#244990 13-Jan-2019 11:03
Send private message

I have some Philips Hue Aphelion downlights that I am now unsure if I can install because of where my ceiling joists are.

 

The placement of the lights would be OK if I can have a couple of them butted right up against the side of a timber joist, but I am confused if it is safe to do this.

 

They are IC rated (abutted and covered), which I thought meant this would be alright - but in the installation instructions there is a diagram saying you need a certain amount of clearance. Isn't this contradictory?

 

The actual install would be done by an electrician, but since my ceiling is lath and plaster I'll likely have to pre-cut the holes myself. However, unless they can be butted up against a joist then I'll need to return them as I won't be able to put them in a suitable position - so I need to know before I do any cutting into the ceiling.

 

If any sparkies on the forum could clarify this for me would be great.

 

Thanks

 

EDIT: I'm talking about having the spring clips running parallel to the joist so the the downlight housing itself is against the joist.

 

EDIT 2: Medium/long term we will be having the old lath and plaster ceiling batoned and jibbed over at which point we'll be able to plan it to have the downlights exactly where we want - but that is a minimum of 6 months away and ideally we would like to have the lights installed sooner.

 

 





 Home:                                                           Work:
Home Work


View this topic in a long page with up to 500 replies per page Create new topic
 1 | 2 | 3
gregmcc
2152 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #2160090 13-Jan-2019 12:16
Send private message

Basically the electricity act requires that manufactures instructions should be followed when installed, when your electrician issues the COC check to see if the manufactures instructions box is ticked.

 

Your electrician can choose to ignore the manufactures instructions and install them against the joist, but should there be any issues then they will be the one held legally responsible.

 

 




richms
28220 posts

Uber Geek

Trusted
Lifetime subscriber

  #2160092 13-Jan-2019 12:20
Send private message

Where does it say it cant be against a joist? That image is just showing the minimum cavity size it can go into?





Richard rich.ms

Paul1977

5060 posts

Uber Geek


  #2160106 13-Jan-2019 12:32
Send private message

richms:

 

Where does it say it cant be against a joist? That image is just showing the minimum cavity size it can go into?

 

 

I assumed it was a clearance thing, rather than the overall cavity size - but I don't actually know.

 

It don't understand how it can specify minimum clearances, but also say it is fine to abut and cover with insulation?




sscribenz
21 posts

Geek

ID Verified

  #2160178 13-Jan-2019 14:15
Send private message

The IC rating, covered and abutted, refers to the ceiling insulation.


gregmcc
2152 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #2160244 13-Jan-2019 15:21
Send private message

Paul1977:

 

richms:

 

Where does it say it cant be against a joist? That image is just showing the minimum cavity size it can go into?

 

 

I assumed it was a clearance thing, rather than the overall cavity size - but I don't actually know.

 

It don't understand how it can specify minimum clearances, but also say it is fine to abut and cover with insulation?

 

 

The light diameter is 125mm the diagram clearly shows a 300mm diameter clearance, this means at least a 87.5mm clearance from the side of the light to timber.


Hammerer
2476 posts

Uber Geek

Lifetime subscriber

  #2160257 13-Jan-2019 15:42
Send private message

gregmcc:

 

The light diameter is 125mm the diagram clearly shows a 300mm diameter clearance, this means at least a 87.5mm clearance from the side of the light to timber.

 

 

I agree with @richms because the diagram is not that descriptive: there's no centre line or centre mark; there's no minimum clearance measurement; and either of these would be expected if the hole had to be centered in the space particular for a fitting of known diameter.

 

 


gregmcc
2152 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #2160260 13-Jan-2019 15:52
Send private message

Hammerer:

 

gregmcc:

 

The light diameter is 125mm the diagram clearly shows a 300mm diameter clearance, this means at least a 87.5mm clearance from the side of the light to timber.

 

 

I agree with @richms because the diagram is not that descriptive: there's no centre line or centre mark; there's no minimum clearance measurement; and either of these would be expected if the hole had to be centered in the space particular for a fitting of known diameter.

 

 

 

 

It's a pretty simple diagram, with very specific minimum dimensions "Min:300mm", you don't have to think too hard, and it obvious that the light is centered and many years of exp. in the trade tells me that the driver built in to the light fitting does get warm and you do not put it right next to timber.


 
 
 

Move to New Zealand's best fibre broadband service (affiliate link). Free setup code: R587125ERQ6VE. Note that to use Quic Broadband you must be comfortable with configuring your own router.
sparkz25
750 posts

Ultimate Geek
Inactive user


  #2160263 13-Jan-2019 16:13
Send private message

If is was me I would need to have a look at the installation.

 

But It's all up to your sparky if he wants to install them, so it might pay to get him to have a look.

 

Im guessing these are leds? is so they would generate a lot less heat than a halogen which should never be installed to celing batten or within 100mm of it.

 

NZECP54 is what you need to read.

 

This has all the clearences and stuff that you need to know, but when we were doing installs and prewires and had no celings in we would put them where it looked best and with plenty of clearance from battens.

 

https://worksafe.govt.nz/dmsdocument/1583-new-zealand-electrical-code-of-practice-for-the-installation-of-recessed-luminaires-and-auxiliary-equipment-nzecp-54-2001

 

 

 

 


gregmcc
2152 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #2160363 13-Jan-2019 16:44
Send private message

sparkz25:

 

If is was me I would need to have a look at the installation.

