I just came home to find my heat pump wasn't operating, sure enough the circuit has been tripped.

 

I switched the CB back on. No issues. After 20 minutes, same thing.

 

This time it won't come on. The heat pump was installed on an existing circuit - unfortunately it's my fault for not quering this with the installer at the time. This was done in August 2016.

 

I've also isolated the heatpump by turning off the outdoor switch and yet the rest of the circuit will not come on. I'm hoping it's just the MCD that is gone?

 

MCD: https://www.hagerelectro.com.au/e-catalogue/energy-distribution/modular-protection-devices/mcbs/mcbs-residential-6ka-c-curve/msn120/18994.htm

 

Heat pump: https://www.mitsubishi-electric.co.nz/heatpump/i/69108B/rapidheat-kj50-floor-console-heat-pump

 

My biggest question is why did it happen?






View this topic in a long page with up to 500 replies per page Create new topic
 1 | 2
295 posts

Ultimate Geek


  #2516753 3-Jul-2020 13:18
Send private message quote this post

Maybe wiring has been damaged. Melted? 

 

Get the electrician around.


5849 posts

Uber Geek


  #2516793 3-Jul-2020 14:21
Send private message quote this post

When this happened to us two houses ago, it turned out that wiring had melted inside the outdoor unit, which had caused a short circuit.  The electrician classified it as fusion and our insurance policy covered this.  So ... two new heat pumps





Mike

 
 
 
 


1825 posts

Uber Geek

Trusted
Lifetime subscriber

  #2516904 3-Jul-2020 17:20
Send private message quote this post

You ask why it didn't want to reset right away, Overload protection on circuit breakers are thermal based, that is the heat rise on the bi-metal strip inside the circuit breaker has to cool down in order to reset, the more severe the overload the greater the heat generated and contained within the circuit breaker, and if it does reset the time before it trips will be shorter. It's kind of like boiling your electric jug, if it's just boiled and you flick the switch again it turns right off as it is already at it's "turn off point or trip point"

 

 

 

Most likely your heat pump has had a failure that has caused an overload condition in the wiring, the circuit breaker has done it's job, not so much a factor that the heat pump is on a shared circuit with power outlets, it's just a bit more inconvenient.

 

 


2272 posts

Uber Geek

Trusted

  #2516919 3-Jul-2020 18:01
Send private message quote this post

I would suggest something like:

 

"I Circuit Breaker A, Take You, Circuit Breaker B, to be my lawfully wedded husband/wife.  Through voltage spikes and dips, blackouts and brownouts I will always be by your side.  You switch me on. With you, my circuit is finally completed"

 

Good luck with your vows.


2170 posts

Uber Geek

Trusted

  #2516927 3-Jul-2020 18:17
Send private message quote this post

^ what a muppet.



921 posts

Ultimate Geek

Subscriber

  #2516974 3-Jul-2020 18:46
Send private message quote this post

Thanks for the replies. I'll get in touch with the heat pump sparky on monday.

 

 

 

gregmcc:

 

You ask why it didn't want to reset right away, Overload protection on circuit breakers are thermal based, that is the heat rise on the bi-metal strip inside the circuit breaker has to cool down in order to reset, the more severe the overload the greater the heat generated and contained within the circuit breaker, and if it does reset the time before it trips will be shorter. It's kind of like boiling your electric jug, if it's just boiled and you flick the switch again it turns right off as it is already at it's "turn off point or trip point"

 

 

 

Most likely your heat pump has had a failure that has caused an overload condition in the wiring, the circuit breaker has done it's job, not so much a factor that the heat pump is on a shared circuit with power outlets, it's just a bit more inconvenient.

 

 

 

 

 

 

Thanks - should this breaker have been a RCD considering its on the same circuit as other outlets (4 doubles and a single)?








921 posts

Ultimate Geek

Subscriber

#2516975 3-Jul-2020 18:47
Send private message quote this post

muppet:

 

I would suggest something like:

 

"I Circuit Breaker A, Take You, Circuit Breaker B, to be my lawfully wedded husband/wife.  Through voltage spikes and dips, blackouts and brownouts I will always be by your side.  You switch me on. With you, my circuit is finally completed"

 

Good luck with your vows.

 

 

 

 

haha - it's been a long week 






 
 
 
 


1825 posts

Uber Geek

Trusted
Lifetime subscriber

  #2516978 3-Jul-2020 19:04
Send private message quote this post

James Bond:

 

Thanks for the replies. I'll get in touch with the heat pump sparky on monday.

 

 

 

gregmcc:

 

You ask why it didn't want to reset right away, Overload protection on circuit breakers are thermal based, that is the heat rise on the bi-metal strip inside the circuit breaker has to cool down in order to reset, the more severe the overload the greater the heat generated and contained within the circuit breaker, and if it does reset the time before it trips will be shorter. It's kind of like boiling your electric jug, if it's just boiled and you flick the switch again it turns right off as it is already at it's "turn off point or trip point"

 

 

 

Most likely your heat pump has had a failure that has caused an overload condition in the wiring, the circuit breaker has done it's job, not so much a factor that the heat pump is on a shared circuit with power outlets, it's just a bit more inconvenient.

 

 

 

 

 

 

Thanks - should this breaker have been a RCD considering its on the same circuit as other outlets (4 doubles and a single)?

 

 

No as a heat pump is not a socket outlet, it is classed as a fixed wired appliance even though in your case it is wired to the same circuit as socket outlets

 

 


2261 posts

Uber Geek


  #2516985 3-Jul-2020 19:29
Send private message quote this post

My money is on rodents.

I haven't seen a circuit breaker fail, but I've seen them do their job plenty of times.

