Topic # 227446 7-Jan-2018 16:46
Send private message quote this post

Please can anyone give advice on heat pumps, I live on the central plateau and my trusty old night store and wood burner are in a state of repair and being 25+ years old parts are not available, so I am looking at installing a heat pump but will keep the log burner in place in case of power cuts or failure of heat pump to do its job.

 

Size required varies from 8.2 Kw high wall mtg recommended by Mitsubishi to a general recommendation of 10-12 Kw.

 

Room size 10x5x2.72m. Ceilings insulated and say 30% of walls are insulated, large bay windows with thermo drapes.

 

We get a fair few frosts and a few mornings down to – 5deg C.

 

 

 

I was going for a Daiken but have been told that Mitsubishi are just as good and a bit cheaper, price is not the main concern I want performance and reliability and I do need a quite one.

 

 

 

Assuming a morning start of say 6:30 is it best to leave the heater on all night at say 10 deg C as opposed to leaving off over night and setting to come on at 6am at 20deg C.

 

 

 

Thank you.


Create new topic
1225 posts

Uber Geek
+1 received by user: 551


  Reply # 1931773 7-Jan-2018 16:52
One person supports this post
Send private message quote this post

Daikin all the way.

 

I put in a 6kw Panasonic last year and regret not grabbing the Daikin.


2473 posts

Uber Geek
+1 received by user: 556


  Reply # 1931800 7-Jan-2018 18:08
Send private message quote this post

i would go for the hypercore Mitsubishi with wifi, i have one and they do what they say they do and are also very quiet.  You are just wasting power if you leave them on all night if you have good instalation, i set mine to come on 40 minutes before i get up and the house is nice and warm


 
 
 
 


2124 posts

Uber Geek
+1 received by user: 702

Subscriber

  Reply # 1931801 7-Jan-2018 18:10
Send private message quote this post

Are you in the TLC lines company area? If so then getting a heatpump would probably increase your lines fees.


If so, consider putting the heatpump on ripple control, and use the fire while the load management is active.

Although if you have electric cooking. Change that to gas. As that would be a bigger reduction in peak demand fees, for only a small amount of gas usage. And you will still be able to cook during powercuts.





7216 posts

Uber Geek
+1 received by user: 2287

Subscriber

  Reply # 1931808 7-Jan-2018 19:16
Send private message quote this post

you cant set the heatpump to 10 degrees, most go down to 16-18 as a minimum. its likely cheaper to turn it off at night if the room is unused and turn it on about 30 mins before you get up or get home


13445 posts

Uber Geek
+1 received by user: 2273

Trusted
Subscriber

  Reply # 1931820 7-Jan-2018 20:09
One person supports this post
Send private message quote this post

If your house gets down to 10 degrees at night you should look at insulation first. A heat pump would hugely increase your bills.

 

Last year when my wife was home all day we left the heat pump on 5am - 10pm, getting up around 6am. The house felt quite a bit warmer than when we turned it on and off as needed. Even if no-one was here I'd consider keeping it turned on 18 degrees during the day in the depths of winter, then increasing to 21 / 22 just before we need it.

 

WiFi control from phone would be good, with a decent time that you can do multiple changes per day. My older Daikin works well. The Fujitsu Nocria I have is quite loud, I wouldn't get another. I use a small Broadlink device I got from ebay to control my older heat pumps from my phone.





AWS Certified Solution Architect Professional, Sysop Administrator Associate, and Developer Associate
TOGAF certified enterprise architect
Professional photographer


Mad Scientist
17727 posts

Uber Geek
+1 received by user: 2172

Trusted
Lifetime subscriber

  Reply # 1931844 7-Jan-2018 20:37
2 people support this post
Send private message quote this post

Daikin or Mitsubishi are good.

 

Always over spec than under spec, you will regret if it's not powerful enough.

 

And, cheaper than renovating the house.


3253 posts

Uber Geek
+1 received by user: 586

Trusted

  Reply # 1931877 7-Jan-2018 21:20
Send private message quote this post

my old house (about 150m2, 2.4metre walls) was all powered by a single 11.2kw system... 10kw for one room, seems over kill.


3776 posts

Uber Geek
+1 received by user: 1861

Lifetime subscriber

  Reply # 1931879 7-Jan-2018 21:34
Send private message quote this post

Batman:

 

Daikin or Mitsubishi are good.

 

Always over spec than under spec, you will regret if it's not powerful enough.

 

And, cheaper than renovating the house.

 

 

As above.

 

Always overspec.

 

Daiken & Mitsubishi are both excellent - I love the almost complete silence of two Mitsi heat pumps in our Wellington house.





Sideface


10277 posts

Uber Geek
+1 received by user: 3172

Trusted
Lifetime subscriber

  Reply # 1931881 7-Jan-2018 21:43
Send private message quote this post

Friends down south swear by Daikin claiming better efficiency when the outside temperatures get very low. We have Fujitsu (4) and they do ice up around 5 C and then have to defrost.

We run ours almost every day, cooling or heating, but not overnight in winter unless it's really really chilly.





2664 posts

Uber Geek
+1 received by user: 400


  Reply # 1931884 7-Jan-2018 22:04
Send private message quote this post

We put in a 6 Kw Fujitsu ABTG18LVTA floor console at the start of last winter. We are very happy with it.

