Topic # 172108 12-May-2015 09:05
Send private message

I need to built a circuit that uses a 12VDC relay to control a 12VDC pump. A relay is being used because the pump is close to the power source but some distance from the control point, and the relay saves long heavy cables ($$$).

The pump is usually controlled by a level switch, but on occasion I need to bypass this and force it to run.

Is it possible to set-up the relay like this: -

The pump is connected to the Normally Open terminal 
The control signal comes from a single pole double throw switch.
- On1: Connects directly to the signal input on the relay, switching on the pump
- CentreOff:  The relay stays open and the pump doesn't run
- On2: Connects to the signal input on the relay via the level switch, switching on the pump only when the level switch is activated.

I would solder the two signal leads together and have a single lead connected to the signal input terminal.  



 






Mike

Filter this topic showing only the reply marked as answer Create new topic
3267 posts

Uber Geek
+1 received by user: 77

Trusted

  Reply # 1302970 12-May-2015 16:44
Send private message

I do not understand your last sentence, but the rest looks fine.  (I also do not usually look in this forum so might not see replies.)




You can never have enough Volvos!


1649 posts

Uber Geek
+1 received by user: 368

Lifetime subscriber

  Reply # 1303006 12-May-2015 17:27
Send private message

basic AOM (auto/off/manual) switch, very easy to do.

In the manual position the relay is powered from the switch
In the auto position the relay is powered via the level switch

the type of switch you are looking for is a 3 position centre off

 
 
 
 




5369 posts

Uber Geek
+1 received by user: 2198


  Reply # 1304551 13-May-2015 14:33
Send private message

Thanks for your reply. I have the switch and the relay sorted.

I'm struggling with how to connect both signal leads to the one relay.

Can I simply join both signal leads to a single lead that is connected to the signal terminal on the relay?
(I guess you would call this a y-junction or t-junction).




gregmcc: basic AOM (auto/off/manual) switch, very easy to do.

In the manual position the relay is powered from the switch
In the auto position the relay is powered via the level switch

the type of switch you are looking for is a 3 position centre off




Mike

68 posts

Master Geek
+1 received by user: 7


  Reply # 1304601 13-May-2015 15:25
One person supports this post
Send private message


Do you wish to over-ride the level control completely (possibly causing overflow) or just force the pump to run when below normal cut-off?

2090 posts

Uber Geek
+1 received by user: 1173


  Reply # 1304698 13-May-2015 17:40
Send private message

Here are your two options.

https://onedrive.live.com/redir?resid=bae8cbde9ef3b738!70509&authkey=!AIcR8csoRuprc-g&v=3&ithint=photo%2cjpg

Edit: sorry cant seem to manage to get OneDrive stuff to display as images.




Location: Dunedin

 

 


550 posts

Ultimate Geek
+1 received by user: 191


  Reply # 1304700 13-May-2015 17:44

Switch you need is ON-OFF-ON.

Connect the relay signal wire to the centre common terminal.
Connect one of the normally open terminals to power.
Connect the other normally open terminal to the level switch.

Moving the switch from the off position will select either manually on or auto from the level switch.

68 posts

Master Geek
+1 received by user: 7


  Reply # 1304717 13-May-2015 18:29
Send private message

If you want to have over-riding control just connect your contact across the existing contact. 

If you want the high-level cut-off to prevent overflow you will need to modify the level controller.

1756 posts

Uber Geek
+1 received by user: 363

Trusted

  Reply # 1305103 14-May-2015 13:04
Send private message

Looks like you just need to parallel the level switch connections ?

Leave your switch at On2 - the level switch, and use the paralleled switch to override the level switch. Though as others have mentioned, you will need to be alert for overflow ...





My thoughts are no longer my own and is probably representative of our media-controlled government




5369 posts

Uber Geek
+1 received by user: 2198


  Reply # 1305331 14-May-2015 17:50
Send private message

I'll post a circuit diagram tomorrow, but in words ...

The system includes: - 
1 x sump, 
1 x 200W submersible 12V DC pump, 
1 x float switch,  1x on-off-on switch.

The objective is to keep the water level in the sump below the level of the float switch i.e. stop the sump from overflowing.  I want the sump to be nearly full most of the time

At times I need to be able to run the pump to almost completely empty the sump, well below the level of the float switch.

So I need two system modes: -
- Auto (float switch activates pump to stop sump overflowing)
- Manual (pump just runs continuously)

This is how most bilge pump circuits in boats work - which is where I got the idea.

What I'm doing differently is adding a relay to turn the pump on and using the switch as the source of the control signal for the relay.  A relay saves me long expensive cable runs, because my power source is close to the pump, but the switch location isn't (can't be).

I want to run leads from the switch to this pin - one via the float switch, and one direct.

