My current UPS, a 1500VA rack-mount APC Smart-UPS SC is failing to take the load during minor power interruptions, so I am looking at possible replacements.

 

While UPS units have come down in price quite a bit, a replacement rack unit currently starts at around 4x the price of the entry-level tower units of equivalent capacity, and I am wondering is these are worth considering instead? They would in theory allow me to increase run time for less money.

 

I recall 15 years ago, I thought my boss was nuts getting the cheapest units he could find (I had an APC Back-UPS Pro at the time), and my position seemed to be justified when they failed during a minor power interruption, while other computers not connected to a UPS remained running.

 

A lot has changed since then however. Even the cheapest units now claim to be line interactive models, and I'm not at all happy with my current APC unit. It likely only needs a new battery, but given it has never told me I needed to replace the battery, and was a replacement (when new) for a unit that constantly complained about the battery needing replacing, I'm inclined to treat it as faulty. Both units came with a very long printout of test results, all of which indicated they passed.

 

With the above in mind, can anyone recommend tower units (1500-2000VA)?

 

My main requirement is to be able to change batteries without disconnecting everything. This isn't included in documentation for the reasonably priced Eaton 5E range, so I suspect it's not possible there.


Create new topic
2816 posts

Uber Geek

Trusted
Lifetime subscriber

  #1987595 3-Apr-2018 13:01
Send private message

I'm happy with the HPE T1500 tower UPS models.  The front pulls off for easy battery replacement.

 

I'm very wary of cheapie no-name UPS models.  I've seen and heard of too many fires or near-fires, and they are rubbish at looking after the batteries.

 

Ideally change batteries every three years.





"4 wheels move the body.  2 wheels move the soul."

“Don't believe anything you read on the net. Except this. Well, including this, I suppose.” Douglas Adams

9802 posts

Uber Geek

Lifetime subscriber

  #1987635 3-Apr-2018 14:03
Send private message

have you changed the batteries? quick cheap simple fix. wholesale on those batteries, likely a few 7ah ones in parallel, is about $15 each.

 

my APC tower one (only a small 720VA one) i was able to change the batteries with out turning everything off.

 

Ive also replaced about 4 Eaton powerware ones with out disconnecting and each had about 10-12 batteries in there.


 
 
 
 




1337 posts

Uber Geek


  #1987641 3-Apr-2018 14:10
Send private message

Jase2985:

 

have you changed the batteries? quick cheap simple fix. wholesale on those batteries, likely a few 7ah ones in parallel, is about $15 each.

 

 

I have not changed the batteries, but I intend to do so irrespective of any replacement.

 

The key point for me is that two of these units have failed to properly report battery condition.


9802 posts

Uber Geek

Lifetime subscriber

  #1987647 3-Apr-2018 14:14
Send private message

does the UPS have the self test set to be on? as it may not know the condition of the battery if its not able to test them regularly (mine does it weekly). and come power outage time its too late.

 

mine failed recently, with a connect battery warning, tested the batteries, they were fine voltage wise with 27.4v but as soon as you put a load on them they would fall below the acceptable voltage level. so replaced the batteries and all was good.


9802 posts

Uber Geek

Lifetime subscriber

  #1987648 3-Apr-2018 14:15
Send private message

what model was it?




1337 posts

Uber Geek


  #1987653 3-Apr-2018 14:21
Send private message

Jase2985:

 

does the UPS have the self test set to be on? as it may not know the condition of the battery if its not able to test them regularly (mine does it weekly). and come power outage time its too late.

 

 

Yes, the self-test is enabled. APC Smart-UPS SC 1500.




1337 posts

Uber Geek


  #1987713 3-Apr-2018 15:26
Send private message

Jase2985:

 

have you changed the batteries? quick cheap simple fix. wholesale on those batteries, likely a few 7ah ones in parallel, is about $15 each.

 

 

On the subject of wholesale batteries, do you have any recommendations?

 

I used to buy replacement batteries for my old Back-UPS Pro from a place on the North Shore (I'm in south Auckland), but I can't recall the name.


 
 
 
 


2816 posts

Uber Geek

Trusted
Lifetime subscriber

  #1987784 3-Apr-2018 17:49
Send private message

SirHumphreyAppleby:

 

I used to buy replacement batteries for my old Back-UPS Pro from a place on the North Shore (I'm in south Auckland), but I can't recall the name.

