#173828 8-Jun-2015 09:39
Send private message

Hi Team,


I need a bit of help / advice from you regarding hot water cylinder.


for past 2 months i have got quite a high power , and we haven't yet started to use the heaters yet for winter.


So i talked to a few people and figured it must be the hot water cylinder so got the Electrician in, who said the thermostat was faulty and changed it.


There has been a slight improvement but not that much. So i carried out monitoring for a week and this is what i found :


Over night, with no appliances used, the power consumption was aprox 15kwh ( for night duration approx 6-8 hrs )


after changing to new thermostat , no appliances used, over night is now stable at 9kwh ( same as above for night duration approx 6-8 hrs )


Now, Day time when there is again no appliances being used, usage is average 10-11 kwh ( for std 8hr working day ) 


I did another test with hot water switch off at MAIN Elec Board, and all appliances switched off ( apart from fridge, cellphones ) , power usage was 1kwh


So I kinda have figured out that the issue is hot water. I feel that the "standby " power consumption by the current hot water cylinder is way too high, which is approx 9 +10 = 19-20 kwh for 1 day. 


But i just need to confirm that is my conclusion corrrect. What do you think , am i on the right track assuming that the hot water is the cause of this situation.


What would a average hot water cylinder consumer whilst on standby / what would a brand new one consume.


Could any one perhaps take a small reading when they go to office , and one when they come back and tell me whats the consumption.


Reason being this will immensely help me to decide, if its  time to get a new cylinder - as this quite a expensive affair. It could cost me upto say $2k for getting new one done.


Appreciate your help,


Cheers !!






View this topic in a long page with up to 500 replies per page Create new topic
 1 | 2 | 3 | 4 | 5 | 6 | ... | 7
  #1319148 8-Jun-2015 09:52
Send private message

to see if it is the hot water cylinder, turn it off and leave it over night and see what happens.

Are you sure that its not leaking? if it is then there will be wasting hot water and needing to be reheated ie using power

sep11guy

660 posts

Ultimate Geek
Inactive user


  #1319150 8-Jun-2015 09:53
Send private message

Jase2985: to see if it is the hot water cylinder, turn it off and leave it over night and see what happens.

Are you sure that its not leaking? if it is then there will be wasting hot water and needing to be reheated ie using power



Yeah I already did that, and mentioned in my original post :: I did another test with hot water switch off at MAIN Elec Board, and all appliances switched off ( apart from fridge, cellphones ) , power usage was 1kwh 


Also, additional notes : 


House is a small 3 bed home, hot water cylinder is from 1965 

timmmay
20580 posts

Uber Geek

Trusted
Lifetime subscriber

  #1319166 8-Jun-2015 10:02
Send private message

15kwh is heaps. I use 5kwh each weekday morning around the time we're having showers. That includes having two heat pumps on for half an hour. We use around 30 units per day - closer to 40 on weekends, most like 25 on weekdays.

I could give you half hourly usage if that's helpful.

Given switching off your hot water drops your usage significantly I suspect you're on the right track. Get on on the roof and check the overflow pipe - see if there's water coming out or recent evidence of water. Be super careful, rooves can be slippery this time of year.

linw
2849 posts

Uber Geek


  #1319167 8-Jun-2015 10:03
Send private message

Errm, Jase, he did turn it off.

Electric heating is pretty simple so there aren't many ways one cistern can be more efficient than another. One factor would be insulation. You need to tell the forum about that. 

But, generally, greater power in equals greater water temp. Would be helpful if you put a thermometer under your hot water tap to measure that. 

There are real experts here who will chime in I am sure.

sep11guy

660 posts

Ultimate Geek
Inactive user


  #1319173 8-Jun-2015 10:15
Send private message

timmmay: 15kwh is heaps. I use 5kwh each weekday morning around the time we're having showers. That includes having two heat pumps on for half an hour. We use around 30 units per day - closer to 40 on weekends, most like 25 on weekdays.

I could give you half hourly usage if that's helpful.

Given switching off your hot water drops your usage significantly I suspect you're on the right track. Get on on the roof and check the overflow pipe - see if there's water coming out or recent evidence of water. Be super careful, rooves can be slippery this time of year.



My last bill , was around 29kwh per day, but going by history, for us its way way to much cause I know that as the bill is higher by approx $80 ( before that it was higher than $160 , which was before i replaced thermostat ) 


I dont want that intricate half hourly usage - if you could just please take 2 readings for me . 1) when you go to office , pls note down whats the meter reads  . 2) when you come back home what does the meter reads. thats all ( this is assuming that no one stays at home during normal business hrs ) .


This would greatly help me to decide if my hot water cylinder is consuming way too much energy for just being on standby 




HaggisKiwi
94 posts

Master Geek


  #1319176 8-Jun-2015 10:16
Send private message

House is a small 3 bed home, hot water cylinder is from 1965 


40 years is pretty good going for a HWC!  We had our 1974 model replaced a couple about 5 years ago when it shat itself, fortunately when plumber & sparky were on site doing our bathroom renovations.

Might be that your HWC has finally given up the ghost & it's internal elements are burning out. What remains is trying to do the whole job & using a lot more power to provide the how water you're used to.