The relay has a single signal input terminal.  I have separately tested connecting a switch to the input terminal directly and via the float switch.  Both work.

What I don't know is whether I can: - 
Join the control leads together at a point between the float switch and the relay; and connect this combined control lead to the relay's signal input terminal.




Mike



5369 posts

Uber Geek
+1 received by user: 2198


  Reply # 1305665 15-May-2015 10:37
Send private message

Thanks for all the replies (and thanks to Clima for helping me via PM).  I think the top circuit in the picture posted by AndrewNZ is what I am trying to do.

Below is a sketch of the circuit I have in mind.  The blue dotted shape encloses the party of the circuit I am unsure about. Basically the connection of

I'm now pretty sure it will work.  Confident enough to risk the relay by testing. 

One last question:  Does the physical orientation of the relay matter e.g. should it always be mounted with the terminals facing down?








Mike

3039 posts

Uber Geek
+1 received by user: 619


  Reply # 1305701 15-May-2015 11:17
Send private message

Hi Mike,

It doesn't matter where you join those wires. You could use a chock block connector with two wires into one hole. You could solder two wires onto the switch terminal or two wires onto the relay terminal or two wires onto the float switch terminal.  Electrically it doesn't matter.

I would make my decision based on what is easiest or the most practical. In other words where is it easiest to join the two wires together. Use the terminal that is easiest to solder two wires onto or the terminal that requires the least amount of wire.

So far as the mounting position of the relay, that doesn't matter too much either.  Do what makes sense and gives easy access to the terminals for fault finding.




Sony Xperia X running Sailfish OS. https://sailfishos.org The true independent open source mobile OS 
Samsung Galaxy Tab S3
Nokia N1
Dell Inspiron 14z i5




5369 posts

Uber Geek
+1 received by user: 2198


  Reply # 1305726 15-May-2015 11:46
Send private message

Thanks for your help.  I should have posted the circuit diagram to start with.embarassed

I usually solder, liquid tape and heat shrink connections. The connections along with the control switch and relay will be in an IP66 enclosure.







Mike

3267 posts

Uber Geek
+1 received by user: 77

Trusted

  Reply # 1306072 15-May-2015 18:54
One person supports this post
Send private message

Ideally you should have a diode across the relay coil in the reverse polarity.  When you switch the relay off there is a magnet field in the coil which collapses resulting in a large negative voltage generated (similar principal to a car ignition coil, and BTW also an electric fence energizer) so a diode is often placed parallel to the coil so that the negative spike is shorted out instead of burning the switch contacts (both the manual and float switches).




You can never have enough Volvos!


3039 posts

Uber Geek
+1 received by user: 619


  Reply # 1306082 15-May-2015 19:14
Send private message

Niel makes a very good point.




Sony Xperia X running Sailfish OS. https://sailfishos.org The true independent open source mobile OS 
Samsung Galaxy Tab S3
Nokia N1
Dell Inspiron 14z i5




5369 posts

Uber Geek
+1 received by user: 2198


  Reply # 1307110 18-May-2015 12:24
Send private message

The relay I am using has inbuilt diode protection.




Mike

Filter this topic showing only the reply marked as answer Create new topic



Twitter »

Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

Orcon announces new always-on internet service for Small Business
Posted 18-Apr-2019 10:19


Spark Sport prices for Rugby World Cup 2019 announced
Posted 16-Apr-2019 07:58


2degrees launches new unlimited mobile plan
Posted 15-Apr-2019 09:35


Redgate brings together major industry speakers for SQL in the City Summits
Posted 13-Apr-2019 12:35


Exported honey authenticated on Blockchain
Posted 10-Apr-2019 21:19


HPE and Nutanix partner to deliver hybrid cloud as a service
Posted 10-Apr-2019 21:12


Southern Cross and ASN sign contract for Southern Cross NEXT
Posted 10-Apr-2019 21:09


Data security top New Zealand consumer priority when choosing a bank
Posted 10-Apr-2019 21:07


Samsung announces first 8K screens to hit New Zealand
Posted 10-Apr-2019 21:03


New cyber-protection and insurance product for businesses launched in APAC
Posted 10-Apr-2019 20:59


Kiwis ensure streaming is never interrupted by opting for uncapped broadband plans
Posted 7-Apr-2019 09:05


DHL Express introduces new MyDHL+ online portal to make shipping easier
Posted 7-Apr-2019 08:51


RackWare hybrid cloud platform removes barriers to enterprise cloud adoption
Posted 7-Apr-2019 08:50


Top partner named at MYOB High Achievers Awards
Posted 7-Apr-2019 08:48


Great ideas start in Gisborne with hackathon event back for another round
Posted 7-Apr-2019 08:42



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.


Support Geekzone »

Our community of supporters help make Geekzone possible. Click the button below to join them.

Support Geezone on PressPatron



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.