 

 

Possibly "IT Power"?  Highly reputable APC service agents who supply batteries for all sorts of UPS devices.  Not the cheapest, but with excellent service levels.





"4 wheels move the body.  2 wheels move the soul."

“Don't believe anything you read on the net. Except this. Well, including this, I suppose.” Douglas Adams

312 posts

Ultimate Geek

Subscriber

  #1988180 4-Apr-2018 13:13
Send private message

SirHumphreyAppleby:

 

My current UPS, a 1500VA rack-mount APC Smart-UPS SC is failing to take the load during minor power interruptions, so I am looking at possible replacements.

 

While UPS units have come down in price quite a bit, a replacement rack unit currently starts at around 4x the price of the entry-level tower units of equivalent capacity, and I am wondering is these are worth considering instead? They would in theory allow me to increase run time for less money.

 

I recall 15 years ago, I thought my boss was nuts getting the cheapest units he could find (I had an APC Back-UPS Pro at the time), and my position seemed to be justified when they failed during a minor power interruption, while other computers not connected to a UPS remained running.

 

A lot has changed since then however. Even the cheapest units now claim to be line interactive models, and I'm not at all happy with my current APC unit. It likely only needs a new battery, but given it has never told me I needed to replace the battery, and was a replacement (when new) for a unit that constantly complained about the battery needing replacing, I'm inclined to treat it as faulty. Both units came with a very long printout of test results, all of which indicated they passed.

 

With the above in mind, can anyone recommend tower units (1500-2000VA)?

 

My main requirement is to be able to change batteries without disconnecting everything. This isn't included in documentation for the reasonably priced Eaton 5E range, so I suspect it's not possible there.

 

 

I just realised i misread change batteries, with charge batteries. Ignore this post :) 

 

 

 

 

 

 

 

 


9802 posts

Uber Geek

Lifetime subscriber

  #1988933 5-Apr-2018 17:46
Send private message

could try Enirgi Power Solutions in Wiri

 

http://www.enirgipower.com.au/locations/new-zealand/


1146 posts

Uber Geek


  #1988944 5-Apr-2018 18:17
Send private message

I use an EATON ups as well and it does weekly self-test. Nevertheless it reports to the server and triggers actions via NUT (Network UPS Tools). There is an access door to the battery compartment which can be opened without disconnecting the plugs.

 

SirHumphreyAppleby:

 

My main requirement is to be able to change batteries without disconnecting everything.

 

 

I'm not sure if you like to change the batteries "online" (hot-replaceable) without shutting down the power sinks. That wouldn't work.





- ISP1: OneBox FTTH modem, 1/.5G, full DS, VLAN7, VoIP + ipTV streaming flat
- ISP2: LTE USB modem + GL-AR750S, 100/40M data plan (wireless fallback)
- NET: OPNsense CI329, ES-16-XG, C2960X-48TS, 3 GWN7630, EL1600+800
- SVR: 9i3C246 32G/24T, 2 H2 16G/500G, N2 4G/1T || 2 remote HC2 14T+4T
- USR: DeskMini 9i5, NUC 8i7HVK, Aspire E5, EliteBook 840, Galaxy Tab, 4K TV
- IoT (EU868): openHAB, CCU3, Vantage ISS 6327, LoRaWAN 4 GWs/15 Nodes
- 3D: 2 Ender-3/Pro, 4 Ultimaker 2E+/3/3+/S5, MPCNC, EleksLaser-A3 Pro
- ipPBX: GO-Box, 2 GRP2613, SPA112 (Fax & W-48, a 1948 Siemens phone)

 

 




1337 posts

Uber Geek


  #1989026 5-Apr-2018 19:51
Send private message

Tinkerisk:

 

I'm not sure if you like to change the batteries "online" (hot-replaceable) without shutting down the power sinks. That wouldn't work.

 

 

It's not absolutely critical that the batteries be hot-swappable, although that is my preference given the increasing amount of things that depend on the computers running (phones, television, security etc.). I do need easy access however.


1146 posts

Uber Geek


  #1995834 14-Apr-2018 00:27
Send private message

The open source NUT s/w is still great and works relable after some tinkering. Now the NUT server will inform all clients attached to the same USV before shutdown and re-initiate communication after power is back.