 

We have cathedral ceilings and a lot of window area (floor to ceiling) and due to the catherdral ceilings the windows have no drapes at the top.  Downstairs is open plan with no way to stop the heat going upstairs though we can shut the door upstairs. So it's heating well over 50 sqr metres with minimal insulation and high ceilings.

 

Other than a couple of very cold foggy mornings it never had to stop to defrost and when it did it was for only 15 minutes or so. Prior to this year the inside temperature would go as low as 5 degrees over night as we were only using a oil column heater while we were up and about.

 

I'd really recommend a floor mount as I think a floor mounted heat pump is more effective for heating.





Sony Xperia X running Sailfish
Jolla C
Nokia N1
Dell Inspiron 14z i5


20554 posts

Uber Geek
+1 received by user: 3954

Trusted
Subscriber

  Reply # 1931892 7-Jan-2018 22:37
Send private message quote this post

Disagree about the overspecing of them. The inverters will go down to about 10% of the max output from what I have been told. This means when requirements are minimal like a 28 degree outside day in summer or about 16 in winter, that the min output is more than is needed and they will cycle off and on completely, with the noise that brings. I have to have the fan set to low on my bedroom one otherwise it ramps it down and up all the time when the needed output is minimal. Thats with a 3.5 or 3.7kw one in a 11m2 room





Richard rich.ms

1382 posts

Uber Geek
+1 received by user: 101

Subscriber

  Reply # 1931922 8-Jan-2018 07:13
Send private message quote this post

Given your location, you need somthing that will have an outdoor operate without a flinch in the winter i.e. run more than happy at -5 for hours. 


2664 posts

Uber Geek
+1 received by user: 400


  Reply # 1931926 8-Jan-2018 07:41
Send private message quote this post

richms:

 

Disagree about the overspecing of them. The inverters will go down to about 10% of the max output from what I have been told. This means when requirements are minimal like a 28 degree outside day in summer or about 16 in winter, that the min output is more than is needed and they will cycle off and on completely, with the noise that brings. I have to have the fan set to low on my bedroom one otherwise it ramps it down and up all the time when the needed output is minimal. Thats with a 3.5 or 3.7kw one in a 11m2 room

 

 

That's probably the case if it's really over sized. However it's still way better to be slightly over then be undersized and have the unit struggling all the time and needing constant defrosting. Because then you use a lot of energy and don't get much heat.





Sony Xperia X running Sailfish
Jolla C
Nokia N1
Dell Inspiron 14z i5


13445 posts

Uber Geek
+1 received by user: 2273

Trusted
Subscriber

  Reply # 1931931 8-Jan-2018 08:13
Send private message quote this post

reven:

 

my old house (about 150m2, 2.4metre walls) was all powered by a single 11.2kw system... 10kw for one room, seems over kill.

 

 

I have one Fujitsu Nocria around 10kw or a bit more heating approx 100 square meters of old but well insulated house. I wouldn't want any smaller. Once the house is up to heat it does spend a fair amount of time off now that we're fully insulated and double glazed.

 

Technofreak:

 

I'd really recommend a floor mount as I think a floor mounted heat pump is more effective for heating.

 

 

If you have space I think they're probably better, and quieter, and less ugly.





AWS Certified Solution Architect Professional, Sysop Administrator Associate, and Developer Associate
TOGAF certified enterprise architect
Professional photographer




45 posts

Geek
+1 received by user: 7


  Reply # 1932254 8-Jan-2018 14:59
Send private message quote this post

Thanks to all that responded you have provided a lot to think over and any more info is very welcome, Thanks.

 

@Aredwood   yes I am with TLC and with their new TOU system about to kick in you can guarantee it will be more expensive I emailed them and await an answer

 

 

 

@Vexxxboy I have heard about hypercore but not sure what it is and yes will go for wifi

 

 

 

@Reven   Point taken


Create new topic



Twitter »

Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

Less news in Facebook News Feed revamp
Posted 15-Jan-2018 13:15


Australian Government contract awarded to Datacom Connect
Posted 11-Jan-2018 08:37


Why New Zealand needs a chief technology officer
Posted 6-Jan-2018 13:59


Amazon release Silk Browser and Firefox for Fire TV
Posted 21-Dec-2017 13:42


New Chief Technology Officer role created
Posted 19-Dec-2017 22:18


All I want for Christmas is a new EV
Posted 19-Dec-2017 19:54


How clever is this: AI will create 2.3 million jobs by 2020
Posted 19-Dec-2017 19:52


NOW to deploy SD-WAN to regional councils
Posted 19-Dec-2017 19:46


Mobile market competition issues ComCom should watch
Posted 18-Dec-2017 10:52


New Zealand government to create digital advisory group
Posted 16-Dec-2017 08:47


Australia datum changes means whole country moving 1.8 metres north-east
Posted 16-Dec-2017 08:39


UAV Traffic Management Trial launching today in New Zealand
Posted 12-Dec-2017 16:06


UFB connections pass 460,000
Posted 11-Dec-2017 11:26


The Warehouse Group to adopt IBM Cloud to support digital transformation
Posted 11-Dec-2017 11:22


Dimension Data peeks into digital business 2018
Posted 11-Dec-2017 10:55



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.