# 251356 20-Jun-2019 21:47
Send private message quote this post

We are moving things around our small 40’s built house, and that means bringing my large desktop PC and my wife's decent sized PC into the same room.  The problem is that the room has very few power sockets on the wall and we will have to “daisy chain”; (ie connect) firstly (1) an extension cord from the socket to (2) x6 socket powerboard then and second (3) shorter extension cord to a final (4) x3 socket powerboard.

 

I will be using x2 power boards with Surge Protection (something like this https://www.bunnings.co.nz/hpm-6-outlet-powerboard-with-surge-protection_p00101825 or will I need something tougher?)

 

The equipment that we will be using on that socket include;

 

 

 

x6 socket powerboard:

 

  • 1xPC (650W PSU)
  • 1x LED monitor
  • 1x inkjet printer
  • X1 desk lamp (40W)
  • (+ the second extension cord plugged in to “daisy-chain” to the second powerboard)

x3 socket powerboard:

 

  • 1xPC (760W PSU)
  • 1x LED monitor
  • 1x free standing floor lamp (40W)

 

 

I'm wondering whether the power draw on a single wall socket will be too much?

 

Is there a way to work out the power draw/capacity of the socket?

 

Look forward to your thoughts and thanks very much in advance.  😄


Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic
 1 | 2 | 3
190 posts

Master Geek
+1 received by user: 61


  # 2261700 20-Jun-2019 22:02
3 people support this post
Send private message quote this post

Assume PC runs at full wattage (unlikely), lamps 40W, LED 40W and printer 40W (all high side)the total wattage is 1610W which is well below the max of 2300W so all fine.

 

 


845 posts

Ultimate Geek
+1 received by user: 115

Trusted

  # 2261715 21-Jun-2019 00:16
3 people support this post
Send private message quote this post

I wouldn’t worry too much, as regardless of what you add, when it gets too much it will trip the breaker/blow the fuse .

 
 
 
 


791 posts

Ultimate Geek
+1 received by user: 388


  # 2261726 21-Jun-2019 06:08
Send private message quote this post

RolemasterGM:

 

I'm wondering whether the power draw on a single wall socket will be too much?

 

Is there a way to work out the power draw/capacity of the socket?

 

 

You can use a clamp meter or one of these to see how much power you are using.

 

https://www.bunnings.co.nz/arlec-energy-cost-electrical-meter_p04410270

 

Your load doesn't seem particularly high. My rack has 21 power outlets alone, most of which are in use. The same UPS which powers the rack also runs three more PCs in the house, and the only time the USP load limit is exceeded (lower than the socket power limit) is when devices are powered up en masse following an outage.




5 posts

Wannabe Geek
+1 received by user: 3


  # 2261727 21-Jun-2019 06:26
One person supports this post
Send private message quote this post

SirHumphreyAppleby:

 

RolemasterGM:

 

I'm wondering whether the power draw on a single wall socket will be too much?

 

Is there a way to work out the power draw/capacity of the socket?

 

 

You can use a clamp meter or one of these to see how much power you are using.

 

https://www.bunnings.co.nz/arlec-energy-cost-electrical-meter_p04410270

 

Your load doesn't seem particularly high. My rack has 21 power outlets alone, most of which are in use. The same UPS which powers the rack also runs three more PCs in the house, and the only time the USP load limit is exceeded (lower than the socket power limit) is when devices are powered up en masse following an outage.

 

 

Excellent thanks all for your very helpful responses. 

 

I guess my other key issue is if there could be any possible dangerous implications (over heating etc) on "daisy-chaining" - ie linking x2 extension cords and x2 surge protected power boards - to one socket. Presume as no one is mentioning it (rather than simply the total Wattage into the socket as mentioned above) is not likely to be a problem/danger. 

 

Thanks again for all your help & SirHumphreyAppleby LOVE your taste in TV shows. Yes Minister/Prime Minister had one of the best scripts of all time! 

 

 


791 posts

Ultimate Geek
+1 received by user: 388


  # 2261729 21-Jun-2019 06:36
One person supports this post
Send private message quote this post

RolemasterGM:

 

I guess my other key issue is if there could be any possible dangerous implications (over heating etc) on "daisy-chaining" - ie linking x2 extension cords and x2 surge protected power boards - to one socket. Presume as no one is mentioning it (rather than simply the total Wattage into the socket as mentioned above) is not likely to be a problem/danger. 

 

Thanks again for all your help & SirHumphreyAppleby LOVE your taste in TV shows. Yes Minister/Prime Minister had one of the best scripts of all time! 

