#161851 21-Jan-2015 18:36
Send private message

I have just received a quote for re-roofing our three bedroom house with colorsteel corrugated iron. At $9700 + GST it was a bit more than I anticipated. Perhaps it is the OSH regs mentioned in earlier posts.

On our roof there is a change of pitch of 6 degrees. There is a 5.2m length, a 6 degree change of pitch, thence another 2.7m. The roofer, on consideration, felt the best solution was to bend the iron at this join. I think his yardstick was that it is less than 8 degrees. He guessed, rightly, that it was.

Reading other posts here, whereby "Little dents become holes, holes become splits through expanding and contracting", I am a little concerned this may impact the life of the roof?

Create new topic

This is a filtered page: currently showing replies marked as answers. Click here to see full discussion.

gazbo
89 posts

Master Geek
+1 received by user: 14


  #1219512 21-Jan-2015 21:55
Send private message

Corrugated roofing should have a minimum pitch of 8 degrees. If less you are supposed to use a different profile. I would be surprised if the manufacturer would warrant it otherwise. 

You are right in regards to bends in sheeting. If gradual or curved it is not quite the same issue.

At the change of pitch upwards you should form a clean break in the sheets and have a transition flashing installed that laps under the higher roof sheet at least 200mm with a turn up or hem at the top of the flashing. The flashing should lap 100mm over the lower sheet. The high end of the lower sheet should also be turned up beneath the flashing. Depending on your wind zone you may need profiled closure strips between the flashing and sheets.

Maxx is necessary in a sea spray zone otherwise Endura will suffice. However, ask for the price difference between the two because if it is minimal then Maxx will last longer. If significant then stick with Endura. Sea spray zones used to be defined as within 500m of the shore (straight line of course). However, places like Wellington sea spray can travel much further.