Get a plumber/sparky in to check the HWC, but based on what you've said it looks like you many need to be budgeting to spend >$1k on replacing your HWC.
In our case, our replacement ended up saving us average $20 p/m over the year.

sep11guy

660 posts

Ultimate Geek
Inactive user


  #1319179 8-Jun-2015 10:20
Send private message

linw: Errm, Jase, he did turn it off.

Electric heating is pretty simple so there aren't many ways one cistern can be more efficient than another. One factor would be insulation. You need to tell the forum about that. 

But, generally, greater power in equals greater water temp. Would be helpful if you put a thermometer under your hot water tap to measure that. 

There are real experts here who will chime in I am sure.


Thanks for your replies, there is no insulation currently, but the home was insulated fully top and bottom few years back and our bills have gone up only for past 2 months.

water temp - last week the elec came and when he changed the thermostat , he first set it to 60C, but then we said it was way too hot, and then he came back next day and he changed it to 55deg C. 




andrewNZ
2487 posts

Uber Geek
Inactive user


  #1319181 8-Jun-2015 10:22
Send private message

My money is on a leak/overflow problem.

BTR

BTR
1527 posts

Uber Geek


  #1319183 8-Jun-2015 10:23
Send private message

I am guessing that by the date of your HWC thats it will be low pressure, have a look at the overflow pipe on the roof and male sure water isn't shooting out, if so the temp thermostat isn't working. I know you have replaced it but the replacement could be faulty.

Based on the age of your cylinder I would replace it, with a brand new cylinder. That way you have something thats more energy efficient because its better insulated and its internals are new.


I replaced my old 180L low pressure HWC with a brand new 300L main pressure cylinder 3-4 years ago and my power bills dropped. 

sep11guy

660 posts

Ultimate Geek
Inactive user


  #1319184 8-Jun-2015 10:27
Send private message

HaggisKiwi: 
Get a plumber/sparky in to check the HWC, but based on what you've said it looks like you many need to be budgeting to spend >$1k on replacing your HWC.
In our case, our replacement ended up saving us average $20 p/m over the year.



A electrician did come in and change the thermostat, which helped the stand by go down from 15kwh to 9kwh on night usage ( when there is no hot water being used at home ) 

but overall consumption is still high, considering that hot water is consuming approx 9+11= 20kwh just for standing and not providing us hot water ( ie no one using hot water)

sep11guy

660 posts

Ultimate Geek
Inactive user


  #1319186 8-Jun-2015 10:29
Send private message

andrewNZ: My money is on a leak/overflow problem.



Do you think that its worth getting this checked ( would this be a plumbers work ? ) before i assume my studies and go on replacing the whole cylinder . Cuz changing the cylinder is quite a expensive affair ( 1.5-2k approx, from what i have heard )

sep11guy

660 posts

Ultimate Geek
Inactive user


  #1319189 8-Jun-2015 10:30
Send private message

 


I replaced my old 180L low pressure HWC with a brand new 300L main pressure cylinder 3-4 years ago and my power bills dropped. 



Thanks for your help, can you please advice what did it cost you approx to get new one installed. 

timmmay
20580 posts

Uber Geek

Trusted
Lifetime subscriber

  #1319191 8-Jun-2015 10:30
Send private message

sep11guy: I dont want that intricate half hourly usage - if you could just please take 2 readings for me . 1) when you go to office , pls note down whats the meter reads  . 2) when you come back home what does the meter reads. thats all ( this is assuming that no one stays at home during normal business hrs ) .

This would greatly help me to decide if my hot water cylinder is consuming way too much energy for just being on standby 


The half hourly usage shows that on Thursday I used 3.16 units between 7am and 5pm, and on Friday I use 2.95 units.

Note that because we have showers at 6am and 6pm the water heater has finished by 7am so it's just maintaining temperature during the day. I only see small blips, plus the constant ticking over of things like the fridge. I can see 4-5 units used between 6 and 7am. Most of our power use is 6-7am and 6-10pm.

andrewNZ
2487 posts

Uber Geek
Inactive user


  #1319195 8-Jun-2015 10:33
Send private message

BTR: I am guessing that by the date of your HWC thats it will be low pressure, have a look at the overflow pipe on the roof and male sure water isn't shooting out, if so the temp thermostat isn't working. I know you have replaced it but the replacement could be faulty.

Based on the age of your cylinder I would replace it, with a brand new cylinder. That way you have something thats more energy efficient because its better insulated and its internals are new.


I replaced my old 180L low pressure HWC with a brand new 300L main pressure cylinder 3-4 years ago and my power bills dropped. 

I'm pretty sure they'd know if the cylinder was boiling, and they've stated the usage went down after the thermostat was changed.

That's also not the only reason for water to be coming out the top. If the Ajax valve is dodgy, there may be a small, barely noticable at a distance, amount of water overflowing. This would significantly increase the amount of power used.

Aredwood
3885 posts

Uber Geek


  #1319197 8-Jun-2015 10:34

As Timmay said you have a water leak. Most likely from the cylinder vent pipe on the roof. Or if you don't have an open vent pipe. There will be a relief valve that will be constantly discharging hot water. And if you are unlucky you will have a copper pipe that is cast into a concrete floor slab that has a leak. If this is the problem best long term fix is to abandon the leaking pipe and install a whole new one.





 1 | 2 | 3 | 4 | 5 | 6 | ... | 7
View this topic in a long page with up to 500 replies per page Create new topic



News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.