Place I know of will just replace the lead acid UPS batteries after any reasonable outage because they seem to be a 1 or 2 shot type thing. On the subsequent outages they would die without warning at a very short runtime.

 

If they are just holding over for a generator to start then fine, but using the lead acid batteries capacity down to near zero seems to be the end of them.

 

Bring on the lithium ones.

 

 

When dimensioning their UPS systems, people often make the mistake of misinterpreting the manufacturer's specifications. A 1600VA UPS can withstand a load of 1600W for approx. 11-12 minutes, after which the batteries are completely discharged – something that should be avoided.

 

Eaton has discharge curves for its UPS systems, which are a little difficult to find, but once you have them, you can quickly see that much lower loads should be expected. My two (soon to be three) UPS units are purely safety UPS units whose sole task is to ensure the safe shutdown of the servers after 15 minutes. This is controlled by a Raspberry Pi, which has full control over the UPS via USB. To do this, it also queries the internal measurement data via USB. Occasionally, it also tests via (small!) partial discharge whether the capacity of the batteries is still sufficient (and not that an outdated battery appears to be OK, but then collapses under load).

 

As already mentioned, normal batteries need to be replaced after 2-3 years, and those with extended capacity after 4-5 years – assuming that they are not kept at temperatures higher than 24°C (which some people in the rack do not always take into account; the cooler, the better for the service life).





     

  • Qui nihil scit, omnia credere debet.
  • Firewalls do NOT stop dragons.
  • In effect we have everything to hide from someone, and no idea who someone is.



Dynamic
4016 posts

Uber Geek
+1 received by user: 1853

ID Verified
Trusted
Lifetime subscriber

  #3436118 20-Nov-2025 09:11
Send private message

Tinkerisk:

 

When dimensioning their UPS systems, people often make the mistake of misinterpreting the manufacturer's specifications. A 1600VA UPS can withstand a load of 1600W for approx. 11-12 minutes, after which the batteries are completely discharged – something that should be avoided.

 

 

I wish that was accurate.  UPS are sold by VA rating... e.g. the 1600VA as you mention.  The Watts rating is always lower, and usually significantly lower.  A 1000VA UPS is typically rated for around 600w, though I don't remember the reasons for this.  If you run a basic UPS at 100% load (600w in this case) you'll only get 2-3 minutes of runtime before the battery dies.  If you run the ups at 50% load, you'll get 12-15 minutes of runtime as the battery is under far less stress (in layman's terms).  This is common across all basic UPS devices of all brands, to the best of my knowledge.

 

Eaton 5S1000i Runtime Graph: Battery Runtimes for Eaton 5S1000i

 

All Eaton Runtime Graphs: https://www.eaton.com/gb/en-gb/products/backup-power-ups-surge-it-power-distribution/backup-power-ups/ups-runtime-graphs-emea.html 





“Don't believe anything you read on the net. Except this. Well, including this, I suppose.” Douglas Adams


Tinkerisk
4800 posts

Uber Geek
+1 received by user: 3660


  #3436436 21-Nov-2025 17:54
Send private message

Dynamic:

 

Tinkerisk:

 

When dimensioning their UPS systems, people often make the mistake of misinterpreting the manufacturer's specifications. A 1600VA UPS can withstand a load of 1600W for approx. 11-12 minutes, after which the batteries are completely discharged – something that should be avoided.

 

 

I wish that was accurate.  UPS are sold by VA rating... e.g. the 1600VA as you mention.  The Watts rating is always lower, and usually significantly lower.  A 1000VA UPS is typically rated for around 600w, though I don't remember the reasons for this.  If you run a basic UPS at 100% load (600w in this case) you'll only get 2-3 minutes of runtime before the battery dies.  If you run the ups at 50% load, you'll get 12-15 minutes of runtime as the battery is under far less stress.

 

 

That is absolutely correct. A load with an effective load in W is the worst case scenario and is almost never reached. However, the apparent load in VA is specified – the higher value ‘sounds better from a marketing perspective’.





     

  • Qui nihil scit, omnia credere debet.
  • Firewalls do NOT stop dragons.
  • In effect we have everything to hide from someone, and no idea who someone is.