I'm looking at fitting a new induction hob and trying to figure out what size cable will need to be run.  It's a tricky cable run and last time I retrofitted an induction hob, there were issues with the existing power supply.

 

The hobs I am looking at all have a rated load of 11kW. 

 

The existing hob is gas with electric ignition, so minimal existing power supply

 

It's about a 20m cable run from the switchboard.





Mike


View this topic in a long page with up to 500 replies per page Create new topic
 1 | 2 | 3
DarthKermit
5346 posts

Uber Geek

Trusted

  #2529332 27-Jul-2020 11:02
Send private message

Surely it's an electrician's job to figure out that.


 
 
 
 

Get easy to use, easy to install Norton antivirus protection against advanced online threats (affiliate link).
zenourn
255 posts

Ultimate Geek

Trusted
DR

  #2529363 27-Jul-2020 11:24
Send private message

Yes, this is a job for an electrician. However, is this 11 kW over a single phase or three phases? In a domestic situation 11 kW over a single phase to an appliance is getting up there. For an EV charger I've got 11 kw over 3 phases for a 10 m run using 2.5 mm^2 cable. 


Daynger
384 posts

Ultimate Geek


  #2529370 27-Jul-2020 11:34
Send private message

You need to check the spec for the cooktop as usually they wont need the full 11Kw (48A!!) supply as they will cycle or limit elements when multiple ones are on.

 

Most likely in the spec somewhere it will say it needs a 32A supply.

 

 




sittingduckz
675 posts

Ultimate Geek


  #2529379 27-Jul-2020 11:49
Send private message

What's the model number?

 

 

 

20m might push it to 10mm2? 





I'm not a complete idiot, I still have some parts missing.


billgates
4626 posts

Uber Geek

Trusted

  #2529396 27-Jul-2020 12:35
Send private message

Our sparky ran 2phase 6mm2 cable for our 11kW induction hob rated at 44amps in our new build. He ran 16mm2 cable for 2 phase connection for mains and submains from outside property.




Do whatever you want to do man.

  

Scott3
3340 posts

Uber Geek

Lifetime subscriber

  #2529403 27-Jul-2020 12:44
Send private message

Daynger:

 

You need to check the spec for the cooktop as usually they wont need the full 11Kw (48A!!) supply as they will cycle or limit elements when multiple ones are on.

 

Most likely in the spec somewhere it will say it needs a 32A supply.

 



Probably something like this:

https://www.fisherpaykel.com/nz/kitchen/cooking-appliances/cooktops/90cm-5-zone-touchslide-induction-cooktop1.CI905DTB3.html

 

Yes the 11.1KW / 48A requirement is after accounting for internal load limiters. The sum or the individual elements power ratings is way higher than 11.1kW, but the unit won't let them all be turned on full power at once to keep the electrical requirements reasonable.

 

Still I hope OP has a multi phase supply to their house. 48A is a lot for a single appliance if you only have a single phase supply and an 80A pole fuse...


andrewNZ
2487 posts

Uber Geek
Inactive user


  #2529410 27-Jul-2020 13:04
Send private message

Lots of factors to be considered, like actual device current rating, how many phases you have available, where does the cable run, what's around it, etc.
An electrician needs to have a look.

But to give you an idea.
11kw single phase is 48A
48A running 20m through house insulation needs 25mm² cable.
48A running 20m clipped to timber and no insulation needs 10mm²
48A running 10m clipped to timber and no insulation needs 6mm²

I'd also question your 20m measurement. Where did it come from. Often a run that looks like 20m can need 30m.

If you want to play with some numbers yourself, download gencalc on your phone.



Scott3
3340 posts

Uber Geek

Lifetime subscriber

  #2529486 27-Jul-2020 14:19
Send private message

As a general rule, most induction cook-tops that draw more than 16A have the ability to connect to multiple phases. (typically only apartment / motel style 30cm wide induction cook-tops have a power draw this low).

 

My induction cook-top (60cm, 32A max draw) has the ability to feed the left & right hand side off separate feeds, allowing for the load to be shared across different phases. (My house has only a single phase supply So I have the the (included) metal bridge between the two connection screws in place, and It is fed via a single 32A phase supply).

 

The 11.1kW F&P cooktop I used as an example has the ability to split the load across three phases. Generally best to share loads around between phases as much as possible (although each individual phase needs to be checked for capacity to do this).

 

 

 

It is quite likely that installing this appliance will require work on the switchboard, which is strictly prohibited without appropriate licences. Might as well get the sparky in for an initial visit to work out wire sizing and distribution across phases (if relevant).

 

 


Amosnz
559 posts

Ultimate Geek

Lifetime subscriber

  #2529488 27-Jul-2020 14:22
Send private message

When I was looking at what was needed for a Spa my sparky friend said he uses a calculator to work it out.  Either web: https://www.nexans.co.nz/eservice/CrossSectionCalculation.nx or app https://apps.apple.com/nz/app/gencalc/id725309423 or  https://play.google.com/store/apps/details?id=com.generalcable.gencalc&hl=en

 

 





Speedtest


gregmcc
2092 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #2529562 27-Jul-2020 15:03
Send private message

andrewNZ: Lots of factors to be considered, like actual device current rating, how many phases you have available, where does the cable run, what's around it, etc.
An electrician needs to have a look.

But to give you an idea.
11kw single phase is 48A
48A running 20m through house insulation needs 25mm² cable.
48A running 20m clipped to timber and no insulation needs 10mm²
48A running 10m clipped to timber and no insulation needs 6mm²

I'd also question your 20m measurement. Where did it come from. Often a run that looks like 20m can need 30m.

If you want to play with some numbers yourself, download gencalc on your phone.

