lifetime subscriber

  Reply # 1859702 6-Sep-2017 13:48
Send private message

 

That's what they came with. (2 pin p and n) 

 

And sorry its red and black wire.

 

 

 

If the socket has an earth connection on it, it must actually have an earth connected, regardless of what plugs in to it

 

 

 

 

Why not? I have a new circuit going in,  I am going to get the sparky to put an RCBO in, it is running 1.5mm cable back to the board, then I have just connected the earth wire from that circuit to my other light circuit. As long as all the earths are connected I don't see the issue?  its an old circuit board there is no RCD's.

 

 

Can't use one earth to service 2 circuits, unless you are familiar with AS/NZS3000 I suggest you leave this to an electrician

 

 

 

 


Create new topic



Twitter »

Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

CPTPP text and National Interest Analysis released for public scrutiny
Posted 21-Feb-2018 19:43


Foodstuffs to trial digitised shopping trolleys
Posted 21-Feb-2018 18:27


2018: The year of zero-login, smart cars & the biometrics of things
Posted 21-Feb-2018 18:25


Intel reimagines data centre storage with new 3D NAND SSDs
Posted 16-Feb-2018 15:21


Ground-breaking business programme begins in Hamilton
Posted 16-Feb-2018 10:18


Government to continue search for first Chief Technology Officer
Posted 12-Feb-2018 20:30


Time to take Appleā€™s iPad Pro seriously
Posted 12-Feb-2018 16:54


New Fujifilm X-A5 brings selfie features to mirrorless camera
Posted 9-Feb-2018 09:12


D-Link ANZ expands connected smart home with new HD Wi-Fi cameras
Posted 9-Feb-2018 09:01


Dragon Professional for Mac V6: Near perfect dictation
Posted 9-Feb-2018 08:26


OPPO announces R11s with claims to be the picture perfect smartphone
Posted 2-Feb-2018 13:28


Vocus Communications wins a place on the TaaS panel
Posted 26-Jan-2018 15:16


SwipedOn raises $1 million capital
Posted 26-Jan-2018 15:15


Slingshot offers unlimited gigabit fibre for under a ton
Posted 25-Jan-2018 13:51


Spark doubles down on wireless broadband
Posted 24-Jan-2018 15:44



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.