- ISP1: OneBox FTTH modem, 1/.5G, full DS, VLAN7, VoIP + ipTV streaming flat
- ISP2: LTE USB modem + GL-AR750S, 100/40M data plan (wireless fallback)
- NET: OPNsense CI329, ES-16-XG, C2960X-48TS, 3 GWN7630, EL1600+800
- SVR: 9i3C246 32G/24T, 2 H2 16G/500G, N2 4G/1T || 2 remote HC2 14T+4T
- USR: DeskMini 9i5, NUC 8i7HVK, Aspire E5, EliteBook 840, Galaxy Tab, 4K TV
- IoT (EU868): openHAB, CCU3, Vantage ISS 6327, LoRaWAN 4 GWs/15 Nodes
- 3D: 2 Ender-3/Pro, 4 Ultimaker 2E+/3/3+/S5, MPCNC, EleksLaser-A3 Pro
- ipPBX: GO-Box, 2 GRP2613, SPA112 (Fax & W-48, a 1948 Siemens phone)

 

 


1146 posts

Uber Geek


  #2000086 21-Apr-2018 01:08
Send private message

Rule of thumb:

 

Take the real power announced by the UPS manufacturer, divide it by 2 and you have the real max. power you can pull without overstressing the battery too much (which reduces it's lifetime drastically). Each 10°C more than 25°C halves lifetime of the battery as well. At 35°C in summer or in a unvented cabinet, don't expect much more than 1,5-2 instead of 3-4 years.

 

 

 

i.e. if the UPS is rated at 800VA/500W, pull not more than 250W (safely available for 10-12 minutes). My system shuts down after 2 minutes power loss to have enough capacity for 2 additional power loss/overvoltage events during the recharging cycle of 8 hours (never mentioned in the logfile up to now).





- ISP1: OneBox FTTH modem, 1/.5G, full DS, VLAN7, VoIP + ipTV streaming flat
- ISP2: LTE USB modem + GL-AR750S, 100/40M data plan (wireless fallback)
- NET: OPNsense CI329, ES-16-XG, C2960X-48TS, 3 GWN7630, EL1600+800
- SVR: 9i3C246 32G/24T, 2 H2 16G/500G, N2 4G/1T || 2 remote HC2 14T+4T
- USR: DeskMini 9i5, NUC 8i7HVK, Aspire E5, EliteBook 840, Galaxy Tab, 4K TV
- IoT (EU868): openHAB, CCU3, Vantage ISS 6327, LoRaWAN 4 GWs/15 Nodes
- 3D: 2 Ender-3/Pro, 4 Ultimaker 2E+/3/3+/S5, MPCNC, EleksLaser-A3 Pro
- ipPBX: GO-Box, 2 GRP2613, SPA112 (Fax & W-48, a 1948 Siemens phone)

 

 


Create new topic




News »

Freeview On Demand app launches on Sony Android TVs
Posted 6-Aug-2020 13:35


UFB hits more than one million connections
Posted 6-Aug-2020 09:42


D-Link A/NZ extends COVR Wi-Fi EasyMesh System series with new three-pack
Posted 4-Aug-2020 15:01


New Zealand software Rfider tracks coffee from Colombia all the way to New Zealand businesses
Posted 3-Aug-2020 10:35


Logitech G launches Pro X Wireless gaming headset
Posted 3-Aug-2020 10:21


Sony Alpha 7S III provides supreme imaging performance
Posted 3-Aug-2020 10:11


Sony introduces first CFexpress Type A memory card
Posted 3-Aug-2020 10:05


Marsello acquires Goody consolidating online and in-store marketing position
Posted 30-Jul-2020 16:26


Fonterra first major customer for Microsoft's New Zealand datacentre
Posted 30-Jul-2020 08:07


Everything we learnt at the IBM Cloud Forum 2020
Posted 29-Jul-2020 14:45


Dropbox launches native HelloSign workflow and data residency in Australia
Posted 29-Jul-2020 12:48


Spark launches 5G in Palmerston North
Posted 29-Jul-2020 09:50


Lenovo brings speed and smarter features to new 5G mobile gaming phone
Posted 28-Jul-2020 22:00


Withings raises $60 million to enable bridge between patients and healthcare
Posted 28-Jul-2020 21:51


QNAP integrates Catalyst Cloud Object Storage into Hybrid Backup solution
Posted 28-Jul-2020 21:40



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.


Support Geekzone »

Our community of supporters help make Geekzone possible. Click the button below to join them.

Support Geezone on PressPatron



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.