 

But It's all up to your sparky if he wants to install them, so it might pay to get him to have a look.

 

Im guessing these are leds? is so they would generate a lot less heat than a halogen which should never be installed to celing batten or within 100mm of it.

 

NZECP54 is what you need to read.

 

This has all the clearences and stuff that you need to know, but when we were doing installs and prewires and had no celings in we would put them where it looked best and with plenty of clearance from battens.

 

https://worksafe.govt.nz/dmsdocument/1583-new-zealand-electrical-code-of-practice-for-the-installation-of-recessed-luminaires-and-auxiliary-equipment-nzecp-54-2001

 

 

 

 

 

 

 

 

This ECP is 17 years old, it does not even mention IC rated light fittings and I suspect it has been superseded well and truly by AS/NZS3000:2017


mattwnz
20183 posts

Uber Geek


  #2160375 13-Jan-2019 17:16
Send private message

Contact the manufacturer and ask if it will void the warranty to have it closer to flammable elements such as joists. From what I understand, IC refers to insulation only, and only insulation that is non flammable, so you should check with the insulation manufacturer as well. Odd that the stuck the IC sticker over the logo that shows this. 


Paul1977

5060 posts

Uber Geek


  #2160383 13-Jan-2019 17:29
Send private message

Thanks for the feedback guys.

 

I was in a lighting place today and asked the guy there, who said very much what everyone hear has - it wants that much clearance from flammable material (which would include a timber joist), possibly because they just haven't paid for the testing required to be able to say it is zero clearance.

 

So while the chances of it anything happening with the low temps coming of an LED are low, if it did happen there could be insurance implications etc if the clearance guidelines aren't followed.

 

I'm having a rethink of the design to try to make it work while still allowing these minimum clearances, and will give a sparkie a call in the morning.


mattwnz
20183 posts

Uber Geek


  #2160388 13-Jan-2019 17:33
Send private message

Paul1977:

 

Thanks for the feedback guys.

 

I was in a lighting place today and asked the guy there, who said very much what everyone hear has - it wants that much clearance from flammable material (which would include a timber joist), possibly because they just haven't paid for the testing required to be able to say it is zero clearance.

 

So while the chances of it anything happening with the low temps coming of an LED are low, if it did happen there could be insurance implications etc if the clearance guidelines aren't followed.

 

I'm having a rethink of the design to try to make it work while still allowing these minimum clearances, and will give a sparkie a call in the morning.

 

 

 

 

I am going through this myself with new light fittings . Yes I think there could potentially be insurance implications if they are installed too close, as it then means they haven't been installed to the manufacturers guidelines..


sparkz25
750 posts

Ultimate Geek
Inactive user


  #2160394 13-Jan-2019 17:40
Send private message

gregmcc:

 

sparkz25:

 

If is was me I would need to have a look at the installation.

 

But It's all up to your sparky if he wants to install them, so it might pay to get him to have a look.

 

Im guessing these are leds? is so they would generate a lot less heat than a halogen which should never be installed to celing batten or within 100mm of it.

 

NZECP54 is what you need to read.

 

This has all the clearences and stuff that you need to know, but when we were doing installs and prewires and had no celings in we would put them where it looked best and with plenty of clearance from battens.

 

https://worksafe.govt.nz/dmsdocument/1583-new-zealand-electrical-code-of-practice-for-the-installation-of-recessed-luminaires-and-auxiliary-equipment-nzecp-54-2001

 

 

 

 

 

 

 

 

This ECP is 17 years old, it does not even mention IC rated light fittings and I suspect it has been superseded well and truly by AS/NZS3000:2017

 

 

looks like AS/NZS 3000/2018 is out now, just having a look through that and you are right it has superseded ECP54


Paul1977

5060 posts

Uber Geek


  #2160399 13-Jan-2019 17:50
Send private message

Thinking about... wouldn't the laths in the lath and plaster ceiling be classed as flammable the same as a timber joist?


mattwnz
20183 posts

Uber Geek


  #2160421 13-Jan-2019 18:33
Send private message

Paul1977:

 

Thinking about... wouldn't the laths in the lath and plaster ceiling be classed as flammable the same as a timber joist?

 

 

 

 

Possibly yes, and may depend on the thickness of the ceiling lining and whether the lathes are in relation to the heatsink. Although normally ceilings are just gib, and the heat sink would be positioned quite a bit above this. Lath and plaster is very old school, so it wouldn't be a typical install. So definitely something to consider. 


 1 | 2 | 3
View this topic in a long page with up to 500 replies per page Create new topic





News and reviews »

Gen Threat Report Reveals Rise in Crypto, Sextortion and Tech Support Scams
Posted 7-Aug-2025 13:09


Logitech G and McLaren Racing Sign New, Expanded Multi-Year Partnership
Posted 7-Aug-2025 13:00


A Third of New Zealanders Fall for Online Scams Says Trend Micro
Posted 7-Aug-2025 12:43


OPPO Releases Its Most Stylish and Compact Smartwatch Yet, the Watch X2 Mini.
Posted 7-Aug-2025 12:37


Epson Launches New High-End EH-LS9000B Home Theatre Laser Projector
Posted 7-Aug-2025 12:34


Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.