 

 

 

While the above answers are correct there are some other factors to take in to account. Will your current mains be big enough to support the extra load of the oven?

 

There is a "Maximum Demand" factor you can apply to this.

 

Keep in mind in real life calculating the cable size some factors have to be taken in to account. For example although calculations can allow for no insulation, the reality is at some point in the cable run it will have to travel thru insulation and the worst case calculation has to be used.

 

best advice is get your electrician to do the calculations as that is the reason they have done an apprenticeship, Joe homeowner has no real idea on current calculations and maximum demand calculations and it can go very wrong very quickly, the end result if not done right will be a fire.

 

 


Tracer
343 posts

Ultimate Geek


  #2529747 27-Jul-2020 17:57
Send private message

Need to figure out what the actual maximum demand from the cooktop is. It's unlikely to need the full 11 kW, so you can factor in some diversity.

 

andrewNZ:
48A running 20m clipped to timber and no insulation needs 10mm²
48A running 10m clipped to timber and no insulation needs 6mm²

 

You must assume insulation will be installed in walls, ceilings, and underfloor in NZ when selecting and installing wiring systems. (See section 3.4.1 of AS/NZS 3000:2007 w/ Amendment 2).

 

-e- I'll just quote the passage, because it's not long:

 

 

In New Zealand only, wiring systems in domestic installations shall be installed on the assumption that thermal insulation in ceilings, walls and under floors, if not currently installed, will be installed in the future. 

 


snnet
1377 posts

Uber Geek


  #2529764 27-Jul-2020 18:55
Send private message

As an earlier post suggests, there is more at play than just full load current. In our wiring rules we have tables for calculating maximum demand. Leave it to the professionals.


Daynger
384 posts

Ultimate Geek


  #2529773 27-Jul-2020 19:31
Send private message

Scott3:

 

Daynger:

 

You need to check the spec for the cooktop as usually they wont need the full 11Kw (48A!!) supply as they will cycle or limit elements when multiple ones are on.

 

Most likely in the spec somewhere it will say it needs a 32A supply.

 



Probably something like this:

https://www.fisherpaykel.com/nz/kitchen/cooking-appliances/cooktops/90cm-5-zone-touchslide-induction-cooktop1.CI905DTB3.html

 

Yes the 11.1KW / 48A requirement is after accounting for internal load limiters. The sum or the individual elements power ratings is way higher than 11.1kW, but the unit won't let them all be turned on full power at once to keep the electrical requirements reasonable.

 

Still I hope OP has a multi phase supply to their house. 48A is a lot for a single appliance if you only have a single phase supply and an 80A pole fuse...

 

 

 

 

Its even worse when you account for most pole fuses in NZ are 63A.

 

I would suggest to OP if it is that 48A unit and you only have a single phase supply that you pick another hob.


MikeAqua

7627 posts

Uber Geek


  #2530039 28-Jul-2020 12:50
Send private message

Actually I made an error, the unit I'm looking at has a rated load of 7.4kW, which should be <32A.

 

https://www.bosch-home.co.nz/productlist/cooking-baking/cooktops/induction-cooktops/PXY875KW1E#/Tabs=section-technicalspecs/Togglebox=-1508568551/Togglebox=1149550223/Togglebox=285469437/ 

 

 

 

Basically I'm trying to figure out of this is at all feasible before I take a day off work and get an electrician on site.

 

If I know the cable rating I need I can get a rough idea whether it's feasible to run.  If I think yes or maybe, I'll engage a professional.  If it looks like a no, I'll get a new gas hob instead.

 

 

 

 





Mike


andrewNZ
2487 posts

Uber Geek
Inactive user


  #2530045 28-Jul-2020 13:01
Send private message

Depends on the real length and many other factors as we've already stated.

BUT, making some big assumptions you probably need 6mm².


 1 | 2 | 3
View this topic in a long page with up to 500 replies per page Create new topic





News and reviews »

New Air Traffic Management Platform and Resilient Buildings a Milestone for Airways
Posted 6-Dec-2023 05:00


Logitech G Launches New Flagship Console Wireless Gaming Headset Astro A50 X
Posted 5-Dec-2023 21:00


NordVPN Helps Users Protect Themselves From Vulnerable Apps
Posted 5-Dec-2023 14:27


First-of-its-Kind Flight Trials Integrate Uncrewed Aircraft Into Controlled Airspace
Posted 5-Dec-2023 13:59


Prodigi Technology Services Announces Strategic Acquisition of Conex
Posted 4-Dec-2023 09:33


Samsung Announces Galaxy AI
Posted 28-Nov-2023 14:48


Epson Launches EH-LS650 Ultra Short Throw Smart Streaming Laser Projector
Posted 28-Nov-2023 14:38


Fitbit Charge 6 Review
Posted 27-Nov-2023 16:21


Cisco Launches New Research Highlighting Gap in Preparedness for AI
Posted 23-Nov-2023 15:50


Seagate Takes Block Storage System to New Heights Reaching 2.5 PB
Posted 23-Nov-2023 15:45


Seagate Nytro 4350 NVMe SSD Delivers Consistent Application Performance and High QoS to Data Centers
Posted 23-Nov-2023 15:38


Amazon Fire TV Stick 4k Max (2nd Generation) Review
Posted 14-Nov-2023 16:17


Over half of New Zealand adults surveyed concerned about AI shopping scams
Posted 3-Nov-2023 10:42


Super Mario Bros. Wonder Launches on Nintendo Switch
Posted 24-Oct-2023 10:56


Google Releases Nest WiFi Pro in New Zealand
Posted 24-Oct-2023 10:18









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.







Lenovo