6 posts

Wannabe Geek


#258556 9-Oct-2019 16:19
Send private message

Hi All,

 

I am in need to of some help with regards to identifying what is causing water dripping (not the little water in the pic) from the water heater external drain pipe (which has caused high water bills in the past few months)

 

I have attached a pic, with some additional pics for different angles to show you my water heater setup

 

Based on the numbers marked in the image, I have noted below the respective valves and pipes to the best of my knowledge but I am new to this, so please do correct me if I am wrong:

 

1. Cold Water Inlet (rising from below the floor)

 

2. Power Supply

 

3. Filter/Non-Return Valve

 

4. Limiting Stop Valve

 

5. Cold Water Expansion Valve EVT

 

6. Is this blue tap a gate valve?

 

7. What is the purpose of this pipe (its cold)

 

8. Cold Pipe, coming out of the top of the cylinder and draining down to outside

 

9. Hot pipe, coming out of the top of the cylinder and supplying hot water to the house.

 

 

 

So the when the mains are open at the water meter, the meter is ticking slowly but continuously. I noticed that the near the waste water outlet (outside the house) there is a small pipe dripping water continuously.

 

I narrowed it down to the water heater area and this external drain pipe connects to the pipe 8. (in the pic) and the EVT (5.)

 

When I close the filter (3.) then the supply to the water heater stops, i.e. the hot water in the taps also stop and the dripping out of the drain pipe stops too.

 

 

 

Is it the cold water expansion valve (5.) which is faulty or is the heater overfilling internally to cause it to drain excess cold water?

 

 

 

NOTE: There is no visible leakage anywhere around or above or below the water heater.

 

Any help would be super great as I would like to DIY this if its possibly a minor issue.

 

 

 

Thanks,

 

Sheldon

 

 

 

 

 

 

 

 

 

 

 


Create new topic
Bung
3438 posts

Uber Geek

Subscriber

  #2333456 9-Oct-2019 17:16
Send private message

Regardless of brand the trouble shooting should be similar. https://apexvalves.co.nz/fault-finding-guides/

RunningMan
6097 posts

Uber Geek


  #2333459 9-Oct-2019 17:20
Send private message

No pics, but the most common reasons would be a leaking expansion/pressure release valve causing water to keep slowly leaking, or a failed thermostat causing it to overheat and release pressure through the expansion valve.

 

If it stops leaking after a while if you turn off the power, it's probably the thermostat causing it to over heat. If it keeps leaking when powered off, then a leaky valve.

 

@aredwood knows a thing or 2 about these.


 
 
 
 


cliffbooth

6 posts

Wannabe Geek


  #2333511 9-Oct-2019 18:07
Send private message


cliffbooth

6 posts

Wannabe Geek


  #2333512 9-Oct-2019 18:09
Send private message

thank you for you quick responses. I will test and proceed accordingly


cliffbooth

6 posts

Wannabe Geek


  #2333521 9-Oct-2019 18:28
Send private message

Hi,

 

Tested and even when (2.) power is switched off, as soon as the Filter Stop (3.) is opened, the water is dripping at the outside drain exit.

 

 

 

 


elbrownos
72 posts

Master Geek


  #2333646 10-Oct-2019 08:23
Send private message

If it is your thermal relief valve (TRV) passing then the pipe from it to the drain will feel warm


cliffbooth

6 posts

Wannabe Geek


  #2333845 10-Oct-2019 10:48
Send private message

Pipe (8.) from top of cylinder, connected to the TRV, is room temperature. Water at the drain outside is cool, not cold though.

 

So does that narrow down to the cold water expansion valve, being the possible fault, causing the cool water to drip continuously through the drain pipe outside?


 
 
 
 


elbrownos
72 posts

Master Geek


  #2334903 10-Oct-2019 11:58
Send private message

Yes that points to either your CWE valve or manual drain valve passing.

 

You could temporarily remove the drain piping (7) to see which is passing.

 

Have you lifted the lever on the CWE valve to flush it?

 

 


cliffbooth

6 posts

Wannabe Geek


  #2335179 10-Oct-2019 18:30
Send private message

I have lifted the lever on the CWE, and water does gush out of the same outlet outside, and then reduces to dripping once I release the lever.

 

I cant remove pipe 7., welded on one side and I am afraid I might break it.

 

What is the purposed of the blue tap (6.)? is that a gate valve? and does it have to be completely clockwise or anti-clockwise or in between? Tried all combinations with this one and the dripping doesnt seem to stop

 

 


Bung
3438 posts

Uber Geek

Subscriber

  #2335212 10-Oct-2019 19:48
Send private message

Opening the blue tap with the cylinder stop valve closed would drain the tank. If you didn't notice any change at the drain outlet maybe the gate valve is stuck shut. The valve wheel should turn quite a few turns winding up and down.

Create new topic




News »

HP unveils new innovations for businesses adapting to rapidly evolving workstyles and workforces
Posted 17-Sep-2020 15:36


GoPro launches new HERO9 Black camera
Posted 17-Sep-2020 09:45


Telecommunications industry launches new 5G Facts website
Posted 17-Sep-2020 07:56


New Zealand ranks 3rd in world in GSMA index
Posted 15-Sep-2020 10:13


Trend Micro Security Suite adds web monitoring to prevent identity theft
Posted 14-Sep-2020 15:37


NVIDIA to acquire Arm for US$ 40 billion
Posted 14-Sep-2020 12:27


Epson launches its next gen A3+ colour EcoTank multi-function printer
Posted 10-Sep-2020 16:08


Sony launches three new native 4K SXRD home cinema projectors
Posted 9-Sep-2020 18:00


Catalyst Cloud brings Kubernetes-based open-source web hosting solution to market
Posted 9-Sep-2020 17:54


Verizon Connect eyes further growth in New Zealand
Posted 8-Sep-2020 09:26


PNY launches XLR8 gaming NVIDIA GeForce RTX 30 series powered by the all-new NVIDIA Ampere architecture
Posted 3-Sep-2020 16:39


NVIDIA delivers greatest-ever generational leap with GeForce RTX 30 Series GPUs
Posted 3-Sep-2020 16:17


Weta Digital advances visual effects and animation in the cloud with AWS
Posted 2-Sep-2020 17:09


Kiwrious lab-in-the-pocket kit designed for schoolchildren
Posted 28-Aug-2020 09:03


Fitbit introduces Sense, its most advanced health smartwatch
Posted 26-Aug-2020 10:14



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.


Support Geekzone »

Our community of supporters help make Geekzone possible. Click the button below to join them.

Support Geezone on PressPatron



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.