This doesn't necessarily need to be a heat pump electrician, in fact it sounds like the heat pump isn't the issue. Any competent sparky should be able to sort this out for you.




Electrician.

 

Location: Dunedin

 

 




921 posts

Ultimate Geek

Subscriber

  #2516998 3-Jul-2020 20:07
Send private message quote this post

andrewNZ: My money is on rodents.

I haven't seen a circuit breaker fail, but I've seen them do their job plenty of times.

This doesn't necessarily need to be a heat pump electrician, in fact it sounds like the heat pump isn't the issue. Any competent sparky should be able to sort this out for you.

 

 

 

This did cross my mind. The house is from 1908 (wiring is early 1990s). I also did wonder if the 10 days of rain we've had recently in Christchurch has had anything to do with it (i.e. water in the outdoor unit).






1 post

Wannabe Geek


  #2517070 3-Jul-2020 22:30
Send private message quote this post

I agree, if you have turned off the AC isolator and the CB is still tripping then its something else in the circuit (or water in the isolator if its outside). Next step would be go round those outlets that are not working and unplug everything then try again, if that works start plugging back in. If there is a fridge on the circuit my money is on that for the defrost element.

 

Agree with the CB failure comment, im an electrician and I dont think I have ever seen a CB fail in that it just starts tripping.




921 posts

Ultimate Geek

Subscriber

  #2517453 5-Jul-2020 07:57
Send private message quote this post

Danite:

 

I agree, if you have turned off the AC isolator and the CB is still tripping then its something else in the circuit (or water in the isolator if its outside). Next step would be go round those outlets that are not working and unplug everything then try again, if that works start plugging back in. If there is a fridge on the circuit my money is on that for the defrost element.

 

Agree with the CB failure comment, im an electrician and I dont think I have ever seen a CB fail in that it just starts tripping.

 

 

 

 

Thanks for the reply - I have a sparky coming tomorrow.

 

Small update: the CB is definetely working as I unplugged everything as you mentioned and see what worked. Fridge not on the circuit.

 

Items such as an espresso machine and Google Home Speaker wouldn't come on however I managed to get one of these going (the LED lit up) and a touch lamp did turn on - however it's almost as the isn't enough voltage in the circuit as the lamp wouldn't go as bright as usual and was slow to get to level (not very stable either).

 

I was able to replicate this with two touch lamps on two different power outlets on the same circuit. I left it at that and switched the circuit back off.






2261 posts

Uber Geek


  #2517553 5-Jul-2020 14:38
Send private message quote this post

Definitely stop trying to reset it, leave the breaker OFF.

A few reasons I say this:
- At some point the short might be blown clear, this could make the fault harder to find.
- Resetting the breaker might be creating a spark. Sparks are bad for obvious reasons.
- A partially cleared fault may allow the breaker to be reset, but still generate significant amounts of heat. Bad for obvious reasons.

Electricity is great, but faults are a significant hazard.




Electrician.

 

Location: Dunedin

 

 




921 posts

Ultimate Geek

Subscriber

  #2517847 6-Jul-2020 09:42
Send private message quote this post

andrewNZ: Definitely stop trying to reset it, leave the breaker OFF.

A few reasons I say this:
- At some point the short might be blown clear, this could make the fault harder to find.
- Resetting the breaker might be creating a spark. Sparks are bad for obvious reasons.
- A partially cleared fault may allow the breaker to be reset, but still generate significant amounts of heat. Bad for obvious reasons.

Electricity is great, but faults are a significant hazard.

 

Thanks - yes I won't be touching it again. Will report back when the sparky has had a look at it.








921 posts

Ultimate Geek

Subscriber

  #2520133 9-Jul-2020 15:09
Send private message quote this post

Sparky found the problem in the spare bedroom:

 

 

We've done a partial renovation but unfortunately we never got to this socket. Sparky said we're lucky and I'd have to agree.

 

I'll probably get them all replaced soon.






 1 | 2
View this topic in a long page with up to 500 replies per page Create new topic




News »

Pre-orders for Huawei MateBook 13 open now
Posted 14-Aug-2020 14:26


Freeview On Demand app launches on Sony Android TVs
Posted 6-Aug-2020 13:35


UFB hits more than one million connections
Posted 6-Aug-2020 09:42


D-Link A/NZ extends COVR Wi-Fi EasyMesh System series with new three-pack
Posted 4-Aug-2020 15:01


New Zealand software Rfider tracks coffee from Colombia all the way to New Zealand businesses
Posted 3-Aug-2020 10:35


Logitech G launches Pro X Wireless gaming headset
Posted 3-Aug-2020 10:21


Sony Alpha 7S III provides supreme imaging performance
Posted 3-Aug-2020 10:11


Sony introduces first CFexpress Type A memory card
Posted 3-Aug-2020 10:05


Marsello acquires Goody consolidating online and in-store marketing position
Posted 30-Jul-2020 16:26


Fonterra first major customer for Microsoft's New Zealand datacentre
Posted 30-Jul-2020 08:07


Everything we learnt at the IBM Cloud Forum 2020
Posted 29-Jul-2020 14:45


Dropbox launches native HelloSign workflow and data residency in Australia
Posted 29-Jul-2020 12:48


Spark launches 5G in Palmerston North
Posted 29-Jul-2020 09:50


Lenovo brings speed and smarter features to new 5G mobile gaming phone
Posted 28-Jul-2020 22:00


Withings raises $60 million to enable bridge between patients and healthcare
Posted 28-Jul-2020 21:51



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.


Support Geekzone »

Our community of supporters help make Geekzone possible. Click the button below to join them.

Support Geezone on PressPatron



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.