But at the same time the black plastic hole (air return?) is leaking when heating too, it stops when the heating stops.
How much the repair job would be? It looks like a easy swap job, diy possible?


![]() ![]() |
Aredwood: Since you say that the water stops dripping when the heating stops. This means that the valve itself is fine. When everything is working normally they will drip approx 1% of the hot water you use. (As the amount that drips depend on the amount of water that needs to be heated, which in turn depends on the amount of hot water you use.
But the drain pipe on the valve is blocked or not installed properly. That plastic fitting is just an air vent, which is doing it's job - allowing the valve to still do it's safety critical functions even though the drain pipe is blocked.
The drain pipe must be made of copper, Must only run downhill, Must not have any kind of valve or other restriction in it. And must discharge somewhere noticeable. (Yes there are other rules but those are the main ones)
Find the other end of the drain pipe and have a look there. Have seen them going into gardens and getting blocked due to the garden getting raised and the end now being underground. If you cant unblock the pipe yourself or otherwise can't figure out why the pipe is not draining - call a plumber.
![]() ![]() |