 

 

It is brilliant. Should be compulsory viewing for all high school students, before they get an opportunity to vote.

 

Poor connections can lead to heat issues. You shouldn't have issues with quality brands like HPM, but I'd stay away from the cheapest of the cheap, particularly at the wall end. I have a few cheap boards. They seem fine, but I wouldn't install those in a location where they were constantly carrying high current.


6763 posts

Uber Geek
+1 received by user: 634

Trusted
Subscriber

  # 2261731 21-Jun-2019 06:59
8 people support this post
Send private message quote this post

Just don't go plugging a heater into the plug strips, if you must use a heater plug directly into the wall socket.

Cyril

1790 posts

Uber Geek
+1 received by user: 435


  # 2261821 21-Jun-2019 10:22
2 people support this post
Send private message quote this post

Some of the power boards have a overcurrent trip switch .

 

Get QUALITY power board & extension cords , dont use Warehouse/mitre10/bunnings generic cheapies
Are HPM still a quality brand ?

 

Some of the generic's are really bad .

 

A better alternative , is to install a dual(2 socket) wall socket , instead of the single.
Very easy to install yourself , Ive put a few into my 1960's house.

 

Or , try & find a power board with a long lead (eliminating the ext lead). Really hard to find for some reason .


 
 
 
 


3907 posts

Uber Geek
+1 received by user: 1216


  # 2261830 21-Jun-2019 10:31
Send private message quote this post

Your total wattage is probably fine, and certainly under the rating for the outlet,

 

My only concern would be the daisy chaining, it will mean that one of the power boards will be quite loaded,

 

A better option would be a double adapter (or replace the outlet with a double one) and then run each extension cord and power board as distinct feeds...


769 posts

Ultimate Geek
+1 received by user: 259


  # 2261836 21-Jun-2019 10:57
Send private message quote this post

Standard 10 amp socket should be good for around 4kw of power drain before tripping the circuit breaker / fuse (I think its 4.4 but could be mistaken).

 

 

If old style house (with ceramic fuses and fuse wire), double check what gauge the fuse wire is, should be 10 or 16 amp, if a MCB, check rating, again likely to be 10 or 16

 

 

Even with commercial / office installations, the run multiple circuits off the one MCB (i.e. a wall of sockets is only likely to feed back to a handful of breakers) as PCs and other normal office equipment doesn't draw much load

474 posts

Ultimate Geek
+1 received by user: 266

Trusted

  # 2261927 21-Jun-2019 12:31
2 people support this post
Send private message quote this post

wellygary:

Your total wattage is probably fine, and certainly under the rating for the outlet,


My only concern would be the daisy chaining, it will mean that one of the power boards will be quite loaded,


A better option would be a double adapter (or replace the outlet with a double one) and then run each extension cord and power board as distinct feeds...



Please don't use a double adapter, they are a fire waiting to happen. Replacing your single plug with a double outlet is a much safer idea. As mentioned above, multiple sockets are normally run from single breakers with no issue. The difference between that, and double adapters etc, is the connections. In the wall, the sparky will have ensured the connections are tight, and they don't move. Double adapters and the like introduce connections which can come loose, partially connect, arc etc - particularly when the weight of plugs pulls then away from the wall.

I've been to too many house fires as a result of these things, don't use them.




551 posts

Ultimate Geek
+1 received by user: 275


  # 2261931 21-Jun-2019 12:49
2 people support this post
Send private message quote this post

Every power board I have seen in NZ has over current protection. If total connected load draws more than 10A, the built in over current protection should trip, protecting the wall socket from overloading.

I should not that neither double plugs or piggy back plugs / extension cords have any form of over current protection, so it is possible to overload the wall socket this way.

It is important to note that the breaker for that circuit won't protect the socket from overloading, only the wire that feeds potentially multiple sockets. Breaker sizes of 16A and 20A are common, clearly more power than can be safely delivered by a single 10A socket. So it pays to be really carefull if connecting multiple loads to a single socket without over-current protection (i.e. double plug) 


22264 posts

Uber Geek
+1 received by user: 4787

Trusted
Subscriber

  # 2261941 21-Jun-2019 13:13
3 people support this post
Send private message quote this post

Scott3:

 

Every power board I have seen in NZ has over current protection. If total connected load draws more than 10A, the built in over current protection should trip, protecting the wall socket from overloading.

I should not that neither double plugs or piggy back plugs / extension cords have any form of over current protection, so it is possible to overload the wall socket this way.

