#201845 6-Sep-2016 15:27
Send private message

We are currently embarking on renovating our kitchen and in the process of getting sub trade quotes. The kitchen company we are using has said we need to get an isolated power supply for our microwave oven.


We are going to use our existing microwave as it is only  few months old. This microwave is currently plugged into a standard wall outlet.  It is going to be  inset into a cabinet in the new kitchen. 


Is this correct that the microwave now has to use an isolated outlet?


Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic
 1 | 2 | 3
networkn
Networkn
32349 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #1624676 6-Sep-2016 15:52
Send private message

Never heard of such things, esp given 99% of the microwaves in NZ wouldn't be on their own one.




antoniosk
2358 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #1624677 6-Sep-2016 15:54
Send private message

We have the same thing - microwave on the shelf. No isolation. 

 

 

 

For every direct wired appliance - ovens, hob, hood and fridge (which is for convenience) - they are on an isolation switch





________

 

Antoniosk


trig42
5809 posts

Uber Geek

ID Verified

  #1624678 6-Sep-2016 15:56
Send private message

I'm not an electrician, but I can't see the logic in it. (If by 'Isolated Power Supply' they/you mean seperate circuit with it's own breaker at the switchboard).

 

Are you sure the kitchen people don't just mean it needs it's own wall socket? It may need a switch outside of the cabinet so you can isolate the power without reaching behind the MWO.

 

A MWO only uses 1000W max. A Kettle or Toaster would use the same, if not more. They don't need their own circuits.




Rikkitic
Awrrr
18657 posts

Uber Geek

Lifetime subscriber

  #1624681 6-Sep-2016 16:00
Send private message

How modern is your house wiring, Mike? How much current does the microwave require? What else is fed from the circuit you want to use? I think there has to be more to it. If this is a requirement in New Zealand, which I very much doubt, there are an awful lot of microwave users in violation.

 

 





Plesse igmore amd axxept applogies in adbance fir anu typos

 


 


Dynamic
3866 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #1624682 6-Sep-2016 16:01
Send private message

I wonder if they mean having an externally accessible switch like your master switch for an oven.

 

A microwave that fits snugly in a new set of kitchen cabinets will be plugged into a socket that can't be reached in an emergency (i.e. microwave emitting smoke).  A separate switch on the wall which will 'isolate' (remote power from) the power socket that microwave is plugged into might be helpful in that situation.





“Don't believe anything you read on the net. Except this. Well, including this, I suppose.” Douglas Adams

 

Referral links to services I use, really like, and may be rewarded if you sign up:
PocketSmith for budgeting and personal finance management.  A great Kiwi company.


tchart
2379 posts

Uber Geek

ID Verified
Trusted

  #1624691 6-Sep-2016 16:24
Send private message

Dynamic:

 

I wonder if they mean having an externally accessible switch like your master switch for an oven.

 

A microwave that fits snugly in a new set of kitchen cabinets will be plugged into a socket that can't be reached in an emergency (i.e. microwave emitting smoke).  A separate switch on the wall which will 'isolate' (remote power from) the power socket that microwave is plugged into might be helpful in that situation.

 

 

We recently built (~6 months ago). Microwave has a dedicated socket. There is no separate switch for this socket - its just a normal socket. AFAIK its not on its own circuit on the circuit board.


Bung
6477 posts

Uber Geek

Subscriber

  #1624692 6-Sep-2016 16:25
Send private message

Our Panasonic microwave came with a recommendation to be on a separate 10A circuit to avoid tripping circuit breakers ( but few circuits would be limited to 10A). The label says 4.5A normal/7.5A initial current.

 

Isolation switch has a special meaning, most outlets may have a functional switch with the circuit breaker being the isolation switch.


 
 
 

Cloud spending continues to surge globally, but most organisations haven’t made the changes necessary to maximise the value and cost-efficiency benefits of their cloud investments. Download the whitepaper From Overspend to Advantage now.
kingjj
1728 posts

Uber Geek

ID Verified
Trusted

  #1624693 6-Sep-2016 16:32
Send private message

Brings back memories of flatting days when the microwave was on the same circuit as the kitchen light... you couldn't use both at the same time or it would trip....

