I have a PEAD 125 ducted heatpump and I want to add a Mitsi MAC-588IF-E Wi-Fi controller to it.  The Wi-Fi controller needs to plug into the CN105 connector on the air handler however CN105 is already occupied by the connection to the wired remote control panel (wall mounted). Does anyone know if I can 'simply' connect these two controllers in parallel?  If so, I would make up a 'double adaptor' cable using the bits from aliexpress.

 

I note the Mitsi website says:

 

 

  • If you have the optional Wi-Fi Interface connected to the indoor unit then unfortunately the Wi-Fi Interface plugs into the same terminal (CN105) as your current wired controller. As there is only one CN105 terminal on each indoor unit it is not possible to have both a wired controller and Wi-Fi Control.

 

However Gemini suggests otherwise, pointing to several aftermarket devices that do it.  I guess my question is wether those devices are just glorified double adaptors? 

 

I found helpful info on CN105 in this post and other relevant info in this 2023 post.

 

 

 

 




catdog
108 posts

Master Geek
+1 received by user: 17


  #3488815 8-May-2026 16:17
Send private message quote this post

peng1nz:

 

Does anyone know if I can 'simply' connect these two controllers in parallel?  If so, I would make up a 'double adaptor' cable using the bits from aliexpress.

 

 

 

 

It's a serial port, so no you cannot just connect two devices in parallel as the TX signals will fight each other. 


peng1nz
51 posts

Master Geek
+1 received by user: 15


  #3488979 8-May-2026 23:00
Send private message quote this post

catdog:

 

It's a serial port, so no you cannot just connect two devices in parallel as the TX signals will fight each other. 

 

 

Thanks for that. Now that I've climbed up into the ceiling to take a look I can see the wired control panel (PAR-40MAA) is NOT using CN105.  (It is instead a two wire interface). I guess the info on Mitsi website must be specific for high wall units as opposed to ducted.  Therefore I was able to plugin the Wi-Fi adaptor and all is now up and running.

 

For reference, CN105 on a PEAD-M125 air handler is the red connector at top right in this photo.

 

 

 