It is important to note that the breaker for that circuit won't protect the socket from overloading, only the wire that feeds potentially multiple sockets. Breaker sizes of 16A and 20A are common, clearly more power than can be safely delivered by a single 10A socket. So it pays to be really carefull if connecting multiple loads to a single socket without over-current protection (i.e. double plug) 

 

 

The overload protection in them is crap, and will often not trip when its getting the plug really hot, or will trip on a sustained 1800 watt load. They are cost engineered pieces of crap that people will opt for the $3 one instead of the $7 one because theyre cheap.





Richard rich.ms

5478 posts

Uber Geek
+1 received by user: 1914


  # 2261975 21-Jun-2019 14:47
4 people support this post
Send private message quote this post

Brunzy: I wouldn’t worry too much, as regardless of what you add, when it gets too much it will trip the breaker/blow the fuse .

 

sen8or: Standard 10 amp socket should be good for around 4kw of power drain before tripping the circuit breaker / fuse (I think its 4.4 but could be mistaken).

 

There's some very dangerous advice being given in this thread. The breaker on a power circuit is there to protect the cable running to the outlet, not the outlet itself. Commonly, this will be rated at 16 or 20 amp. The outlet itself is only rated to 10 amp. Pulling enough current through a single 10 amp outlet to trip a 20 amp breaker (which incidently, will be more than 20 amps and is time dependant as well) will be massively overloading the outlet and probably result in a melted outlet, if not fire.

 

Basically, you are well into the danger zone for a fire before the breaker trips if all that current is going through a single outlet.


3181 posts

Uber Geek
+1 received by user: 698

Trusted

  # 2261991 21-Jun-2019 14:57
One person supports this post
Send private message quote this post

Brunzy: I wouldn’t worry too much, as regardless of what you add, when it gets too much it will trip the breaker/blow the fuse .

I don't think this is correct. The maximum power a 10 amp power point is designed to supply is 2400 watts. The fuse or CB will be able to deliver in excess of 10 amps. Drawing more than 10 amps from a power point isn't a smart idea.




Sony Xperia X running Sailfish OS. https://sailfishos.org The true independent open source mobile OS 
Samsung Galaxy Tab S3
Nokia N1
Dell Inspiron 14z i5


3181 posts

Uber Geek
+1 received by user: 698

Trusted

  # 2261994 21-Jun-2019 15:04
One person supports this post
Send private message quote this post

sen8or: Standard 10 amp socket should be good for around 4kw of power drain before tripping the circuit breaker / fuse (I think its 4.4 but could be mistaken).



I think you are mistaken. As far as I know 2400 watts (2.4kw) is the maximum you should draw from a 10 amp socket. See my post above.





Sony Xperia X running Sailfish OS. https://sailfishos.org The true independent open source mobile OS 
Samsung Galaxy Tab S3
Nokia N1
Dell Inspiron 14z i5


 1 | 2 | 3
Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic



Twitter and LinkedIn »



Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

Huawei's scholarship programme showcases international business to Kiwi undergrads
Posted 22-Jul-2019 17:53


Spark Sport launches across a range of new devices
Posted 22-Jul-2019 13:19


Dunedin selects Telensa to deliver smart street lighting for 15,000 LEDs
Posted 18-Jul-2019 10:21


Sprint announces a connected wallet card with built-in IoT support
Posted 18-Jul-2019 08:36


Educational tool developed at Otago makes international launch
Posted 17-Jul-2019 21:57


Symantec introduces cloud access security solution
Posted 17-Jul-2019 21:48


New Zealand government unveils new digital service to make business easier
Posted 16-Jul-2019 17:35


Scientists unveil image of quantum entanglement
Posted 13-Jul-2019 06:00


Hackers to be challenged at University of Waikato
Posted 12-Jul-2019 21:34


OPPO Reno Z now available in New Zealand
Posted 12-Jul-2019 21:28


Sony introduces WF-1000XM3 wireless headphones with noise cancellation
Posted 8-Jul-2019 16:56


Xero announces new smarter tools, push into the North American market
Posted 19-Jun-2019 17:20


New report by Unisys shows New Zealanders want action by social platform companies and police to monitor social media sites
Posted 19-Jun-2019 17:09


ASB adds Google Pay option to contactless payments
Posted 19-Jun-2019 17:05


New Zealand PC Market declines on the back of high channel inventory, IDC reports
Posted 18-Jun-2019 17:35



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.


Support Geekzone »

Our community of supporters help make Geekzone possible. Click the button below to join them.

Support Geezone on PressPatron



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.