 

We had our kitchen rewired last year and the microwave is on the same circuit as the fridge and dishwasher. No separate switch or anything.


mdooher
Hmm, what to write...
1424 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #1624696 6-Sep-2016 16:37
Send private message

They are probably recommending you be able to reach the switch with the microwave in place, not a bad idea, I might even say a good idea, same reason you don't put the dishwasher plug behind it.....however not legally required. Only the hob or a free standing range require such a switch.

 

also if the food in your microwave catches fire, or you left the tin foil on, just turn it off on the front and wait.

 

 

 

If you are getting a new plug put in they might mean you need an RCD fitted to that circuit





Matthew


gregmcc
2147 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #1624700 6-Sep-2016 16:46
Send private message

short and simple no, but I think they mean something else.

 

 

 

As the m'wave is in it's own little spot in the kitchen joinery the power point for it will be behind the m'wave, ideally you will need a separate "isolation" switch somewhere nearby that is easily accessible, similar to what is usually done with a dish washer.

 

 

 

....Yes I am an Electrician.

 

 


gregmcc
2147 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #1624704 6-Sep-2016 16:50
Send private message

mdooher:

 

They are probably recommending you be able to reach the switch with the microwave in place, not a bad idea, I might even say a good idea, same reason you don't put the dishwasher plug behind it.....however not legally required. Only the hob or a free standing range require such a switch.

 

also if the food in your microwave catches fire, or you left the tin foil on, just turn it off on the front and wait.

 

 

 

If you are getting a new plug put in they might mean you need an RCD fitted to that circuit

 

 

 

 

Isolation switches are only mandatory on socket outlets above 32Amp, 32A or below common sense should kick in - in the event of something going wrong how easily can you unplug the device, if you can't then it's time for an accessible switch somewhere.

 

 


MikeB4

18435 posts

Uber Geek

ID Verified
Trusted

  #1624706 6-Sep-2016 16:53
Send private message

The wall plug will be easy to reach in an emergency

neb

neb
11294 posts

Uber Geek

Trusted
Lifetime subscriber

  #1624780 6-Sep-2016 20:05
Send private message

Dynamic:

A microwave that fits snugly in a new set of kitchen cabinets will be plugged into a socket that can't be reached in an emergency (i.e. microwave emitting smoke).  A separate switch on the wall which will 'isolate' (remote power from) the power socket that microwave is plugged into might be helpful in that situation.

 

 

That would be one possible explanation, but then it'd also apply to almost every other appliance in the house: fridge, TV (in a cabinet), stereo/AV/DVD player (cabinet), dishwasher, washing machine, etc. Just thinking of my house and those of friends/neighbours, the only thing that has an accessible switch is usually the washing machine, and even then it's often above/beside the machine that's hypothetically on fire. In any case in the event of an electrical fire the first thing I'd do is flip the main house circuit breaker ("Shut them all down. Hurry! Oh, no"). Then figure out which circuit it was on after you've dealt with the fire.

solutionz
589 posts

Ultimate Geek
Inactive user


  #1624800 6-Sep-2016 20:48
Send private message

Having just taken a product though standards testing I can tell you that "Household and similar electrical appliances" are required to have an accessible means of disconnection ("isolation") for safety being either:

 

A) Approved appliance mains inlet switch (microwaves don't usually have these).

 

B) Physical disconnection from supply lead (microwaves usually have fixed lead)

 

C) Physical disconnection from mains outlet (probably inaccessible due to inset cabinet).

 

D) Approved mains outlet switch (your only remaining option).

 

 

 

Yes @neb same goes for all those other appliances. The approved user manuals will all contain a clause to the effect of:

 

"To turn this apparatus off completely, you must disconnect it from the wall outlet. Consequently, the wall outlet and power plug must be readily accessible at all times."

 

 


MikeB4

18435 posts

Uber Geek

ID Verified
Trusted

  #1624808 6-Sep-2016 20:57
Send private message

We have an electrician coming tomorrow to quote, I will take into account all that's been said here and what the electrician says, he is the professional and will see first hand what

 

The install is.


 1 | 2 | 3
Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic





News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.